[TRNSYS-users] Ambient temperature
David BRADLEY
d.bradley at tess-inc.com
Tue Dec 23 11:36:30 PST 2014
Mihai,
Type109 was found to have a number of issues and so was rewritten
with the release of Trnsys17. If you are using a later version of
Trnsys16, you might may have access to either Type933 or Type15 and I
would highly recommend that you change to using one of these in place of
Type109 since you are reading from a *.tm2 file. Type933 and Type15 are
the same Type but were released at different times.
Kind regards,
David
On 12/19/2014 04:49, Mihai T. wrote:
> Hello!
>
> I made a simulation in Trnsys to evaluate the heating demand for a
> office building. Now I need to compare the trnsys results with some
> results obtained using another method.
>
> Please help me to find how TYPE 109 calculates „Ambient temperature”
> and how the correspondence with the solar radiation values at the
> correct time moments is ensured. I am asking you this because the
> ambient temperature used in simulation is not the same with ambient
> temperature from the weather data file (dry bulb temperature in the
> file '...\Trnsys16\Weather\Meteonorm\Europe\RO-Bucuresti-154200.tm2').
> I cannot find this information in Trnsys Manual.
>
> The problem found is that, if a shift is made (with 1/2h) to the dry
> bulb temperature (by averaging two values at 2 consecutive time
> moments in order to place the average values in the middle of the hour
> and to match the moment considered for solar calculations), the result
> is a mismatch between ambient temperature and solar radiation values
> (with 1 h difference).
> I have performed the solar calculation using Perez model and I have
> found the same values as the ones calculated in trnsys, but with 1
> hour shift (to have a correct match between temperatures and radiation
> the latter should be moved forward with 1 hour).
>
> Please advise and give me some explanations on the calculation
> procedure used in trnsys.
>
> Thank you for your support,
> Mihai Toderașc
>
>
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20141223/072e8314/attachment-0004.htm>
More information about the TRNSYS-users
mailing list