Aisha,
It can be done but it requires some manual modifications of the
TRNSYS input file (*.dck) outside of the Studio. Below are the basic
steps that you need to follow:
1. first, you need to make a *.b17 file for each one of the cases that
you want to run in your parametric study. Save each one with a different
name.
2. Open the *.dck in TRNEdit and find the ASSIGN statement that
corresponds to the *.b17 file. It should look something like the following:
ASSIGN "building\DHS_Baseline(v2).b17" 31
3. Following the syntax given, make an ASSIGN statement for each of the
cases that you want to run. Give a different number to each one but
search through the *.dck and make sure that the numbers that you choose
are not used in another ASSIGN statement. For example:
ASSIGN "building\DHS_Baseline(v2)_case1.b17" 31
ASSIGN "building\DHS_Baseline(v2)_case2.b17" 32
ASSIGN "building\DHS_Baseline(v2)_case3.b17" 33
ASSIGN "building\DHS_Baseline(v2)_case4.b17" 34
4. Find the section that defines Type56. It might look something like:
UNIT 5 TYPE 56 DHS ICE
*$UNIT_NAME DHS ICE
*$MODEL .\Loads and Structures\Multi-Zone Building\Type56.tmf
*$POSITION 479 301
*$LAYER Main #
*$#
PARAMETERS 3
31 ! 1 Logical unit for building description file (.bui)
0 ! 2 Star network calculation switch
5. you need to add a CONSTANTS statement before the definition of Type56
so that the logical unit number containing the building description file
is given by a variable name instead of by a numerical value. You will
have something like the following (changes are noted in red):
CONSTANTS 1
LU_56 = 31
UNIT 5 TYPE 56 DHS ICE
*$UNIT_NAME DHS ICE
*$MODEL .\Loads and Structures\Multi-Zone Building\Type56.tmf
*$POSITION 479 301
*$LAYER Main #
*$#
PARAMETERS 3
LU_56 ! 1 Logical unit for building description file (.bui)
0 ! 2 Star network calculation switch
6. lastly, create a parametric table in TRNEdit that has as many runs a
you have cases and which redefines the value of the constant LU_56 for
each run according to the numbers that you chose for your ASSIGN
statements in step 3.
Kind regards,
David
On 11/28/2014 08:42, Ayesha Mohammed Al Qubaisi wrote:
>
> Dear all,
>
> I would like to do a parametric study in which I can change the wall
> materials defined in TRNbuild and see the change on the building
> loads.( Cooling loads)
>
> can someone let me know how to do this easily ?
>
> For the meantime, I do this manually, by changing it in TRNbuild every
> time.
>
> Please let me know ?
>
> Thank you for your time,
>
> Aisha
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20141201/5068a1ca/attachment-0001.htm>
More information about the TRNSYS-users
mailing list