[TRNSYS-users] Window data generated by Window software lead to Trnsys Warning

Antoine Gautier antoine.gautier at solamen.fr
Tue Apr 15 02:41:14 PDT 2014


Dear users

 

I get the following warnings using window data generated by Window software
6.3. I do not get any error during window data generation. Do you know what
I should correct? (I included the detailed window data hereunder.)

Thanks a lot for your help.

 

*** Notice at time        :         0.000000

    Generated by Unit     :    27

    Generated by Type     :    56

    Message               : winlib reader: Incorrect visual transmission
values encountered in Window-ID        116. for an angle of    0 °.
Incorrect value    0.603 will be limited to the possible physically maximum
0.561! Please check your window data!

 

*** Notice at time        :         0.000000

    Generated by Unit     :    27

    Generated by Type     :    56

    Message               :  winlib reader: incorrect selectivity of
visual+solar transmission caused a negative value for nonvisual Transmission
Tra_ang_nonvis =   -0.026 for Window-ID        116 at an angle of    0 °
Tra_ang_nonvis is set to 0 for this angle

 

 

Window v6.3.36.0  DOE-2 Data File : Multi Band Calculation

Unit System : SI

Name        : CofelyAxima WINDOW LIB

Desc        : VitragePorteDeRetz

Window ID   : 116

Tilt        : 90.0

Glazings    : 2

Frame       :  1 Al w/break            5.680

Spacer      :  1 Class1                2.330  -0.010   0.138

Total Height: 2400.0 mm

Total Width : 3000.0 mm

Glass Height: 2285.7 mm

Glass Width : 2885.7 mm

Mullion     : None

Gap        Thick    Cond  dCond    Vis   dVis   Dens   dDens     Pr     dPr

1 Air (10%) 16.0 0.01706  5.392  2.066  6.311  1.733 -0.0061  0.676 -0.0001

2              0       0      0      0      0      0       0      0       0

3              0       0      0      0      0      0       0      0       0

4              0       0      0      0      0      0       0      0       0

5              0       0      0      0      0      0       0      0       0

Angle     0    10    20    30    40    50    60    70    80    90 Hemis

Tsol  0.216 0.218 0.215 0.211 0.205 0.194 0.171 0.125 0.059 0.000 0.181

Abs1  0.357 0.361 0.365 0.367 0.365 0.363 0.362 0.347 0.265 0.001 0.352

Abs2  0.007 0.008 0.008 0.008 0.008 0.008 0.008 0.007 0.005 0.000 0.007

Abs3      0     0     0     0     0     0     0     0     0     0     0

Abs4      0     0     0     0     0     0     0     0     0     0     0

Abs5      0     0     0     0     0     0     0     0     0     0     0

Abs6      0     0     0     0     0     0     0     0     0     0     0

Rfsol 0.419 0.414 0.413 0.415 0.422 0.435 0.460 0.521 0.671 0.999 0.449

Rbsol 0.491 0.487 0.484 0.482 0.482 0.487 0.506 0.562 0.688 1.000 0.504

Tvis  0.603 0.607 0.598 0.588 0.573 0.543 0.476 0.348 0.164 0.000 0.505

Rfvis 0.140 0.133 0.130 0.133 0.145 0.166 0.208 0.306 0.531 0.999 0.194

Rbvis 0.181 0.176 0.174 0.178 0.191 0.218 0.276 0.408 0.659 1.000 0.254

SHGC  0.243 0.245 0.242 0.238 0.233 0.222 0.198 0.151 0.078 0.000 0.207

SC: 0.28

Layer ID#        11403    11004        0        0        0        0

Tir              0.000    0.000        0        0        0        0

Emis F           0.837    0.837        0        0        0        0

Emis B           0.013    0.837        0        0        0        0

Thickness(mm)      6.0      4.0        0        0        0        0

Cond(W/m2-K     ) 166.7    250.0        0        0        0        0

Spectral File C-L XTREME 6 PLANILUX 4mm         None         None
None         None

Overall and Center of Glass Ig U-values (W/m2-K)

Outdoor Temperature                 -17.8 C      15.6 C      26.7 C
37.8 C

Solar      WdSpd  hcout hrout  hin

(W/m2)     (m/s)     (W/m2-K)

0        0.00   4.00  3.28  6.56  1.15 1.15  0.89 0.89  0.91 0.91  0.96 0.96

0        6.71  30.84  3.19  6.61  1.38 1.38  0.97 0.97  0.98 0.98  1.05 1.05

783        0.00   4.00  3.89  5.81  1.15 1.15  0.89 0.89  0.91 0.91  0.96
0.96

783        6.71  30.84  3.34  6.47  1.38 1.38  0.97 0.97  0.98 0.98  1.05
1.05

 

 

--

Antoine Gautier

Solamen

+33 6 58 24 02 60