[TRNSYS-users] Two boreholes and one heat pump installation
David BRADLEY
d.bradley at tess-inc.com
Fri Apr 11 14:26:41 PDT 2014
Matthieu,
You are correct that you can have only one instance of Type557 in a
project. We have a Type1557 that I can send you; it is simply a copy of
Type557 but renumbered. This will allow you to define two bore "fields"
but keep in mind that there will be no thermal interaction between the
two bores apart from the impact of the fluid passing through the pipes.
In other words the bores won't know of each others' existence. Please
simply send me the contents of your user17.id file (please don't copy
the whole list!) and I'll get you the additional files needed.
As to your other question; the data file is not specific to one or
another heatpump. It is quite generic and can be used to model the
performance of any number of heat pumps and of heat pump sizes. If you
have a specific heat pump in mind then I would recommend that you go the
manufacturer's website and look for the performance data specific to
that machine. Once you normalize its data you will probably find that
the data file looks quite similar to the generic file.
Kind regards,
David
On 4/9/2014 09:08, Matthieu Saint-Ellier (215419) wrote:
> Dear TRNSYS users and support team,
>
> I am dealing with a project containing a water-water heat pump and two
> U-tubes boreholes (Vertical ground heat exchangers).
>
> The objective of this project is to extract energy from one of the
> borehole and try to store it in the other one thanks to the heat pump
> in order to use this energy in cold season for instance.
>
> I would like to simulate this installation in an easy way on TRNSYS
> software.
>
> In the first place, my problem is that on TRNSYS you can only have one
> borehole (Vertical ground heat exchanger) per project. However, in my
> model I would need two of these.
> Therefore, I would like to know if there is any way to solve this
> problem or otherwise, which components of the TRNSYS library could be
> used to simulate the storage of energy in a borehole.
>
> In the second place, the refrigerant of the heat pump I use is the
> 407C. But is seems that the attached file
> *WWHP_Heating-Normalized.dat* located in /.\Tess
> Models\SampleCatalogData\Water-to-WaterHeatPump\Normalized/ only
> contains datas about the R134a refrigerant. I woud like to know how we
> can deal with other refrigerant.
>
> Thank you very much.
>
> Regards.
>
>
> *--
>
> Matthieu SAINT-ELLIER*
> 00 33 6 37 97 00 91
> VIA University College
> Horsens
> Denmark
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20140411/a0c0d8e7/attachment-0004.htm>
More information about the TRNSYS-users
mailing list