[TRNSYS-users] Heat exchnager problem heat transfer

David BRADLEY d.bradley at tess-inc.com
Thu Apr 3 13:57:54 PDT 2014


Barto,
   I would recommend that you approach this by using an online plotter 
to debug the simulation. Plot the temperature and flow rate of the 
liquid leaving each of the devices around your flow loops. You can also 
plot the output signal from your controller. I think you'll probably 
find some kind of a mismatch (likely in the flow rates). A couple of 
hints: make sure that you have some piping in your collector / pump / 
heat exchanger loop and that the total volume of the pipes is greater 
than the amount of liquid that your pump can transfer in one time step. 
This will probably mean using a pretty short time step.
Regards,
  David


On 4/3/2014 05:00, Barto Pene wrote:
> Hi all,
>
> I modeling solar collector system with storage tank used in 
> pre-heating the air (with heat exchanger water-air).
> As a storage tank I'm using Type 60c and do the standard connections 
> between circ.pump, controller.... the solar collector I connect with 
> the heat exchanger (inside the tank). I insert another circulating 
> pump connecting it to the flow and temperature at Inlet 1 of the tank 
> and Then the flow and temperature of Outlet 1(Type 60C) I connect  to 
> the source inlet of the heat-exchanger (Type 5 or Type 650...)  on the 
> other load side are defined the necessary parameters for air.....
> But in the simulation the outlet temperature 1 from the storage tank 
> and the source outlet temp. from the heat exchanger are the same i.e. 
> like there is no heat exchange (also the same happens if I connect 
> with the aux.heater Type 6 there is also no temp.increase).
> What am I doing wrong should I change the storage tank or...?
>
> Regards
> Barto
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users

-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20140403/3d86a63d/attachment-0004.htm>


More information about the TRNSYS-users mailing list