David BRADLEY
d.bradley at tess-inc.com
Mon Apr 7 10:37:04 PDT 2014
Dev,
Adding thermal capacitance to the model itself would involve changing
the source code and asking for some additional parameters so that you
would be able to solve the first order differential equation that
describes the behavior. You'd need a Fortran compiler in order to
modify, recompile, and relink the code into a modified component. You
would also need to change the proforma.
Another method that you could use to accomplish something like the
same effect without modifying the source code would be to put a tank
model (Type534 ideally) either directly upstream or directly downstream
of the boiler. This would at least account for the thermal capacitance
and standby losses of the liquid volume associated with the boiler.
Best,
David
On 4/7/2014 01:22, Sharma Dev wrote:
>
> Dear All,
>
> Could anyone tell me how to include a thermal capacitance into the
> boiler Type 751, please?
>
> Dev Sharma
>
> Institute for Renewable Energy
>
> *EURAC*research
>
> Institute for Renewable Energy
> Via Luis-Zuegg 11, I-39100 Bolzano
>
> t +39 0471 055 600
>
> f +39 0471 055 699
>
> _dev.sharma at eurac.edu_
>
> _www.eurac.edu <http://www.eurac.edu/>_
>
> *EURAC*research
>
> Legal Seat
>
> Viale Druso 1, I-39100 Bolzano
>
>
> This transmission is intended only for the use of the addressee and
> may contain confidential or legally privileged information.
> If you receive this transmission by error, please notify the author
> immediately by mail and delete all copies of this transmission and any
> attachments.
> Any use or dissemination of this communication is strictly prohibited
> by the "Privacy-Code", D.Lgs. 196/2003 and may lead to penal
> prosecution and liability for damages.
>
> PThink before you print
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20140407/76b18eb1/attachment-0001.htm>
More information about the TRNSYS-users
mailing list