[TRNSYS-users] Type 1716: ROTARY DESICANT DEHUMIDIFIER - Maximum air flow rate?
David BRADLEY
d.bradley at tess-inc.com
Mon Sep 16 14:24:41 PDT 2013
Marcus,
Make sure that you are using a short timestep (1-5 minutes) and that
there is enough thermal capacitance in your flow loops. It may be that
10000 kg/h of air flowing through the device in the course of one time
step is causing the system to be unstable. There was a recent post on
this forum concerning a cooling tower connected to an absorption chiller
that turned out to be exactly the same problem; far too much energy
transferred in a system with far too little capacitance for the time
step selected. The time step has to be shorter than the time constant of
your system.
Kind regards,
David
On 9/15/2013 08:36, Marcus wrote:
> I am running type 1716. When I run with 1000 kg/hr flow, it simulates
> fine. When I increase to 10000, it causes psychometric SAT error at
> -273K.
>
> So far, I will use the wheel at 1/10 the flow, and then multiply after
> the wheel to get back to our design flow, just wondering if this is a
> known bug or I suppose the model isn't valid at such a flow rate?
>
> Cheers,
> Marcus
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20130916/c55ec93c/attachment-0004.htm>
More information about the TRNSYS-users
mailing list