Joshua,
Pumps typically set the flow rate for a loop based on their rated
flow rate and the value of the input control signal. There are some pump
models that will allow you to set the control signal to a value greater
than 1 and therefore to exceed the pump's rated flow rate. I would
recommend that you break your flow loop by removing one of the
connections (the one that returns to the pump would be best). Then use
an online plotter to look at the temperature and flow rate coming out of
each component in the loop. Verify that you do not have any incorrect
connections. Once you are convinced that there are no connection
problems, reconnect the loop but disconnect whatever is connected to
your pump's control signal. Force the control signal to be a known value
either by setting a constant input value or by setting an equation. I
think these tests will probably lead you to the problem.
Kind regards,
David
On 9/27/2013 09:47, Joshua Chia wrote:
> Hi
>
> I'm trying to design a closed cycle hot water system for use with a
> Heat Exchanger with a Solar Collector, pump and tank. I want to be
> able to set the mass flow rate of the system but it seems that even
> though I've set the maximum flow rate in the pump, the actual flow
> rate is way higher than that. I'm guessing it is due to the tank. Can
> anyone help me out on what to do with the tank? I only want a simple
> tank with 1 inlet and 1 outlet and the mass flow rate to be the one i
> determine it to be.
>
> Many Thanks
>
> --
> Regards
> Joshua
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20130927/7d59f65c/attachment-0001.htm>
More information about the TRNSYS-users
mailing list