[TRNSYS-users] problem of sky temperatures
Marion Hiller
Hiller at Transsolar.com
Thu Sep 19 01:30:32 PDT 2013
Pauline,
the view factor entered in TRNbuild is used for longwave radiation exchange of external surfaces.
As stated the value is used as a weighting factor between ground (Input 4) and sky temperature (Input3).
(See also Page 155 of 05-MultizoneBuilding.pdf)
If you have set both inputs to the same value a changing value of Fsky doesn't have an impact.
For diffuse radiation calculation the slope of the surface is used. In addition, the shading mask includes
a sunlit fraction for isotropic diffuse radiation.
Marion
Dipl.-Ing. Marion Hiller
Transsolar Energietechnik GmbH
Curiestraße 2
70563 Stuttgart
Telefon: +49 711 67976-0
http://www.trnsys.de<http://www.trnsys.de/>
Transsolar: KlimaEngineering- Technologien für energieeffizientes Bauen und Nutzerkomfort in Gebäuden
Stuttgart - München - New York - Paris
Geschäftsführer :Diplom-Ingenieur Matthias Schuler, Diplom-Ingenieur Thomas Auer, Diplom-Physiker Stefan Holst, Diplom-Betriebswirt Dieter Schnelle
Eingetragen beim Amtsgericht Stuttgart HRB 23347,
Steuernummer: 99073/00911,USt-IdNr.: DE 152272639
________________________________
Von: trnsys-users-bounces at cae.wisc.edu [mailto:trnsys-users-bounces at cae.wisc.edu] Im Auftrag von Pauline GELIN
Gesendet: Donnerstag, 19. September 2013 09:33
An: David BRADLEY
Cc: trnsys-users (trnsys-users at cae.wisc.edu)
Betreff: Re: [TRNSYS-users] problem of sky temperatures
Thank you for your answer. Indeed, I read these differences in the manual but I don't know for which case we need to use one or other of these sky temperatures definition.
In fact, I have another question about the effects of the value view factor given for walls and windows.
According to TRNBUILD manual (page 72), the view factor must impact diffuse and long wave radiation as well as convective heat transfer coefficients, so it is especially important for windows.
When I wanted to check these impacts using the IDSHAD outputs (total diffuse radiation on outside of external surface) with differents values of view factors (equal to 0 or 0.5 or 1) for walls and windows, I saw no difference in the results.
Could you explain to me these results ?Should I use another outputs to check these impacts? Am I wrong or right ?Is my understanding of the view factor false?
Thanks a lot in advance for your answers.
Best Regards,
Pauline GELIN
Ingénieur Conception environnementale
[cid:image004.jpg at 01CE062A.F4C2C000]
[cid:image006.jpg at 01CE062A.F4C2C000]
10 avenue des canuts
69120 VAULX EN VELIN
T : 04.37.45.33.33
Ligne directe : 04.37.45.33.47
www.katene.coop
www.quadriplus-groupe.com<http://www.quadriplus-groupe.com>
www.woopa.coop<http://www.woopa.coop>
De : David BRADLEY [mailto:d.bradley at tess-inc.com]
Envoyé : mercredi 18 septembre 2013 19:06
À : Pauline GELIN
Cc : trnsys-users (trnsys-users at cae.wisc.edu)
Objet : Re: problem of sky temperatures
Pauline,
Type69 and Type15 use different algorithms for computing sky temperature. The algorithms are discussed in the 04 Mathematical Reference manual.
Kind regards,
David
On 9/18/2013 08:40, Pauline GELIN wrote:
Hello,
sorry to ask again the same question but I can't understand why the values of sky temperature from weather component type 15 and from component 69 (with inputs from the same type 15) are different.
Anyone could help me to understand?
Hanks a lot for your answers.
Best Regards,
Pauline GELIN
Ingénieur Conception environnementale
[cid:image004.jpg at 01CE062A.F4C2C000]
[cid:image006.jpg at 01CE062A.F4C2C000]
10 avenue des canuts
69120 VAULX EN VELIN
T : 04.37.45.33.33
Ligne directe : 04.37.45.33.47
www.katene.coop
www.quadriplus-groupe.com<http://www.quadriplus-groupe.com>
www.woopa.coop<http://www.woopa.coop>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20130919/0a84d424/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1718 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20130919/0a84d424/attachment-0002.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1058 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20130919/0a84d424/attachment-0003.jpg>
More information about the TRNSYS-users
mailing list