[TRNSYS-users] Components order

David BRADLEY d.bradley at tess-inc.com
Fri Nov 15 12:52:26 PST 2013


Alessandro,
   Yes, the component order can have an impact on the simulation's 
convergence although it is rare in my experience. The TRNSYS kernel 
calls the components in the order in which they appear in the input 
file. The kernel also determines that convergence has not been reached 
after 30 iterations in a timestep (although you can change the 
30-iteration limit if you wish). If you have components in an illogical 
order, it may take the system more iterations to solve than if you have 
the components in a logical order. If you have got a complex system 
anyway (where multiple iterations are needed in order to solve) then an 
non-ideal component order can push you over the iteration limit.
   I try to adjust the component order so that the components appear in 
"flow order" - in other words so that the components are called in the 
same order in which liquid flows through them. Of course there are often 
loops so you have to decide a component that will be first in the list. 
Since pumps set the flow for all downstream components, they are a good 
choice.
Kind regards,
  David


On 11/15/2013 06:44, Bellini Alessandro wrote:
>
> Dear TRNSYS Users,
>
> I have some convergence problems running a Complex Solar Thermal 
> System (30 active components) when I made parametrical analysis.
>
> The model stop at certain time of simulation without giving error in 
> the .LST file and "freezing the screen".
>
> I have enough thermal capacity (pipes and storages) in every circuit 
> so I try to solve the problem changing the "components order" in the 
> "Global Info" and for some cases this solution works well.
>
> Have anybody found the same problem?
>
> I would like to know if there are rules to follow in the "components 
> order" definition or where I can find some information about it?
>
> Thanks for the support
>
> Regards
>
> Alessandro Bellini
>
> Institute for Renewable Energy
>
> *EURAC*research
>
> Institute for Renewable Energy
> Via Luis-Zuegg 11, I-39100 Bolzano
>
> t +39 0471 055 647
>
> f +39 0471 055 699
>
> alessandro.bellini at eurac.edu <mailto:alessandro.bellini at eurac.edu>
>
> _www.eurac.edu <http://www.eurac.edu/>_
>
> *EURAC*research
>
> Legal Seat
>
> Viale Druso 1, I-39100 Bolzano
>
>
> This transmission is intended only for the use of the addressee and 
> may contain confidential or legally privileged information.
> If you receive this transmission by error, please notify the author 
> immediately by mail and delete all copies of this transmission and any 
> attachments.
> Any use or dissemination of this communication is strictly prohibited 
> by the "Privacy-Code", D.Lgs. 196/2003 and may lead to penal 
> prosecution and liability for damages.
>
> PThink before you print
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users

-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20131115/3ba2a82c/attachment-0004.htm>


More information about the TRNSYS-users mailing list