[TRNSYS-users] Absorption Chiller - behavior - URGENT

dev sharma devsharmami at gmail.com
Thu May 2 01:42:27 PDT 2013


Hej All,

I am trying to model a solar based absorption cycle.

The experimental data with me, has following observations:
1. If I change just the hot water flowrate (reduced to half), the
capacity of the chiller reduces considerably (approx by 40%).
In model: Instead of reduction in capacity, the temperature drop of
hot water increases.
2. If I change just the hot water inlet temperature (by over 10 DegC
i.e 92-80), the capacity drop is considerable again( approx 60%)
In model: Instead of reduction in capacity, the temperature drop of
hot water is in w different range that's all. (80-70 DegC).

I have changed the data file for type 107 in terms of operating
temperature i.e from initial 108-116DegC to 70-95DegC.

I am attaching the modified data file.

Can someone please help me to modify this data file to suit the above
mentioned trends?

Thanks
Dev Sharma

-- 
Dev Sharma
Erasmus Mundus Masters in Sustainable Energy
KTH, Stockholm & UPC, Barcelona
Mobile: +34635104882 (Spain)
-------------- next part --------------
0	0.1	0.2	0.3	0.4	0.5	0.6	0.7	0.8	0.9	1	!Fraction	of	Design	Load
5.556	6.111	6.667	7.222	7.778	8.889	10	!Chilled	Water	Setpoint	(C)				
26.667	29.444	32.222	!Entering	Cooling	Water	Temperature	(C)							
70	76.25	82.5	88.75	95	!Inlet	Hot	Water	Temperature	(C)	Load	CHW	Set	ECWT	IHWT
0.9878	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	5.556	26.667	70		
1.0367	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	5.556	26.667	76.25		
1.0837	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	5.556	26.667	82.5		
1.1041	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	5.556	26.667	88.75		
1.1265	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	5.556	26.667	95		
0.8612	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	5.556	29.444	70		
0.9102	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	5.556	29.444	76.25		
0.9571	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	5.556	29.444	82.5		
0.9796	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	5.556	29.444	88.75		
1	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	5.556	29.444	95		
0.7347	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	5.556	32.222	70		
0.7857	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	5.556	32.222	76.25		
0.8327	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	5.556	32.222	82.5		
0.8531	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	5.556	32.222	88.75		
0.8735	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	5.556	32.222	95		
1.0102	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	6.111	26.667	70		
1.0592	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	6.111	26.667	76.25		
1.1061	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	6.111	26.667	82.5		
1.1286	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	6.111	26.667	88.75		
1.149	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	6.111	26.667	95		
0.8837	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	6.111	29.444	70		
0.9327	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	6.111	29.444	76.25		
0.9776	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	6.111	29.444	82.5		
1	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	6.111	29.444	88.75		
1.0224	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	6.111	29.444	95		
0.7571	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	6.111	32.222	70		
0.8061	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	6.111	32.222	76.25		
0.8531	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	6.111	32.222	82.5		
0.8735	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	6.111	32.222	88.75		
0.8959	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	6.111	32.222	95		
1.0306	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	6.667	26.667	70		
1.0816	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	6.667	26.667	76.25		
1.1286	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	6.667	26.667	82.5		
1.151	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	6.667	26.667	88.75		
1.1714	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	6.667	26.667	95		
0.9041	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	6.667	29.444	70		
0.9531	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	6.667	29.444	76.25		
1	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	6.667	29.444	82.5		
1.0224	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	6.667	29.444	88.75		
1.0449	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	6.667	29.444	95		
0.7776	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	6.667	32.222	70		
0.8265	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	6.667	32.222	76.25		
0.8735	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	6.667	32.222	82.5		
0.8959	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	6.667	32.222	88.75		
0.9163	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	6.667	32.222	95		
1.0531	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	7.222	26.667	70		
1.1041	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	7.222	26.667	76.25		
1.151	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	7.222	26.667	82.5		
1.1735	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	7.222	26.667	88.75		
1.1959	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	7.222	26.667	95		
0.9245	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	7.222	29.444	70		
0.9755	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	7.222	29.444	76.25		
1.0224	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	7.222	29.444	82.5		
1.0449	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	7.222	29.444	88.75		
1.0673	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	7.222	29.444	95		
0.798	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	7.222	32.222	70		
0.8469	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	7.222	32.222	76.25		
0.8939	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	7.222	32.222	82.5		
0.9163	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	7.222	32.222	88.75		
0.9388	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	7.222	32.222	95		
1.0755	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	7.778	26.667	70		
1.1265	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	7.778	26.667	76.25		
1.1755	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	7.778	26.667	82.5		
1.198	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	7.778	26.667	88.75		
1.2184	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	7.778	26.667	95		
0.9469	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	7.778	29.444	70		
0.998	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	7.778	29.444	76.25		
1.0449	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	7.778	29.444	82.5		
1.0673	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	7.778	29.444	88.75		
1.0898	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	7.778	29.444	95		
0.8184	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	7.778	32.222	70		
0.8694	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	7.778	32.222	76.25		
0.9163	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	7.778	32.222	82.5		
0.9388	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	7.778	32.222	88.75		
0.9592	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	7.778	32.222	95		
1.1204	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	8.889	26.667	70		
1.1735	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	8.889	26.667	76.25		
1.2204	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	8.889	26.667	82.5		
1.2449	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	8.889	26.667	88.75		
1.2673	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	8.889	26.667	95		
0.9898	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	8.889	29.444	70		
1.0408	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	8.889	29.444	76.25		
1.0898	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	8.889	29.444	82.5		
1.1122	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	8.889	29.444	88.75		
1.1347	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	8.889	29.444	95		
0.8592	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	8.889	32.222	70		
0.9102	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	8.889	32.222	76.25		
0.9592	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	8.889	32.222	82.5		
0.9816	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	8.889	32.222	88.75		
1.0041	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	8.889	32.222	95		
1.1673	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	10	26.667	70		
1.2204	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	10	26.667	76.25		
1.2694	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	10	26.667	82.5		
1.2898	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	10	26.667	88.75		
1.2898	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	10	26.667	95		
1.0347	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	10	29.444	70		
1.0857	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	10	29.444	76.25		
1.1347	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	10	29.444	82.5		
1.1592	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	10	29.444	88.75		
1.1796	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	10	29.444	95		
0.902	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	10	32.222	70		
0.9531	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	10	32.222	76.25		
1.002	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	10	32.222	82.5		
1.0245	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	10	32.222	88.75		
1.0469	0	!Capacity	and	Design	Energy	Input	Fraction	at	0	10	32.222	95		
0.9878	0.099	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	5.556	26.667	70		
1.0367	0.099	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	5.556	26.667	76.25		
1.0837	0.099	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	5.556	26.667	82.5		
1.1041	0.099	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	5.556	26.667	88.75		
1.1265	0.099	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	5.556	26.667	95		
0.8612	0.102	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	5.556	29.444	70		
0.9102	0.102	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	5.556	29.444	76.25		
0.9571	0.102	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	5.556	29.444	82.5		
0.9796	0.102	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	5.556	29.444	88.75		
1	0.102	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	5.556	29.444	95		
0.7347	0.104	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	5.556	32.222	70		
0.7857	0.104	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	5.556	32.222	76.25		
0.8327	0.104	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	5.556	32.222	82.5		
0.8531	0.104	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	5.556	32.222	88.75		
0.8735	0.104	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	5.556	32.222	95		
1.0102	0.098	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	6.111	26.667	70		
1.0592	0.098	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	6.111	26.667	76.25		
1.1061	0.098	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	6.111	26.667	82.5		
1.1286	0.098	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	6.111	26.667	88.75		
1.149	0.098	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	6.111	26.667	95		
0.8837	0.101	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	6.111	29.444	70		
0.9327	0.101	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	6.111	29.444	76.25		
0.9776	0.101	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	6.111	29.444	82.5		
1	0.101	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	6.111	29.444	88.75		
1.0224	0.101	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	6.111	29.444	95		
0.7571	0.104	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	6.111	32.222	70		
0.8061	0.104	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	6.111	32.222	76.25		
0.8531	0.104	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	6.111	32.222	82.5		
0.8735	0.104	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	6.111	32.222	88.75		
0.8959	0.104	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	6.111	32.222	95		
1.0306	0.098	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	6.667	26.667	70		
1.0816	0.098	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	6.667	26.667	76.25		
1.1286	0.098	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	6.667	26.667	82.5		
1.151	0.098	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	6.667	26.667	88.75		
1.1714	0.098	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	6.667	26.667	95		
0.9041	0.1	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	6.667	29.444	70		
0.9531	0.1	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	6.667	29.444	76.25		
1	0.1	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	6.667	29.444	82.5		
1.0224	0.1	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	6.667	29.444	88.75		
1.0449	0.1	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	6.667	29.444	95		
0.7776	0.103	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	6.667	32.222	70		
0.8265	0.103	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	6.667	32.222	76.25		
0.8735	0.103	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	6.667	32.222	82.5		
0.8959	0.103	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	6.667	32.222	88.75		
0.9163	0.103	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	6.667	32.222	95		
1.0531	0.097	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	7.222	26.667	70		
1.1041	0.097	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	7.222	26.667	76.25		
1.151	0.097	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	7.222	26.667	82.5		
1.1735	0.097	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	7.222	26.667	88.75		
1.1959	0.097	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	7.222	26.667	95		
0.9245	0.099	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	7.222	29.444	70		
0.9755	0.099	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	7.222	29.444	76.25		
1.0224	0.099	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	7.222	29.444	82.5		
1.0449	0.099	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	7.222	29.444	88.75		
1.0673	0.099	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	7.222	29.444	95		
0.798	0.102	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	7.222	32.222	70		
0.8469	0.102	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	7.222	32.222	76.25		
0.8939	0.102	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	7.222	32.222	82.5		
0.9163	0.102	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	7.222	32.222	88.75		
0.9388	0.102	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	7.222	32.222	95		
1.0755	0.096	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	7.778	26.667	70		
1.1265	0.096	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	7.778	26.667	76.25		
1.1755	0.096	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	7.778	26.667	82.5		
1.198	0.096	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	7.778	26.667	88.75		
1.2184	0.096	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	7.778	26.667	95		
0.9469	0.098	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	7.778	29.444	70		
0.998	0.098	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	7.778	29.444	76.25		
1.0449	0.098	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	7.778	29.444	82.5		
1.0673	0.098	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	7.778	29.444	88.75		
1.0898	0.098	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	7.778	29.444	95		
0.8184	0.101	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	7.778	32.222	70		
0.8694	0.101	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	7.778	32.222	76.25		
0.9163	0.101	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	7.778	32.222	82.5		
0.9388	0.101	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	7.778	32.222	88.75		
0.9592	0.101	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	7.778	32.222	95		
1.1204	0.095	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	8.889	26.667	70		
1.1735	0.095	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	8.889	26.667	76.25		
1.2204	0.095	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	8.889	26.667	82.5		
1.2449	0.095	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	8.889	26.667	88.75		
1.2673	0.095	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	8.889	26.667	95		
0.9898	0.097	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	8.889	29.444	70		
1.0408	0.097	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	8.889	29.444	76.25		
1.0898	0.097	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	8.889	29.444	82.5		
1.1122	0.097	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	8.889	29.444	88.75		
1.1347	0.097	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	8.889	29.444	95		
0.8592	0.1	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	8.889	32.222	70		
0.9102	0.1	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	8.889	32.222	76.25		
0.9592	0.1	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	8.889	32.222	82.5		
0.9816	0.1	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	8.889	32.222	88.75		
1.0041	0.1	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	8.889	32.222	95		
1.1673	0.094	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	10	26.667	70		
1.2204	0.094	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	10	26.667	76.25		
1.2694	0.094	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	10	26.667	82.5		
1.2898	0.094	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	10	26.667	88.75		
1.2898	0.094	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	10	26.667	95		
1.0347	0.096	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	10	29.444	70		
1.0857	0.096	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	10	29.444	76.25		
1.1347	0.096	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	10	29.444	82.5		
1.1592	0.096	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	10	29.444	88.75		
1.1796	0.096	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	10	29.444	95		
0.902	0.098	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	10	32.222	70		
0.9531	0.098	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	10	32.222	76.25		
1.002	0.098	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	10	32.222	82.5		
1.0245	0.098	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	10	32.222	88.75		
1.0469	0.098	!Capacity	and	Design	Energy	Input	Fraction	at	0.1	10	32.222	95		
0.9878	0.198	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	5.556	26.667	70		
1.0367	0.198	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	5.556	26.667	76.25		
1.0837	0.198	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	5.556	26.667	82.5		
1.1041	0.198	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	5.556	26.667	88.75		
1.1265	0.198	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	5.556	26.667	95		
0.8612	0.204	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	5.556	29.444	70		
0.9102	0.204	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	5.556	29.444	76.25		
0.9571	0.204	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	5.556	29.444	82.5		
0.9796	0.204	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	5.556	29.444	88.75		
1	0.204	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	5.556	29.444	95		
0.7347	0.208	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	5.556	32.222	70		
0.7857	0.208	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	5.556	32.222	76.25		
0.8327	0.208	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	5.556	32.222	82.5		
0.8531	0.208	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	5.556	32.222	88.75		
0.8735	0.208	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	5.556	32.222	95		
1.0102	0.196	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	6.111	26.667	70		
1.0592	0.196	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	6.111	26.667	76.25		
1.1061	0.196	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	6.111	26.667	82.5		
1.1286	0.196	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	6.111	26.667	88.75		
1.149	0.196	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	6.111	26.667	95		
0.8837	0.202	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	6.111	29.444	70		
0.9327	0.202	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	6.111	29.444	76.25		
0.9776	0.202	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	6.111	29.444	82.5		
1	0.202	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	6.111	29.444	88.75		
1.0224	0.202	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	6.111	29.444	95		
0.7571	0.208	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	6.111	32.222	70		
0.8061	0.208	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	6.111	32.222	76.25		
0.8531	0.208	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	6.111	32.222	82.5		
0.8735	0.208	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	6.111	32.222	88.75		
0.8959	0.208	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	6.111	32.222	95		
1.0306	0.196	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	6.667	26.667	70		
1.0816	0.196	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	6.667	26.667	76.25		
1.1286	0.196	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	6.667	26.667	82.5		
1.151	0.196	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	6.667	26.667	88.75		
1.1714	0.196	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	6.667	26.667	95		
0.9041	0.2	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	6.667	29.444	70		
0.9531	0.2	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	6.667	29.444	76.25		
1	0.2	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	6.667	29.444	82.5		
1.0224	0.2	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	6.667	29.444	88.75		
1.0449	0.2	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	6.667	29.444	95		
0.7776	0.206	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	6.667	32.222	70		
0.8265	0.206	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	6.667	32.222	76.25		
0.8735	0.206	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	6.667	32.222	82.5		
0.8959	0.206	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	6.667	32.222	88.75		
0.9163	0.206	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	6.667	32.222	95		
1.0531	0.194	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	7.222	26.667	70		
1.1041	0.194	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	7.222	26.667	76.25		
1.151	0.194	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	7.222	26.667	82.5		
1.1735	0.194	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	7.222	26.667	88.75		
1.1959	0.194	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	7.222	26.667	95		
0.9245	0.198	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	7.222	29.444	70		
0.9755	0.198	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	7.222	29.444	76.25		
1.0224	0.198	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	7.222	29.444	82.5		
1.0449	0.198	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	7.222	29.444	88.75		
1.0673	0.198	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	7.222	29.444	95		
0.798	0.204	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	7.222	32.222	70		
0.8469	0.204	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	7.222	32.222	76.25		
0.8939	0.204	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	7.222	32.222	82.5		
0.9163	0.204	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	7.222	32.222	88.75		
0.9388	0.204	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	7.222	32.222	95		
1.0755	0.192	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	7.778	26.667	70		
1.1265	0.192	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	7.778	26.667	76.25		
1.1755	0.192	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	7.778	26.667	82.5		
1.198	0.192	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	7.778	26.667	88.75		
1.2184	0.192	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	7.778	26.667	95		
0.9469	0.196	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	7.778	29.444	70		
0.998	0.196	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	7.778	29.444	76.25		
1.0449	0.196	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	7.778	29.444	82.5		
1.0673	0.196	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	7.778	29.444	88.75		
1.0898	0.196	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	7.778	29.444	95		
0.8184	0.202	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	7.778	32.222	70		
0.8694	0.202	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	7.778	32.222	76.25		
0.9163	0.202	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	7.778	32.222	82.5		
0.9388	0.202	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	7.778	32.222	88.75		
0.9592	0.202	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	7.778	32.222	95		
1.1204	0.19	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	8.889	26.667	70		
1.1735	0.19	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	8.889	26.667	76.25		
1.2204	0.19	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	8.889	26.667	82.5		
1.2449	0.19	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	8.889	26.667	88.75		
1.2673	0.19	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	8.889	26.667	95		
0.9898	0.194	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	8.889	29.444	70		
1.0408	0.194	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	8.889	29.444	76.25		
1.0898	0.194	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	8.889	29.444	82.5		
1.1122	0.194	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	8.889	29.444	88.75		
1.1347	0.194	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	8.889	29.444	95		
0.8592	0.2	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	8.889	32.222	70		
0.9102	0.2	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	8.889	32.222	76.25		
0.9592	0.2	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	8.889	32.222	82.5		
0.9816	0.2	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	8.889	32.222	88.75		
1.0041	0.2	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	8.889	32.222	95		
1.1673	0.188	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	10	26.667	70		
1.2204	0.188	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	10	26.667	76.25		
1.2694	0.188	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	10	26.667	82.5		
1.2898	0.188	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	10	26.667	88.75		
1.2898	0.188	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	10	26.667	95		
1.0347	0.192	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	10	29.444	70		
1.0857	0.192	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	10	29.444	76.25		
1.1347	0.192	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	10	29.444	82.5		
1.1592	0.192	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	10	29.444	88.75		
1.1796	0.192	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	10	29.444	95		
0.902	0.196	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	10	32.222	70		
0.9531	0.196	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	10	32.222	76.25		
1.002	0.196	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	10	32.222	82.5		
1.0245	0.196	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	10	32.222	88.75		
1.0469	0.196	!Capacity	and	Design	Energy	Input	Fraction	at	0.2	10	32.222	95		
0.9878	0.297	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	5.556	26.667	70		
1.0367	0.297	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	5.556	26.667	76.25		
1.0837	0.297	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	5.556	26.667	82.5		
1.1041	0.297	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	5.556	26.667	88.75		
1.1265	0.297	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	5.556	26.667	95		
0.8612	0.306	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	5.556	29.444	70		
0.9102	0.306	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	5.556	29.444	76.25		
0.9571	0.306	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	5.556	29.444	82.5		
0.9796	0.306	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	5.556	29.444	88.75		
1	0.306	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	5.556	29.444	95		
0.7347	0.312	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	5.556	32.222	70		
0.7857	0.312	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	5.556	32.222	76.25		
0.8327	0.312	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	5.556	32.222	82.5		
0.8531	0.312	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	5.556	32.222	88.75		
0.8735	0.312	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	5.556	32.222	95		
1.0102	0.294	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	6.111	26.667	70		
1.0592	0.294	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	6.111	26.667	76.25		
1.1061	0.294	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	6.111	26.667	82.5		
1.1286	0.294	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	6.111	26.667	88.75		
1.149	0.294	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	6.111	26.667	95		
0.8837	0.303	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	6.111	29.444	70		
0.9327	0.303	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	6.111	29.444	76.25		
0.9776	0.303	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	6.111	29.444	82.5		
1	0.303	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	6.111	29.444	88.75		
1.0224	0.303	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	6.111	29.444	95		
0.7571	0.312	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	6.111	32.222	70		
0.8061	0.312	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	6.111	32.222	76.25		
0.8531	0.312	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	6.111	32.222	82.5		
0.8735	0.312	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	6.111	32.222	88.75		
0.8959	0.312	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	6.111	32.222	95		
1.0306	0.294	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	6.667	26.667	70		
1.0816	0.294	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	6.667	26.667	76.25		
1.1286	0.294	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	6.667	26.667	82.5		
1.151	0.294	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	6.667	26.667	88.75		
1.1714	0.294	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	6.667	26.667	95		
0.9041	0.3	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	6.667	29.444	70		
0.9531	0.3	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	6.667	29.444	76.25		
1	0.3	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	6.667	29.444	82.5		
1.0224	0.3	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	6.667	29.444	88.75		
1.0449	0.3	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	6.667	29.444	95		
0.7776	0.309	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	6.667	32.222	70		
0.8265	0.309	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	6.667	32.222	76.25		
0.8735	0.309	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	6.667	32.222	82.5		
0.8959	0.309	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	6.667	32.222	88.75		
0.9163	0.309	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	6.667	32.222	95		
1.0531	0.291	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	7.222	26.667	70		
1.1041	0.291	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	7.222	26.667	76.25		
1.151	0.291	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	7.222	26.667	82.5		
1.1735	0.291	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	7.222	26.667	88.75		
1.1959	0.291	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	7.222	26.667	95		
0.9245	0.297	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	7.222	29.444	70		
0.9755	0.297	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	7.222	29.444	76.25		
1.0224	0.297	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	7.222	29.444	82.5		
1.0449	0.297	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	7.222	29.444	88.75		
1.0673	0.297	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	7.222	29.444	95		
0.798	0.306	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	7.222	32.222	70		
0.8469	0.306	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	7.222	32.222	76.25		
0.8939	0.306	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	7.222	32.222	82.5		
0.9163	0.306	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	7.222	32.222	88.75		
0.9388	0.306	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	7.222	32.222	95		
1.0755	0.288	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	7.778	26.667	70		
1.1265	0.288	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	7.778	26.667	76.25		
1.1755	0.288	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	7.778	26.667	82.5		
1.198	0.288	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	7.778	26.667	88.75		
1.2184	0.288	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	7.778	26.667	95		
0.9469	0.294	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	7.778	29.444	70		
0.998	0.294	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	7.778	29.444	76.25		
1.0449	0.294	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	7.778	29.444	82.5		
1.0673	0.294	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	7.778	29.444	88.75		
1.0898	0.294	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	7.778	29.444	95		
0.8184	0.303	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	7.778	32.222	70		
0.8694	0.303	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	7.778	32.222	76.25		
0.9163	0.303	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	7.778	32.222	82.5		
0.9388	0.303	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	7.778	32.222	88.75		
0.9592	0.303	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	7.778	32.222	95		
1.1204	0.285	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	8.889	26.667	70		
1.1735	0.285	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	8.889	26.667	76.25		
1.2204	0.285	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	8.889	26.667	82.5		
1.2449	0.285	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	8.889	26.667	88.75		
1.2673	0.285	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	8.889	26.667	95		
0.9898	0.291	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	8.889	29.444	70		
1.0408	0.291	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	8.889	29.444	76.25		
1.0898	0.291	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	8.889	29.444	82.5		
1.1122	0.291	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	8.889	29.444	88.75		
1.1347	0.291	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	8.889	29.444	95		
0.8592	0.3	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	8.889	32.222	70		
0.9102	0.3	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	8.889	32.222	76.25		
0.9592	0.3	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	8.889	32.222	82.5		
0.9816	0.3	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	8.889	32.222	88.75		
1.0041	0.3	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	8.889	32.222	95		
1.1673	0.282	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	10	26.667	70		
1.2204	0.282	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	10	26.667	76.25		
1.2694	0.282	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	10	26.667	82.5		
1.2898	0.282	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	10	26.667	88.75		
1.2898	0.282	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	10	26.667	95		
1.0347	0.288	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	10	29.444	70		
1.0857	0.288	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	10	29.444	76.25		
1.1347	0.288	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	10	29.444	82.5		
1.1592	0.288	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	10	29.444	88.75		
1.1796	0.288	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	10	29.444	95		
0.902	0.294	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	10	32.222	70		
0.9531	0.294	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	10	32.222	76.25		
1.002	0.294	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	10	32.222	82.5		
1.0245	0.294	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	10	32.222	88.75		
1.0469	0.294	!Capacity	and	Design	Energy	Input	Fraction	at	0.3	10	32.222	95		
0.9878	0.396	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	5.556	26.667	70		
1.0367	0.396	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	5.556	26.667	76.25		
1.0837	0.396	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	5.556	26.667	82.5		
1.1041	0.396	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	5.556	26.667	88.75		
1.1265	0.396	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	5.556	26.667	95		
0.8612	0.408	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	5.556	29.444	70		
0.9102	0.408	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	5.556	29.444	76.25		
0.9571	0.408	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	5.556	29.444	82.5		
0.9796	0.408	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	5.556	29.444	88.75		
1	0.408	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	5.556	29.444	95		
0.7347	0.416	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	5.556	32.222	70		
0.7857	0.416	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	5.556	32.222	76.25		
0.8327	0.416	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	5.556	32.222	82.5		
0.8531	0.416	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	5.556	32.222	88.75		
0.8735	0.416	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	5.556	32.222	95		
1.0102	0.392	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	6.111	26.667	70		
1.0592	0.392	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	6.111	26.667	76.25		
1.1061	0.392	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	6.111	26.667	82.5		
1.1286	0.392	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	6.111	26.667	88.75		
1.149	0.392	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	6.111	26.667	95		
0.8837	0.404	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	6.111	29.444	70		
0.9327	0.404	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	6.111	29.444	76.25		
0.9776	0.404	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	6.111	29.444	82.5		
1	0.404	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	6.111	29.444	88.75		
1.0224	0.404	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	6.111	29.444	95		
0.7571	0.416	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	6.111	32.222	70		
0.8061	0.416	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	6.111	32.222	76.25		
0.8531	0.416	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	6.111	32.222	82.5		
0.8735	0.416	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	6.111	32.222	88.75		
0.8959	0.416	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	6.111	32.222	95		
1.0306	0.392	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	6.667	26.667	70		
1.0816	0.392	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	6.667	26.667	76.25		
1.1286	0.392	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	6.667	26.667	82.5		
1.151	0.392	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	6.667	26.667	88.75		
1.1714	0.392	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	6.667	26.667	95		
0.9041	0.4	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	6.667	29.444	70		
0.9531	0.4	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	6.667	29.444	76.25		
1	0.4	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	6.667	29.444	82.5		
1.0224	0.4	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	6.667	29.444	88.75		
1.0449	0.4	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	6.667	29.444	95		
0.7776	0.412	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	6.667	32.222	70		
0.8265	0.412	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	6.667	32.222	76.25		
0.8735	0.412	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	6.667	32.222	82.5		
0.8959	0.412	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	6.667	32.222	88.75		
0.9163	0.412	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	6.667	32.222	95		
1.0531	0.388	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	7.222	26.667	70		
1.1041	0.388	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	7.222	26.667	76.25		
1.151	0.388	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	7.222	26.667	82.5		
1.1735	0.388	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	7.222	26.667	88.75		
1.1959	0.388	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	7.222	26.667	95		
0.9245	0.396	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	7.222	29.444	70		
0.9755	0.396	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	7.222	29.444	76.25		
1.0224	0.396	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	7.222	29.444	82.5		
1.0449	0.396	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	7.222	29.444	88.75		
1.0673	0.396	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	7.222	29.444	95		
0.798	0.408	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	7.222	32.222	70		
0.8469	0.408	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	7.222	32.222	76.25		
0.8939	0.408	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	7.222	32.222	82.5		
0.9163	0.408	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	7.222	32.222	88.75		
0.9388	0.408	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	7.222	32.222	95		
1.0755	0.384	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	7.778	26.667	70		
1.1265	0.384	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	7.778	26.667	76.25		
1.1755	0.384	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	7.778	26.667	82.5		
1.198	0.384	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	7.778	26.667	88.75		
1.2184	0.384	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	7.778	26.667	95		
0.9469	0.392	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	7.778	29.444	70		
0.998	0.392	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	7.778	29.444	76.25		
1.0449	0.392	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	7.778	29.444	82.5		
1.0673	0.392	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	7.778	29.444	88.75		
1.0898	0.392	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	7.778	29.444	95		
0.8184	0.404	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	7.778	32.222	70		
0.8694	0.404	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	7.778	32.222	76.25		
0.9163	0.404	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	7.778	32.222	82.5		
0.9388	0.404	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	7.778	32.222	88.75		
0.9592	0.404	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	7.778	32.222	95		
1.1204	0.38	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	8.889	26.667	70		
1.1735	0.38	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	8.889	26.667	76.25		
1.2204	0.38	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	8.889	26.667	82.5		
1.2449	0.38	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	8.889	26.667	88.75		
1.2673	0.38	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	8.889	26.667	95		
0.9898	0.388	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	8.889	29.444	70		
1.0408	0.388	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	8.889	29.444	76.25		
1.0898	0.388	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	8.889	29.444	82.5		
1.1122	0.388	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	8.889	29.444	88.75		
1.1347	0.388	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	8.889	29.444	95		
0.8592	0.4	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	8.889	32.222	70		
0.9102	0.4	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	8.889	32.222	76.25		
0.9592	0.4	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	8.889	32.222	82.5		
0.9816	0.4	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	8.889	32.222	88.75		
1.0041	0.4	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	8.889	32.222	95		
1.1673	0.376	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	10	26.667	70		
1.2204	0.376	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	10	26.667	76.25		
1.2694	0.376	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	10	26.667	82.5		
1.2898	0.376	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	10	26.667	88.75		
1.2898	0.376	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	10	26.667	95		
1.0347	0.384	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	10	29.444	70		
1.0857	0.384	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	10	29.444	76.25		
1.1347	0.384	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	10	29.444	82.5		
1.1592	0.384	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	10	29.444	88.75		
1.1796	0.384	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	10	29.444	95		
0.902	0.392	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	10	32.222	70		
0.9531	0.392	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	10	32.222	76.25		
1.002	0.392	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	10	32.222	82.5		
1.0245	0.392	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	10	32.222	88.75		
1.0469	0.392	!Capacity	and	Design	Energy	Input	Fraction	at	0.4	10	32.222	95		
0.9878	0.495	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	5.556	26.667	70		
1.0367	0.495	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	5.556	26.667	76.25		
1.0837	0.495	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	5.556	26.667	82.5		
1.1041	0.495	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	5.556	26.667	88.75		
1.1265	0.495	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	5.556	26.667	95		
0.8612	0.51	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	5.556	29.444	70		
0.9102	0.51	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	5.556	29.444	76.25		
0.9571	0.51	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	5.556	29.444	82.5		
0.9796	0.51	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	5.556	29.444	88.75		
1	0.51	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	5.556	29.444	95		
0.7347	0.52	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	5.556	32.222	70		
0.7857	0.52	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	5.556	32.222	76.25		
0.8327	0.52	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	5.556	32.222	82.5		
0.8531	0.52	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	5.556	32.222	88.75		
0.8735	0.52	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	5.556	32.222	95		
1.0102	0.49	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	6.111	26.667	70		
1.0592	0.49	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	6.111	26.667	76.25		
1.1061	0.49	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	6.111	26.667	82.5		
1.1286	0.49	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	6.111	26.667	88.75		
1.149	0.49	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	6.111	26.667	95		
0.8837	0.505	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	6.111	29.444	70		
0.9327	0.505	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	6.111	29.444	76.25		
0.9776	0.505	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	6.111	29.444	82.5		
1	0.505	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	6.111	29.444	88.75		
1.0224	0.505	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	6.111	29.444	95		
0.7571	0.52	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	6.111	32.222	70		
0.8061	0.52	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	6.111	32.222	76.25		
0.8531	0.52	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	6.111	32.222	82.5		
0.8735	0.52	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	6.111	32.222	88.75		
0.8959	0.52	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	6.111	32.222	95		
1.0306	0.49	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	6.667	26.667	70		
1.0816	0.49	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	6.667	26.667	76.25		
1.1286	0.49	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	6.667	26.667	82.5		
1.151	0.49	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	6.667	26.667	88.75		
1.1714	0.49	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	6.667	26.667	95		
0.9041	0.5	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	6.667	29.444	70		
0.9531	0.5	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	6.667	29.444	76.25		
1	0.5	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	6.667	29.444	82.5		
1.0224	0.5	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	6.667	29.444	88.75		
1.0449	0.5	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	6.667	29.444	95		
0.7776	0.515	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	6.667	32.222	70		
0.8265	0.515	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	6.667	32.222	76.25		
0.8735	0.515	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	6.667	32.222	82.5		
0.8959	0.515	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	6.667	32.222	88.75		
0.9163	0.515	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	6.667	32.222	95		
1.0531	0.485	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	7.222	26.667	70		
1.1041	0.485	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	7.222	26.667	76.25		
1.151	0.485	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	7.222	26.667	82.5		
1.1735	0.485	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	7.222	26.667	88.75		
1.1959	0.485	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	7.222	26.667	95		
0.9245	0.495	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	7.222	29.444	70		
0.9755	0.495	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	7.222	29.444	76.25		
1.0224	0.495	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	7.222	29.444	82.5		
1.0449	0.495	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	7.222	29.444	88.75		
1.0673	0.495	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	7.222	29.444	95		
0.798	0.51	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	7.222	32.222	70		
0.8469	0.51	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	7.222	32.222	76.25		
0.8939	0.51	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	7.222	32.222	82.5		
0.9163	0.51	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	7.222	32.222	88.75		
0.9388	0.51	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	7.222	32.222	95		
1.0755	0.48	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	7.778	26.667	70		
1.1265	0.48	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	7.778	26.667	76.25		
1.1755	0.48	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	7.778	26.667	82.5		
1.198	0.48	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	7.778	26.667	88.75		
1.2184	0.48	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	7.778	26.667	95		
0.9469	0.49	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	7.778	29.444	70		
0.998	0.49	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	7.778	29.444	76.25		
1.0449	0.49	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	7.778	29.444	82.5		
1.0673	0.49	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	7.778	29.444	88.75		
1.0898	0.49	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	7.778	29.444	95		
0.8184	0.505	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	7.778	32.222	70		
0.8694	0.505	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	7.778	32.222	76.25		
0.9163	0.505	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	7.778	32.222	82.5		
0.9388	0.505	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	7.778	32.222	88.75		
0.9592	0.505	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	7.778	32.222	95		
1.1204	0.475	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	8.889	26.667	70		
1.1735	0.475	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	8.889	26.667	76.25		
1.2204	0.475	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	8.889	26.667	82.5		
1.2449	0.475	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	8.889	26.667	88.75		
1.2673	0.475	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	8.889	26.667	95		
0.9898	0.485	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	8.889	29.444	70		
1.0408	0.485	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	8.889	29.444	76.25		
1.0898	0.485	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	8.889	29.444	82.5		
1.1122	0.485	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	8.889	29.444	88.75		
1.1347	0.485	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	8.889	29.444	95		
0.8592	0.5	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	8.889	32.222	70		
0.9102	0.5	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	8.889	32.222	76.25		
0.9592	0.5	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	8.889	32.222	82.5		
0.9816	0.5	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	8.889	32.222	88.75		
1.0041	0.5	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	8.889	32.222	95		
1.1673	0.47	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	10	26.667	70		
1.2204	0.47	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	10	26.667	76.25		
1.2694	0.47	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	10	26.667	82.5		
1.2898	0.47	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	10	26.667	88.75		
1.2898	0.47	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	10	26.667	95		
1.0347	0.48	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	10	29.444	70		
1.0857	0.48	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	10	29.444	76.25		
1.1347	0.48	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	10	29.444	82.5		
1.1592	0.48	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	10	29.444	88.75		
1.1796	0.48	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	10	29.444	95		
0.902	0.49	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	10	32.222	70		
0.9531	0.49	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	10	32.222	76.25		
1.002	0.49	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	10	32.222	82.5		
1.0245	0.49	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	10	32.222	88.75		
1.0469	0.49	!Capacity	and	Design	Energy	Input	Fraction	at	0.5	10	32.222	95		
0.9878	0.594	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	5.556	26.667	70		
1.0367	0.594	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	5.556	26.667	76.25		
1.0837	0.594	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	5.556	26.667	82.5		
1.1041	0.594	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	5.556	26.667	88.75		
1.1265	0.594	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	5.556	26.667	95		
0.8612	0.612	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	5.556	29.444	70		
0.9102	0.612	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	5.556	29.444	76.25		
0.9571	0.612	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	5.556	29.444	82.5		
0.9796	0.612	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	5.556	29.444	88.75		
1	0.612	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	5.556	29.444	95		
0.7347	0.624	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	5.556	32.222	70		
0.7857	0.624	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	5.556	32.222	76.25		
0.8327	0.624	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	5.556	32.222	82.5		
0.8531	0.624	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	5.556	32.222	88.75		
0.8735	0.624	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	5.556	32.222	95		
1.0102	0.588	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	6.111	26.667	70		
1.0592	0.588	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	6.111	26.667	76.25		
1.1061	0.588	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	6.111	26.667	82.5		
1.1286	0.588	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	6.111	26.667	88.75		
1.149	0.588	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	6.111	26.667	95		
0.8837	0.606	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	6.111	29.444	70		
0.9327	0.606	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	6.111	29.444	76.25		
0.9776	0.606	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	6.111	29.444	82.5		
1	0.606	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	6.111	29.444	88.75		
1.0224	0.606	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	6.111	29.444	95		
0.7571	0.624	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	6.111	32.222	70		
0.8061	0.624	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	6.111	32.222	76.25		
0.8531	0.624	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	6.111	32.222	82.5		
0.8735	0.624	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	6.111	32.222	88.75		
0.8959	0.624	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	6.111	32.222	95		
1.0306	0.588	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	6.667	26.667	70		
1.0816	0.588	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	6.667	26.667	76.25		
1.1286	0.588	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	6.667	26.667	82.5		
1.151	0.588	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	6.667	26.667	88.75		
1.1714	0.588	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	6.667	26.667	95		
0.9041	0.6	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	6.667	29.444	70		
0.9531	0.6	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	6.667	29.444	76.25		
1	0.6	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	6.667	29.444	82.5		
1.0224	0.6	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	6.667	29.444	88.75		
1.0449	0.6	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	6.667	29.444	95		
0.7776	0.618	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	6.667	32.222	70		
0.8265	0.618	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	6.667	32.222	76.25		
0.8735	0.618	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	6.667	32.222	82.5		
0.8959	0.618	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	6.667	32.222	88.75		
0.9163	0.618	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	6.667	32.222	95		
1.0531	0.582	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	7.222	26.667	70		
1.1041	0.582	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	7.222	26.667	76.25		
1.151	0.582	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	7.222	26.667	82.5		
1.1735	0.582	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	7.222	26.667	88.75		
1.1959	0.582	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	7.222	26.667	95		
0.9245	0.594	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	7.222	29.444	70		
0.9755	0.594	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	7.222	29.444	76.25		
1.0224	0.594	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	7.222	29.444	82.5		
1.0449	0.594	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	7.222	29.444	88.75		
1.0673	0.594	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	7.222	29.444	95		
0.798	0.612	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	7.222	32.222	70		
0.8469	0.612	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	7.222	32.222	76.25		
0.8939	0.612	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	7.222	32.222	82.5		
0.9163	0.612	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	7.222	32.222	88.75		
0.9388	0.612	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	7.222	32.222	95		
1.0755	0.576	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	7.778	26.667	70		
1.1265	0.576	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	7.778	26.667	76.25		
1.1755	0.576	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	7.778	26.667	82.5		
1.198	0.576	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	7.778	26.667	88.75		
1.2184	0.576	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	7.778	26.667	95		
0.9469	0.588	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	7.778	29.444	70		
0.998	0.588	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	7.778	29.444	76.25		
1.0449	0.588	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	7.778	29.444	82.5		
1.0673	0.588	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	7.778	29.444	88.75		
1.0898	0.588	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	7.778	29.444	95		
0.8184	0.606	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	7.778	32.222	70		
0.8694	0.606	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	7.778	32.222	76.25		
0.9163	0.606	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	7.778	32.222	82.5		
0.9388	0.606	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	7.778	32.222	88.75		
0.9592	0.606	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	7.778	32.222	95		
1.1204	0.57	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	8.889	26.667	70		
1.1735	0.57	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	8.889	26.667	76.25		
1.2204	0.57	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	8.889	26.667	82.5		
1.2449	0.57	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	8.889	26.667	88.75		
1.2673	0.57	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	8.889	26.667	95		
0.9898	0.582	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	8.889	29.444	70		
1.0408	0.582	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	8.889	29.444	76.25		
1.0898	0.582	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	8.889	29.444	82.5		
1.1122	0.582	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	8.889	29.444	88.75		
1.1347	0.582	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	8.889	29.444	95		
0.8592	0.6	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	8.889	32.222	70		
0.9102	0.6	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	8.889	32.222	76.25		
0.9592	0.6	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	8.889	32.222	82.5		
0.9816	0.6	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	8.889	32.222	88.75		
1.0041	0.6	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	8.889	32.222	95		
1.1673	0.564	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	10	26.667	70		
1.2204	0.564	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	10	26.667	76.25		
1.2694	0.564	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	10	26.667	82.5		
1.2898	0.564	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	10	26.667	88.75		
1.2898	0.564	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	10	26.667	95		
1.0347	0.576	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	10	29.444	70		
1.0857	0.576	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	10	29.444	76.25		
1.1347	0.576	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	10	29.444	82.5		
1.1592	0.576	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	10	29.444	88.75		
1.1796	0.576	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	10	29.444	95		
0.902	0.588	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	10	32.222	70		
0.9531	0.588	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	10	32.222	76.25		
1.002	0.588	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	10	32.222	82.5		
1.0245	0.588	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	10	32.222	88.75		
1.0469	0.588	!Capacity	and	Design	Energy	Input	Fraction	at	0.6	10	32.222	95		
0.9878	0.693	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	5.556	26.667	70		
1.0367	0.693	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	5.556	26.667	76.25		
1.0837	0.693	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	5.556	26.667	82.5		
1.1041	0.693	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	5.556	26.667	88.75		
1.1265	0.693	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	5.556	26.667	95		
0.8612	0.714	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	5.556	29.444	70		
0.9102	0.714	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	5.556	29.444	76.25		
0.9571	0.714	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	5.556	29.444	82.5		
0.9796	0.714	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	5.556	29.444	88.75		
1	0.714	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	5.556	29.444	95		
0.7347	0.728	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	5.556	32.222	70		
0.7857	0.728	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	5.556	32.222	76.25		
0.8327	0.728	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	5.556	32.222	82.5		
0.8531	0.728	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	5.556	32.222	88.75		
0.8735	0.728	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	5.556	32.222	95		
1.0102	0.686	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	6.111	26.667	70		
1.0592	0.686	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	6.111	26.667	76.25		
1.1061	0.686	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	6.111	26.667	82.5		
1.1286	0.686	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	6.111	26.667	88.75		
1.149	0.686	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	6.111	26.667	95		
0.8837	0.707	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	6.111	29.444	70		
0.9327	0.707	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	6.111	29.444	76.25		
0.9776	0.707	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	6.111	29.444	82.5		
1	0.707	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	6.111	29.444	88.75		
1.0224	0.707	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	6.111	29.444	95		
0.7571	0.728	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	6.111	32.222	70		
0.8061	0.728	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	6.111	32.222	76.25		
0.8531	0.728	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	6.111	32.222	82.5		
0.8735	0.728	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	6.111	32.222	88.75		
0.8959	0.728	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	6.111	32.222	95		
1.0306	0.686	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	6.667	26.667	70		
1.0816	0.686	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	6.667	26.667	76.25		
1.1286	0.686	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	6.667	26.667	82.5		
1.151	0.686	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	6.667	26.667	88.75		
1.1714	0.686	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	6.667	26.667	95		
0.9041	0.7	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	6.667	29.444	70		
0.9531	0.7	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	6.667	29.444	76.25		
1	0.7	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	6.667	29.444	82.5		
1.0224	0.7	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	6.667	29.444	88.75		
1.0449	0.7	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	6.667	29.444	95		
0.7776	0.721	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	6.667	32.222	70		
0.8265	0.721	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	6.667	32.222	76.25		
0.8735	0.721	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	6.667	32.222	82.5		
0.8959	0.721	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	6.667	32.222	88.75		
0.9163	0.721	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	6.667	32.222	95		
1.0531	0.679	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	7.222	26.667	70		
1.1041	0.679	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	7.222	26.667	76.25		
1.151	0.679	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	7.222	26.667	82.5		
1.1735	0.679	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	7.222	26.667	88.75		
1.1959	0.679	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	7.222	26.667	95		
0.9245	0.693	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	7.222	29.444	70		
0.9755	0.693	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	7.222	29.444	76.25		
1.0224	0.693	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	7.222	29.444	82.5		
1.0449	0.693	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	7.222	29.444	88.75		
1.0673	0.693	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	7.222	29.444	95		
0.798	0.714	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	7.222	32.222	70		
0.8469	0.714	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	7.222	32.222	76.25		
0.8939	0.714	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	7.222	32.222	82.5		
0.9163	0.714	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	7.222	32.222	88.75		
0.9388	0.714	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	7.222	32.222	95		
1.0755	0.672	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	7.778	26.667	70		
1.1265	0.672	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	7.778	26.667	76.25		
1.1755	0.672	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	7.778	26.667	82.5		
1.198	0.672	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	7.778	26.667	88.75		
1.2184	0.672	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	7.778	26.667	95		
0.9469	0.686	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	7.778	29.444	70		
0.998	0.686	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	7.778	29.444	76.25		
1.0449	0.686	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	7.778	29.444	82.5		
1.0673	0.686	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	7.778	29.444	88.75		
1.0898	0.686	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	7.778	29.444	95		
0.8184	0.707	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	7.778	32.222	70		
0.8694	0.707	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	7.778	32.222	76.25		
0.9163	0.707	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	7.778	32.222	82.5		
0.9388	0.707	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	7.778	32.222	88.75		
0.9592	0.707	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	7.778	32.222	95		
1.1204	0.665	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	8.889	26.667	70		
1.1735	0.665	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	8.889	26.667	76.25		
1.2204	0.665	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	8.889	26.667	82.5		
1.2449	0.665	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	8.889	26.667	88.75		
1.2673	0.665	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	8.889	26.667	95		
0.9898	0.679	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	8.889	29.444	70		
1.0408	0.679	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	8.889	29.444	76.25		
1.0898	0.679	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	8.889	29.444	82.5		
1.1122	0.679	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	8.889	29.444	88.75		
1.1347	0.679	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	8.889	29.444	95		
0.8592	0.7	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	8.889	32.222	70		
0.9102	0.7	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	8.889	32.222	76.25		
0.9592	0.7	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	8.889	32.222	82.5		
0.9816	0.7	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	8.889	32.222	88.75		
1.0041	0.7	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	8.889	32.222	95		
1.1673	0.658	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	10	26.667	70		
1.2204	0.658	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	10	26.667	76.25		
1.2694	0.658	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	10	26.667	82.5		
1.2898	0.658	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	10	26.667	88.75		
1.2898	0.658	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	10	26.667	95		
1.0347	0.672	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	10	29.444	70		
1.0857	0.672	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	10	29.444	76.25		
1.1347	0.672	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	10	29.444	82.5		
1.1592	0.672	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	10	29.444	88.75		
1.1796	0.672	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	10	29.444	95		
0.902	0.686	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	10	32.222	70		
0.9531	0.686	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	10	32.222	76.25		
1.002	0.686	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	10	32.222	82.5		
1.0245	0.686	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	10	32.222	88.75		
1.0469	0.686	!Capacity	and	Design	Energy	Input	Fraction	at	0.7	10	32.222	95		
0.9878	0.792	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	5.556	26.667	70		
1.0367	0.792	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	5.556	26.667	76.25		
1.0837	0.792	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	5.556	26.667	82.5		
1.1041	0.792	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	5.556	26.667	88.75		
1.1265	0.792	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	5.556	26.667	95		
0.8612	0.816	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	5.556	29.444	70		
0.9102	0.816	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	5.556	29.444	76.25		
0.9571	0.816	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	5.556	29.444	82.5		
0.9796	0.816	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	5.556	29.444	88.75		
1	0.816	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	5.556	29.444	95		
0.7347	0.832	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	5.556	32.222	70		
0.7857	0.832	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	5.556	32.222	76.25		
0.8327	0.832	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	5.556	32.222	82.5		
0.8531	0.832	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	5.556	32.222	88.75		
0.8735	0.832	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	5.556	32.222	95		
1.0102	0.784	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	6.111	26.667	70		
1.0592	0.784	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	6.111	26.667	76.25		
1.1061	0.784	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	6.111	26.667	82.5		
1.1286	0.784	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	6.111	26.667	88.75		
1.149	0.784	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	6.111	26.667	95		
0.8837	0.808	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	6.111	29.444	70		
0.9327	0.808	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	6.111	29.444	76.25		
0.9776	0.808	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	6.111	29.444	82.5		
1	0.808	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	6.111	29.444	88.75		
1.0224	0.808	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	6.111	29.444	95		
0.7571	0.832	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	6.111	32.222	70		
0.8061	0.832	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	6.111	32.222	76.25		
0.8531	0.832	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	6.111	32.222	82.5		
0.8735	0.832	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	6.111	32.222	88.75		
0.8959	0.832	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	6.111	32.222	95		
1.0306	0.784	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	6.667	26.667	70		
1.0816	0.784	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	6.667	26.667	76.25		
1.1286	0.784	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	6.667	26.667	82.5		
1.151	0.784	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	6.667	26.667	88.75		
1.1714	0.784	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	6.667	26.667	95		
0.9041	0.8	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	6.667	29.444	70		
0.9531	0.8	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	6.667	29.444	76.25		
1	0.8	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	6.667	29.444	82.5		
1.0224	0.8	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	6.667	29.444	88.75		
1.0449	0.8	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	6.667	29.444	95		
0.7776	0.824	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	6.667	32.222	70		
0.8265	0.824	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	6.667	32.222	76.25		
0.8735	0.824	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	6.667	32.222	82.5		
0.8959	0.824	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	6.667	32.222	88.75		
0.9163	0.824	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	6.667	32.222	95		
1.0531	0.776	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	7.222	26.667	70		
1.1041	0.776	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	7.222	26.667	76.25		
1.151	0.776	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	7.222	26.667	82.5		
1.1735	0.776	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	7.222	26.667	88.75		
1.1959	0.776	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	7.222	26.667	95		
0.9245	0.792	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	7.222	29.444	70		
0.9755	0.792	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	7.222	29.444	76.25		
1.0224	0.792	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	7.222	29.444	82.5		
1.0449	0.792	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	7.222	29.444	88.75		
1.0673	0.792	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	7.222	29.444	95		
0.798	0.816	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	7.222	32.222	70		
0.8469	0.816	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	7.222	32.222	76.25		
0.8939	0.816	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	7.222	32.222	82.5		
0.9163	0.816	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	7.222	32.222	88.75		
0.9388	0.816	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	7.222	32.222	95		
1.0755	0.768	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	7.778	26.667	70		
1.1265	0.768	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	7.778	26.667	76.25		
1.1755	0.768	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	7.778	26.667	82.5		
1.198	0.768	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	7.778	26.667	88.75		
1.2184	0.768	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	7.778	26.667	95		
0.9469	0.784	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	7.778	29.444	70		
0.998	0.784	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	7.778	29.444	76.25		
1.0449	0.784	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	7.778	29.444	82.5		
1.0673	0.784	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	7.778	29.444	88.75		
1.0898	0.784	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	7.778	29.444	95		
0.8184	0.808	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	7.778	32.222	70		
0.8694	0.808	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	7.778	32.222	76.25		
0.9163	0.808	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	7.778	32.222	82.5		
0.9388	0.808	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	7.778	32.222	88.75		
0.9592	0.808	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	7.778	32.222	95		
1.1204	0.76	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	8.889	26.667	70		
1.1735	0.76	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	8.889	26.667	76.25		
1.2204	0.76	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	8.889	26.667	82.5		
1.2449	0.76	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	8.889	26.667	88.75		
1.2673	0.76	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	8.889	26.667	95		
0.9898	0.776	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	8.889	29.444	70		
1.0408	0.776	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	8.889	29.444	76.25		
1.0898	0.776	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	8.889	29.444	82.5		
1.1122	0.776	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	8.889	29.444	88.75		
1.1347	0.776	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	8.889	29.444	95		
0.8592	0.8	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	8.889	32.222	70		
0.9102	0.8	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	8.889	32.222	76.25		
0.9592	0.8	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	8.889	32.222	82.5		
0.9816	0.8	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	8.889	32.222	88.75		
1.0041	0.8	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	8.889	32.222	95		
1.1673	0.752	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	10	26.667	70		
1.2204	0.752	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	10	26.667	76.25		
1.2694	0.752	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	10	26.667	82.5		
1.2898	0.752	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	10	26.667	88.75		
1.2898	0.752	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	10	26.667	95		
1.0347	0.768	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	10	29.444	70		
1.0857	0.768	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	10	29.444	76.25		
1.1347	0.768	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	10	29.444	82.5		
1.1592	0.768	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	10	29.444	88.75		
1.1796	0.768	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	10	29.444	95		
0.902	0.784	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	10	32.222	70		
0.9531	0.784	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	10	32.222	76.25		
1.002	0.784	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	10	32.222	82.5		
1.0245	0.784	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	10	32.222	88.75		
1.0469	0.784	!Capacity	and	Design	Energy	Input	Fraction	at	0.8	10	32.222	95		
0.9878	0.891	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	5.556	26.667	70		
1.0367	0.891	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	5.556	26.667	76.25		
1.0837	0.891	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	5.556	26.667	82.5		
1.1041	0.891	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	5.556	26.667	88.75		
1.1265	0.891	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	5.556	26.667	95		
0.8612	0.918	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	5.556	29.444	70		
0.9102	0.918	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	5.556	29.444	76.25		
0.9571	0.918	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	5.556	29.444	82.5		
0.9796	0.918	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	5.556	29.444	88.75		
1	0.918	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	5.556	29.444	95		
0.7347	0.936	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	5.556	32.222	70		
0.7857	0.936	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	5.556	32.222	76.25		
0.8327	0.936	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	5.556	32.222	82.5		
0.8531	0.936	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	5.556	32.222	88.75		
0.8735	0.936	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	5.556	32.222	95		
1.0102	0.882	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	6.111	26.667	70		
1.0592	0.882	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	6.111	26.667	76.25		
1.1061	0.882	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	6.111	26.667	82.5		
1.1286	0.882	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	6.111	26.667	88.75		
1.149	0.882	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	6.111	26.667	95		
0.8837	0.909	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	6.111	29.444	70		
0.9327	0.909	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	6.111	29.444	76.25		
0.9776	0.909	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	6.111	29.444	82.5		
1	0.909	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	6.111	29.444	88.75		
1.0224	0.909	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	6.111	29.444	95		
0.7571	0.936	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	6.111	32.222	70		
0.8061	0.936	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	6.111	32.222	76.25		
0.8531	0.936	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	6.111	32.222	82.5		
0.8735	0.936	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	6.111	32.222	88.75		
0.8959	0.936	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	6.111	32.222	95		
1.0306	0.882	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	6.667	26.667	70		
1.0816	0.882	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	6.667	26.667	76.25		
1.1286	0.882	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	6.667	26.667	82.5		
1.151	0.882	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	6.667	26.667	88.75		
1.1714	0.882	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	6.667	26.667	95		
0.9041	0.9	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	6.667	29.444	70		
0.9531	0.9	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	6.667	29.444	76.25		
1	0.9	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	6.667	29.444	82.5		
1.0224	0.9	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	6.667	29.444	88.75		
1.0449	0.9	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	6.667	29.444	95		
0.7776	0.927	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	6.667	32.222	70		
0.8265	0.927	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	6.667	32.222	76.25		
0.8735	0.927	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	6.667	32.222	82.5		
0.8959	0.927	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	6.667	32.222	88.75		
0.9163	0.927	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	6.667	32.222	95		
1.0531	0.873	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	7.222	26.667	70		
1.1041	0.873	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	7.222	26.667	76.25		
1.151	0.873	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	7.222	26.667	82.5		
1.1735	0.873	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	7.222	26.667	88.75		
1.1959	0.873	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	7.222	26.667	95		
0.9245	0.891	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	7.222	29.444	70		
0.9755	0.891	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	7.222	29.444	76.25		
1.0224	0.891	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	7.222	29.444	82.5		
1.0449	0.891	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	7.222	29.444	88.75		
1.0673	0.891	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	7.222	29.444	95		
0.798	0.918	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	7.222	32.222	70		
0.8469	0.918	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	7.222	32.222	76.25		
0.8939	0.918	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	7.222	32.222	82.5		
0.9163	0.918	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	7.222	32.222	88.75		
0.9388	0.918	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	7.222	32.222	95		
1.0755	0.864	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	7.778	26.667	70		
1.1265	0.864	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	7.778	26.667	76.25		
1.1755	0.864	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	7.778	26.667	82.5		
1.198	0.864	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	7.778	26.667	88.75		
1.2184	0.864	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	7.778	26.667	95		
0.9469	0.882	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	7.778	29.444	70		
0.998	0.882	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	7.778	29.444	76.25		
1.0449	0.882	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	7.778	29.444	82.5		
1.0673	0.882	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	7.778	29.444	88.75		
1.0898	0.882	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	7.778	29.444	95		
0.8184	0.909	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	7.778	32.222	70		
0.8694	0.909	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	7.778	32.222	76.25		
0.9163	0.909	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	7.778	32.222	82.5		
0.9388	0.909	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	7.778	32.222	88.75		
0.9592	0.909	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	7.778	32.222	95		
1.1204	0.855	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	8.889	26.667	70		
1.1735	0.855	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	8.889	26.667	76.25		
1.2204	0.855	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	8.889	26.667	82.5		
1.2449	0.855	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	8.889	26.667	88.75		
1.2673	0.855	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	8.889	26.667	95		
0.9898	0.873	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	8.889	29.444	70		
1.0408	0.873	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	8.889	29.444	76.25		
1.0898	0.873	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	8.889	29.444	82.5		
1.1122	0.873	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	8.889	29.444	88.75		
1.1347	0.873	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	8.889	29.444	95		
0.8592	0.9	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	8.889	32.222	70		
0.9102	0.9	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	8.889	32.222	76.25		
0.9592	0.9	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	8.889	32.222	82.5		
0.9816	0.9	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	8.889	32.222	88.75		
1.0041	0.9	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	8.889	32.222	95		
1.1673	0.846	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	10	26.667	70		
1.2204	0.846	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	10	26.667	76.25		
1.2694	0.846	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	10	26.667	82.5		
1.2898	0.846	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	10	26.667	88.75		
1.2898	0.846	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	10	26.667	95		
1.0347	0.864	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	10	29.444	70		
1.0857	0.864	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	10	29.444	76.25		
1.1347	0.864	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	10	29.444	82.5		
1.1592	0.864	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	10	29.444	88.75		
1.1796	0.864	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	10	29.444	95		
0.902	0.882	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	10	32.222	70		
0.9531	0.882	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	10	32.222	76.25		
1.002	0.882	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	10	32.222	82.5		
1.0245	0.882	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	10	32.222	88.75		
1.0469	0.882	!Capacity	and	Design	Energy	Input	Fraction	at	0.9	10	32.222	95		
0.9878	0.99	!Capacity	and	Design	Energy	Input	Fraction	at	1	5.556	26.667	70		
1.0367	0.99	!Capacity	and	Design	Energy	Input	Fraction	at	1	5.556	26.667	76.25		
1.0837	0.99	!Capacity	and	Design	Energy	Input	Fraction	at	1	5.556	26.667	82.5		
1.1041	0.99	!Capacity	and	Design	Energy	Input	Fraction	at	1	5.556	26.667	88.75		
1.1265	0.99	!Capacity	and	Design	Energy	Input	Fraction	at	1	5.556	26.667	95		
0.8612	1.02	!Capacity	and	Design	Energy	Input	Fraction	at	1	5.556	29.444	70		
0.9102	1.02	!Capacity	and	Design	Energy	Input	Fraction	at	1	5.556	29.444	76.25		
0.9571	1.02	!Capacity	and	Design	Energy	Input	Fraction	at	1	5.556	29.444	82.5		
0.9796	1.02	!Capacity	and	Design	Energy	Input	Fraction	at	1	5.556	29.444	88.75		
1	1.02	!Capacity	and	Design	Energy	Input	Fraction	at	1	5.556	29.444	95		
0.7347	1.04	!Capacity	and	Design	Energy	Input	Fraction	at	1	5.556	32.222	70		
0.7857	1.04	!Capacity	and	Design	Energy	Input	Fraction	at	1	5.556	32.222	76.25		
0.8327	1.04	!Capacity	and	Design	Energy	Input	Fraction	at	1	5.556	32.222	82.5		
0.8531	1.04	!Capacity	and	Design	Energy	Input	Fraction	at	1	5.556	32.222	88.75		
0.8735	1.04	!Capacity	and	Design	Energy	Input	Fraction	at	1	5.556	32.222	95		
1.0102	0.98	!Capacity	and	Design	Energy	Input	Fraction	at	1	6.111	26.667	70		
1.0592	0.98	!Capacity	and	Design	Energy	Input	Fraction	at	1	6.111	26.667	76.25		
1.1061	0.98	!Capacity	and	Design	Energy	Input	Fraction	at	1	6.111	26.667	82.5		
1.1286	0.98	!Capacity	and	Design	Energy	Input	Fraction	at	1	6.111	26.667	88.75		
1.149	0.98	!Capacity	and	Design	Energy	Input	Fraction	at	1	6.111	26.667	95		
0.8837	1.01	!Capacity	and	Design	Energy	Input	Fraction	at	1	6.111	29.444	70		
0.9327	1.01	!Capacity	and	Design	Energy	Input	Fraction	at	1	6.111	29.444	76.25		
0.9776	1.01	!Capacity	and	Design	Energy	Input	Fraction	at	1	6.111	29.444	82.5		
1	1.01	!Capacity	and	Design	Energy	Input	Fraction	at	1	6.111	29.444	88.75		
1.0224	1.01	!Capacity	and	Design	Energy	Input	Fraction	at	1	6.111	29.444	95		
0.7571	1.04	!Capacity	and	Design	Energy	Input	Fraction	at	1	6.111	32.222	70		
0.8061	1.04	!Capacity	and	Design	Energy	Input	Fraction	at	1	6.111	32.222	76.25		
0.8531	1.04	!Capacity	and	Design	Energy	Input	Fraction	at	1	6.111	32.222	82.5		
0.8735	1.04	!Capacity	and	Design	Energy	Input	Fraction	at	1	6.111	32.222	88.75		
0.8959	1.04	!Capacity	and	Design	Energy	Input	Fraction	at	1	6.111	32.222	95		
1.0306	0.98	!Capacity	and	Design	Energy	Input	Fraction	at	1	6.667	26.667	70		
1.0816	0.98	!Capacity	and	Design	Energy	Input	Fraction	at	1	6.667	26.667	76.25		
1.1286	0.98	!Capacity	and	Design	Energy	Input	Fraction	at	1	6.667	26.667	82.5		
1.151	0.98	!Capacity	and	Design	Energy	Input	Fraction	at	1	6.667	26.667	88.75		
1.1714	0.98	!Capacity	and	Design	Energy	Input	Fraction	at	1	6.667	26.667	95		
0.9041	1	!Capacity	and	Design	Energy	Input	Fraction	at	1	6.667	29.444	70		
0.9531	1	!Capacity	and	Design	Energy	Input	Fraction	at	1	6.667	29.444	76.25		
1	1	!Capacity	and	Design	Energy	Input	Fraction	at	1	6.667	29.444	82.5		
1.0224	1	!Capacity	and	Design	Energy	Input	Fraction	at	1	6.667	29.444	88.75		
1.0449	1	!Capacity	and	Design	Energy	Input	Fraction	at	1	6.667	29.444	95		
0.7776	1.03	!Capacity	and	Design	Energy	Input	Fraction	at	1	6.667	32.222	70		
0.8265	1.03	!Capacity	and	Design	Energy	Input	Fraction	at	1	6.667	32.222	76.25		
0.8735	1.03	!Capacity	and	Design	Energy	Input	Fraction	at	1	6.667	32.222	82.5		
0.8959	1.03	!Capacity	and	Design	Energy	Input	Fraction	at	1	6.667	32.222	88.75		
0.9163	1.03	!Capacity	and	Design	Energy	Input	Fraction	at	1	6.667	32.222	95		
1.0531	0.97	!Capacity	and	Design	Energy	Input	Fraction	at	1	7.222	26.667	70		
1.1041	0.97	!Capacity	and	Design	Energy	Input	Fraction	at	1	7.222	26.667	76.25		
1.151	0.97	!Capacity	and	Design	Energy	Input	Fraction	at	1	7.222	26.667	82.5		
1.1735	0.97	!Capacity	and	Design	Energy	Input	Fraction	at	1	7.222	26.667	88.75		
1.1959	0.97	!Capacity	and	Design	Energy	Input	Fraction	at	1	7.222	26.667	95		
0.9245	0.99	!Capacity	and	Design	Energy	Input	Fraction	at	1	7.222	29.444	70		
0.9755	0.99	!Capacity	and	Design	Energy	Input	Fraction	at	1	7.222	29.444	76.25		
1.0224	0.99	!Capacity	and	Design	Energy	Input	Fraction	at	1	7.222	29.444	82.5		
1.0449	0.99	!Capacity	and	Design	Energy	Input	Fraction	at	1	7.222	29.444	88.75		
1.0673	0.99	!Capacity	and	Design	Energy	Input	Fraction	at	1	7.222	29.444	95		
0.798	1.02	!Capacity	and	Design	Energy	Input	Fraction	at	1	7.222	32.222	70		
0.8469	1.02	!Capacity	and	Design	Energy	Input	Fraction	at	1	7.222	32.222	76.25		
0.8939	1.02	!Capacity	and	Design	Energy	Input	Fraction	at	1	7.222	32.222	82.5		
0.9163	1.02	!Capacity	and	Design	Energy	Input	Fraction	at	1	7.222	32.222	88.75		
0.9388	1.02	!Capacity	and	Design	Energy	Input	Fraction	at	1	7.222	32.222	95		
1.0755	0.96	!Capacity	and	Design	Energy	Input	Fraction	at	1	7.778	26.667	70		
1.1265	0.96	!Capacity	and	Design	Energy	Input	Fraction	at	1	7.778	26.667	76.25		
1.1755	0.96	!Capacity	and	Design	Energy	Input	Fraction	at	1	7.778	26.667	82.5		
1.198	0.96	!Capacity	and	Design	Energy	Input	Fraction	at	1	7.778	26.667	88.75		
1.2184	0.96	!Capacity	and	Design	Energy	Input	Fraction	at	1	7.778	26.667	95		
0.9469	0.98	!Capacity	and	Design	Energy	Input	Fraction	at	1	7.778	29.444	70		
0.998	0.98	!Capacity	and	Design	Energy	Input	Fraction	at	1	7.778	29.444	76.25		
1.0449	0.98	!Capacity	and	Design	Energy	Input	Fraction	at	1	7.778	29.444	82.5		
1.0673	0.98	!Capacity	and	Design	Energy	Input	Fraction	at	1	7.778	29.444	88.75		
1.0898	0.98	!Capacity	and	Design	Energy	Input	Fraction	at	1	7.778	29.444	95		
0.8184	1.01	!Capacity	and	Design	Energy	Input	Fraction	at	1	7.778	32.222	70		
0.8694	1.01	!Capacity	and	Design	Energy	Input	Fraction	at	1	7.778	32.222	76.25		
0.9163	1.01	!Capacity	and	Design	Energy	Input	Fraction	at	1	7.778	32.222	82.5		
0.9388	1.01	!Capacity	and	Design	Energy	Input	Fraction	at	1	7.778	32.222	88.75		
0.9592	1.01	!Capacity	and	Design	Energy	Input	Fraction	at	1	7.778	32.222	95		
1.1204	0.95	!Capacity	and	Design	Energy	Input	Fraction	at	1	8.889	26.667	70		
1.1735	0.95	!Capacity	and	Design	Energy	Input	Fraction	at	1	8.889	26.667	76.25		
1.2204	0.95	!Capacity	and	Design	Energy	Input	Fraction	at	1	8.889	26.667	82.5		
1.2449	0.95	!Capacity	and	Design	Energy	Input	Fraction	at	1	8.889	26.667	88.75		
1.2673	0.95	!Capacity	and	Design	Energy	Input	Fraction	at	1	8.889	26.667	95		
0.9898	0.97	!Capacity	and	Design	Energy	Input	Fraction	at	1	8.889	29.444	70		
1.0408	0.97	!Capacity	and	Design	Energy	Input	Fraction	at	1	8.889	29.444	76.25		
1.0898	0.97	!Capacity	and	Design	Energy	Input	Fraction	at	1	8.889	29.444	82.5		
1.1122	0.97	!Capacity	and	Design	Energy	Input	Fraction	at	1	8.889	29.444	88.75		
1.1347	0.97	!Capacity	and	Design	Energy	Input	Fraction	at	1	8.889	29.444	95		
0.8592	1	!Capacity	and	Design	Energy	Input	Fraction	at	1	8.889	32.222	70		
0.9102	1	!Capacity	and	Design	Energy	Input	Fraction	at	1	8.889	32.222	76.25		
0.9592	1	!Capacity	and	Design	Energy	Input	Fraction	at	1	8.889	32.222	82.5		
0.9816	1	!Capacity	and	Design	Energy	Input	Fraction	at	1	8.889	32.222	88.75		
1.0041	1	!Capacity	and	Design	Energy	Input	Fraction	at	1	8.889	32.222	95		
1.1673	0.94	!Capacity	and	Design	Energy	Input	Fraction	at	1	10	26.667	70		
1.2204	0.94	!Capacity	and	Design	Energy	Input	Fraction	at	1	10	26.667	76.25		
1.2694	0.94	!Capacity	and	Design	Energy	Input	Fraction	at	1	10	26.667	82.5		
1.2898	0.94	!Capacity	and	Design	Energy	Input	Fraction	at	1	10	26.667	88.75		
1.2898	0.94	!Capacity	and	Design	Energy	Input	Fraction	at	1	10	26.667	95		
1.0347	0.96	!Capacity	and	Design	Energy	Input	Fraction	at	1	10	29.444	70		
1.0857	0.96	!Capacity	and	Design	Energy	Input	Fraction	at	1	10	29.444	76.25		
1.1347	0.96	!Capacity	and	Design	Energy	Input	Fraction	at	1	10	29.444	82.5		
1.1592	0.96	!Capacity	and	Design	Energy	Input	Fraction	at	1	10	29.444	88.75		
1.1796	0.96	!Capacity	and	Design	Energy	Input	Fraction	at	1	10	29.444	95		
0.902	0.98	!Capacity	and	Design	Energy	Input	Fraction	at	1	10	32.222	70		
0.9531	0.98	!Capacity	and	Design	Energy	Input	Fraction	at	1	10	32.222	76.25		
1.002	0.98	!Capacity	and	Design	Energy	Input	Fraction	at	1	10	32.222	82.5		
1.0245	0.98	!Capacity	and	Design	Energy	Input	Fraction	at	1	10	32.222	88.75		
1.0469	0.98	!Capacity	and	Design	Energy	Input	Fraction	at	1	10	32.222	95		


More information about the TRNSYS-users mailing list