[TRNSYS-users] radiator type 1231
David BRADLEY
d.bradley at tess-inc.com
Mon Jul 1 08:24:49 PDT 2013
Enyuan,
Type1231 was developed based on correlations to model a heating
radiator, not a cooling radiator and it is likely that the correlations
simply do not hold true in cooling applications. I would look to a
different model. I would also be a bit careful; most in-room cooling
radiators operate above the dewpoint because getting condensation all
over their surfaces causes other problems.
As for connecting Type1231's output to Type56, define an energy gain
input (as opposed to a constant value or a schedule) in the zone that
contains the radiator. Then connect the Type1231 heat transfer output to
the gain input. I would recommend that you split the gain about 80%
convective and 20% radiative. Despite their name, most radiators do
significant heating by convection.
Best,
David
On 6/28/2013 13:34, Enyuan Hu wrote:
> Dear all,
>
> I'm trying to model radiant cooling using the type 1231 radiator in
> TESS library for TRNSYS 17. The model may be loose for cooling as
> condensation is not considered, but we want to have some idea of the
> effect when only convection and radiation are dominant. I'm looking
> for answers to two questions:
>
> 1. Is there any example or tutorial that shows how the radiator can be
> used with type 56, or how they communicate?
>
> 2. In searching previous threads on using the radiator, it seemed that
> there's restriction on the inlet water temperature, that it, it must
> be at least 0.5C above the room temperature. Can we circumvent this
> restriction?
>
> Thanks.
> Enyuan
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20130701/456fd624/attachment-0004.htm>
More information about the TRNSYS-users
mailing list