[TRNSYS-users] Energy balance for one zone (Ntype 904)
王洋
wanghongyang1767 at gmail.com
Tue Jan 29 03:05:26 PST 2013
Dear all,
I have some questions about Energy balance for one zone (Ntype 904).
1) For Qtrans, it might be stored thermal energy (>0?) in the wall or
directly transmitted (<0?) through the wall. But I want to calculate the
two parts exactly, i.e. how to calculate the part of stored thermal energy
in the wall and directly transmitted energy, separatedly?
2) For Qsolgain, does it mean Ntype 14 +15? or only Ntype 75?
What relationship between Qsolgain and Solar_rad. (kWh) in
T56_stdoutput.sum file? Are both the same? or included relationship?
3) For Qgint, is it Ntype 7 + 13? Is it equal to Int_gains in
T56_stdoutput.sum file?
4) I want to calculate Heat Loss (or energy consumption) in a zone e.g. in
winter, whether or not the heat loss includes Qinf + Qvent +DQairdt+ Qtrans
(only the part of directly transmitted through the wall, not the part of
stored part, that is why I ask 1))?
For the actual heat gain e.g. in winter in one zone, it only includes Qgint
+ Qsolgain?
However, Qheat and Qcool should be Heat loss or heat gain?
Many thanks in advance!
Br.
yang wang
2013/1/23 王洋 <wanghongyang1767 at gmail.com>
>
>
>
> 2013/1/21 王洋 <wanghongyang1767 at gmail.com>
>
>>
>> 2013/1/18 王洋 <wanghongyang1767 at gmail.com>
>>
>>>
>>>
>>> 2013/1/8 <trnsys-users-request at cae.wisc.edu>
>>>
>>>> Send TRNSYS-users mailing list submissions to
>>>> trnsys-users at cae.wisc.edu
>>>>
>>>> To subscribe or unsubscribe via the World Wide Web, visit
>>>> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>>>> or, via email, send a message with subject or body 'help' to
>>>> trnsys-users-request at cae.wisc.edu
>>>>
>>>> You can reach the person managing the list at
>>>> trnsys-users-owner at cae.wisc.edu
>>>>
>>>> When replying, please edit your Subject line so it is more specific
>>>> than "Re: Contents of TRNSYS-users digest..."
>>>>
>>>> Today's Topics:
>>>>
>>>> 1. Re: 2 independet + 1 dependent variables in look-up files
>>>> (David BRADLEY)
>>>> 2. Re: Type94a - multi array will be wrongly calculated
>>>> (David BRADLEY)
>>>> 3. Hybrid dessicant dehumidifier (Graham S. Wright)
>>>>
>>>>
>>>> ---------- 已转发邮件 ----------
>>>> From: David BRADLEY <d.bradley at tess-inc.com>
>>>> To: leen peeters <l.f.r.peeters at gmail.com>
>>>> Cc: "trnsys-users at cae.wisc.edu" <TRNSYS-users at cae.wisc.edu>,
>>>> vanreeth.b at bxl.daikineurope.com
>>>> Date: Tue, 08 Jan 2013 09:10:04 -0600
>>>> Subject: Re: [TRNSYS-users] 2 independet + 1 dependent variables in
>>>> look-up files
>>>> Leen,
>>>> Unless I am misunderstanding what you want to do, the solution is
>>>> quite easy as long as you are able and willing to write a new Type; TRNSYS
>>>> has a built-in kernel subroutine called InterpolateData (formerly called
>>>> DynamicData) that performs exactly the function that you are looking for.
>>>> The subroutine is called from a Type with the values of as many as 6
>>>> independent variables. The subroutine looks through an external file, finds
>>>> and returns the values of as many as 10 dependent variables that correspond
>>>> to the input values. The subroutine interpolates linearly between values
>>>> but cannot extrapolate beyond the range of values that is given in the data
>>>> file.
>>>>
>>>> Before you go too far down the path of writing a new heat pump model,
>>>> I would recommend that you look through the TESS HVAC Library documentation
>>>> on existing heat pump models and also take a look at the code of some of
>>>> those models. Most of them stay away from energy rate control (in which a
>>>> precalculated load is imposed on the heat pump) and stick with temperature
>>>> level control (in which case heat pump capacity and fraction of full load
>>>> power are computed based on inlet and ambient conditions.) Those models may
>>>> be what you are looking for or could be modified with little effort to
>>>> better suit your needs.
>>>> Best,
>>>> David
>>>>
>>>>
>>>>
>>>> On 1/8/2013 06:35, leen peeters wrote:
>>>>
>>>> Hi all,
>>>>
>>>> We are trying to model more accurately a heat pump for which the
>>>> performance should ideally be read out from a text or excel file.
>>>> The data depend on 3 parameters (outdoor and indoor air temperature,
>>>> requested output).
>>>> Part load ratios are hard to define, as the actual capacity depends on
>>>> the model type and the outdoor conditions. So it seems logic to use excell.
>>>> However, values are not a function, but should be looked up in the excell
>>>> table, potentially interpolated, ... and to make it more challenging, the
>>>> final SPF does depend on PLR, outdoor and indoor temperature. So it is not
>>>> just using the external temperature and required capacity to calculate PLR
>>>> and consequently use that PLR plus indoor temperature to calculate SPF.
>>>>
>>>> Calling 6 different excell files in a simulation of 8760*4 steps will
>>>> take considerable time. The current standard TRNSYS look up model allows
>>>> two independent parameters defining the output ... so insufficiently
>>>> accurate.
>>>>
>>>> any suggestions on how to solve that?
>>>>
>>>> thanks,
>>>>
>>>> leen
>>>>
>>>>
>>>> _______________________________________________
>>>> TRNSYS-users mailing listTRNSYS-users at cae.wisc.eduhttps://mailman.cae.wisc.edu/listinfo/trnsys-users
>>>>
>>>>
>>>> --
>>>> ***************************
>>>> David BRADLEY
>>>> Principal
>>>> Thermal Energy Systems Specialists, LLC
>>>> 22 North Carroll Street - suite 370
>>>> Madison, WI 53703 USA
>>>>
>>>> P:+1.608.274.2577
>>>> F:+1.608.278.1475d.bradley at tess-inc.com
>>>> http://www.tess-inc.comhttp://www.trnsys.com
>>>>
>>>>
>>>>
>>>> ---------- 已转发邮件 ----------
>>>> From: David BRADLEY <d.bradley at tess-inc.com>
>>>> To: Olaf Scholz <olaf.scholz at online.de>
>>>> Cc: trnsys-users at cae.wisc.edu
>>>> Date: Tue, 08 Jan 2013 09:16:30 -0600
>>>> Subject: Re: [TRNSYS-users] Type94a - multi array will be wrongly
>>>> calculated
>>>> Olaf,
>>>> I have used multiple instances of Type94 to compute the output of
>>>> differently oriented PV arrays a number of times and have gotten good
>>>> results so I suspect that there may be a problem in the way the model has
>>>> been defined. One complexity of Type94 is that it has two power outputs;
>>>> one that gives the power at the maximum power point (and therefore assumes
>>>> that the array is equipped with a maximum power point tracking (MPPT)
>>>> device) and another that gives the array power at a particular load
>>>> voltage. This second output is used for direct-connected systems that do
>>>> not have an MPPT and in this case, the load voltage is an input to the
>>>> model. Make sure that you are looking at the maximum power point power when
>>>> you compare the output of the three arrays; otherwise, the problem may be
>>>> that the load voltage on the array is so low that the power output of the
>>>> array is minimal no matter what its orientation. If you are unable to find
>>>> the solution then I would recommend that you send your project to your
>>>> distributor for further assistance.
>>>> Best,
>>>> David
>>>>
>>>>
>>>> On 1/8/2013 03:12, Olaf Scholz wrote:
>>>>
>>>> I created a PV collector field consisting of three fields (type 94a)
>>>> for 3 incident directions (east, south, west) all 94a- modules are
>>>> connected tot o a type109 weather generator. The total incident radiation
>>>> for the three directions seems to be calculated correctly (output of
>>>> type109 for three different surfaces). But the power output of the PV
>>>> modules seems to be always the same, which is not correct. Do you have a
>>>> solution for that ?****
>>>>
>>>> It seems to be the used input variable in type 94a is always the same,
>>>> so that only the last value is used for the calculation.****
>>>>
>>>> ** **
>>>>
>>>> *Olaf*****
>>>>
>>>> ** **
>>>>
>>>>
>>>> _______________________________________________
>>>> TRNSYS-users mailing listTRNSYS-users at cae.wisc.eduhttps://mailman.cae.wisc.edu/listinfo/trnsys-users
>>>>
>>>>
>>>> --
>>>> ***************************
>>>> David BRADLEY
>>>> Principal
>>>> Thermal Energy Systems Specialists, LLC
>>>> 22 North Carroll Street - suite 370
>>>> Madison, WI 53703 USA
>>>>
>>>> P:+1.608.274.2577
>>>> F:+1.608.278.1475d.bradley at tess-inc.com
>>>> http://www.tess-inc.comhttp://www.trnsys.com
>>>>
>>>>
>>>>
>>>> ---------- 已转发邮件 ----------
>>>> From: "Graham S. Wright" <graham at wrightonsustainability.com>
>>>> To: trnsys-users at cae.wisc.edu
>>>> Cc:
>>>> Date: Tue, 8 Jan 2013 09:20:31 -0600
>>>> Subject: [TRNSYS-users] Hybrid dessicant dehumidifier
>>>>
>>>> Hello,
>>>>
>>>> I am wondering if some one has made a TRNSYS component for this thing,
>>>> or if there is a way to model it with existing ones. The DryCool HD
>>>> dessicant dehumidifier by Munters. See screenshot below from the manual.
>>>>
>>>> Thanks,
>>>>
>>>> Graham S. Wright
>>>> Passive House Institute US
>>>>
>>>>
>>>> _______________________________________________
>>>> TRNSYS-users mailing list
>>>> TRNSYS-users at cae.wisc.edu
>>>> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>>>>
>>>>
>>>
>>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20130129/2412470c/attachment-0005.htm>
More information about the TRNSYS-users
mailing list