[TRNSYS-users] Convection heat tranfer coefficients in Type 56
marcello.caciolo at cofelyaxima-gdfsuez.com
marcello.caciolo at cofelyaxima-gdfsuez.com
Mon Jan 28 01:33:52 PST 2013
Dear TRNSYS users,
I am currently modeling a building with Thermo-activated building systems (TABS). As a first step, I try to compare TRNSYS results with stationary calculations provided by TABS manufacturer.
A first simulation shows very different results. After few investigation, the main difference between TRNSYS and manufacturer calculation is due to convection heat transfer coefficients. Indeed, I activated in Type 56 automatic calculation for hconv for TABS surfaces. Temperature differences are very low, in the order of 1-2 degrees. In this case, the correlation:
Hconv = alpha * DT ^0.31
Gives convection coefficients in the order of 5-10 (kJ/h)/(m2K) , even lower or much lower than standard coefficient for isothermal surfaces (11 (kJ/h)/(m2K) ). On the other hand, manufacturer data show convection coefficients in the order of 20-40 (kJ/h)/(m2K).
My question is double:
1) Which is the origin of the standard coefficients (constants: 7.2 and 3.888, exponent: 0.31) used in the automatic calculation of hconv?
2) Do you have any experience in TABS? If yes, which value/correlation of hconv seems reasonable to you for these systems?
Thank you for your attention.
Best regards,
Marcello Caciolo
Responsable Outils et Méthodes d'Analyse Energétique
[cid:image001.jpg at 01CDFD41.70D68160]
Cellule Efficacité Energétique et Environnementale - Pôle Projets et Réalisations
46 Boulevard de la Prairie au Duc
BP 40119 - 44201 Nantes Cedex 02
Tél.: +33 02 40 41 06 57
marcello.caciolo at cofelyaxima-gdfsuez.com<mailto:prenom.nom at aximaseitha-gdfsuez.com>
P Pensez à l'environnement avant d'imprimer ce message
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20130128/4a5e9308/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 4267 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20130128/4a5e9308/attachment-0005.jpg>
More information about the TRNSYS-users
mailing list