[TRNSYS-users] Converting kJ/hr to kWh type46
Jeff Thornton
thornton at tess-inc.com
Fri Jan 18 12:31:26 PST 2013
When you integrate kJ/h in Type 46 you get units of kJ. To convert
kJ to kWh you divide the number by 3600:
kJ * 1 h/3600 s = kJ/s *
Hours = kW * Hours = kWh
This is most easily done in Excel after the
simulation is complete but you could do it before the integrator and use
an equation.
Jeff
---
Jeff Thornton
_President - TESS LLC_
_22
N. Carroll Street, Madison WI USA 53703_
_Office: (608) 274-2577 Fax:
(608) 278-1475_
_www.tess-inc.com_
_E-Mail: thornton at tess-inc.com_
On 01/18/2013 10:09 am, Patrick Fabriek wrote:
> Dear Trnsys user,
>
> Maybe this is a frequently asked question but I will ask hehe.
>
> The output units of type 56 is not really useful to me and I would
like to convert this.
>
> Im using a type 46 with automatic monthly
periods as output for my type 56 building model. How can I convert this
output file into kWh?
>
> Do I have to divide the monthly output over
3600?
>
> Example : January 2.8e6 [kJ/hr ] to bring it to kWh I
multiply it by 3600.
>
> Is this correct?
>
> Kind Regards.
>
>
Patrick Fabriek