[TRNSYS-users] Beam radiation warnings with type 56
David BRADLEY
d.bradley at tess-inc.com
Sun Jan 6 11:32:08 PST 2013
Martin,
Carefully check the "angle of incidence," "beam'" and "total"
radiation connections between your weather component (probably Type15)
and the building (Type56). I would imagine that one of them is
incorrect. Make sure that the surfaces that you have defined in the
weather processor correspond correctly to the orientations that you have
defined for your building in TRNBuild. Warnings are there to help you
correct problems in your input file. While it is possible to increase
the number of them that are allowed before the simulation terminates in
error, every effort should be made to understand and correct the
warnings first.
Best,
David
On 12/31/2012 04:47, Martin Ssembatya wrote:
> Hello there,
>
> I am using using type 56 to model the cooling loads that are to be
> served by a solar cooling system. However, i am getting a number of
> warnings for some periods of the year related to the beam radiation
> incident to one of the orientations. The warnings read, "/Beam
> radiation greater than 0 occurred for an incident angle of 90.00
> greater than 90 degrees for orientation 1. Beam radiation has been set
> to 0/!. These warnings keep re - occurring for very many simulation
> time steps and eventually, it becomes a fatal error after the maximum
> number of warnings per simulation is exceeded. How can i increase the
> maximum number of warnings per simulation in order to dodge this
> problem, because i cant see any way else i can solve this warnings
> problem? I have tried to increase the "Before 'WARNING' value in the
> studio cards, but nothing works out. Or is there someone who has ever
> gotten a similar problem to kindly help me with some suggestions of
> how i can go about this problem??
>
> Kind regards and happy 2013
> Martin
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20130106/4bced84a/attachment-0001.htm>
More information about the TRNSYS-users
mailing list