Cristi,
   The Type31 "simple buried pipe" in Trnsys16 was no different than the 
standard Type31 that is in the standard Hydronics library in both 
Trnsys16 and Trnsys17. The only difference was in the proforma, which 
had a modified icon and in which the third input was labeled "ground 
temperature" instead of "environment temperature." You can continue to 
use type31 in Trnsys17. Please be aware, though that the ground 
temperature around the Type31 pipe will not be affected in any way by 
the energy transfer between the ground and the pipe.
Best,
  David


On 2/28/2013 07:15, C. Ionescu wrote:
>
> Hello!
>
> Can anyone tell me if there is a possibility to impose the ground 
> temperature to a "buried pipe" in TRNSYS 17 (E.g. Type 952)?
>
> I have measured data for ground temperature variation and, according 
> to this, I want to simulate the variation of the fluid temperature 
> inside the pipe.
>
> In TRNSYS 16 there was Type 31 (simple buried pipe), but in TRNSYS 17 
> all the types for buried pipes use calculated temperature of the ground.
>
> Thank you,
>
> Cristi
>
> ? ? ? ?
>
> <http://www.incredimail.com/?id=621159&did=10501&ppd=2820,201206281812,9,1,1036046467946521095&rui=104461716&app_test_id=0&sd=20130228> 
>
>
> FREE Animations for your email 
> <http://www.incredimail.com/?id=621159&did=10501&ppd=2820,201206281812,9,1,1036046467946521095&rui=104461716&app_test_id=0&sd=20130228> 
> 	
>
> 	<http://www.incredimail.com/?id=621159&did=10501&ppd=2820,201206281812,9,1,1036046467946521095&rui=104461716&app_test_id=0&sd=20130228>
> 	
>
> 	<http://www.incredimail.com/?id=621159&did=10501&ppd=2820,201206281812,9,1,1036046467946521095&rui=104461716&app_test_id=0&sd=20130228>
> 	
> <http://www.incredimail.com/?id=621159&did=10501&ppd=2820,201206281812,9,1,1036046467946521095&rui=104461716&app_test_id=0&sd=20130228>
> 	<http://www.incredimail.com/?id=621159&did=10501&ppd=2820,201206281812,9,1,1036046467946521095&rui=104461716&app_test_id=0&sd=20130228>
> 	Click Here! 
> <http://www.incredimail.com/?id=621159&did=10501&ppd=2820,201206281812,9,1,1036046467946521095&rui=104461716&app_test_id=0&sd=20130228> 
> 	<http://www.incredimail.com/?id=621159&did=10501&ppd=2820,201206281812,9,1,1036046467946521095&rui=104461716&app_test_id=0&sd=20130228>
> 	<http://www.incredimail.com/?id=621159&did=10501&ppd=2820,201206281812,9,1,1036046467946521095&rui=104461716&app_test_id=0&sd=20130228>
>
> 	<http://www.incredimail.com/?id=621159&did=10501&ppd=2820,201206281812,9,1,1036046467946521095&rui=104461716&app_test_id=0&sd=20130228>
> 	
>
> 	<http://www.incredimail.com/?id=621159&did=10501&ppd=2820,201206281812,9,1,1036046467946521095&rui=104461716&app_test_id=0&sd=20130228>
> 	
>
> <http://www.incredimail.com/?id=621159&did=10501&ppd=2820,201206281812,9,1,1036046467946521095&rui=104461716&app_test_id=0&sd=20130228> 
>
>
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users

-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20130228/e1b38550/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 12626 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20130228/e1b38550/attachment-0002.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 20662 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20130228/e1b38550/attachment-0003.gif>


More information about the TRNSYS-users mailing list