[TRNSYS-users] Floor vs Ceiling when both active?
David BRADLEY
d.bradley at tess-inc.com
Wed Dec 18 13:23:04 PST 2013
Ajit,
Got it. I thought for some reason that your two surfaces were
back-to-back and made up a ceiling of one zone and the floor of the one
above, not a floor and a ceiling in the same airnode.
In any case, if you look in the airnode window and click on each of
your "walls" you'll notice that there is a number listed in blue to the
right of the "geosurf" field. This is a surface number indicator. When
you then go into the output manager, and start selecting your surfaces,
you'll notice those same numbers listed.
Best,
David
On 12/18/2013 14:49, Ajit Naik wrote:
>
> Thanks David. I think I need a bit of clarification though:
>
> I am just modeling the one airnode representing my level (call it
> level 5), and presuming that the imaginary levels 6 and 4 are at a
> constant temp by designating both the floor and ceiling of floor 5 as
> boundary constructions. There are no actual adjacent airnodes
> representing level 6 or 4 present. However, I still wish to consider
> the effect of level 4's radiant system on level 5 via the floor in
> addition to the effect of level 5's radiant ceiling. When trying to
> distinguish the floor from the ceiling here, I run into trouble.
>
> I thought about creating ideally conditioned "dummy" airnodes for
> levels 6 & 4 and defining the radiant surfaces as adjacent
> constructions to overcome this, but wanted to know if there's an
> easier method of telling floor from ceiling with the model as-is.
>
> Thanks again!
>
> Ajit Naik
>
> Energy Engineer
>
> *dbHMS
> *303 W Erie Street, Suite 510
>
> Chicago, IL 60654
>
> p (312) 915-0557 x308
>
> f (312) 915-0558
>
> www.dbhms.com
>
> *From:*trnsys-users-bounces at cae.wisc.edu
> [mailto:trnsys-users-bounces at cae.wisc.edu] *On Behalf Of *David BRADLEY
> *Sent:* Wednesday, December 18, 2013 12:11 PM
> *To:* TRNSYS users mailing list at the Solar Energy Lab, UW-Madison
> *Subject:* Re: [TRNSYS-users] Floor vs Ceiling when both active?
>
> Ajit,
> I would have defined a single construction separating the airnode
> above from the airnode below (instead of defining two BOUNDARY
> surfaces). To get the surface temperature of the ceiling side of the
> construction, select the airnode that contains the ceiling when you
> are in the TRNBuild output manager. Change to "surface outputs" and
> select the TSI ntype (ntype17).
> Best,
> David
>
> On 12/18/2013 11:25, Ajit Naik wrote:
>
> Hello All,
>
> I am modeling a single floor of multi-story building with an
> in-ceiling radiant system. I have defined an active surface has a
> carpet on the "floor" side and exposed concrete on the "ceiling"
> side.
>
> I naturally defined the ceiling of the airnode as an active
> surface, but also defined the floor as an active surface as well
> to account for the effects of the underlying level's radiant
> ceiling. Both the ceiling and the floor of the airnode are defined
> as boundary surfaces with a fixed temperature on the other side.
>
> Here's my problem -- I am interested in recording the airnode's
> CEILING temperature (at the exposed concrete surface) -- but
> within TRNBUILD the ceiling and floor both have identical surface
> areas and I cannot tell which is which! The only differentiable
> marker I observe is the surface type. Is there any simple way to
> find which of the two surfaces is the Ceiling in this case?
>
> Thank you!!
>
> Ajit
>
> Ajit Naik
>
> Energy Engineer
>
> *dbHMS
> *303 W Erie Street, Suite 510
>
> Chicago, IL 60654
>
> p (312) 915-0557 x308
>
> f (312) 915-0558
>
> www.dbhms.com
>
>
>
>
> _______________________________________________
>
> TRNSYS-users mailing list
>
> TRNSYS-users at cae.wisc.edu <mailto:TRNSYS-users at cae.wisc.edu>
>
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>
>
>
> --
> ***************************
> David BRADLEY
> Principal
> Thermal Energy Systems Specialists, LLC
> 22 North Carroll Street - suite 370
> Madison, WI 53703 USA
>
> P:+1.608.274.2577
> F:+1.608.278.1475
> d.bradley at tess-inc.com <mailto:d.bradley at tess-inc.com>
>
> http://www.tess-inc.com
> http://www.trnsys.com
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com