[TRNSYS-users] MULTIPLE AIRNODES IN A ZONE
David BRADLEY
d.bradley at tess-inc.com
Tue Aug 6 15:13:15 PDT 2013
Juan,
You would need to use TRNFlow or CONTAM (Type97) to calculate the
rates at which air flows from one zone to another based on the
temperature and pressure differences within your building. Type56 can,
however, calculate the effect of known air flow rates between zones.
Since implementing a TRNFlow or CONTAM airflow model is somewhat
complicated, you might start off by assuming some interzonal air flow
rates to see what the impact of those air flow rates is on the
stratification and comfort within the building. If you assume a
reasonably low air exchange rate and find that the comfort results are
not significantly different from those when you assume a high air
exchange rate then you can save yourself the time and energy of
implementing the air flow model.
Kind regards,
David
On 8/6/2013 03:15, JUAN FRANCISCO BELMONTE TOLEDO wrote:
>
> Hello all.
>
> I'm modeling a living room of 4m height, conditioned by cooling
> ceiling panels and I'm evaluating the possibility of using multiple
> airnodes to simulate the stratification of the temperature within and
> its influence on comfort parameters, but I have some preliminary
> questions about it:
>
> ¿I have to calculate (don't know, for example with TRNFLOW) or
> estimate the air flow exchange between airnodes or TRNBUILD is capable
> of simulating the buoyancy air flow phenomena automatically....?.
>
> Thank you.
>
> *Juan Francisco Belmonte Toledo*
>
> Dpto. de Mecánica Aplicada e Ing. de Proyectos
>
> Universidad de Castilla-La Mancha
>
> Juanf.belmonte at uclm.es <mailto:Juanf.belmonte at uclm.es>
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20130806/051d8369/attachment-0004.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 569 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20130806/051d8369/attachment-0004.gif>
More information about the TRNSYS-users
mailing list