[TRNSYS-users] error - messase 48
David BRADLEY
d.bradley at tess-inc.com
Wed Sep 5 13:01:12 PDT 2012
Christina,
The label names that you have chosen for your Type65 online plotter
(Cold side outlet flow rate_FWH_6, Cold side outlet tempertureFWH6)
cannot have spaces in them. The labels are delineated by spaces so
spaces within a label name aren't allowed.
Best,
David
On 9/5/2012 06:10, Christina Tsechelidou wrote:
> Dear trnsys users,
>
> I have a problem and I need your help..
> I simulate a small project but whet i run it it appears an error with
> message 48:
>
> "TRNSYS Message 48 : The TRNSYS processor has reported that an
> unrecognized control card was found while trying to read the input
> file. This error can be caused by underspecifying a required number of
> items in the input file. For example, specifiying only 9 parameters
> after a "PARAMETERS 10" card has been read can cause this error. The
> line that caused this error is listed in the reported information
> below. Reported information : Cold-side"
>
> I simulate a solar field of troughs and an oil heater exchanger and I
> put an online plotter to see what happens with the temperatures and
> flows.
> Can you tell me what is going wrong and I cannot take results?I
> enclose the project to test it.
>
> Thank you in advance,
> Tsechelidou Christina
>
>
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120905/9b558099/attachment-0005.htm>
More information about the TRNSYS-users
mailing list