[TRNSYS-users] Storage tank - input inconsistency when 10min interval
David BRADLEY
d.bradley at tess-inc.com
Fri Sep 21 08:50:06 PDT 2012
Michal,
There may not really be a problem here. TRNSYS outputs are averages
over each timestep and inputs are assumed to be constant over a
timestep. As a result the inputs to Type534 are assumed to be the
average flow rate over your 10 minute period. Type9 also gives you
various options for what kind of data you are giving it (averages over
the timestep, instantaneous values at the end of the timestep, etc.). If
you have integrated flows over the 10 minute periods, you can use an
equation to back out what the average flow rate was over the period.
Kind regards,
David
On 9/19/2012 09:26, Michał Klimas wrote:
>
> Dear All,
>
> I’m trying to simulate water flow through storage tank ( type 534).
> I’ve got real measurements of water temp. and flow with 10min interval
> (using type 9e) but units of tank inputs can only be kg/s or kg/h and
> so on.
>
> My simulation TIMESTEP must be 10 min (1/6 as an equation) so I cannot
> interpolate any data.
>
> Do you have any idea how to solve this problem ?
>
> best regards
>
> Michal Klimas
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120921/c8805722/attachment-0001.htm>
More information about the TRNSYS-users
mailing list