[TRNSYS-users] Temperature level control is not working
Michael Diekerhof
Michael.diekerhof at web.de
Mon Oct 29 23:41:46 PDT 2012
Dear all,
in my masterthesis I am trying to connect a heat pump (type401) to a
buffer storage and then to type 56. But the first step was to change
from energy rated control to temperature level control; so I followed
the TRNSYS tutorial. But somehow the indoor air temperature (kitchen) is
not controlled at all. I´ve checked it twice and as i can see i did
everything exactly like the tutorial explained. As long as I am not able
to control this temperature around 20°C I shouldn´t think about
implementing a heat pump and a storage.
I attached the project and the bui.file and as you can see the heating
is on and especially in the cold months (e.g. january) the room
temperature is abnormaly high.
I am very thankful for any suggestion how to control the T_Air_Kitchen
around 20°C ! I have no idea what could be wrong right now and at my
university there´s no one who has experiences with TRNSYS. So thanks in
advance!
Best,
Michael
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Tutorial.tpf
Type: application/octet-stream
Size: 158026 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20121030/46ca5926/attachment-0005.obj>
-------------- next part --------------
*****************************************************************************************************************************************************************************************************************************************************************************************************************************************************************************************************************
* TRNBuild 2.0.200
*****************************************************************************************************************************************************************************************************************************************************************************************************************************************************************************************************************
* BUILDING DESCRIPTIONS FILE TRNSYS
* FOR BUILDING: C:\Trnsys17\MyProjects\Tutorial\Building_Tutorial_Restaurant.bui
* GET BY WORKING WITH TRNBuild 1.0 for Windows
*****************************************************************************************************************************************************************************************************************************************************************************************************************************************************************************************************************
*
*----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* C o m m e n t s
*----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* P r o j e c t
*----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*+++ PROJECT
*+++ TITLE=RESTAURANT EXAMPLE
*+++ DESCRIPTION=TRNSYS MAIN REFERENCE MANUAL
*+++ CREATED=SOLAR ENERGY LABORATORY
*+++ ADDRESS=MADISON, WI USA
*+++ CITY=
*+++ SWITCH=UNDEFINED
*----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* P r o p e r t i e s
*----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
PROPERTIES
DENSITY=1.204 : CAPACITY=1.012 : PRESSURE=101325.000 : HVAPOR=2454.0 : SIGMA=2.041e-007 : RTEMP=293.15
*--- alpha calculation -------------------
KFLOORUP=7.2 : EFLOORUP=0.31 : KFLOORDOWN=3.888 : EFLOORDOWN=0.31
KCEILUP=7.2 : ECEILUP=0.31 : KCEILDOWN=3.888 : ECEILDOWN=0.31
KVERTICAL=5.76 : EVERTICAL=0.3
*
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
TYPES
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
*
*----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* L a y e r s
*----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
LAYER GYPSUM
CONDUCTIVITY= 2.62 : CAPACITY= 0.75 : DENSITY= 1601
LAYER INSULATION
CONDUCTIVITY= 0.155 : CAPACITY= 0.75 : DENSITY= 32
LAYER STUCCO
CONDUCTIVITY= 2.49 : CAPACITY= 0.75 : DENSITY= 1858
LAYER WOOD
CONDUCTIVITY= 0.418 : CAPACITY= 2.25 : DENSITY= 592
LAYER CONCRETE
CONDUCTIVITY= 6.23 : CAPACITY= 0.75 : DENSITY= 2242
LAYER STONE
CONDUCTIVITY= 5.17 : CAPACITY= 1.5 : DENSITY= 881
LAYER CLAYTILE
CONDUCTIVITY= 3 : CAPACITY= 0.84 : DENSITY= 1000
LAYER PLASTBOARD
CONDUCTIVITY= 1.9 : CAPACITY= 0.84 : DENSITY= 1200
LAYER AIRSPACE
RESISTANCE= 0.05
LAYER ROOFING
CONDUCTIVITY= 2.5 : CAPACITY= 1 : DENSITY= 2100
*----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* I n p u t s
*----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
INPUTS HOUTSIDE M_DOT_KITCH T_IN_KITCH RH_IN_KITCH M_DOT_DINING T_IN_DINING RH_IN_DINING
*----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* S c h e d u l e s
*----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
SCHEDULE WEEKDAY
HOURS =0.000 8.000 10.000 12.000 14.000 17.000 22.000 24.0
VALUES=0 5. 2. 10. 2. 10. 0 0
SCHEDULE WEEKEND
HOURS =0.000 8.000 10.000 12.000 14.000 17.000 22.000 24.0
VALUES=0 10. 5. 10. 4. 10. 0 0
SCHEDULE OCCUPANCY
HOURS =0.000 7.000 22.000 24.0
VALUES=0 1. 0 0
SCHEDULE CUSTOMERS
DAYS=1 2 3 4 5 6 7
HOURLY=WEEKDAY WEEKDAY WEEKDAY WEEKDAY WEEKDAY WEEKEND WEEKEND
*----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* W a l l s
*----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
WALL OUTSIDE
LAYERS = GYPSUM INSULATION STUCCO
THICKNESS= 0.019 0.076 0.025
ABS-FRONT= 0.9 : ABS-BACK= 0.8
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = 11 : HBACK= INPUT 1*HOUTSIDE
WALL INSIDE
LAYERS = GYPSUM WOOD GYPSUM
THICKNESS= 0.019 0.058 0.019
ABS-FRONT= 0.8 : ABS-BACK= 0.8
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = 11 : HBACK= 11
WALL FLOOR
LAYERS = STONE INSULATION CONCRETE
THICKNESS= 0.025 0.076 0.102
ABS-FRONT= 0.8 : ABS-BACK= 0
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = 11 : HBACK= 1e-005
WALL ROOF
LAYERS = PLASTBOARD AIRSPACE INSULATION CONCRETE ROOFING
THICKNESS= 0.016 0 0.076 0.102 0.006
ABS-FRONT= 0.8 : ABS-BACK= 0.9
EPS-FRONT= 0.9 : EPS-BACK= 0.9
HFRONT = 11 : HBACK= INPUT 1*HOUTSIDE
*----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* W i n d o w s
*----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
WINDOW DOUBLE
WINID=2001 : HINSIDE=11 : HOUTSIDE=72 : SLOPE=90 : SPACID=0 : WWID=0.77 : WHEIG=1.08 : FFRAME=0.15 : UFRAME=8.17 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : CCISHADE=0.5 : EPSFRAME=0.9 : EPSISHADE=0.9 : ITSHADECLOSE=648 : ITSHADEOPEN=576
*----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* D e f a u l t G a i n s
*----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* O t h e r G a i n s
*----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
GAIN PEOPLE
CONVECTIVE=150 : RADIATIVE=70 : HUMIDITY=0.058
GAIN LIGHTS
CONVECTIVE=300 : RADIATIVE=1500 : HUMIDITY=0
GAIN STOVES
CONVECTIVE=10000 : RADIATIVE=5000 : HUMIDITY=0.1
GAIN FREEZER
CONVECTIVE=1500 : RADIATIVE=0 : HUMIDITY=0
*----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* C o m f o r t
*----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* I n f i l t r a t i o n
*----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
INFILTRATION SOUTH
AIRCHANGE=SCHEDULE 0.03*CUSTOMERS+0.5
INFILTRATION NORTH
AIRCHANGE=0.5
*----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* V e n t i l a t i o n
*----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
VENTILATION KITCHEN
TEMPERATURE=INPUT 1*T_IN_KITCH
AIRCHANGE=INPUT 0.005*M_DOT_KITCH
HUMIDITY=INPUT 1*RH_IN_KITCH
VENTILATION DINING
TEMPERATURE=INPUT 1*T_IN_DINING
AIRCHANGE=INPUT 0.0025*M_DOT_DINING
HUMIDITY=INPUT 1*RH_IN_DINING
*----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* C o o l i n g
*----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
COOLING KITCHEN
ON=26
POWER=50000
HUMIDITY=100
*----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* H e a t i n g
*----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
HEATING HEATER
ON=SCHEDULE 5*OCCUPANCY+15
POWER=50000
HUMIDITY=0
RRAD=0
*
*----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e s
*----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONES DINING KITCHEN STORAGE
*----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* O r i e n t a t i o n s
*----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
HEMISPHERE NORTHERN
ORIENTATIONS NORTH SOUTH EAST WEST HORIZONTAL
*
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
BUILDING
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
*
*----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e DINING / A i r n o d e DINING
*----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE DINING
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL : FSOLAIR=0
AIRNODE DINING
WALL =OUTSIDE : SURF= 1 : AREA= 35 : EXTERNAL : ORI=SOUTH : FSKY=0.5
WINDOW=DOUBLE : SURF= 2 : AREA= 10 : EXTERNAL : ORI=SOUTH : FSKY=0.5
WALL =OUTSIDE : SURF= 3 : AREA= 35 : EXTERNAL : ORI=WEST : FSKY=0.5
WALL =OUTSIDE : SURF= 4 : AREA= 35 : EXTERNAL : ORI=EAST : FSKY=0.5
WALL =INSIDE : SURF= 5 : AREA= 22.5 : INTERNAL
WALL =INSIDE : SURF= 6 : AREA= 22.5 : ADJACENT=STORAGE : ADJ_SURF=16 : FRONT
WALL =FLOOR : SURF= 7 : AREA= 112.5 : BOUNDARY=10
WALL =ROOF : SURF= 8 : AREA= 112.5 : EXTERNAL : ORI=HORIZONTAL : FSKY=1
WALL =INSIDE : SURF= 9 : AREA= 22.5 : ADJACENT=KITCHEN : ADJ_SURF=10 : FRONT
REGIME
GAIN = PEOPLE : SCALE= SCHEDULE 5*CUSTOMERS : GEOPOS= 0
GAIN = LIGHTS : SCALE= SCHEDULE 2*OCCUPANCY : GEOPOS= 0
INFILTRATION= SOUTH
VENTILATION = DINING
CAPACITANCE = 500 : VOLUME= 337.5 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e KITCHEN / A i r n o d e KITCHEN
*----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE KITCHEN
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL : FSOLAIR=0
AIRNODE KITCHEN
WALL =INSIDE : SURF= 10 : AREA= 22.5 : ADJACENT=DINING : ADJ_SURF=9 : BACK : COUPL=SCHEDULE 2.5*CUSTOMERS
WALL =OUTSIDE : SURF= 11 : AREA= 22.5 : EXTERNAL : ORI=WEST : FSKY=0.5
WALL =OUTSIDE : SURF= 12 : AREA= 22.5 : EXTERNAL : ORI=NORTH : FSKY=0.5
WALL =INSIDE : SURF= 13 : AREA= 22.5 : ADJACENT=STORAGE : ADJ_SURF=17 : BACK
WALL =FLOOR : SURF= 14 : AREA= 56.25 : BOUNDARY=10
WALL =ROOF : SURF= 15 : AREA= 56.25 : EXTERNAL : ORI=HORIZONTAL : FSKY=1
REGIME
GAIN = PEOPLE : SCALE= SCHEDULE 0.5*CUSTOMERS : GEOPOS= 0
GAIN = LIGHTS : SCALE= SCHEDULE 1*OCCUPANCY : GEOPOS= 0
GAIN = STOVES : SCALE= SCHEDULE 1*OCCUPANCY : GEOPOS= 0
INFILTRATION= NORTH
VENTILATION = KITCHEN
CAPACITANCE = 250 : VOLUME= 168.75 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e STORAGE / A i r n o d e STORAGE
*----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE STORAGE
RADIATIONMODE
BEAM=STANDARD : DIFFUSE=STANDARD : LONGWAVE=STANDARD : GEOMODE=MANUAL : FSOLAIR=0
AIRNODE STORAGE
WALL =INSIDE : SURF= 16 : AREA= 22.5 : ADJACENT=DINING : ADJ_SURF=6 : BACK
WALL =INSIDE : SURF= 17 : AREA= 22.5 : ADJACENT=KITCHEN : ADJ_SURF=13 : FRONT
WALL =OUTSIDE : SURF= 18 : AREA= 22.5 : EXTERNAL : ORI=NORTH : FSKY=0.5
WALL =OUTSIDE : SURF= 19 : AREA= 22.5 : EXTERNAL : ORI=EAST : FSKY=0.5
WALL =FLOOR : SURF= 20 : AREA= 56.25 : BOUNDARY=10
WALL =ROOF : SURF= 21 : AREA= 56.25 : EXTERNAL : ORI=HORIZONTAL : FSKY=1
REGIME
GAIN = FREEZER : SCALE= 1 : GEOPOS= 0
INFILTRATION= NORTH
CAPACITANCE = 250 : VOLUME= 168.75 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* O u t p u t s
*----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
OUTPUTS
TRANSFER : TIMEBASE=1.000
AIRNODES = DINING KITCHEN STORAGE
NTYPES = 1 : TAIR - air temperature of airnode
= 2 : QSENS - sensible energy demand of airnode, heating(-), cooling(+)
= 3 : QCSURF - total convection to air from all surfaces within airnode (incl. internal shading)
= 4 : QINF - sensible infiltration energy gain of airnode
= 5 : QVENT - sensible ventilation energy gain of airnode
= 6 : QCOUP - sensible coupling energy gain of airnode
= 7 : QGCONV - internal convective gains of airnode
= 8 : DQAIR - change in internal sensible energy of airnode air since beginning of simulation
= 9 : RELHUM - relativ humidity of airnode air
AIRNODES = DINING
NTYPES = 17 : SURF = 1, 3, 4, 5, 6, 7, 8, 9, 2, : TSI - inside surface temperature
*----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* E n d
*----------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
END
_EXTENSION_WINPOOL_START_
WINDOW 4.1 DOE-2 Data File : Multi Band Calculation
Unit System : SI
Name : TRNSYS 15 WINDOW LIB
Desc : Waermeschutzglas,Ar, 1.4 71/59
Window ID : 2001
Tilt : 90.0
Glazings : 2
Frame : 11 2.270
Spacer : 1 Class1 2.330 -0.010 0.138
Total Height: 1219.2 mm
Total Width : 914.4 mm
Glass Height: 1079.5 mm
Glass Width : 774.7 mm
Mullion : None
Gap Thick Cond dCond Vis dVis Dens dDens Pr dPr
1 Argon 16.0 0.01620 5.000 2.110 6.300 1.780 -0.0060 0.680 0.00066
2 0 0 0 0 0 0 0 0 0
3 0 0 0 0 0 0 0 0 0
4 0 0 0 0 0 0 0 0 0
5 0 0 0 0 0 0 0 0 0
Angle 0 10 20 30 40 50 60 70 80 90 Hemis
Tsol 0.426 0.428 0.422 0.413 0.402 0.380 0.333 0.244 0.113 0.000 0.354
Abs1 0.118 0.118 0.120 0.123 0.129 0.135 0.142 0.149 0.149 0.000 0.132
Abs2 0.190 0.192 0.198 0.201 0.200 0.199 0.199 0.185 0.117 0.000 0.191
Abs3 0 0 0 0 0 0 0 0 0 0 0
Abs4 0 0 0 0 0 0 0 0 0 0 0
Abs5 0 0 0 0 0 0 0 0 0 0 0
Abs6 0 0 0 0 0 0 0 0 0 0 0
Rfsol 0.266 0.262 0.260 0.262 0.269 0.286 0.326 0.422 0.621 1.000 0.314
Rbsol 0.215 0.209 0.207 0.210 0.219 0.237 0.272 0.356 0.560 0.999 0.260
Tvis 0.706 0.710 0.701 0.688 0.670 0.635 0.556 0.403 0.188 0.000 0.590
Rfvis 0.121 0.115 0.114 0.118 0.132 0.163 0.228 0.376 0.649 1.000 0.203
Rbvis 0.103 0.096 0.093 0.096 0.108 0.132 0.179 0.286 0.520 0.999 0.162
SHGC 0.589 0.593 0.591 0.586 0.574 0.551 0.505 0.405 0.218 0.000 0.518
SC: 0.55
Layer ID# 9052 9065 0 0 0 0
Tir 0.000 0.000 0 0 0 0
Emis F 0.840 0.140 0 0 0 0
Emis B 0.840 0.840 0 0 0 0
Thickness(mm) 4.0 4.0 0 0 0 0
Cond(W/m2-C ) 225.0 225.0 0 0 0 0
Spectral File None None None None None None
Overall and Center of Glass Ig U-values (W/m2-C)
Outdoor Temperature -17.8 C 15.6 C 26.7 C 37.8 C
Solar WdSpd hcout hrout hin
(W/m2) (m/s) (W/m2-C)
0 0.00 12.25 3.25 7.62 1.54 1.54 1.31 1.31 1.35 1.35 1.47 1.47
0 6.71 25.47 3.21 7.64 1.62 1.62 1.36 1.36 1.40 1.40 1.53 1.53
783 0.00 12.25 3.39 7.99 1.69 1.69 1.54 1.54 1.51 1.51 1.54 1.54
783 6.71 25.47 3.30 7.81 1.79 1.79 1.63 1.63 1.58 1.58 1.59 1.59
*** END OF LIBRARY ***
***************************************************************************************************
*WinID Description Design U-Value g-value T-sol Rf-sol T-vis
***************************************************************************************************
2001 Waermeschutzglas,Ar, 1.4 71/59 4/16/4 1.4 0.589 0.426 0.266 0.706
_EXTENSION_WINPOOL_END_
_EXTENSION_BuildingGeometry_START_
_EXTENSION_BuildingGeometry_END_
_EXTENSION_VirtualSurfaceGeometry_START_
_EXTENSION_VirtualSurfaceGeometry_END_
_EXTENSION_ExternalShadingGeometry_START_
_EXTENSION_ExternalShadingGeometry_END_
_EXTENSION_GeoPositionGeometry_START_
_EXTENSION_GeoPositionGeometry_END_