[TRNSYS-users] Heat Recovery ventilation system
Jeff Thornton
thornton at tess-inc.com
Fri Oct 12 10:08:55 PDT 2012
<Do you mean we must buy TESS HVAC Library for TRNSYS?
Is there no
other methods to model exhaust air/fresh
air Heat Recovery Ventilation
System in Simulation Studio? E.g. using Equation or other component/Type
in Simulation studio?>
You can use a sensible heat exchanger model and
a series of equations and Type 33 psychrometrics models - but this gets
pretty tricky - especially if condensation occurs. Nothing is horribly
difficult in modeling these systems but using a model which accounts for
all of the possibilities will make it a lot easier. Good luck with your
study!
Jeff
---
Jeff Thornton
_President - TESS LLC_
_22 N.
Carroll Street, Madison WI USA 53703_
_Office: (608) 274-2577 Fax:
(608) 278-1475_
_www.tess-inc.com_
_E-Mail: thornton at tess-inc.com_
On 10/12/2012 4:13 am, 王洋 wrote:
> Dear Jeff Thornton,
>
> Many
thanks for your reply!
>
> Do you mean we must buy TESS HVAC Library
for TRNSYS?
> Is there no other methods to model exhaust air/fresh
> air
Heat Recovery Ventilation System in Simulation Studio? E.g. using
Equation or other component/Type in Simulation studio?
>
> Many thanks
in advance!
> Br.
>
> wang
>
>> Today's Topics:
>>
>> 1. Re: Heat
Recovery ventilation system (Jeff Thornton)
>>
>> ---------- 已转发邮件
----------
>> From: Jeff Thornton <thornton at tess-inc.com [54]>
>> To:
<trnsys-users at cae.wisc.edu [55]>
>> Cc:
>> Date: Thu, 11 Oct 2012
12:09:33 -0500
>> Subject: Re: [TRNSYS-users] Heat Recovery ventilation
system
>>
>> There are several heat recovery models in the TESS HVAC
Library for TRNSYS. The general descriptions of these models may be
downloaded from www.TRNSYS.com [56] by following the TESS Libraries
link.
>>
>> 1. Modifying connection line properties ? (Santeri
Siren)
>> 2. Re: Modifying connection line properties ? (Angel
Carrera)
>> 3. Re: Fwd: Converging error (??)
>>
>> ---------- 已转发邮件
----------
>> From: Santeri Siren <santeri.siren1 at gmail.com [57]>
>> To:
"trnsys käyttäjät" <trnsys-users at cae.wisc.edu [58]>
>> Cc:
>> Date:
Wed, 10 Oct 2012 12:46:29 +0300
>> Subject: [TRNSYS-users] Modifying
connection line properties ?
>> Dear users,
>>
>> is there a way to
modify the properties (e.g. change color or weight) of multiple
connection lines between components at the same time. It takes a lot of
time to change line properties one at a time.
>>
>> best regards,
>>
>> Santeri Siren
>>
>> ---------- 已转发邮件 ----------
>> From: Angel
Carrera <angel.carrera at aiguasol.coop [59]>
>> To: Santeri Siren
<santeri.siren1 at gmail.com [60]>
>> Cc: "trnsys käyttäjät"
<trnsys-users at cae.wisc.edu [61]>
>> Date: Wed, 10 Oct 2012 12:08:48
+0200
>> Subject: Re: [TRNSYS-users] Modifying connection line
properties ?
>>
>> Dear Santeri,
>>
>> right-click on a connection
with the style you wish to copy and choose and choose "copy style".
Them, you can copy this to another line just right-clicking on it and
selecting "apply style"
>>
>> Angel
>>
>> 2012/10/10 Santeri Siren
<santeri.siren1 at gmail.com [62]>
>>
>>> Dear users,
>>>
>>> is there a
way to modify the properties (e.g. change color or weight) of multiple
connection lines between components at the same time. It takes a lot of
time to change line properties one at a time.
>>>
>>> best
regards,
>>>
>>> Santeri Siren
>>>
>>>
_______________________________________________
>>> TRNSYS-users mailing
list
>>> TRNSYS-users at cae.wisc.edu [1]
>>>
https://mailman.cae.wisc.edu/listinfo/trnsys-users [2]
>>
>> --
>>
NGEL CARRERA
>>
>> Consultor Senior
>> Àrea tècnica
>>
>> Sistemes
Avançats d'Energia Solar Tèrmica SCCL
>> C/ Roger de Llúria, 29 3r 2a
08009 Barcelona
>> Mòbil: (+34) 663 27 66 80
>> Tel: (+34) 93 342 47 55
Ext:2015
>> Fax: (+34) 93 342 47 56
>>
>> angel.carrera at aiguasol.coop
[63]
>> http://www.aiguasol.coop [64]
>>
>> ---------- 已转发邮件
----------
>> From: 王洋 <wanghongyang1767 at gmail.com [65]>
>> To: hotline
<hotline at transsolar.com [66]>
>> Cc: trnsys-users
<trnsys-users at cae.wisc.edu [67]>
>> Date: Wed, 10 Oct 2012 13:37:23
+0200
>> Subject: Re: [TRNSYS-users] Fwd: Converging error
>> Dear
Marion,
>>
>> Many thanks for your patient reply!
>>
>> 1) I use
TRNSYS 16, there is no TSGRD in TYPE 56.
>> 2) The height over sea level
of Default is 0 m I used.
>> 3) You are right. I tried to use *.tm2
weather data, this Error disappeared! But my Userdefined weather data is
TRN/TRY weather data. Why does it result in aforementioned Errors
(Converging error by my past emails)?
>> If I must use our own TRN/TRY
weather data, how to avoid this Converging error?
>> 4) Yes, The data
reader Type 9 is placed after the building now for my simulation., Do
you mean Type 9 should be placed before the Building Type 56? Is
Better?
>>
>> Many thanks in advance!
>>
>> Br.
>>
>> wang
>>
>>
2012/10/10 hotline <hotline at transsolar.com [68]>
>>
>>> Dear Wang,
>>>
>>> there are several issues within your simulation concerning the
outside longwave exchange of external surfaces
>>>
>>> 1.) You didn't
connect TSGRD such that it is set 0 => If you have no information set it
Tamb
>>>
>>> 2.) For Sky temperature calculation with Type 69, you
forgot to enter the height above sea level.
>>>
>>> 3.) You read the
ambient temperature and the relative air humditiy from a userdefined
file by type 9
>>> instead of using the data from the weather file.
>>> This file wasn't attached, but it might be an error source
especially when interpolating incorrect data.
>>> For testing, please
use the ambient temperature and rel. humidity from the assigned weather
file throughout your simulation.
>>> Please check your userdefined data
and the outputs of Type 9 WITHOUT connecting them to TYPE 56.
>>>
>>>
4.) In addition, please check the component order. The data reader Type
9 is placed after the building.
>>>
>>> Marion
>>>
>>>
-------------------------
>>>
>>> VON: 王洋
[mailto:wanghongyang1767 at gmail.com [6]]
>>> GESENDET: Montag, 8.
Oktober 2012 15:31
>>> AN: trnsys-users at cae.wisc.edu [7]; hotline
>>>
BETREFF: Fwd: Converging error
>>>
>>> Dear Marion and TRNSYS
Users,
>>>
>>> Thanks for your reply!
>>>
>>> I checked all you
mentioned, I can't find any special/abnormal settings. Furthermore, it
runs well when the time step is 1 hour. For other steps e.g. 0.1 h, 0.2
h or 0.5 h, it appears that ERROR.
>>>
>>> Please help me have a look
at the attached project if you are free.
>>>
>>> Many thanks in
advance!
>>>
>>> br.
>>>
>>> wang
>>>
>>> ---------- Forwarded
message ----------
>>> From: 王洋 <wanghongyang1767 at gmail.com [8]>
>>>
Date: 2012/9/28
>>> Subject: Converging error
>>> To:
trnsys-users at cae.wisc.edu [9], hotline at transsolar.com [10]
>>>
>>>
---------- 已转发邮件 ----------
>>> From: "hotline" <hotline at transsolar.com
[11]>
>>> To: trnsys-users <trnsys-users at cae.wisc.edu [12]>
>>> Cc:
>>>
Date: Fri, 28 Sep 2012 12:02:00 +0200
>>> Subject: Re: [TRNSYS-users]
Converging error
>>>
>>> Wang,
>>>
>>> This problem may occur from
incorrect ambient condition settings:
>>>
>>> Please check the
following inputs of Type 56
>>>
>>> 1- TAMB
>>>
>>> 2- RELHUMAMB
>>>
>>> 3- TSKY
>>>
>>> 4- TSGRD
>>>
>>> In addition make sure
that in the BUI file the surface
>>>
>>> - outside emissitive is ≤ 1
>>>
>>> - outside convective heat transfer coefficient ist set to
reasonable value
>>>
>>> If the error presits, we need the complete
project to give further advice.
>>>
>>> Marion
>>>
>>> 2012/9/28
<trnsys-users-request at cae.wisc.edu [13]>
>>>
>>> Send TRNSYS-users
mailing list submissions to
>>> trnsys-users at cae.wisc.edu [14]
>>>
>>>
To subscribe or unsubscribe via the World Wide Web, visit
>>>
https://mailman.cae.wisc.edu/listinfo/trnsys-users [15]
>>> or, via
email, send a message with subject or body 'help' to
>>>
trnsys-users-request at cae.wisc.edu [16]
>>>
>>> You can reach the person
managing the list at
>>> trnsys-users-owner at cae.wisc.edu [17]
>>>
>>>
When replying, please edit your Subject line so it is more specific
>>>
than "Re: Contents of TRNSYS-users digest..."
>>>
>>> Today's
Topics:
>>>
>>> 1. Re: problem with iterations?? (Matt Duffy)
>>> 2.
Re: problem with iterations?? (Marion Hiller)
>>> 3. Re: Converging
error (hotline)
>>>
>>> ---------- 已转发邮件 ----------
>>> From: Matt
Duffy <duffy at tess-inc.com [18]>
>>> To: <trnsys-users at cae.wisc.edu
[19]>
>>> Cc:
>>> Date: Thu, 27 Sep 2012 12:04:24 -0500
>>> Subject:
Re: [TRNSYS-users] problem with iterations??
>>>
>>> Karol,
>>>
>>>
I noticed from your listing (*.lst) file that your working directory is
located on your computer's desktop directory. This is not recommended
due to the potential issues with the Windows OS system and write
privleges. I would first try changing your working directory to the
".MyProjects" directory or in a folder right on the "C:" drive. I am not
certain that this is the issue with the TRNEXE, but if the problem
persists, please contact your distributor, techsupport at tess-inc.com
[20].
>>>
>>> Best regards,
>>>
>>> Matt Duffy
>>>
>>> TRNSYS on
Facebook [21]
>>>
>>> On 2012-09-27 03:46, Karol Bandurski wrote:
>>>
>>>> Dear All,
>>>>
>>>> I try to simulate dwelling with natural
ventilation. I set some algorithm for window opening and ideal heating
for colder part of year for each zone with set temperature depending on
time of day.
>>>>
>>>> When I run my yearly simulation it stop in one
moment and TRNEXE is frozen... There is even no error! Then I can only
turn off TRNEXE.
>>>>
>>>> Only think what appear (many times) in .lst
file is
>>>>
>>>> Notice: More than 6 iterations for internal
regulation HEATING/COOLING.
>>>>
>>>> I will be grateful for any
advice!
>>>>
>>>> I enclose .lst file.
>>>>
>>>> Regards,
>>>>
>>>> ------------------------------------------------
>>>>
>>>> Karol
Bandurski MSc.
>>>>
>>>> Institute of Environmental Engineering [3]
>>>>
>>>> Poznan University of Technology
>>>>
>>>>
www.ee.put.poznan.pl [4]
>>>>
>>>> www.put.poznan.pl [5]
>>>
>>>
---------- 已转发邮件 ----------
>>> From: "Marion Hiller"
<hiller at transsolar.com [22]>
>>> To: "karol.bandurski"
<karol.bandurski at put.poznan.pl [23]>
>>> Cc: trnsys-users
<trnsys-users at cae.wisc.edu [24]>
>>> Date: Fri, 28 Sep 2012 08:53:53
+0200
>>> Subject: Re: [TRNSYS-users] problem with iterations??
>>>
>>> Karol,
>>>
>>> In general the notice has nothing to do with a
frozen TRNEXE.exe,
>>>
>>> it is just an information.
>>>
>>> The
message indicates that the internal controller for turning on the
>>>
>>> integrated heating/cooling has convergence problems and a deadband
is applied to promote convergence.
>>>
>>> This may be the case at the
moment of turning ON or OFF something.
>>>
>>> After 6 internal
iterations a deadband is added to promote convergence.
>>>
>>> If the
convergence isn't reached after 12 iterations a warning is written to
the lst/log file.
>>>
>>> Regards,
>>>
>>> Marion
>>>
>>>
DIPL.-ING. MARION HILLER
>>> TRANSSOLAR: KLIMAENGINEERING -
TECHNOLOGIEN FR ENERGIEEFFIZIENTES BAUEN UND NUTZERKOMFORT IN GEBUDE
>>> Munich - New York - Stuttgart + 49.711.67976.0
>>>
>>> Transsolar
Energietechnik GmbH, Curiestrasse 2, 70563 Stuttgart
>>> Amtsgericht
Stuttgart - HRB 23347, Steuernummer 99073/00911, USt-IdNr.: DE152272639
>>>
>>> GESCHFTSFHRER: DIPL.ING. MATTHIAS SCHULER, DIPL.ING. THOMAS
AUER, DIPL.PHYS. STEFAN HOLST, PROF. DIPL.-ING. BLEICHER
>>>
>>>
-------------------------
>>>
>>> VON: Karol Bandurski
[mailto:karol.bandurski at put.poznan.pl [25]]
>>> GESENDET: Donnerstag,
27. September 2012 10:47
>>> AN: trnsys-users at cae.wisc.edu [26]
>>>
BETREFF: [TRNSYS-users] problem with iterations??
>>>
>>> Dear All,
>>>
>>> I try to simulate dwelling with natural ventilation. I set
some algorithm for window opening and ideal heating for colder part of
year for each zone with set temperature depending on time of day.
>>>
>>> When I run my yearly simulation it stop in one moment and TRNEXE is
frozen... There is even no error! Then I can only turn off TRNEXE.
>>>
>>> Only think what appear (many times) in .lst file is
>>>
>>>
Notice: More than 6 iterations for internal regulation HEATING/COOLING.
>>>
>>> I will be grateful for any advice!
>>>
>>> I enclose .lst
file.
>>>
>>> Regards,
>>>
>>>
------------------------------------------------
>>>
>>> Karol
Bandurski MSc.
>>>
>>> Institute of Environmental Engineering [27]
>>>
>>> Poznan University of Technology
>>>
>>> www.ee.put.poznan.pl
[28]
>>>
>>> www.put.poznan.pl [29]
>>>
>>> ---------- 已转发邮件
----------
>>> From: "hotline" <hotline at transsolar.com [30]>
>>> To:
trnsys-users <trnsys-users at cae.wisc.edu [31]>
>>> Cc:
>>> Date: Fri, 28
Sep 2012 12:02:00 +0200
>>> Subject: Re: [TRNSYS-users] Converging error
>>>
>>> Wang,
>>>
>>> This problem may occur from incorrect ambient
condition settings:
>>>
>>> Please check the following inputs of Type
56
>>>
>>> 1- TAMB
>>>
>>> 2- RELHUMAMB
>>>
>>> 3- TSKY
>>>
>>>
4- TSGRD
>>>
>>> In addition make sure that in the BUI file the
surface
>>>
>>> - outside emissitive is ≤ 1
>>>
>>> - outside
convective heat transfer coefficient ist set to reasonable value
>>>
>>> If the error presits, we need the complete project to give further
advice.
>>>
>>> Marion
>>>
>>> -------------------------
>>>
>>>
VON: 王洋 [mailto:wanghongyang1767 at gmail.com [32]]
>>> GESENDET:
Donnerstag, 27. September 2012 11:49
>>> AN: trnsys-users at cae.wisc.edu
[33]
>>> BETREFF: [TRNSYS-users] Converging error
>>>
>>> Dear
all,
>>>
>>> I met a converging error when I changed simulation time
step 1 hour into 0.1 hour or 0.2 hour or 0.01 hour as follows:
>>>
>>>
*** Fatal Error at time : 3972.000000
>>> Generated by Unit : 56
>>>
Generated by Type : 56
>>> Message : outside temperature of 2(external)
wall in zone 1at time 3972.00 not converged!
>>>
>>> Please tell me
some possible solutions for that if you know. The attached is its
Listing File.
>>>
>>> Many thanks in advance!
>>> Br.
>>>
>>> wang
>>>
>>> 2012/9/27 <trnsys-users-request at cae.wisc.edu [34]>
>>>
>>> Send
TRNSYS-users mailing list submissions to
>>> trnsys-users at cae.wisc.edu
[35]
>>>
>>> To subscribe or unsubscribe via the World Wide Web,
visit
>>> https://mailman.cae.wisc.edu/listinfo/trnsys-users [36]
>>>
or, via email, send a message with subject or body 'help' to
>>>
trnsys-users-request at cae.wisc.edu [37]
>>>
>>> You can reach the person
managing the list at
>>> trnsys-users-owner at cae.wisc.edu [38]
>>>
>>>
When replying, please edit your Subject line so it is more specific
>>>
than "Re: Contents of TRNSYS-users digest..."
>>>
>>> Today's
Topics:
>>>
>>> 1. Doctoral Fellowships at TERI University, India (R.K.
Singh)
>>> 2. problem with iterations?? (Karol Bandurski)
>>>
>>>
---------- 已转发邮件 ----------
>>> From: "R.K. Singh"
<singh.ramkishore at gmail.com [39]>
>>> To: TRNSYS-users at cae.wisc.edu
[40]
>>> Cc:
>>> Date: Thu, 27 Sep 2012 10:04:34 +0530
>>> Subject:
[TRNSYS-users] Doctoral Fellowships at TERI University, India
>>>
>>>
TERI University is currently inviting applications for Doctoral
programmes in Bioresources/Biotechnology;Natural Resource Management,
Energy and Environment and Regulatory and Policy studies for semester
starting january 2013. A range of scholarship opportunities are also
available for the students in specific areas, the details of which can
be accessed through the following link.
>>>
>>>
http://teriuniversity.ac.in/index.php?option=com_content&view=article&id=54
[41]
>>>
>>> The last date for application is October 31st, 2012. The
details regarding fee, eligibility and other requirements can be
accessed through
http://teriuniversity.ac.in/index.php?option=com_program [42]
>>>
>>>
For any further details please get in touch with Dr. Sapna A Narula,
Associate Professor sapna.narula at teriuniversity.ac.in [43].
>>>
>>>
***********************************************
>>> Dr. Ramkishore
Singh
>>> Department of Energy & Environment
>>> TERI University
>>>
Tel: 91-11-26122222, Ext. 1302
>>> Fax: 91-11-26122874
>>> Web:
www.teriuniversity.ac.in [44]
>>>
***********************************************
>>>
>>> ----------
已转发邮件 ----------
>>> From: "Karol Bandurski"
<karol.bandurski at put.poznan.pl [45]>
>>> To: <trnsys-users at cae.wisc.edu
[46]>
>>> Cc:
>>> Date: Thu, 27 Sep 2012 10:46:49 +0200
>>> Subject:
[TRNSYS-users] problem with iterations??
>>>
>>> Dear All,
>>>
>>> I
try to simulate dwelling with natural ventilation. I set some algorithm
for window opening and ideal heating for colder part of year for each
zone with set temperature depending on time of day.
>>>
>>> When I run
my yearly simulation it stop in one moment and TRNEXE is frozen... There
is even no error! Then I can only turn off TRNEXE.
>>>
>>> Only think
what appear (many times) in .lst file is
>>>
>>> Notice: More than 6
iterations for internal regulation HEATING/COOLING.
>>>
>>> I will be
grateful for any advice!
>>>
>>> I enclose .lst file.
>>>
>>>
Regards,
>>>
>>> ------------------------------------------------
>>>
>>> Karol Bandurski MSc.
>>>
>>> Institute of Environmental
Engineering [47]
>>>
>>> Poznan University of Technology
>>>
>>>
www.ee.put.poznan.pl [48]
>>>
>>> www.put.poznan.pl [49]
>>>
>>>
_______________________________________________
>>> TRNSYS-users mailing
list
>>> TRNSYS-users at cae.wisc.edu [50]
>>>
https://mailman.cae.wisc.edu/listinfo/trnsys-users [51]
>>>
>>>
_______________________________________________
>>> TRNSYS-users mailing
list
>>> TRNSYS-users at cae.wisc.edu [52]
>>>
https://mailman.cae.wisc.edu/listinfo/trnsys-users [53]
>>
>>
_______________________________________________
>> TRNSYS-users mailing
list
>> TRNSYS-users at cae.wisc.edu [69]
>>
https://mailman.cae.wisc.edu/listinfo/trnsys-users
[70]
_______________________________________________
TRNSYS-users
mailing list
TRNSYS-users at cae.wisc.edu
[71]
https://mailman.cae.wisc.edu/listinfo/trnsys-users [72]
Links:
------
[1] mailto:TRNSYS-users at cae.wisc.edu
[2]
https://mailman.cae.wisc.edu/listinfo/trnsys-users
[3]
http://www.ee.put.poznan.pl/
[4] http://www.ee.put.poznan.pl/
[5]
http://www.put.poznan.pl/
[6] mailto:wanghongyang1767 at gmail.com
[7]
mailto:trnsys-users at cae.wisc.edu
[8]
mailto:wanghongyang1767 at gmail.com
[9]
mailto:trnsys-users at cae.wisc.edu
[10] mailto:hotline at transsolar.com
[11]
mailto:hotline at transsolar.com
[12] mailto:trnsys-users at cae.wisc.edu
[13]
mailto:trnsys-users-request at cae.wisc.edu
[14]
mailto:trnsys-users at cae.wisc.edu
[15]
https://mailman.cae.wisc.edu/listinfo/trnsys-users
[16]
mailto:trnsys-users-request at cae.wisc.edu
[17]
mailto:trnsys-users-owner at cae.wisc.edu
[18]
mailto:duffy at tess-inc.com
[19] mailto:trnsys-users at cae.wisc.edu
[20]
mailto:techsupport at tess-inc.com
[21] http://www.facebook.com/TRNSYS
[22]
mailto:hiller at transsolar.com
[23]
mailto:karol.bandurski at put.poznan.pl
[24]
mailto:trnsys-users at cae.wisc.edu
[25]
mailto:karol.bandurski at put.poznan.pl
[26]
mailto:trnsys-users at cae.wisc.edu
[27] http://www.ee.put.poznan.pl/
[28]
http://www.ee.put.poznan.pl/
[29] http://www.put.poznan.pl/
[30]
mailto:hotline at transsolar.com
[31] mailto:trnsys-users at cae.wisc.edu
[32]
mailto:wanghongyang1767 at gmail.com
[33]
mailto:trnsys-users at cae.wisc.edu
[34]
mailto:trnsys-users-request at cae.wisc.edu
[35]
mailto:trnsys-users at cae.wisc.edu
[36]
https://mailman.cae.wisc.edu/listinfo/trnsys-users
[37]
mailto:trnsys-users-request at cae.wisc.edu
[38]
mailto:trnsys-users-owner at cae.wisc.edu
[39]
mailto:singh.ramkishore at gmail.com
[40]
mailto:TRNSYS-users at cae.wisc.edu
[41]
http://teriuniversity.ac.in/index.php?option=com_content&view=article&id=54
[42]
http://teriuniversity.ac.in/index.php?option=com_program
[43]
mailto:sapna.narula at teriuniversity.ac.in
[44]
http://www.teriuniversity.ac.in
[45]
mailto:karol.bandurski at put.poznan.pl
[46]
mailto:trnsys-users at cae.wisc.edu
[47] http://www.ee.put.poznan.pl/
[48]
http://www.ee.put.poznan.pl/
[49] http://www.put.poznan.pl/
[50]
mailto:TRNSYS-users at cae.wisc.edu
[51]
https://mailman.cae.wisc.edu/listinfo/trnsys-users
[52]
mailto:TRNSYS-users at cae.wisc.edu
[53]
https://mailman.cae.wisc.edu/listinfo/trnsys-users
[54]
mailto:thornton at tess-inc.com
[55] mailto:trnsys-users at cae.wisc.edu
[56]
http://www.TRNSYS.com
[57] mailto:santeri.siren1 at gmail.com
[58]
mailto:trnsys-users at cae.wisc.edu
[59]
mailto:angel.carrera at aiguasol.coop
[60]
mailto:santeri.siren1 at gmail.com
[61]
mailto:trnsys-users at cae.wisc.edu
[62]
mailto:santeri.siren1 at gmail.com
[63]
mailto:angel.carrera at aiguasol.coop
[64] http://www.aiguasol.coop/
[65]
mailto:wanghongyang1767 at gmail.com
[66]
mailto:hotline at transsolar.com
[67] mailto:trnsys-users at cae.wisc.edu
[68]
mailto:hotline at transsolar.com
[69] mailto:TRNSYS-users at cae.wisc.edu
[70]
https://mailman.cae.wisc.edu/listinfo/trnsys-users
[71]
mailto:TRNSYS-users at cae.wisc.edu
[72]
https://mailman.cae.wisc.edu/listinfo/trnsys-users
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20121012/e645874f/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: blocked.gif
Type: image/gif
Size: 118 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20121012/e645874f/attachment-0005.gif>
More information about the TRNSYS-users
mailing list