[TRNSYS-users] Heat Recovery ventilation system

王洋 wanghongyang1767 at gmail.com
Tue Oct 23 03:03:58 PDT 2012


Dear all,

Could anyone please pass me some relative examples for Heat Recovery
ventilation system using a sensible heat exchanger model and a series of
equations and Type 33 psychrometrics models? Or please tell me where could
I find some relative examples?


Since I can not find any Examples from TRNSYS/Examples file for that. For a
beginner, it is too difficult if no examples.

Many thanks in advance!

Br.
wang

2012/10/19 王洋 <wanghongyang1767 at gmail.com>

>
>
> 2012/10/15 王洋 <wanghongyang1767 at gmail.com>
>
>>
>>
>>
>>
>> 2012/10/15 王洋 <wanghongyang1767 at gmail.com>
>>
>>> Dear Jeff,
>>>
>>>
>>> Many thanks for your reply!
>>>
>>> You can use a sensible heat exchanger model and a series of equations
>>> and Type 33 psychrometrics models - but this gets pretty tricky -
>>> especially if condensation occurs.  Nothing is horribly difficult in
>>> modeling these systems but using a model which accounts for all of the
>>> possibilities will make it a lot easier.
>>>
>>> Could you please pass me some relative examples for Heat Recovery
>>> ventilation system using a sensible heat exchanger model and a series
>>> of equations and Type 33 psychrometrics models? Or please tell me where
>>> could I find some relative examples?
>>>
>>> Since I can not find any Examples from TRNSYS/Examples file for that.
>>> For a beginner, it is too difficult if no examples.
>>>
>>> Many thanks in advance!
>>> Br.
>>>
>>> wang
>>>
>>>
>>>
>>> 2012/10/12 <trnsys-users-request at cae.wisc.edu>
>>>
>>>> Send TRNSYS-users mailing list submissions to
>>>>         trnsys-users at cae.wisc.edu
>>>>
>>>> To subscribe or unsubscribe via the World Wide Web, visit
>>>>         https://mailman.cae.wisc.edu/listinfo/trnsys-users
>>>> or, via email, send a message with subject or body 'help' to
>>>>         trnsys-users-request at cae.wisc.edu
>>>>
>>>> You can reach the person managing the list at
>>>>         trnsys-users-owner at cae.wisc.edu
>>>>
>>>> When replying, please edit your Subject line so it is more specific
>>>> than "Re: Contents of TRNSYS-users digest..."
>>>>
>>>> Today's Topics:
>>>>
>>>>    1. Re: Heat Recovery ventilation system (Jeff Thornton)
>>>>
>>>>
>>>> ---------- 已转发邮件 ----------
>>>> From: Jeff Thornton <thornton at tess-inc.com>
>>>> To: <trnsys-users at cae.wisc.edu>
>>>> Cc:
>>>> Date: Fri, 12 Oct 2012 12:08:55 -0500
>>>>
>>>> Subject: Re: [TRNSYS-users] Heat Recovery ventilation system
>>>> **
>>>>
>>>> <Do you mean we must buy TESS HVAC Library for TRNSYS?
>>>>
>>>> Is there no other methods to model exhaust air/fresh
>>>> air Heat Recovery Ventilation System in Simulation Studio? E.g. using
>>>> Equation or other component/Type in Simulation studio?>
>>>>
>>>>
>>>>
>>>> You can use a sensible heat exchanger model and a series of equations
>>>> and Type 33 psychrometrics models - but this gets pretty tricky -
>>>> especially if condensation occurs.  Nothing is horribly difficult in
>>>> modeling these systems but using a model which accounts for all of the
>>>> possibilities will make it a lot easier.  Good luck with your study!
>>>>
>>>>
>>>>
>>>> Jeff
>>>>
>>>>
>>>>
>>>> ---
>>>>
>>>> Jeff Thornton
>>>>
>>>> *President - TESS LLC*
>>>>
>>>> *22 N. Carroll Street, Madison WI USA 53703*
>>>>
>>>> *Office: (608) 274-2577  Fax: (608) 278-1475*
>>>>
>>>> *www.tess-inc.com*
>>>>
>>>> *E-Mail: thornton at tess-inc.com*
>>>>
>>>>
>>>>
>>>> On 10/12/2012 4:13 am, 王洋 wrote:
>>>>
>>>>   Dear Jeff Thornton,
>>>>
>>>> Many thanks for your reply!
>>>>
>>>> Do you mean we must buy TESS HVAC Library for TRNSYS?
>>>> Is there no other methods to model exhaust air/fresh
>>>> air Heat Recovery Ventilation System in Simulation Studio? E.g. using Equation
>>>> or other component/Type in Simulation studio?
>>>>
>>>> Many thanks in advance!
>>>> Br.
>>>>
>>>> wang
>>>>
>>>>>
>>>>> Today's Topics:
>>>>>
>>>>>    1. Re: Heat Recovery ventilation system (Jeff Thornton)
>>>>>
>>>>>
>>>>> ---------- 已转发邮件 ----------
>>>>> From: Jeff Thornton <thornton at tess-inc.com>
>>>>> To: <trnsys-users at cae.wisc.edu>
>>>>> Cc:
>>>>> Date: Thu, 11 Oct 2012 12:09:33 -0500
>>>>> Subject: Re: [TRNSYS-users] Heat Recovery ventilation system
>>>>>
>>>>> There are several heat recovery models in the TESS HVAC Library for
>>>>> TRNSYS.  The general descriptions of these models may be downloaded from
>>>>> www.TRNSYS.com by following the TESS Libraries link.
>>>>>
>>>>>
>>>>>
>>>>> *
>>>>> *
>>>>> *    1. Modifying connection line properties ? (Santeri Siren)
>>>>>    2. Re: Modifying connection line properties ? (Angel Carrera)
>>>>>    3. Re: Fwd: Converging error (??)
>>>>>
>>>>>
>>>>> ---------- 已转发邮件 ----------
>>>>> From: Santeri Siren <santeri.siren1 at gmail.com>
>>>>> To: "trnsys käyttäjät" <trnsys-users at cae.wisc.edu>
>>>>> Cc:
>>>>> Date: Wed, 10 Oct 2012 12:46:29 +0300
>>>>> Subject: [TRNSYS-users] Modifying connection line properties ?
>>>>> Dear users,
>>>>>
>>>>> is there a way to modify the properties (e.g. change color or weight)
>>>>> of multiple connection lines between components at the same time. It takes
>>>>> a lot of time to change line properties one at a time.
>>>>>
>>>>> best regards,
>>>>>
>>>>> Santeri Siren
>>>>>
>>>>>
>>>>> ---------- 已转发邮件 ----------
>>>>> From: Angel Carrera <angel.carrera at aiguasol.coop>
>>>>> To: Santeri Siren <santeri.siren1 at gmail.com>
>>>>> Cc: "trnsys käyttäjät" <trnsys-users at cae.wisc.edu>
>>>>> Date: Wed, 10 Oct 2012 12:08:48 +0200
>>>>> Subject: Re: [TRNSYS-users] Modifying connection line properties ?
>>>>>
>>>>> Dear Santeri,
>>>>>
>>>>> right-click on a connection with the style you wish to copy and choose
>>>>> and choose "copy style". Them, you can copy this to another line just
>>>>> right-clicking on it and selecting "apply style"
>>>>>
>>>>> Angel
>>>>>
>>>>> *
>>>>>
>>>>> 2012/10/10 Santeri Siren <santeri.siren1 at gmail.com>
>>>>>
>>>>>> Dear users,
>>>>>>
>>>>>> is there a way to modify the properties (e.g. change color or weight)
>>>>>> of multiple connection lines between components at the same time. It takes
>>>>>> a lot of time to change line properties one at a time.
>>>>>>
>>>>>> best regards,
>>>>>>
>>>>>> Santeri Siren
>>>>>>
>>>>>> _______________________________________________
>>>>>> TRNSYS-users mailing list
>>>>>> TRNSYS-users at cae.wisc.edu
>>>>>> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>>>>>>
>>>>>>  *
>>>>>
>>>>>
>>>>> --
>>>>> Àngel Carrera
>>>>>
>>>>> Consultor Senior
>>>>> Àrea tècnica
>>>>>
>>>>> Sistemes Avançats d'Energia Solar Tèrmica SCCL
>>>>> C/ Roger de Llúria, 29 3r 2a 08009 Barcelona
>>>>> Mòbil: (+34) 663 27 66 80
>>>>> Tel: (+34) 93 342 47 55 Ext:2015
>>>>> Fax: (+34) 93 342 47 56
>>>>>
>>>>> angel.carrera at aiguasol.coop
>>>>> http://www.aiguasol.coop
>>>>>
>>>>>
>>>>> ---------- 已转发邮件 ----------
>>>>> From: 王洋 <wanghongyang1767 at gmail.com>
>>>>> To: hotline <hotline at transsolar.com>
>>>>> Cc: trnsys-users <trnsys-users at cae.wisc.edu>
>>>>> Date: Wed, 10 Oct 2012 13:37:23 +0200
>>>>> Subject: Re: [TRNSYS-users] Fwd: Converging error
>>>>> Dear Marion,
>>>>>
>>>>> Many thanks for your patient reply!
>>>>>
>>>>> 1) I use TRNSYS 16, there is no TSGRD in TYPE 56.
>>>>> 2) The height over sea level of Default is 0 m I used.
>>>>> 3) You are right. I tried to use *.tm2 weather data, this Error
>>>>> disappeared! But my Userdefined weather data is TRN/TRY weather data.
>>>>> Why does it result in aforementioned Errors (Converging error by my past
>>>>> emails)?
>>>>> If I must use our own TRN/TRY weather data, how to avoid this
>>>>> Converging error?
>>>>> 4) Yes, The data reader Type 9 is placed after the building now for
>>>>> my simulation., Do you mean Type 9 should be placed before the
>>>>> Building Type 56? Is Better?
>>>>>
>>>>> Many thanks in advance!
>>>>>
>>>>> Br.
>>>>>
>>>>> wang
>>>>>
>>>>> *
>>>>> 2012/10/10 hotline <hotline at transsolar.com>
>>>>>
>>>>>>     Dear Wang,
>>>>>>
>>>>>>
>>>>>>
>>>>>> there are several issues within your simulation concerning the
>>>>>> outside longwave exchange of external surfaces
>>>>>>
>>>>>>
>>>>>>
>>>>>> 1.)     You didn’t connect TSGRD such that it is set 0 =>  If you
>>>>>> have no information set it Tamb
>>>>>>
>>>>>> 2.)     For Sky temperature calculation with Type 69, you forgot to
>>>>>> enter the height above sea level.
>>>>>>
>>>>>> 3.)     You read the ambient temperature and the relative air
>>>>>> humditiy from a userdefined file by type 9
>>>>>> instead of using the data from the weather file.
>>>>>> This file wasn’t attached, but it might be an error source especially
>>>>>> when interpolating incorrect data.
>>>>>> For testing, please use the ambient temperature and rel. humidity
>>>>>> from the assigned weather file throughout your simulation.
>>>>>> Please check your userdefined data and the outputs of Type 9 WITHOUT
>>>>>> connecting them to TYPE 56.
>>>>>>
>>>>>> 4.)     In addition, please check the component order. The data
>>>>>> reader Type 9 is placed after the building.
>>>>>>
>>>>>>
>>>>>>
>>>>>> Marion
>>>>>>
>>>>>>
>>>>>>
>>>>>>
>>>>>> ------------------------------
>>>>>>
>>>>>>
>>>>>> *Von:* 王洋 [mailto:wanghongyang1767 at gmail.com]
>>>>>> *Gesendet:* Montag, 8. Oktober 2012 15:31
>>>>>> *An:* trnsys-users at cae.wisc.edu; hotline
>>>>>> *Betreff:* Fwd: Converging error
>>>>>>
>>>>>>
>>>>>>
>>>>>>
>>>>>>
>>>>>> Dear Marion and TRNSYS Users,
>>>>>>
>>>>>> Thanks for your reply!
>>>>>>
>>>>>> I checked all you mentioned, I can't find any special/abnormal
>>>>>> settings. Furthermore, it runs well when the time step is 1 hour. For other
>>>>>> steps e.g. 0.1 h, 0.2 h or 0.5 h, it appears that ERROR.
>>>>>>
>>>>>> Please help me have a look at the attached project if you are free.
>>>>>>
>>>>>> Many thanks in advance!
>>>>>>
>>>>>> br.
>>>>>>
>>>>>> wang
>>>>>>
>>>>>> ---------- Forwarded message ----------
>>>>>> From: *王洋* <wanghongyang1767 at gmail.com>
>>>>>> Date: 2012/9/28
>>>>>> Subject: Converging error
>>>>>> To: trnsys-users at cae.wisc.edu, hotline at transsolar.com
>>>>>>
>>>>>>
>>>>>>
>>>>>> ---------- 已转发邮件 ----------
>>>>>> From: "hotline" <hotline at transsolar.com>
>>>>>> To: trnsys-users <trnsys-users at cae.wisc.edu>
>>>>>> Cc:
>>>>>> Date: Fri, 28 Sep 2012 12:02:00 +0200
>>>>>> Subject: Re: [TRNSYS-users] Converging error
>>>>>>
>>>>>> Wang,
>>>>>>
>>>>>>
>>>>>>
>>>>>> This problem may occur from incorrect ambient condition settings:
>>>>>>
>>>>>> Please check the following inputs of Type 56
>>>>>>
>>>>>> 1- TAMB
>>>>>>
>>>>>> 2- RELHUMAMB
>>>>>>
>>>>>> 3- TSKY
>>>>>>
>>>>>> 4- TSGRD
>>>>>>
>>>>>>
>>>>>>
>>>>>> In addition make sure that in the BUI file the surface
>>>>>>
>>>>>> -         outside emissitive is ≤ 1
>>>>>>
>>>>>> -         outside convective heat transfer coefficient ist set to
>>>>>> reasonable value
>>>>>>
>>>>>>
>>>>>>
>>>>>> If the error presits, we need the complete project to give further
>>>>>> advice.
>>>>>>
>>>>>>
>>>>>>
>>>>>>
>>>>>>
>>>>>> Marion
>>>>>>
>>>>>> 2012/9/28 <trnsys-users-request at cae.wisc.edu>
>>>>>>
>>>>>> Send TRNSYS-users mailing list submissions to
>>>>>>         trnsys-users at cae.wisc.edu
>>>>>>
>>>>>> To subscribe or unsubscribe via the World Wide Web, visit
>>>>>>         https://mailman.cae.wisc.edu/listinfo/trnsys-users
>>>>>> or, via email, send a message with subject or body 'help' to
>>>>>>         trnsys-users-request at cae.wisc.edu
>>>>>>
>>>>>> You can reach the person managing the list at
>>>>>>         trnsys-users-owner at cae.wisc.edu
>>>>>>
>>>>>> When replying, please edit your Subject line so it is more specific
>>>>>> than "Re: Contents of TRNSYS-users digest..."
>>>>>>
>>>>>> Today's Topics:
>>>>>>
>>>>>>    1. Re: problem with iterations?? (Matt Duffy)
>>>>>>    2. Re: problem with iterations?? (Marion Hiller)
>>>>>>    3. Re: Converging error (hotline)
>>>>>>
>>>>>>
>>>>>> ---------- 已转发邮件 ----------
>>>>>> From: Matt Duffy <duffy at tess-inc.com>
>>>>>> To: <trnsys-users at cae.wisc.edu>
>>>>>> Cc:
>>>>>> Date: Thu, 27 Sep 2012 12:04:24 -0500
>>>>>> Subject: Re: [TRNSYS-users] problem with iterations??
>>>>>>
>>>>>> Karol,
>>>>>>
>>>>>>
>>>>>>
>>>>>> I noticed from your listing (*.lst) file that your working directory
>>>>>> is located on your computer's desktop directory. This is not recommended
>>>>>> due to the potential issues with the Windows OS system and write privleges.
>>>>>> I would first try changing your working directory to the ".\MyProjects"
>>>>>> directory or in a folder right on the "C:" drive. I am not certain that
>>>>>> this is the issue with the TRNEXE, but if the problem persists, please
>>>>>> contact your distributor, techsupport at tess-inc.com.
>>>>>>
>>>>>>
>>>>>>
>>>>>> Best regards,
>>>>>>
>>>>>>
>>>>>> Matt Duffy
>>>>>>
>>>>>>
>>>>>>
>>>>>> TRNSYS on Facebook <http://www.facebook.com/TRNSYS>
>>>>>>
>>>>>> On 2012-09-27 03:46, Karol Bandurski wrote:
>>>>>>
>>>>>>   Dear All,
>>>>>>
>>>>>>
>>>>>>
>>>>>> I try to simulate dwelling with natural ventilation. I set some
>>>>>> algorithm for window opening and ideal heating for colder part of year for
>>>>>> each zone with set temperature depending on time of day.
>>>>>>
>>>>>>
>>>>>>
>>>>>> When I run my yearly simulation it stop in one moment and TRNEXE is
>>>>>> frozen... There is even no error! Then I can only turn off TRNEXE.
>>>>>>
>>>>>>
>>>>>>
>>>>>> Only think what appear (many times) in .lst file is
>>>>>>
>>>>>>
>>>>>>
>>>>>> Notice: More than 6 iterations for internal regulation
>>>>>> HEATING/COOLING.
>>>>>>
>>>>>>
>>>>>>
>>>>>> I will be grateful for any advice!
>>>>>>
>>>>>>
>>>>>>
>>>>>> I enclose .lst file.
>>>>>>
>>>>>>
>>>>>>
>>>>>> Regards,
>>>>>>
>>>>>>
>>>>>>
>>>>>> ------------------------------------------------
>>>>>>
>>>>>> Karol Bandurski MSc.
>>>>>>
>>>>>> Institute of Environmental Engineering <http://www.ee.put.poznan.pl/>
>>>>>>
>>>>>> Poznan University of Technology
>>>>>>
>>>>>> www.ee.put.poznan.pl
>>>>>>
>>>>>> www.put.poznan.pl
>>>>>>
>>>>>>
>>>>>>
>>>>>>
>>>>>>
>>>>>> ---------- 已转发邮件 ----------
>>>>>> From: "Marion Hiller" <hiller at transsolar.com>
>>>>>> To: "karol.bandurski" <karol.bandurski at put.poznan.pl>
>>>>>> Cc: trnsys-users <trnsys-users at cae.wisc.edu>
>>>>>> Date: Fri, 28 Sep 2012 08:53:53 +0200
>>>>>> Subject: Re: [TRNSYS-users] problem with iterations??
>>>>>>
>>>>>> Karol,
>>>>>>
>>>>>>
>>>>>>
>>>>>> In general the notice has nothing to do with a frozen TRNEXE.exe,
>>>>>>
>>>>>> it is just an information.
>>>>>>
>>>>>>
>>>>>>
>>>>>> The message indicates that the internal controller for turning on the
>>>>>>
>>>>>> integrated heating/cooling has convergence problems and a deadband is
>>>>>> applied to promote convergence.
>>>>>>
>>>>>> This may be the case at the moment of turning ON or OFF something.
>>>>>>
>>>>>> After 6 internal iterations a deadband is added to promote
>>>>>> convergence.
>>>>>>
>>>>>> If the convergence isn’t reached after 12 iterations a warning is
>>>>>> written to the lst/log file.
>>>>>>
>>>>>>
>>>>>>
>>>>>> Regards,
>>>>>>
>>>>>>
>>>>>>
>>>>>> Marion
>>>>>>
>>>>>>
>>>>>>
>>>>>>
>>>>>>
>>>>>> *Dipl.-Ing. **Marion Hiller **
>>>>>> **TRANSSOLAR: KlimaEngineering - Technologien für energieeffizientes
>>>>>> Bauen und Nutzerkomfort in Gebäude **
>>>>>> Munich - New York - Stuttgart + 49.711.67976.0
>>>>>>
>>>>>> **Transsolar Energietechnik GmbH, Curiestrasse 2, 70563 Stuttgart
>>>>>> Amtsgericht Stuttgart - HRB 23347, Steuernummer
>>>>>> 99073/00911, USt-IdNr.: DE152272639*
>>>>>>
>>>>>> *Geschäftsführer: Dipl.Ing. Matthias Schuler, Dipl.Ing. Thomas Auer,
>>>>>> Dipl.Phys. Stefan Holst, Prof. Dipl.-Ing. Bleicher *
>>>>>>
>>>>>>
>>>>>>
>>>>>>
>>>>>>  ------------------------------
>>>>>>
>>>>>>
>>>>>>
>>>>>>
>>>>>> *Von:* Karol Bandurski [mailto:karol.bandurski at put.poznan.pl]
>>>>>> *Gesendet:* Donnerstag, 27. September 2012 10:47
>>>>>> *An:* trnsys-users at cae.wisc.edu
>>>>>> *Betreff:* [TRNSYS-users] problem with iterations??
>>>>>>
>>>>>>
>>>>>>
>>>>>> Dear All,
>>>>>>
>>>>>>
>>>>>>
>>>>>> I try to simulate dwelling with natural ventilation. I set some
>>>>>> algorithm for window opening and ideal heating for colder part of year for
>>>>>> each zone with set temperature depending on time of day.
>>>>>>
>>>>>>
>>>>>>
>>>>>> When I run my yearly simulation it stop in one moment and TRNEXE is
>>>>>> frozen... There is even no error! Then I can only turn off TRNEXE.
>>>>>>
>>>>>>
>>>>>>
>>>>>> Only think what appear (many times) in .lst file is
>>>>>>
>>>>>>
>>>>>>
>>>>>> Notice: More than 6 iterations for internal regulation
>>>>>> HEATING/COOLING.
>>>>>>
>>>>>>
>>>>>>
>>>>>> I will be grateful for any advice!
>>>>>>
>>>>>>
>>>>>>
>>>>>> I enclose .lst file.
>>>>>>
>>>>>>
>>>>>>
>>>>>> Regards,
>>>>>>
>>>>>>
>>>>>>
>>>>>> ------------------------------------------------
>>>>>>
>>>>>> Karol Bandurski MSc.
>>>>>>
>>>>>> Institute of Environmental Engineering <http://www.ee.put.poznan.pl/>
>>>>>>
>>>>>> Poznan University of Technology
>>>>>>
>>>>>> www.ee.put.poznan.pl
>>>>>>
>>>>>> www.put.poznan.pl
>>>>>>
>>>>>>
>>>>>>
>>>>>>
>>>>>>
>>>>>> ---------- 已转发邮件 ----------
>>>>>> From: "hotline" <hotline at transsolar.com>
>>>>>> To: trnsys-users <trnsys-users at cae.wisc.edu>
>>>>>> Cc:
>>>>>> Date: Fri, 28 Sep 2012 12:02:00 +0200
>>>>>> Subject: Re: [TRNSYS-users] Converging error
>>>>>>
>>>>>> Wang,
>>>>>>
>>>>>>
>>>>>>
>>>>>> This problem may occur from incorrect ambient condition settings:
>>>>>>
>>>>>> Please check the following inputs of Type 56
>>>>>>
>>>>>> 1- TAMB
>>>>>>
>>>>>> 2- RELHUMAMB
>>>>>>
>>>>>> 3- TSKY
>>>>>>
>>>>>> 4- TSGRD
>>>>>>
>>>>>>
>>>>>>
>>>>>> In addition make sure that in the BUI file the surface
>>>>>>
>>>>>> -         outside emissitive is ≤ 1
>>>>>>
>>>>>> -         outside convective heat transfer coefficient ist set to
>>>>>> reasonable value
>>>>>>
>>>>>>
>>>>>>
>>>>>> If the error presits, we need the complete project to give further
>>>>>> advice.
>>>>>>
>>>>>>
>>>>>>
>>>>>>
>>>>>>
>>>>>> Marion
>>>>>>   ------------------------------
>>>>>>
>>>>>>
>>>>>>
>>>>>>
>>>>>> *Von:* 王洋 [mailto:wanghongyang1767 at gmail.com]
>>>>>> *Gesendet:* Donnerstag, 27. September 2012 11:49
>>>>>> *An:* trnsys-users at cae.wisc.edu
>>>>>> *Betreff:* [TRNSYS-users] Converging error
>>>>>>
>>>>>>
>>>>>>
>>>>>> Dear all,
>>>>>>
>>>>>> I met a converging error when I changed simulation time step 1 hour
>>>>>> into 0.1 hour or 0.2 hour or 0.01 hour as follows:
>>>>>>
>>>>>> *** Fatal Error at time   :      3972.000000
>>>>>>     Generated by Unit     :    56
>>>>>>     Generated by Type     :    56
>>>>>>     Message               : outside temperature of    2(external)
>>>>>> wall in zone   1at time  3972.00 not converged!
>>>>>>
>>>>>> Please tell me some possible solutions for that if you know. The
>>>>>> attached is its Listing File.
>>>>>>
>>>>>> Many thanks in advance!
>>>>>> Br.
>>>>>>
>>>>>> wang
>>>>>>
>>>>>>  2012/9/27 <trnsys-users-request at cae.wisc.edu>
>>>>>>
>>>>>> Send TRNSYS-users mailing list submissions to
>>>>>>         trnsys-users at cae.wisc.edu
>>>>>>
>>>>>> To subscribe or unsubscribe via the World Wide Web, visit
>>>>>>         https://mailman.cae.wisc.edu/listinfo/trnsys-users
>>>>>> or, via email, send a message with subject or body 'help' to
>>>>>>         trnsys-users-request at cae.wisc.edu
>>>>>>
>>>>>> You can reach the person managing the list at
>>>>>>         trnsys-users-owner at cae.wisc.edu
>>>>>>
>>>>>> When replying, please edit your Subject line so it is more specific
>>>>>> than "Re: Contents of TRNSYS-users digest..."
>>>>>>
>>>>>> Today's Topics:
>>>>>>
>>>>>>    1. Doctoral Fellowships at TERI University, India (R.K. Singh)
>>>>>>    2. problem with iterations?? (Karol Bandurski)
>>>>>>
>>>>>>
>>>>>> ---------- 已转发邮件 ----------
>>>>>> From: "R.K. Singh" <singh.ramkishore at gmail.com>
>>>>>> To: TRNSYS-users at cae.wisc.edu
>>>>>> Cc:
>>>>>> Date: Thu, 27 Sep 2012 10:04:34 +0530
>>>>>> Subject: [TRNSYS-users] Doctoral Fellowships at TERI University,
>>>>>> India
>>>>>>
>>>>>> TERI University is currently inviting applications for Doctoral
>>>>>> programmes in  Bioresources/Biotechnology;Natural Resource Management,
>>>>>> Energy and Environment and Regulatory and Policy studies for semester
>>>>>> starting january 2013. A range of scholarship opportunities  are also
>>>>>> available  for the students in specific areas, the details of which can be
>>>>>> accessed through  the following link.
>>>>>>
>>>>>>
>>>>>> http://teriuniversity.ac.in/index.php?option=com_content&view=article&id=54
>>>>>>
>>>>>> The last date for application is October  31st, 2012. The details
>>>>>> regarding fee, eligibility and other requirements can be accessed through
>>>>>> http://teriuniversity.ac.in/index.php?option=com_program
>>>>>>
>>>>>>
>>>>>>
>>>>>> For any further details please get in touch with Dr. Sapna A Narula,
>>>>>> Associate Professor sapna.narula at teriuniversity.ac.in.
>>>>>>
>>>>>>
>>>>>>
>>>>>> ***********************************************
>>>>>> Dr. Ramkishore Singh
>>>>>> Department of Energy & Environment
>>>>>> TERI University
>>>>>> Tel: 91-11-26122222, Ext. 1302
>>>>>> Fax: 91-11-26122874
>>>>>> Web: www.teriuniversity.ac.in
>>>>>> ***********************************************
>>>>>>
>>>>>>
>>>>>>
>>>>>>
>>>>>> ---------- 已转发邮件 ----------
>>>>>> From: "Karol Bandurski" <karol.bandurski at put.poznan.pl>
>>>>>> To: <trnsys-users at cae.wisc.edu>
>>>>>> Cc:
>>>>>> Date: Thu, 27 Sep 2012 10:46:49 +0200
>>>>>> Subject: [TRNSYS-users] problem with iterations??
>>>>>>
>>>>>> Dear All,
>>>>>>
>>>>>>
>>>>>>
>>>>>> I try to simulate dwelling with natural ventilation. I set some
>>>>>> algorithm for window opening and ideal heating for colder part of year for
>>>>>> each zone with set temperature depending on time of day.
>>>>>>
>>>>>>
>>>>>>
>>>>>> When I run my yearly simulation it stop in one moment and TRNEXE is
>>>>>> frozen... There is even no error! Then I can only turn off TRNEXE.
>>>>>>
>>>>>>
>>>>>>
>>>>>> Only think what appear (many times) in .lst file is
>>>>>>
>>>>>>
>>>>>>
>>>>>> Notice: More than 6 iterations for internal regulation
>>>>>> HEATING/COOLING.
>>>>>>
>>>>>>
>>>>>>
>>>>>> I will be grateful for any advice!
>>>>>>
>>>>>>
>>>>>>
>>>>>> I enclose .lst file.
>>>>>>
>>>>>>
>>>>>>
>>>>>> Regards,
>>>>>>
>>>>>>
>>>>>>
>>>>>> ------------------------------------------------
>>>>>>
>>>>>> Karol Bandurski MSc.
>>>>>>
>>>>>> Institute of Environmental Engineering <http://www.ee.put.poznan.pl/>
>>>>>>
>>>>>> Poznan University of Technology
>>>>>>
>>>>>> www.ee.put.poznan.pl
>>>>>>
>>>>>> www.put.poznan.pl
>>>>>>
>>>>>>
>>>>>>
>>>>>>
>>>>>> _______________________________________________
>>>>>> TRNSYS-users mailing list
>>>>>> TRNSYS-users at cae.wisc.edu
>>>>>> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>>>>>>
>>>>>>
>>>>>>
>>>>>>
>>>>>> _______________________________________________
>>>>>> TRNSYS-users mailing list
>>>>>> TRNSYS-users at cae.wisc.edu
>>>>>> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>>>>>>
>>>>>>
>>>>>>
>>>>>>
>>>>>>
>>>>>  *
>>>>>
>>>>> _______________________________________________
>>>>> TRNSYS-users mailing list
>>>>> TRNSYS-users at cae.wisc.edu
>>>>> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>>>>>
>>>>> *
>>>>>
>>>>
>>>> _______________________________________________
>>>> TRNSYS-users mailing list
>>>> TRNSYS-users at cae.wisc.edu
>>>> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>>>>
>>>>
>>>>
>>>> _______________________________________________
>>>> TRNSYS-users mailing list
>>>> TRNSYS-users at cae.wisc.edu
>>>> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>>>>
>>>>
>>>
>>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20121023/74a11009/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 118 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20121023/74a11009/attachment-0001.gif>


More information about the TRNSYS-users mailing list