[TRNSYS-users] Type2b
Flynn Ciaran
ciaran.flynn at aalto.fi
Fri Oct 19 09:14:03 PDT 2012
Hello,
After having read the documentation and online help, I am still having trouble with the type 2b and I was wondering if you could please help me out. My problem is the following:
I used the example file SDHW, where the Type2b is connected as follows:
Upper limit TH = solar collector output temperature
Lower limit TL = tank to heat source temperature
Monitoring temperature TIN = tank to load temperature
Upper deadband ΔTH = 15 degrees
Lower deadband ΔTL = 0 degrees
Then I went through the documented equations (Eq. 4.1-1 to Eq.4.1-4). However in the simulation results, when I take a look at time steps 4064.25 to 4065 (as an example), I find the following:
Time step
4064.25
4064.5
4064.75
4065
(TH-TL)
-1.373
7.008
1.618
2.304
γi
0
0
0
1
γo
0
0
1
1
>From what I see, time step 4064.75 does not agree with Eq. 4.1-3 since (TH-TL) is still below the upper deadband even though the controller is turned on (it should remain off until (TH-TL) is greater than or equal to the upper deadband). Maybe I am misreading the input/output controller values?
Any help would be greatly appreciated.
Thanks,
Ciaran