Johnson,
Apologies for the delay in responding. There are a number of generic
models in TRNSYS that would suit your needs (such as Type42, or even a
simple equation). The difficulty that you face is in obtaining realistic
information from the manufacturer of the transformers, UPS, and PDU.
They should be able to give you some information about the heat
generated by their equipment under normal operating conditions,
including standby mode which you will need when the data center is
running at part load (incidentally, I have never seen this situation!
Data centers that I have run across basically use the same amount of
energy and dump the same amount of heat into the space all the time!)
Once you obtain the performance and efficiency of the equipment at
part load then you need to add a gain to the Type56 zone that represents
your data center. You can specify the gain either as a schedule in
TRNBuild or as an input.
Best,
David
On 10/8/2012 22:13, Johnson Chua wrote:
> Dear all trnsys users
> I am trying to do an electrical supply heat gain for data center
> including the electrical components such as transformer, USP and PDU.
> As the data center will be running in part load condition in different
> timing of the day. This will affect the power consumption and the heat
> gain of the electrical components.
> But I am unable to model a similar model of the efficiency for the
> transformer, USP and PDU which will account the heat gain to Data
> Center simulation. Hope that expert in trnsys will be able to provide
> me an approach of my problem as I am newbie to the Trnsys software.
> Thank you
> Regards
> Johnson
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20121016/47bcfd83/attachment-0001.htm>
More information about the TRNSYS-users
mailing list