[TRNSYS-users] Fwd: Converging error
hotline
hotline at transsolar.com
Wed Oct 10 02:37:36 PDT 2012
Dear Wang,
there are several issues within your simulation concerning the outside
longwave exchange of external surfaces
1.) You didn’t connect TSGRD such that it is set 0 => If you have
no information set it Tamb
2.) For Sky temperature calculation with Type 69, you forgot to
enter the height above sea level.
3.) You read the ambient temperature and the relative air humditiy
from a userdefined file by type 9
instead of using the data from the weather file.
This file wasn’t attached, but it might be an error source especially
when interpolating incorrect data.
For testing, please use the ambient temperature and rel. humidity from
the assigned weather file throughout your simulation.
Please check your userdefined data and the outputs of Type 9 WITHOUT
connecting them to TYPE 56.
4.) In addition, please check the component order. The data reader
Type 9 is placed after the building.
Marion
_____
Von: 王洋 [mailto:wanghongyang1767 at gmail.com]
Gesendet: Montag, 8. Oktober 2012 15:31
An: trnsys-users at cae.wisc.edu; hotline
Betreff: Fwd: Converging error
Dear Marion and TRNSYS Users,
Thanks for your reply!
I checked all you mentioned, I can't find any special/abnormal settings.
Furthermore, it runs well when the time step is 1 hour. For other steps
e.g. 0.1 h, 0.2 h or 0.5 h, it appears that ERROR.
Please help me have a look at the attached project if you are free.
Many thanks in advance!
br.
wang
---------- Forwarded message ----------
From: 王洋 <wanghongyang1767 at gmail.com>
Date: 2012/9/28
Subject: Converging error
To: trnsys-users at cae.wisc.edu, hotline at transsolar.com
---------- 已转发邮件 ----------
From: "hotline" <hotline at transsolar.com>
To: trnsys-users <trnsys-users at cae.wisc.edu>
Cc:
Date: Fri, 28 Sep 2012 12:02:00 +0200
Subject: Re: [TRNSYS-users] Converging error
Wang,
This problem may occur from incorrect ambient condition settings:
Please check the following inputs of Type 56
1- TAMB
2- RELHUMAMB
3- TSKY
4- TSGRD
In addition make sure that in the BUI file the surface
- outside emissitive is ≤ 1
- outside convective heat transfer coefficient ist set to
reasonable value
If the error presits, we need the complete project to give further
advice.
Marion
2012/9/28 <trnsys-users-request at cae.wisc.edu>
Send TRNSYS-users mailing list submissions to
trnsys-users at cae.wisc.edu
To subscribe or unsubscribe via the World Wide Web, visit
https://mailman.cae.wisc.edu/listinfo/trnsys-users
or, via email, send a message with subject or body 'help' to
trnsys-users-request at cae.wisc.edu
You can reach the person managing the list at
trnsys-users-owner at cae.wisc.edu
When replying, please edit your Subject line so it is more specific
than "Re: Contents of TRNSYS-users digest..."
Today's Topics:
1. Re: problem with iterations?? (Matt Duffy)
2. Re: problem with iterations?? (Marion Hiller)
3. Re: Converging error (hotline)
---------- 已转发邮件 ----------
From: Matt Duffy <duffy at tess-inc.com>
To: <trnsys-users at cae.wisc.edu>
Cc:
Date: Thu, 27 Sep 2012 12:04:24 -0500
Subject: Re: [TRNSYS-users] problem with iterations??
Karol,
I noticed from your listing (*.lst) file that your working directory is
located on your computer's desktop directory. This is not recommended
due to the potential issues with the Windows OS system and write
privleges. I would first try changing your working directory to the
".\MyProjects" directory or in a folder right on the "C:" drive. I am
not certain that this is the issue with the TRNEXE, but if the problem
persists, please contact your distributor, techsupport at tess-inc.com.
Best regards,
Matt Duffy
TRNSYS on Facebook
On 2012-09-27 03:46, Karol Bandurski wrote:
Dear All,
I try to simulate dwelling with natural ventilation. I set some
algorithm for window opening and ideal heating for colder part of
year for each zone with set temperature depending on time of day.
When I run my yearly simulation it stop in one moment and TRNEXE is
frozen… There is even no error! Then I can only turn off TRNEXE.
Only think what appear (many times) in .lst file is
Notice: More than 6 iterations for internal regulation
HEATING/COOLING.
I will be grateful for any advice!
I enclose .lst file.
Regards,
------------------------------------------------
Karol Bandurski MSc.
Institute of Environmental Engineering
Poznan University of Technology
www.ee.put.poznan.pl
www.put.poznan.pl
---------- 已转发邮件 ----------
From: "Marion Hiller" <hiller at transsolar.com>
To: "karol.bandurski" <karol.bandurski at put.poznan.pl>
Cc: trnsys-users <trnsys-users at cae.wisc.edu>
Date: Fri, 28 Sep 2012 08:53:53 +0200
Subject: Re: [TRNSYS-users] problem with iterations??
Karol,
In general the notice has nothing to do with a frozen TRNEXE.exe,
it is just an information.
The message indicates that the internal controller for turning on the
integrated heating/cooling has convergence problems and a deadband is
applied to promote convergence.
This may be the case at the moment of turning ON or OFF something.
After 6 internal iterations a deadband is added to promote convergence.
If the convergence isn’t reached after 12 iterations a warning is
written to the lst/log file.
Regards,
Marion
Dipl.-Ing. Marion Hiller
TRANSSOLAR: KlimaEngineering - Technologien für energieeffizientes Bauen
und Nutzerkomfort in Gebäude
Munich - New York - Stuttgart + 49.711.67976.0
Transsolar Energietechnik GmbH, Curiestrasse 2, 70563 Stuttgart
Amtsgericht Stuttgart - HRB 23347, Steuernummer 99073/00911, USt-IdNr.:
DE152272639
Geschäftsführer: Dipl.Ing. Matthias Schuler, Dipl.Ing. Thomas Auer,
Dipl.Phys. Stefan Holst, Prof. Dipl.-Ing. Bleicher
_____
Von: Karol Bandurski [mailto:karol.bandurski at put.poznan.pl]
Gesendet: Donnerstag, 27. September 2012 10:47
An: trnsys-users at cae.wisc.edu
Betreff: [TRNSYS-users] problem with iterations??
Dear All,
I try to simulate dwelling with natural ventilation. I set some
algorithm for window opening and ideal heating for colder part of year
for each zone with set temperature depending on time of day.
When I run my yearly simulation it stop in one moment and TRNEXE is
frozen... There is even no error! Then I can only turn off TRNEXE.
Only think what appear (many times) in .lst file is
Notice: More than 6 iterations for internal regulation HEATING/COOLING.
I will be grateful for any advice!
I enclose .lst file.
Regards,
------------------------------------------------
Karol Bandurski MSc.
Institute of Environmental Engineering
Poznan University of Technology
www.ee.put.poznan.pl
www.put.poznan.pl
---------- 已转发邮件 ----------
From: "hotline" <hotline at transsolar.com>
To: trnsys-users <trnsys-users at cae.wisc.edu>
Cc:
Date: Fri, 28 Sep 2012 12:02:00 +0200
Subject: Re: [TRNSYS-users] Converging error
Wang,
This problem may occur from incorrect ambient condition settings:
Please check the following inputs of Type 56
1- TAMB
2- RELHUMAMB
3- TSKY
4- TSGRD
In addition make sure that in the BUI file the surface
- outside emissitive is ≤ 1
- outside convective heat transfer coefficient ist set to
reasonable value
If the error presits, we need the complete project to give further
advice.
Marion
_____
Von: 王洋 [mailto:wanghongyang1767 at gmail.com]
Gesendet: Donnerstag, 27. September 2012 11:49
An: trnsys-users at cae.wisc.edu
Betreff: [TRNSYS-users] Converging error
Dear all,
I met a converging error when I changed simulation time step 1 hour into
0.1 hour or 0.2 hour or 0.01 hour as follows:
*** Fatal Error at time : 3972.000000
Generated by Unit : 56
Generated by Type : 56
Message : outside temperature of 2(external) wall
in zone 1at time 3972.00 not converged!
Please tell me some possible solutions for that if you know. The
attached is its Listing File.
Many thanks in advance!
Br.
wang
2012/9/27 <trnsys-users-request at cae.wisc.edu>
Send TRNSYS-users mailing list submissions to
trnsys-users at cae.wisc.edu
To subscribe or unsubscribe via the World Wide Web, visit
https://mailman.cae.wisc.edu/listinfo/trnsys-users
or, via email, send a message with subject or body 'help' to
trnsys-users-request at cae.wisc.edu
You can reach the person managing the list at
trnsys-users-owner at cae.wisc.edu
When replying, please edit your Subject line so it is more specific
than "Re: Contents of TRNSYS-users digest..."
Today's Topics:
1. Doctoral Fellowships at TERI University, India (R.K. Singh)
2. problem with iterations?? (Karol Bandurski)
---------- 已转发邮件 ----------
From: "R.K. Singh" <singh.ramkishore at gmail.com>
To: TRNSYS-users at cae.wisc.edu
Cc:
Date: Thu, 27 Sep 2012 10:04:34 +0530
Subject: [TRNSYS-users] Doctoral Fellowships at TERI University, India
TERI University is currently inviting applications for Doctoral
programmes in Bioresources/Biotechnology;Natural Resource Management,
Energy and Environment and Regulatory and Policy studies for semester
starting january 2013. A range of scholarship opportunities are also
available for the students in specific areas, the details of which can
be accessed through the following link.
http://teriuniversity.ac.in/index.php?option=com_content&view=article&id
=54
The last date for application is October 31st, 2012. The details
regarding fee, eligibility and other requirements can be accessed
through http://teriuniversity.ac.in/index.php?option=com_program
For any further details please get in touch with Dr. Sapna A Narula,
Associate Professor sapna.narula at teriuniversity.ac.in.
***********************************************
Dr. Ramkishore Singh
Department of Energy & Environment
TERI University
Tel: 91-11-26122222, Ext. 1302
Fax: 91-11-26122874
Web: www.teriuniversity.ac.in
***********************************************
---------- 已转发邮件 ----------
From: "Karol Bandurski" <karol.bandurski at put.poznan.pl>
To: <trnsys-users at cae.wisc.edu>
Cc:
Date: Thu, 27 Sep 2012 10:46:49 +0200
Subject: [TRNSYS-users] problem with iterations??
Dear All,
I try to simulate dwelling with natural ventilation. I set some
algorithm for window opening and ideal heating for colder part of year
for each zone with set temperature depending on time of day.
When I run my yearly simulation it stop in one moment and TRNEXE is
frozen... There is even no error! Then I can only turn off TRNEXE.
Only think what appear (many times) in .lst file is
Notice: More than 6 iterations for internal regulation HEATING/COOLING.
I will be grateful for any advice!
I enclose .lst file.
Regards,
------------------------------------------------
Karol Bandurski MSc.
Institute of Environmental Engineering
Poznan University of Technology
www.ee.put.poznan.pl
www.put.poznan.pl
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at cae.wisc.edu
https://mailman.cae.wisc.edu/listinfo/trnsys-users
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at cae.wisc.edu
https://mailman.cae.wisc.edu/listinfo/trnsys-users
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20121010/0bf61c36/attachment-0001.htm>
More information about the TRNSYS-users
mailing list