David BRADLEY
d.bradley at tess-inc.com
Mon Oct 1 08:24:32 PDT 2012
Gary,
There is a bit of room for interpretation in your question; I'm not
sure whether the setpoint to which you refer is the temperature of the
chilled water that the absorption chiller is providing or whether it is
the room temperature that you want to maintain. I am guessing that you
want to change the room temperature setpoint and that you have defined
your zone temperature using the HEAT and COOL types inside TRNBuild. If
that is the case, then here are the steps you need to take:
1. turn OFF the automatic HEAT and COOL types in TRNBuild so that the
zone temperature floats.
2. in the Simulation Studio, define a thermostat (Type108 would be a
good choice) that watches the zone temperature and has the same set
point schedule that you previously defined in TRNBuild. The output of
this thermostat model is going to be the control signal input to your
cooling equipment.
3. decide how you want to remove energy from the sapce (fan coil,
radiant cooled slabs, etc.) and choose an appropriate model.
4. define a water loop that includes a pump, the delivery device, a
thermal storage tank (Type534 would be a good choice), and the
absorption chiller.
5. connect the cooling signal output of the thermostat model to both the
pump and the chiller control signal.
One work of caution: in most circumstances, the absorption chiller is
not directly connected to the delivery device. There are usually two
loops. If there are multiple energy delivery devices then they are
usually on a secondary loop while the absorption chiller is on a primary
loop
(http://www.nanomagnetics.org/chilledwatertips/constant_volumen_constant_speed.php)
Alternatively, you can have a situation where there is a chilled water
distribution loop with a pump that draws chilled water from a tank,
passes it to the load, and returns warmer water to the tank. The pump
runs based on a thermostat that watches the zone temperature. The
chiller is on a separate loop that pumps water from the tank, cools it
down with the chiller and returns it to the tank. A thermostat that
watches the tank temperature and turns on the chiller and a pump when
needed.
There is a tutorial online that would be well worth reading; I think
it will fill in some of the gaps in what I have explained above.
http://sel.me.wisc.edu/trnsys/downloads/tutorials_and_examples/tlc_tutorial.pdf
Best,
David
On 9/30/2012 04:53, KUM GARY wrote:
> Hi all,
>
> I would like to know how should i model type 107 chiller to respond to
> the different temperature setpoint of the day needed for my building
> in TRNbuild?
>
> Thanks
> Gary
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com