[TRNSYS-users] Fwd: Error creating the wall transfer function	coeffients
    王洋 
    wanghongyang1767 at gmail.com
       
    Mon Nov 19 01:31:41 PST 2012
    
    
  
Dear Leen, Jean, Marion, Benoit and others,
Many thanks for your reply!
I checked my Wall's thickness and thermal property etc. again. Why needs it
9 hours as the timebase? I think maybe it is due to my Ground floor (it is
the basement's floor of the building) which includes about 0.99 m's Air
Layer.
When I changed it into 0.1 m, the min. timebase 2.5 hours can work without
the ERROR:Error creating the wall transfer function coeffients.
Therefore, I'd like to ask you,
1) Is it normal for TRNBuild setting how large the timebase is maximally? 5
hours or others?
2) How to solve this problem of the ground floor with about 0.99 m's Air
Layer? But our building project indeed has
the ground floor with about 0.99 m's Air Layer. I can't reduce it into
0.1m? Is the only way to  try the active layer approach of The group of
Michael Kummert in Montreal?
Please see the Attached INF file.
Thanks in advance!
Br.
wang
2012/11/17 Benoit Delcroix <benoit.delcroix at polymtl.ca>
>  Hello,
>
> I'm one of the students of Michaël Kummert working on a new method to
> generate the tranfer functions. I thing I can help you for your problem. As
> Leen said, TRNSYS is unable to generate the transfer functions coefficients
> for a heavy and insulated wall with a low timebase. In the TRNBuild
> project, you can modify that value and increase it to allow TRNSYS to
> generate the transfer functions. Actually, TRNSYS is unable to generate the
> transfer function as soon as the Fourier number of the wall (thermal
> diffusivity * timebase / thhickness²) is lower than 0.0005. To check that,
> TRNBuild make the sum of one of the coefficients series (a, b or c). The 3
> sums are equal and means, according to TRNBuild (I don't personally think
> so...but it's like this), the Fourier number.
>
> As Leen said, it exists a trick. You can use an active layer to split the
> wall in 2 and then forcing TRNSYS to generate 2 series of transfer
> functions coefficients for the same wall. As the 2 parts are thinner, you
> could use a better timebase value. When you insert the active layer in the
> wall, try to split the layer with the lowest Fourier number. And then to
> insert the active layer, use the expert mode that allows you to insert an
> equivalent conductivity. Insert the biggest value you can. Like that, the
> active layer is negligible at the thermal point of view. Actually, the
> active layer is acting as a mini-zone to split the wall. It is a little
> tricky but it works...before having better solution.
>
> Good luck for your project and have a nice week-end,
>
> Benoit
>
> Le 2012-11-17 14:43, trnsys-users-request at cae.wisc.edu a écrit :
>
> Send TRNSYS-users mailing list submissions to
> 	trnsys-users at cae.wisc.edu
>
> To subscribe or unsubscribe via the World Wide Web, visit
> 	https://mailman.cae.wisc.edu/listinfo/trnsys-users
> or, via email, send a message with subject or body 'help' to
> 	trnsys-users-request at cae.wisc.edu
>
> You can reach the person managing the list at
> 	trnsys-users-owner at cae.wisc.edu
>
> When replying, please edit your Subject line so it is more specific
> than "Re: Contents of TRNSYS-users digest..."
>
>
>
> Today's Topics:
>
>    1. Re: Fwd: Error creating the wall transfer function	coeffients
>       (leen peeters)
>
>
>
> _______________________________________________
> TRNSYS-users mailing listTRNSYS-users at cae.wisc.eduhttps://mailman.cae.wisc.edu/listinfo/trnsys-users
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20121119/e19ffdc4/attachment-0005.htm>
-------------- next part --------------
*********************************************************************************************************************************************************************************************************
*  TRNBuild   1.0.94
*********************************************************************************************************************************************************************************************************
*   BUILDING DESCRIPTIONS FILE TRNSYS
*   FOR BUILDING:   V:\Gr_Biomasse\Pr_Laufend\102239_FOSBOS_2009\8 Wang\program\TRNSYS\Nov5_Building\BuildingProject12.inf
*   GET BY WORKING WITH TRNBuild 1.0 for Windows
*********************************************************************************************************************************************************************************************************
*
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  C o m m e n t s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*#C ----------------------------------------------------  TYPES --------------------------------- *
*#C
*#C -----------------------------------------------------LAYERS --------------------------------- *
*#C
*#C -------------------------------------------------------- INPUTS ----------------------------- *
*#C
*#C ------------------------------------------------------SCHEDULES ----------------------------- *
*#C
*#C -------------------------------------------------------- WALLS ------------------------------ *
*#C
*#C ------------------------------------------------------ WINDOWS ------------------------------ *
*#C
*#C -------------------------------------------------------- GAINS ------------------------------ *
*#C
*#C -------------------------------------------------------- COMFORT----------------------------- *
*#C
*#C ---------------------------------------------------- INFILTRATION --------------------------- *
*#C
*#C ---------------------------------------------------- VENTILATION ---------------------------- *
*#C
*#C ------------------------------------------------------- HEATING ----------------------------- *
*#C
*#C -------------------------------------------------- ORIENTATIONS ----------------------------- *
*#C
*#C -------------------------------------------------------- ZONES ------------------------------ *
*#C
*#C ------------------------------------------------------- BUILDING ---------------------------- *
*#C
*#C ------------------------------- GEOSURF ----------------------------------------------------- *
*#C
*#C --------------------------------------------------- OUTPUTS --------------------------------- *
*#C
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  P r o j e c t
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*+++ PROJECT
*+++ TITLE=FOS
*+++ DESCRIPTION=SCHOOL
*+++ CREATED=WANG
*+++ ADDRESS=ERDING
*+++ CITY=MUNICH
*+++ SWITCH=UNDEFINED
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  P r o p e r t i e s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
PROPERTIES
 DENSITY=1.204 : CAPACITY=1.012 : HVAPOR=2454.0 : SIGMA=2.041e-007 : RTEMP=293.15
*--- alpha calculation -------------------
 KFLOORUP=7.2 : EFLOORUP=0.31 : KFLOORDOWN=3.888 : EFLOORDOWN=0.31
 KCEILUP=7.2 : ECEILUP=0.31 : KCEILDOWN=3.888 : ECEILDOWN=0.31
 KVERTICAL=5.76 : EVERTICAL=0.3
*
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
TYPES
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
*
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  L a y e r s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
LAYER CONCRETE
 CONDUCTIVITY=   7.56 : CAPACITY=    0.8 : DENSITY=   2400
LAYER INSUL
 CONDUCTIVITY= 0.1152 : CAPACITY=    0.8 : DENSITY=     40
LAYER INSULROOF
 CONDUCTIVITY=  0.126 : CAPACITY=    0.8 : DENSITY=     40
LAYER ESTRICH
 CONDUCTIVITY=   2.16 : CAPACITY=      1 : DENSITY=    800
LAYER AIRLAYER
 CONDUCTIVITY=0.09252 : CAPACITY=  1.005 : DENSITY=  1.205
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  I n p u t s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
INPUTS CNAT_1 T_COOL_ON S_NORTH S_SOUTH S_EAST S_WEST BRIGHT WINTER SUMMER TCOOL
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  S c h e d u l e s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
SCHEDULE WEEKEND
 HOURS =0.000 1.000 24.0
 VALUES=0 0 0 
SCHEDULE OCCUPANCY
 HOURS =0.000 7.000 9.750 10.000 11.500 11.750 13.250 14.000 16.250 24.0
 VALUES=0 1. 0 1. 0 1. 0 1. 0 0 
SCHEDULE SUMMER_OCCUPANCY
 DAYS=1 2 3 4 5 6 7
 HOURLY=OCCUPANCY OCCUPANCY OCCUPANCY OCCUPANCY OCCUPANCY WEEKEND WEEKEND
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  W a l l s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
WALL OUTWALL
 LAYERS   = CONCRETE INSUL 
 THICKNESS= 0.26     0.24  
 ABS-FRONT= 0.75  : ABS-BACK= 0.3  
 HFRONT   = 11 : HBACK= 64
WALL INTWALL
 LAYERS   = CONCRETE 
 THICKNESS= 0.125    
 ABS-FRONT= 0.6   : ABS-BACK= 0.6  
 HFRONT   = 11 : HBACK= 11
WALL INTFLOOR
 LAYERS   = ESTRICH CONCRETE 
 THICKNESS= 0.065   0.15     
 ABS-FRONT= 0.8   : ABS-BACK= 0.4  
 HFRONT   = 11 : HBACK= 11
WALL ROOF
 LAYERS   = CONCRETE INSULROOF 
 THICKNESS= 0.3      0.36      
 ABS-FRONT= 0.35  : ABS-BACK= 0.75 
 HFRONT   = 11 : HBACK= 64
WALL GROUNDFLOOR
 LAYERS   = AIRLAYER CONCRETE INSUL 
 THICKNESS= 0.99     0.4      0.2   
 ABS-FRONT= 0.6   : ABS-BACK= 0.6  
 HFRONT   = 11 : HBACK= 999
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  W i n d o w s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
WINDOW TRIPLE
 WINID=4001 : HINSIDE=11 : HOUTSIDE=64 : SLOPE=90 : SPACID=1 : WWID=2.5 : WHEIG=2.8 : FFRAME=0.1896 : UFRAME=3.852 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
 CCISHADE=0.5
WINDOW POS016
 WINID=4001 : HINSIDE=11 : HOUTSIDE=64 : SLOPE=90 : SPACID=1 : WWID=1.03 : WHEIG=0.8 : FFRAME=0.496 : UFRAME=4.644 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
 CCISHADE=0.5
WINDOW POS015_016
 WINID=4001 : HINSIDE=11 : HOUTSIDE=64 : SLOPE=90 : SPACID=1 : WWID=1.03 : WHEIG=1.6 : FFRAME=0.3246 : UFRAME=4.644 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
 CCISHADE=0.5
WINDOW POS005_008
 WINID=4001 : HINSIDE=11 : HOUTSIDE=64 : SLOPE=90 : SPACID=1 : WWID=2.92 : WHEIG=2.8 : FFRAME=0.2882 : UFRAME=4.572 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
 CCISHADE=0.5
WINDOW POS005_010
 WINID=4001 : HINSIDE=11 : HOUTSIDE=64 : SLOPE=90 : SPACID=1 : WWID=1.67 : WHEIG=2.8 : FFRAME=0.26 : UFRAME=4.572 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
 CCISHADE=0.5
WINDOW POS2_010_005
 WINID=4001 : HINSIDE=11 : HOUTSIDE=64 : SLOPE=90 : SPACID=1 : WWID=2.92 : WHEIG=2.8 : FFRAME=0.2286 : UFRAME=4.572 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
 CCISHADE=0.5
WINDOW POS005_009
 WINID=4001 : HINSIDE=11 : HOUTSIDE=64 : SLOPE=90 : SPACID=1 : WWID=2.08 : WHEIG=2.85 : FFRAME=0.1809 : UFRAME=4.572 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
 CCISHADE=0.5
WINDOW POS005
 WINID=4001 : HINSIDE=11 : HOUTSIDE=64 : SLOPE=90 : SPACID=1 : WWID=0.417 : WHEIG=2.85 : FFRAME=0.44 : UFRAME=4.104 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
 CCISHADE=0.5
WINDOW POS027
 WINID=4001 : HINSIDE=11 : HOUTSIDE=64 : SLOPE=90 : SPACID=1 : WWID=1.28 : WHEIG=2.85 : FFRAME=0.397 : UFRAME=4.14 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
 CCISHADE=0.5
WINDOW POS010
 WINID=4001 : HINSIDE=11 : HOUTSIDE=64 : SLOPE=90 : SPACID=1 : WWID=1.25 : WHEIG=2.25 : FFRAME=0.185 : UFRAME=4.572 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
 CCISHADE=0.5
WINDOW POS023
 WINID=4001 : HINSIDE=11 : HOUTSIDE=64 : SLOPE=90 : SPACID=1 : WWID=1.25 : WHEIG=2.25 : FFRAME=0.296 : UFRAME=4.068 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
 CCISHADE=0.5
WINDOW POS025
 WINID=4001 : HINSIDE=11 : HOUTSIDE=64 : SLOPE=90 : SPACID=1 : WWID=2.08 : WHEIG=2.825 : FFRAME=0.212 : UFRAME=3.924 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
 CCISHADE=0.5
WINDOW POS013_027
 WINID=4001 : HINSIDE=11 : HOUTSIDE=64 : SLOPE=90 : SPACID=1 : WWID=1.25 : WHEIG=2.8 : FFRAME=0.312 : UFRAME=4.464 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
 CCISHADE=0.5
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  D e f a u l t  G a i n s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
GAIN PERS_ISO01
 CONVECTIVE=144 : RADIATIVE=72 : HUMIDITY=0.059
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  O t h e r  G a i n s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  C o m f o r t
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  I n f i l t r a t i o n
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
INFILTRATION INFIL001
 AIRCHANGE=0.01
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  V e n t i l a t i o n
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
VENTILATION VENTMECH
 TEMPERATURE=INPUT 2*WINTER+17
 AIRCHANGE=SCHEDULE 2.38*SUMMER_OCCUPANCY+0.37
 HUMIDITY=50
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  C o o l i n g
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
COOLING COOL001
 ON=INPUT 1*TCOOL
 POWER=999999999
 HUMIDITY=100
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  H e a t i n g
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
HEATING HEAT001
 ON=INPUT 20*WINTER
 POWER=999999999
 HUMIDITY=0
 RRAD=0.4
*
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  Z o n e s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONES ROOM228 ZONE31 ZONE10 ZONE1 ZONE17 ZONE19 ZONE8 ZONE9 ZONE6 ZONE11 ZONE4 ZONE5 ZONE2 ZONE7 ZONE12 ZONE3 ZONE14 ZONE13 ZONE24 ZONE29 ZONE15 ZONE27 ZONE20 ZONE26 ZONE30 ZONE22 ZONE18 ZONE25 ;
 ZONE21
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  O r i e n t a t i o n s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ORIENTATIONS NORTH SOUTH EAST WEST HORIZONTAL
*
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
BUILDING
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
*
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  Z o n e  ROOM228  /  A i r n o d e  ROOM228
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ROOM228
AIRNODE ROOM228
WALL  =INTWALL    : SURF=  1 : AREA=     29.33 : BOUNDARY=IDENTICAL : GEOSURF=0.1
WALL  =OUTWALL    : SURF=  2 : AREA=     11.77 : EXTERNAL : ORI=SOUTH : FSKY=0.5
WINDOW=TRIPLE     : SURF=  3 : AREA=     17.56 : EXTERNAL : ORI=SOUTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_SOUTH
WALL  =INTFLOOR   : SURF=  6 : AREA=     57.21 : BOUNDARY=IDENTICAL : GEOSURF=0.6
WALL  =ROOF       : SURF=  7 : AREA=     79.91 : EXTERNAL : ORI=HORIZONTAL : FSKY=0.5
WALL  =INTWALL    : SURF= 18 : AREA=     30.35 : ADJACENT=ZONE31 : BACK : GEOSURF=0.1
WALL  =INTWALL    : SURF= 27 : AREA=     30.35 : ADJACENT=ZONE10 : BACK : GEOSURF=0.1
WALL  =INTFLOOR   : SURF=386 : AREA=         4 : ADJACENT=ZONE18 : BACK
WALL  =INTFLOOR   : SURF=393 : AREA=      18.7 : ADJACENT=ZONE18 : BACK
 REGIME
 GAIN        = PERS_ISO01 : SCALE= SCHEDULE 31*SUMMER_OCCUPANCY
 INFILTRATION= INFIL001
 VENTILATION = VENTMECH
 COOLING     = COOL001
 HEATING     = HEAT001
 CAPACITANCE = 2301.4  : VOLUME= 239.73  : TINITIAL= 20      : PHINITIAL= 50      : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  Z o n e  ZONE31  /  A i r n o d e  ZONE31
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE31
AIRNODE ZONE31
WALL  =OUTWALL    : SURF=  8 : AREA=     18.44 : EXTERNAL : ORI=SOUTH : FSKY=0.5
WINDOW=TRIPLE     : SURF=  9 : AREA=     17.56 : EXTERNAL : ORI=SOUTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_SOUTH
WALL  =OUTWALL    : SURF= 10 : AREA=     17.94 : EXTERNAL : ORI=SOUTH : FSKY=0.5
WINDOW=TRIPLE     : SURF= 11 : AREA=     17.56 : EXTERNAL : ORI=SOUTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_SOUTH
WALL  =INTWALL    : SURF= 12 : AREA=        36 : ADJACENT=ZONE1 : FRONT : GEOSURF=0.1
WALL  =INTWALL    : SURF= 13 : AREA=      35.5 : ADJACENT=ZONE1 : FRONT : GEOSURF=0.1
WALL  =OUTWALL    : SURF= 14 : AREA=     30.35 : EXTERNAL : ORI=WEST : FSKY=0.5 : GEOSURF=0.1
WALL  =INTWALL    : SURF= 16 : AREA=      60.7 : INTERNAL : GEOSURF=0.1
WALL  =INTWALL    : SURF= 17 : AREA=     30.35 : ADJACENT=ROOM228 : FRONT : GEOSURF=0.1
WALL  =ROOF       : SURF=  5 : AREA=      86.8 : EXTERNAL : ORI=HORIZONTAL : FSKY=0.5
WALL  =INTFLOOR   : SURF= 19 : AREA=      10.2 : BOUNDARY=IDENTICAL : GEOSURF=0.1
WALL  =ROOF       : SURF= 20 : AREA=      85.5 : EXTERNAL : ORI=HORIZONTAL : FSKY=0.5
WALL  =INTFLOOR   : SURF= 21 : AREA=     37.92 : BOUNDARY=IDENTICAL : GEOSURF=0.3
WALL  =INTFLOOR   : SURF= 62 : AREA=      27.1 : ADJACENT=ZONE17 : FRONT
WALL  =INTFLOOR   : SURF= 64 : AREA=      49.5 : ADJACENT=ZONE19 : FRONT : GEOSURF=0.1
WALL  =INTFLOOR   : SURF=378 : AREA=     47.58 : ADJACENT=ZONE18 : BACK
WALL  =INTFLOOR   : SURF=379 : AREA=      10.2 : BOUNDARY=IDENTICAL
 REGIME
 GAIN        = PERS_ISO01 : SCALE= SCHEDULE 52*SUMMER_OCCUPANCY
 INFILTRATION= INFIL001
 VENTILATION = VENTMECH
 COOLING     = COOL001
 HEATING     = HEAT001
 CAPACITANCE = 4596.48 : VOLUME= 478.8   : TINITIAL= 20      : PHINITIAL= 50      : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  Z o n e  ZONE10  /  A i r n o d e  ZONE10
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE10
AIRNODE ZONE10
WALL  =OUTWALL    : SURF= 22 : AREA=     17.94 : EXTERNAL : ORI=SOUTH : FSKY=0.5
WINDOW=TRIPLE     : SURF= 23 : AREA=     17.56 : EXTERNAL : ORI=SOUTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_SOUTH
WALL  =INTWALL    : SURF= 24 : AREA=      35.5 : ADJACENT=ZONE1 : FRONT : GEOSURF=0.1
WALL  =INTWALL    : SURF= 26 : AREA=     30.35 : ADJACENT=ROOM228 : FRONT
WALL  =INTWALL    : SURF=  4 : AREA=      60.7 : INTERNAL
WALL  =ROOF       : SURF= 28 : AREA=      85.5 : EXTERNAL : ORI=HORIZONTAL : FSKY=0.5
WALL  =INTFLOOR   : SURF= 29 : AREA=      85.5 : ADJACENT=ZONE1 : FRONT : GEOSURF=0.2
WALL  =OUTWALL    : SURF= 31 : AREA=     17.94 : EXTERNAL : ORI=SOUTH : FSKY=0.5
WINDOW=TRIPLE     : SURF= 32 : AREA=     17.56 : EXTERNAL : ORI=SOUTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_SOUTH
WALL  =INTWALL    : SURF= 33 : AREA=      35.5 : ADJACENT=ZONE1 : FRONT
WALL  =INTWALL    : SURF= 35 : AREA=      60.7 : INTERNAL
WALL  =INTWALL    : SURF= 36 : AREA=      60.7 : INTERNAL
WALL  =ROOF       : SURF= 37 : AREA=      85.5 : EXTERNAL : ORI=HORIZONTAL : FSKY=0.5
WALL  =INTFLOOR   : SURF= 38 : AREA=      85.5 : ADJACENT=ZONE1 : FRONT : GEOSURF=0.2
WALL  =OUTWALL    : SURF= 42 : AREA=     17.94 : EXTERNAL : ORI=SOUTH : FSKY=0.5
WINDOW=TRIPLE     : SURF= 43 : AREA=     17.56 : EXTERNAL : ORI=SOUTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_SOUTH
WALL  =INTWALL    : SURF= 44 : AREA=      35.5 : ADJACENT=ZONE1 : FRONT
WALL  =ROOF       : SURF= 48 : AREA=      85.5 : EXTERNAL : ORI=HORIZONTAL : FSKY=0.5
WALL  =INTFLOOR   : SURF= 49 : AREA=      85.5 : ADJACENT=ZONE1 : FRONT : GEOSURF=0.1
WALL  =OUTWALL    : SURF= 51 : AREA=     18.44 : EXTERNAL : ORI=SOUTH : FSKY=0.5
WINDOW=TRIPLE     : SURF= 52 : AREA=     17.56 : EXTERNAL : ORI=SOUTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_SOUTH
WALL  =INTWALL    : SURF= 53 : AREA=        36 : ADJACENT=ZONE1 : FRONT : GEOSURF=0.1
WALL  =OUTWALL    : SURF= 56 : AREA=     30.35 : EXTERNAL : ORI=EAST : FSKY=0.5
WALL  =ROOF       : SURF= 57 : AREA=     86.78 : EXTERNAL : ORI=HORIZONTAL : FSKY=0.5
WALL  =INTFLOOR   : SURF= 58 : AREA=     22.28 : ADJACENT=ZONE1 : FRONT : GEOSURF=0.1
WALL  =INTFLOOR   : SURF= 60 : AREA=      64.5 : ADJACENT=ZONE17 : FRONT : GEOSURF=0.2
 REGIME
 GAIN        = PERS_ISO01 : SCALE= SCHEDULE 104*SUMMER_OCCUPANCY
 INFILTRATION= INFIL001
 VENTILATION = VENTMECH
 COOLING     = COOL001
 HEATING     = HEAT001
 CAPACITANCE = 9216    : VOLUME= 960     : TINITIAL= 20      : PHINITIAL= 50      : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  Z o n e  ZONE1  /  A i r n o d e  ZONE1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE1
AIRNODE ZONE1
WALL  =INTWALL    : SURF= 25 : AREA=      35.5 : ADJACENT=ZONE10 : BACK
WALL  =INTFLOOR   : SURF= 30 : AREA=      85.5 : ADJACENT=ZONE10 : BACK
WALL  =INTWALL    : SURF= 34 : AREA=      35.5 : ADJACENT=ZONE10 : BACK
WALL  =INTFLOOR   : SURF= 39 : AREA=      85.5 : ADJACENT=ZONE10 : BACK
WALL  =INTWALL    : SURF= 40 : AREA=        36 : ADJACENT=ZONE31 : BACK
WALL  =INTWALL    : SURF= 41 : AREA=      35.5 : ADJACENT=ZONE31 : BACK
WALL  =INTWALL    : SURF= 45 : AREA=      35.5 : ADJACENT=ZONE10 : BACK
WALL  =INTFLOOR   : SURF= 50 : AREA=      85.5 : ADJACENT=ZONE10 : BACK
WALL  =INTWALL    : SURF= 54 : AREA=        36 : ADJACENT=ZONE10 : BACK
WALL  =INTFLOOR   : SURF= 59 : AREA=     22.28 : ADJACENT=ZONE10 : BACK
WALL  =INTWALL    : SURF= 67 : AREA=      21.7 : ADJACENT=ZONE19 : BACK
WALL  =INTWALL    : SURF= 69 : AREA=     8.925 : ADJACENT=ZONE8 : BACK
WALL  =INTWALL    : SURF= 46 : AREA=      8.93 : ADJACENT=ZONE8 : BACK
WALL  =INTWALL    : SURF= 89 : AREA=       9.3 : ADJACENT=ZONE8 : BACK
WALL  =INTWALL    : SURF=101 : AREA=      25.6 : ADJACENT=ZONE9 : BACK
WALL  =INTWALL    : SURF=105 : AREA=        17 : ADJACENT=ZONE9 : BACK
WALL  =INTWALL    : SURF=113 : AREA=       9.3 : ADJACENT=ZONE6 : BACK
WALL  =INTWALL    : SURF=118 : AREA=      25.6 : ADJACENT=ZONE12 : BACK
WALL  =INTWALL    : SURF=125 : AREA=       9.3 : ADJACENT=ZONE5 : BACK
WALL  =INTWALL    : SURF=133 : AREA=       9.3 : ADJACENT=ZONE5 : BACK
WALL  =INTWALL    : SURF=142 : AREA=      26.7 : ADJACENT=ZONE7 : BACK
WALL  =INTWALL    : SURF=146 : AREA=     17.75 : ADJACENT=ZONE7 : BACK
WALL  =INTWALL    : SURF=149 : AREA=      9.32 : ADJACENT=ZONE2 : BACK
WALL  =INTWALL    : SURF=161 : AREA=       8.5 : ADJACENT=ZONE2 : BACK
WALL  =INTWALL    : SURF=167 : AREA=       8.5 : ADJACENT=ZONE2 : BACK
WALL  =INTWALL    : SURF=175 : AREA=      9.33 : ADJACENT=ZONE2 : BACK
WALL  =INTWALL    : SURF=183 : AREA=      9.33 : ADJACENT=ZONE2 : BACK
WALL  =INTWALL    : SURF=192 : AREA=       8.9 : ADJACENT=ZONE2 : BACK
WALL  =INTWALL    : SURF=208 : AREA=       8.1 : ADJACENT=ZONE2 : BACK
WALL  =INTWALL    : SURF=216 : AREA=       8.1 : ADJACENT=ZONE2 : BACK
WALL  =INTWALL    : SURF=226 : AREA=      8.91 : ADJACENT=ZONE2 : BACK
WALL  =INTFLOOR   : SURF=232 : AREA=     20.45 : ADJACENT=ZONE2 : BACK
WALL  =INTWALL    : SURF=234 : AREA=      8.91 : ADJACENT=ZONE2 : BACK
WALL  =INTWALL    : SURF=243 : AREA=     8.925 : ADJACENT=ZONE11 : BACK
WALL  =INTWALL    : SURF=253 : AREA=     8.925 : ADJACENT=ZONE11 : BACK
WALL  =INTWALL    : SURF=261 : AREA=     8.925 : ADJACENT=ZONE11 : BACK
WALL  =INTWALL    : SURF=273 : AREA=     8.925 : ADJACENT=ZONE14 : BACK
WALL  =INTWALL    : SURF=295 : AREA=     12.75 : ADJACENT=ZONE14 : BACK
WALL  =INTWALL    : SURF=301 : AREA=     12.75 : ADJACENT=ZONE14 : BACK
WALL  =INTWALL    : SURF=307 : AREA=     12.75 : ADJACENT=ZONE14 : BACK
WALL  =INTWALL    : SURF=313 : AREA=     13.26 : ADJACENT=ZONE14 : BACK
WALL  =INTWALL    : SURF=323 : AREA=       8.5 : ADJACENT=ZONE13 : BACK
WALL  =INTWALL    : SURF=330 : AREA=       8.5 : ADJACENT=ZONE13 : BACK
WALL  =INTWALL    : SURF=338 : AREA=      25.9 : ADJACENT=ZONE20 : BACK
WALL  =INTWALL    : SURF=342 : AREA=        17 : ADJACENT=ZONE20 : BACK
WALL  =INTWALL    : SURF=351 : AREA=      11.9 : ADJACENT=ZONE17 : BACK
WALL  =INTWALL    : SURF=360 : AREA=      28.3 : ADJACENT=ZONE17 : BACK
WALL  =INTWALL    : SURF=362 : AREA=      32.1 : ADJACENT=ZONE17 : BACK
WALL  =INTWALL    : SURF=372 : AREA=     20.87 : ADJACENT=ZONE18 : BACK
WALL  =INTWALL    : SURF=382 : AREA=     7.125 : ADJACENT=ZONE18 : BACK
WALL  =INTWALL    : SURF=384 : AREA=      7.91 : ADJACENT=ZONE18 : BACK
WALL  =INTWALL    : SURF=391 : AREA=     24.15 : ADJACENT=ZONE18 : BACK
 REGIME
 CAPACITANCE = 0.12    : VOLUME= 0.1     : TINITIAL= 20      : PHINITIAL= 50      : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  Z o n e  ZONE17  /  A i r n o d e  ZONE17
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE17
AIRNODE ZONE17
WALL  =INTFLOOR   : SURF= 61 : AREA=      64.5 : ADJACENT=ZONE10 : BACK
WALL  =INTFLOOR   : SURF= 63 : AREA=      27.1 : ADJACENT=ZONE31 : BACK
WALL  =OUTWALL    : SURF=349 : AREA=      11.9 : EXTERNAL : ORI=SOUTH : FSKY=0.5
WALL  =INTWALL    : SURF=350 : AREA=      11.9 : ADJACENT=ZONE1 : FRONT
WALL  =OUTWALL    : SURF=352 : AREA=      32.1 : EXTERNAL : ORI=WEST : FSKY=0.5
WALL  =INTWALL    : SURF=353 : AREA=      32.1 : ADJACENT=ZONE19 : FRONT
WALL  =INTFLOOR   : SURF=355 : AREA=      27.1 : ADJACENT=ZONE30 : FRONT
WALL  =OUTWALL    : SURF=357 : AREA=     19.86 : EXTERNAL : ORI=SOUTH : FSKY=0.5
WINDOW=POS010     : SURF=358 : AREA=      8.44 : EXTERNAL : ORI=SOUTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_SOUTH
WALL  =INTWALL    : SURF=359 : AREA=      28.3 : ADJACENT=ZONE1 : FRONT
WALL  =INTWALL    : SURF=361 : AREA=      32.1 : ADJACENT=ZONE1 : FRONT
WALL  =INTFLOOR   : SURF=363 : AREA=      64.5 : ADJACENT=ZONE22 : FRONT : GEOSURF=0.6
 REGIME
 INFILTRATION= INFIL001
 CAPACITANCE = 2332.8  : VOLUME= 243     : TINITIAL= 20      : PHINITIAL= 50      : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  Z o n e  ZONE19  /  A i r n o d e  ZONE19
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE19
AIRNODE ZONE19
WALL  =INTFLOOR   : SURF= 65 : AREA=      49.5 : ADJACENT=ZONE31 : BACK
WALL  =INTWALL    : SURF= 66 : AREA=      21.7 : ADJACENT=ZONE1 : FRONT
WALL  =INTWALL    : SURF=354 : AREA=      32.1 : ADJACENT=ZONE17 : BACK
WALL  =OUTWALL    : SURF=396 : AREA=      6.94 : EXTERNAL : ORI=SOUTH : FSKY=0.5
WINDOW=POS025     : SURF=397 : AREA=     14.76 : EXTERNAL : ORI=SOUTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_SOUTH
WALL  =INTWALL    : SURF=398 : AREA=      32.1 : BOUNDARY=IDENTICAL
WALL  =INTFLOOR   : SURF=399 : AREA=      49.5 : ADJACENT=ZONE30 : FRONT : GEOSURF=0.6
 REGIME
 INFILTRATION= INFIL001
 CAPACITANCE = 1445.2  : VOLUME= 150.54  : TINITIAL= 20      : PHINITIAL= 50      : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  Z o n e  ZONE8  /  A i r n o d e  ZONE8
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE8
AIRNODE ZONE8
WALL  =INTWALL    : SURF= 68 : AREA=     8.925 : ADJACENT=ZONE1 : FRONT
WALL  =INTWALL    : SURF= 70 : AREA=     25.58 : ADJACENT=ZONE9 : FRONT
WALL  =OUTWALL    : SURF= 72 : AREA=     16.95 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=TRIPLE     : SURF= 73 : AREA=     17.56 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL  =OUTWALL    : SURF= 74 : AREA=     29.07 : EXTERNAL : ORI=WEST : FSKY=0.5
WALL  =INTWALL    : SURF= 75 : AREA=     58.14 : INTERNAL
WALL  =INTFLOOR   : SURF= 76 : AREA=     86.78 : ADJACENT=ZONE6 : FRONT
WALL  =INTFLOOR   : SURF= 78 : AREA=     86.78 : ADJACENT=ZONE11 : FRONT : GEOSURF=0.3
WALL  =INTWALL    : SURF= 15 : AREA=      8.93 : ADJACENT=ZONE1 : FRONT
WALL  =INTWALL    : SURF= 47 : AREA=     25.07 : ADJACENT=ZONE4 : FRONT
WALL  =OUTWALL    : SURF= 80 : AREA=     16.44 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=TRIPLE     : SURF= 81 : AREA=     17.56 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL  =INTWALL    : SURF= 82 : AREA=     58.14 : INTERNAL
WALL  =INTWALL    : SURF= 83 : AREA=     58.14 : INTERNAL
WALL  =INTFLOOR   : SURF= 84 : AREA=      85.5 : ADJACENT=ZONE5 : FRONT
WALL  =INTFLOOR   : SURF= 86 : AREA=      85.5 : ADJACENT=ZONE11 : FRONT : GEOSURF=0.3
WALL  =INTWALL    : SURF= 88 : AREA=       9.3 : ADJACENT=ZONE1 : FRONT
WALL  =INTWALL    : SURF= 90 : AREA=      24.7 : ADJACENT=ZONE4 : FRONT
WALL  =OUTWALL    : SURF= 94 : AREA=     16.44 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=TRIPLE     : SURF= 95 : AREA=     17.56 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL  =INTFLOOR   : SURF= 98 : AREA=      85.5 : ADJACENT=ZONE11 : FRONT : GEOSURF=0.3
WALL  =INTFLOOR   : SURF= 96 : AREA=      85.5 : ADJACENT=ZONE5 : FRONT
WALL  =INTWALL    : SURF=198 : AREA=     29.07 : ADJACENT=ZONE2 : BACK
 REGIME
 GAIN        = PERS_ISO01 : SCALE= SCHEDULE 78*SUMMER_OCCUPANCY
 INFILTRATION= INFIL001
 VENTILATION = VENTMECH
 COOLING     = COOL001
 HEATING     = HEAT001
 CAPACITANCE = 6909.12 : VOLUME= 719.7   : TINITIAL= 20      : PHINITIAL= 50      : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  Z o n e  ZONE9  /  A i r n o d e  ZONE9
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE9
AIRNODE ZONE9
WALL  =INTWALL    : SURF= 71 : AREA=     25.58 : ADJACENT=ZONE8 : BACK
WALL  =INTWALL    : SURF=100 : AREA=      25.6 : ADJACENT=ZONE1 : FRONT
WALL  =OUTWALL    : SURF=102 : AREA=     14.52 : EXTERNAL : ORI=WEST : FSKY=0.5
WINDOW=POS016     : SURF=103 : AREA=      2.48 : EXTERNAL : ORI=WEST : FSKY=0.5 : ESHADE=INPUT 0.7*S_WEST
WALL  =INTWALL    : SURF=104 : AREA=        17 : ADJACENT=ZONE1 : FRONT : GEOSURF=0.1
WALL  =INTFLOOR   : SURF=106 : AREA=      37.6 : ADJACENT=ZONE7 : FRONT
WALL  =INTFLOOR   : SURF=108 : AREA=      37.6 : ADJACENT=ZONE12 : FRONT : GEOSURF=0.6
 REGIME
 GAIN        = PERS_ISO01 : SCALE= SCHEDULE 2*SUMMER_OCCUPANCY
 INFILTRATION= INFIL001
 COOLING     = COOL001
 HEATING     = HEAT001
 CAPACITANCE = 889.92  : VOLUME= 92.7    : TINITIAL= 20      : PHINITIAL= 50      : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  Z o n e  ZONE6  /  A i r n o d e  ZONE6
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE6
AIRNODE ZONE6
WALL  =INTFLOOR   : SURF= 77 : AREA=     86.78 : ADJACENT=ZONE8 : BACK : GEOSURF=0.6
WALL  =INTWALL    : SURF=110 : AREA=      26.7 : ADJACENT=ZONE7 : FRONT
WALL  =INTWALL    : SURF=112 : AREA=       9.3 : ADJACENT=ZONE1 : FRONT
WALL  =OUTWALL    : SURF=114 : AREA=     18.44 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=TRIPLE     : SURF=119 : AREA=     17.56 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL  =OUTWALL    : SURF=120 : AREA=     30.35 : EXTERNAL : ORI=WEST : FSKY=0.5
WALL  =INTWALL    : SURF=121 : AREA=     30.35 : ADJACENT=ZONE5 : FRONT
WALL  =ROOF       : SURF=123 : AREA=     86.78 : EXTERNAL : ORI=HORIZONTAL : FSKY=0.5
 REGIME
 GAIN        = PERS_ISO01 : SCALE= SCHEDULE 26*SUMMER_OCCUPANCY
 INFILTRATION= INFIL001
 VENTILATION = VENTMECH
 COOLING     = COOL001
 HEATING     = HEAT001
 CAPACITANCE = 2295.35 : VOLUME= 239.1   : TINITIAL= 20      : PHINITIAL= 50      : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  Z o n e  ZONE11  /  A i r n o d e  ZONE11
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE11
AIRNODE ZONE11
WALL  =INTFLOOR   : SURF= 79 : AREA=     86.78 : ADJACENT=ZONE8 : BACK
WALL  =INTFLOOR   : SURF= 87 : AREA=      85.5 : ADJACENT=ZONE8 : BACK
WALL  =INTFLOOR   : SURF= 99 : AREA=      85.5 : ADJACENT=ZONE8 : BACK
WALL  =INTWALL    : SURF= 92 : AREA=      25.6 : ADJACENT=ZONE12 : FRONT
WALL  =INTWALL    : SURF=242 : AREA=     8.925 : ADJACENT=ZONE1 : FRONT
WALL  =OUTWALL    : SURF=244 : AREA=     19.76 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=POS005_009 : SURF=245 : AREA=     14.75 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL  =OUTWALL    : SURF=246 : AREA=     29.07 : EXTERNAL : ORI=WEST : FSKY=0.5
WALL  =INTWALL    : SURF=247 : AREA=     58.14 : INTERNAL
WALL  =INTWALL    : SURF=248 : AREA=     58.14 : INTERNAL
WALL  =INTFLOOR   : SURF=250 : AREA=     86.78 : ADJACENT=ZONE24 : FRONT : GEOSURF=0.3
WALL  =INTWALL    : SURF=252 : AREA=     8.925 : ADJACENT=ZONE1 : FRONT
WALL  =INTWALL    : SURF=254 : AREA=    33.575 : ADJACENT=ZONE4 : FRONT
WALL  =OUTWALL    : SURF=256 : AREA=     24.94 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=TRIPLE     : SURF=257 : AREA=     17.56 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL  =INTFLOOR   : SURF=258 : AREA=   106.875 : ADJACENT=ZONE24 : FRONT : GEOSURF=0.4
WALL  =INTWALL    : SURF=260 : AREA=     8.925 : ADJACENT=ZONE1 : FRONT
WALL  =INTWALL    : SURF=262 : AREA=    16.575 : ADJACENT=ZONE4 : FRONT
WALL  =OUTWALL    : SURF=264 : AREA=     13.56 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=POS005_010 : SURF=265 : AREA=     11.94 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL  =INTFLOOR   : SURF=266 : AREA=        51 : ADJACENT=ZONE29 : FRONT : GEOSURF=0.3
WALL  =INTFLOOR   : SURF=268 : AREA=    13.125 : BOUNDARY=IDENTICAL
WALL  =INTWALL    : SURF=269 : AREA=     29.07 : ADJACENT=ZONE14 : FRONT
 REGIME
 GAIN        = PERS_ISO01 : SCALE= SCHEDULE 68*SUMMER_OCCUPANCY
 INFILTRATION= INFIL001
 VENTILATION = VENTMECH
 COOLING     = COOL001
 HEATING     = HEAT001
 CAPACITANCE = 6909.98 : VOLUME= 719.79  : TINITIAL= 20      : PHINITIAL= 50      : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  Z o n e  ZONE4  /  A i r n o d e  ZONE4
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE4
AIRNODE ZONE4
WALL  =INTWALL    : SURF= 55 : AREA=     25.07 : ADJACENT=ZONE8 : BACK
WALL  =INTWALL    : SURF= 91 : AREA=      24.7 : ADJACENT=ZONE8 : BACK
WALL  =INTWALL    : SURF=127 : AREA=      26.2 : ADJACENT=ZONE5 : BACK
WALL  =INTWALL    : SURF=135 : AREA=      26.2 : ADJACENT=ZONE5 : BACK
WALL  =INTWALL    : SURF=255 : AREA=    33.575 : ADJACENT=ZONE11 : BACK
WALL  =INTWALL    : SURF=263 : AREA=    16.575 : ADJACENT=ZONE11 : BACK
WALL  =INTWALL    : SURF=283 : AREA=       9.2 : ADJACENT=ZONE14 : BACK
 REGIME
 CAPACITANCE = 0.12    : VOLUME= 0.1     : TINITIAL= 20      : PHINITIAL= 50      : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  Z o n e  ZONE5  /  A i r n o d e  ZONE5
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE5
AIRNODE ZONE5
WALL  =INTFLOOR   : SURF= 85 : AREA=      85.5 : ADJACENT=ZONE8 : BACK : GEOSURF=0.3
WALL  =INTFLOOR   : SURF= 97 : AREA=      85.5 : ADJACENT=ZONE8 : BACK : GEOSURF=0.3
WALL  =INTWALL    : SURF=122 : AREA=     30.35 : ADJACENT=ZONE6 : BACK
WALL  =INTWALL    : SURF=124 : AREA=       9.3 : ADJACENT=ZONE1 : FRONT
WALL  =INTWALL    : SURF=126 : AREA=      26.2 : ADJACENT=ZONE4 : FRONT
WALL  =OUTWALL    : SURF=128 : AREA=     17.94 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=TRIPLE     : SURF=129 : AREA=     17.56 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL  =INTWALL    : SURF=130 : AREA=      60.7 : INTERNAL
WALL  =ROOF       : SURF=131 : AREA=      85.5 : EXTERNAL : ORI=HORIZONTAL : FSKY=0.5
WALL  =INTWALL    : SURF=132 : AREA=       9.3 : ADJACENT=ZONE1 : FRONT
WALL  =INTWALL    : SURF=134 : AREA=      26.2 : ADJACENT=ZONE4 : FRONT
WALL  =OUTWALL    : SURF=136 : AREA=     17.94 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=TRIPLE     : SURF=137 : AREA=     17.56 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL  =INTWALL    : SURF=138 : AREA=     30.35 : ADJACENT=ZONE2 : FRONT
WALL  =ROOF       : SURF=140 : AREA=      85.5 : EXTERNAL : ORI=HORIZONTAL : FSKY=0.5
 REGIME
 GAIN        = PERS_ISO01 : SCALE= SCHEDULE 52*SUMMER_OCCUPANCY
 INFILTRATION= INFIL001
 VENTILATION = VENTMECH
 COOLING     = COOL001
 HEATING     = HEAT001
 CAPACITANCE = 4613.75 : VOLUME= 480.6   : TINITIAL= 20      : PHINITIAL= 50      : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  Z o n e  ZONE2  /  A i r n o d e  ZONE2
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE2
AIRNODE ZONE2
WALL  =OUTWALL    : SURF=115 : AREA=     17.94 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=TRIPLE     : SURF=116 : AREA=     17.56 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL  =INTWALL    : SURF=139 : AREA=     30.35 : ADJACENT=ZONE5 : BACK
WALL  =INTWALL    : SURF=148 : AREA=      9.32 : ADJACENT=ZONE1 : FRONT
WALL  =INTWALL    : SURF=150 : AREA=     26.18 : ADJACENT=ZONE3 : FRONT
WALL  =INTWALL    : SURF=152 : AREA=      60.7 : INTERNAL
WALL  =INTWALL    : SURF=153 : AREA=      60.7 : INTERNAL
WALL  =INTWALL    : SURF=154 : AREA=      60.7 : INTERNAL
WALL  =INTWALL    : SURF=155 : AREA=      60.7 : INTERNAL
WALL  =ROOF       : SURF=156 : AREA=      85.5 : EXTERNAL : ORI=HORIZONTAL : FSKY=0.5
WALL  =INTFLOOR   : SURF=157 : AREA=       171 : INTERNAL : GEOSURF=0.2
WALL  =INTWALL    : SURF=158 : AREA=        27 : ADJACENT=ZONE3 : FRONT
WALL  =INTWALL    : SURF=160 : AREA=       8.5 : ADJACENT=ZONE1 : FRONT
WALL  =OUTWALL    : SURF=162 : AREA=     17.94 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=TRIPLE     : SURF=163 : AREA=     17.56 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL  =ROOF       : SURF=164 : AREA=      85.5 : EXTERNAL : ORI=HORIZONTAL : FSKY=0.5
WALL  =INTFLOOR   : SURF=165 : AREA=       171 : INTERNAL : GEOSURF=0.2
WALL  =INTWALL    : SURF=166 : AREA=       8.5 : ADJACENT=ZONE1 : FRONT
WALL  =INTWALL    : SURF=168 : AREA=    35.875 : ADJACENT=ZONE3 : FRONT
WALL  =OUTWALL    : SURF=170 : AREA=    23.995 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=POS005_008 : SURF=171 : AREA=     20.38 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL  =ROOF       : SURF=172 : AREA=   106.875 : EXTERNAL : ORI=HORIZONTAL : FSKY=0.5
WALL  =INTFLOOR   : SURF=173 : AREA=    213.75 : INTERNAL : GEOSURF=0.2
WALL  =INTWALL    : SURF=174 : AREA=      9.33 : ADJACENT=ZONE1 : FRONT
WALL  =INTWALL    : SURF=176 : AREA=    17.295 : ADJACENT=ZONE3 : FRONT
WALL  =OUTWALL    : SURF=178 : AREA=     14.69 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=POS005_010 : SURF=179 : AREA=     11.94 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL  =ROOF       : SURF=180 : AREA=    64.125 : EXTERNAL : ORI=HORIZONTAL : FSKY=0.5
WALL  =INTFLOOR   : SURF=181 : AREA=    128.25 : INTERNAL : GEOSURF=0.2
WALL  =INTWALL    : SURF=182 : AREA=      9.33 : ADJACENT=ZONE1 : FRONT
WALL  =INTWALL    : SURF=184 : AREA=      26.7 : ADJACENT=ZONE3 : FRONT
WALL  =OUTWALL    : SURF=186 : AREA=     18.47 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=TRIPLE     : SURF=188 : AREA=     17.56 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL  =OUTWALL    : SURF=187 : AREA=     30.35 : EXTERNAL : ORI=EAST : FSKY=0.5
WALL  =ROOF       : SURF=189 : AREA=     86.78 : EXTERNAL : ORI=HORIZONTAL : FSKY=0.5
WALL  =INTFLOOR   : SURF=190 : AREA=    173.56 : INTERNAL : GEOSURF=0.2
WALL  =INTWALL    : SURF=191 : AREA=       8.9 : ADJACENT=ZONE1 : FRONT
WALL  =INTWALL    : SURF=193 : AREA=      25.1 : ADJACENT=ZONE3 : FRONT
WALL  =OUTWALL    : SURF=195 : AREA=     16.44 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=TRIPLE     : SURF=196 : AREA=     17.56 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL  =INTWALL    : SURF=197 : AREA=     29.07 : ADJACENT=ZONE8 : FRONT
WALL  =INTWALL    : SURF=199 : AREA=     58.14 : INTERNAL
WALL  =INTWALL    : SURF=200 : AREA=     58.14 : INTERNAL
WALL  =INTWALL    : SURF=201 : AREA=     58.14 : INTERNAL
WALL  =INTWALL    : SURF=202 : AREA=     58.14 : INTERNAL
WALL  =INTFLOOR   : SURF=203 : AREA=      85.5 : ADJACENT=ZONE14 : FRONT
WALL  =INTWALL    : SURF=205 : AREA=      25.9 : ADJACENT=ZONE3 : FRONT
WALL  =INTWALL    : SURF=207 : AREA=       8.1 : ADJACENT=ZONE1 : FRONT
WALL  =OUTWALL    : SURF=209 : AREA=     16.44 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=TRIPLE     : SURF=210 : AREA=     17.56 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL  =INTFLOOR   : SURF=211 : AREA=      85.5 : ADJACENT=ZONE13 : FRONT
WALL  =INTWALL    : SURF=213 : AREA=      34.4 : ADJACENT=ZONE3 : FRONT
WALL  =INTWALL    : SURF=215 : AREA=       8.1 : ADJACENT=ZONE1 : FRONT
WALL  =OUTWALL    : SURF=217 : AREA=     22.12 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=POS2_010_005 : SURF=218 : AREA=     20.38 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL  =INTFLOOR   : SURF=219 : AREA=     42.75 : ADJACENT=ZONE13 : FRONT
WALL  =INTFLOOR   : SURF=221 : AREA=      85.5 : ADJACENT=ZONE14 : FRONT
WALL  =INTWALL    : SURF=223 : AREA=     16.59 : ADJACENT=ZONE3 : FRONT
WALL  =INTWALL    : SURF=225 : AREA=      8.91 : ADJACENT=ZONE1 : FRONT
WALL  =OUTWALL    : SURF=227 : AREA=     13.56 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=POS005_010 : SURF=228 : AREA=     11.94 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL  =INTFLOOR   : SURF=229 : AREA=      44.6 : ADJACENT=ZONE14 : FRONT
WALL  =INTFLOOR   : SURF=231 : AREA=     20.45 : ADJACENT=ZONE1 : FRONT
WALL  =INTWALL    : SURF=233 : AREA=      8.91 : ADJACENT=ZONE1 : FRONT
WALL  =INTWALL    : SURF=235 : AREA=      25.6 : ADJACENT=ZONE3 : FRONT
WALL  =OUTWALL    : SURF=239 : AREA=     16.95 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=TRIPLE     : SURF=240 : AREA=     17.56 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL  =OUTWALL    : SURF=237 : AREA=     29.07 : EXTERNAL : ORI=EAST : FSKY=0.5
WALL  =INTFLOOR   : SURF=238 : AREA=      45.5 : ADJACENT=ZONE14 : FRONT
 REGIME
 GAIN        = PERS_ISO01 : SCALE= SCHEDULE 233*SUMMER_OCCUPANCY
 INFILTRATION= INFIL001
 VENTILATION = VENTMECH
 COOLING     = COOL001
 HEATING     = HEAT001
 CAPACITANCE = 23025.4 : VOLUME= 2398.48 : TINITIAL= 20      : PHINITIAL= 50      : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  Z o n e  ZONE7  /  A i r n o d e  ZONE7
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE7
AIRNODE ZONE7
WALL  =INTFLOOR   : SURF=107 : AREA=      37.6 : ADJACENT=ZONE9 : BACK : GEOSURF=0.6
WALL  =INTWALL    : SURF=111 : AREA=      26.7 : ADJACENT=ZONE6 : BACK
WALL  =INTWALL    : SURF=141 : AREA=      26.7 : ADJACENT=ZONE1 : FRONT
WALL  =OUTWALL    : SURF=143 : AREA=     12.79 : EXTERNAL : ORI=WEST : FSKY=0.5
WINDOW=POS015_016 : SURF=144 : AREA=      4.96 : EXTERNAL : ORI=WEST : FSKY=0.5 : ESHADE=INPUT 0.7*S_WEST
WALL  =INTWALL    : SURF=145 : AREA=     17.75 : ADJACENT=ZONE1 : FRONT
WALL  =ROOF       : SURF=147 : AREA=      37.6 : EXTERNAL : ORI=HORIZONTAL : FSKY=0.5
 REGIME
 GAIN        = PERS_ISO01 : SCALE= SCHEDULE 2*SUMMER_OCCUPANCY
 INFILTRATION= INFIL001
 COOLING     = COOL001
 HEATING     = HEAT001
 CAPACITANCE = 889.92  : VOLUME= 92.7    : TINITIAL= 20      : PHINITIAL= 50      : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  Z o n e  ZONE12  /  A i r n o d e  ZONE12
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE12
AIRNODE ZONE12
WALL  =INTFLOOR   : SURF=109 : AREA=      37.6 : ADJACENT=ZONE9 : BACK
WALL  =INTWALL    : SURF=117 : AREA=      25.6 : ADJACENT=ZONE1 : FRONT
WALL  =INTWALL    : SURF= 93 : AREA=      25.6 : ADJACENT=ZONE11 : BACK
 REGIME
 CAPACITANCE = 0.12    : VOLUME= 0.1     : TINITIAL= 20      : PHINITIAL= 50      : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  Z o n e  ZONE3  /  A i r n o d e  ZONE3
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE3
AIRNODE ZONE3
WALL  =INTWALL    : SURF=151 : AREA=     26.18 : ADJACENT=ZONE2 : BACK
WALL  =INTWALL    : SURF=159 : AREA=        27 : ADJACENT=ZONE2 : BACK
WALL  =INTWALL    : SURF=169 : AREA=    35.875 : ADJACENT=ZONE2 : BACK
WALL  =INTWALL    : SURF=177 : AREA=    17.295 : ADJACENT=ZONE2 : BACK
WALL  =INTWALL    : SURF=185 : AREA=      26.7 : ADJACENT=ZONE2 : BACK
WALL  =INTWALL    : SURF=194 : AREA=      25.1 : ADJACENT=ZONE2 : BACK
WALL  =INTWALL    : SURF=206 : AREA=      25.9 : ADJACENT=ZONE2 : BACK
WALL  =INTWALL    : SURF=214 : AREA=      34.4 : ADJACENT=ZONE2 : BACK
WALL  =INTWALL    : SURF=224 : AREA=     16.59 : ADJACENT=ZONE2 : BACK
WALL  =INTWALL    : SURF=236 : AREA=      25.6 : ADJACENT=ZONE2 : BACK
WALL  =INTFLOOR   : SURF=344 : AREA=    38.125 : ADJACENT=ZONE20 : BACK
 REGIME
 CAPACITANCE = 0.12    : VOLUME= 0.1     : TINITIAL= 20      : PHINITIAL= 50      : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  Z o n e  ZONE14  /  A i r n o d e  ZONE14
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE14
AIRNODE ZONE14
WALL  =INTFLOOR   : SURF=204 : AREA=      85.5 : ADJACENT=ZONE2 : BACK
WALL  =INTFLOOR   : SURF=222 : AREA=      85.5 : ADJACENT=ZONE2 : BACK
WALL  =INTFLOOR   : SURF=230 : AREA=      44.6 : ADJACENT=ZONE2 : BACK
WALL  =INTFLOOR   : SURF=241 : AREA=      45.5 : ADJACENT=ZONE2 : BACK
WALL  =INTWALL    : SURF=270 : AREA=     29.07 : ADJACENT=ZONE11 : BACK
WALL  =INTWALL    : SURF=271 : AREA=     8.925 : ADJACENT=ZONE1 : FRONT
WALL  =INTWALL    : SURF=272 : AREA=    25.075 : ADJACENT=ZONE15 : FRONT
WALL  =OUTWALL    : SURF=275 : AREA=     19.25 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=POS005_009 : SURF=276 : AREA=     14.75 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL  =INTWALL    : SURF=249 : AREA=      29.1 : ADJACENT=ZONE13 : FRONT
WALL  =INTFLOOR   : SURF=278 : AREA=      85.5 : ADJACENT=ZONE27 : FRONT : GEOSURF=0.3
WALL  =INTWALL    : SURF=280 : AREA=      24.8 : ADJACENT=ZONE15 : FRONT
WALL  =INTWALL    : SURF=282 : AREA=       9.2 : ADJACENT=ZONE4 : FRONT
WALL  =OUTWALL    : SURF=284 : AREA=     22.06 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=POS005_010 : SURF=285 : AREA=     11.94 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL  =INTWALL    : SURF=286 : AREA=      29.1 : ADJACENT=ZONE13 : FRONT
WALL  =INTWALL    : SURF=288 : AREA=      40.4 : INTERNAL
WALL  =INTWALL    : SURF=289 : AREA=      40.4 : INTERNAL
WALL  =INTWALL    : SURF=290 : AREA=      40.4 : INTERNAL
WALL  =INTWALL    : SURF=291 : AREA=      40.4 : INTERNAL
WALL  =INTFLOOR   : SURF=292 : AREA=      85.5 : ADJACENT=ZONE27 : FRONT : GEOSURF=0.3
WALL  =INTWALL    : SURF=294 : AREA=     12.75 : ADJACENT=ZONE1 : FRONT
WALL  =OUTWALL    : SURF=296 : AREA=      9.25 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=POS005     : SURF=297 : AREA=       3.5 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL  =INTFLOOR   : SURF=298 : AREA=      22.3 : ADJACENT=ZONE27 : FRONT : GEOSURF=0.1
WALL  =INTWALL    : SURF=300 : AREA=     12.75 : ADJACENT=ZONE1 : FRONT
WALL  =OUTWALL    : SURF=302 : AREA=      9.25 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=POS005     : SURF=303 : AREA=       3.5 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL  =INTFLOOR   : SURF=304 : AREA=      22.3 : ADJACENT=ZONE27 : FRONT
WALL  =INTWALL    : SURF=306 : AREA=     12.75 : ADJACENT=ZONE1 : FRONT
WALL  =OUTWALL    : SURF=308 : AREA=       6.4 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=POS027     : SURF=309 : AREA=      6.35 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL  =INTFLOOR   : SURF=310 : AREA=      22.3 : ADJACENT=ZONE27 : FRONT : GEOSURF=0.1
WALL  =INTWALL    : SURF=312 : AREA=     13.26 : ADJACENT=ZONE1 : FRONT
WALL  =OUTWALL    : SURF=314 : AREA=      9.76 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=POS005     : SURF=315 : AREA=       3.5 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL  =OUTWALL    : SURF=316 : AREA=      20.2 : EXTERNAL : ORI=EAST : FSKY=0.5
WALL  =INTFLOOR   : SURF=317 : AREA=      23.2 : ADJACENT=ZONE27 : FRONT
 REGIME
 GAIN        = PERS_ISO01 : SCALE= SCHEDULE 22*SUMMER_OCCUPANCY
 INFILTRATION= INFIL001
 VENTILATION = VENTMECH
 COOLING     = COOL001
 HEATING     = HEAT001
 CAPACITANCE = 6932.16 : VOLUME= 722.1   : TINITIAL= 20      : PHINITIAL= 50      : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  Z o n e  ZONE13  /  A i r n o d e  ZONE13
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE13
AIRNODE ZONE13
WALL  =INTFLOOR   : SURF=212 : AREA=      85.5 : ADJACENT=ZONE2 : BACK
WALL  =INTFLOOR   : SURF=220 : AREA=     42.75 : ADJACENT=ZONE2 : BACK
WALL  =INTWALL    : SURF=277 : AREA=      29.1 : ADJACENT=ZONE14 : BACK
WALL  =INTWALL    : SURF=287 : AREA=      29.1 : ADJACENT=ZONE14 : BACK
WALL  =INTWALL    : SURF=320 : AREA=      25.9 : ADJACENT=ZONE20 : FRONT
WALL  =INTWALL    : SURF=322 : AREA=       8.5 : ADJACENT=ZONE1 : FRONT
WALL  =OUTWALL    : SURF=324 : AREA=     19.25 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=POS005_009 : SURF=325 : AREA=     14.75 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL  =INTWALL    : SURF=326 : AREA=     58.14 : INTERNAL
WALL  =INTFLOOR   : SURF=327 : AREA=      85.5 : ADJACENT=ZONE27 : FRONT : GEOSURF=0.6
WALL  =INTWALL    : SURF=329 : AREA=       8.5 : ADJACENT=ZONE1 : FRONT
WALL  =INTWALL    : SURF=331 : AREA=       8.5 : ADJACENT=ZONE15 : FRONT
WALL  =OUTWALL    : SURF=333 : AREA=     10.65 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=POS027     : SURF=334 : AREA=      6.35 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL  =INTFLOOR   : SURF=335 : AREA=     42.75 : ADJACENT=ZONE27 : FRONT
 REGIME
 GAIN        = PERS_ISO01 : SCALE= SCHEDULE 29*SUMMER_OCCUPANCY
 INFILTRATION= INFIL001
 VENTILATION = VENTMECH
 COOLING     = COOL001
 HEATING     = HEAT001
 CAPACITANCE = 3430    : VOLUME= 357.3   : TINITIAL= 20      : PHINITIAL= 50      : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  Z o n e  ZONE24  /  A i r n o d e  ZONE24
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE24
AIRNODE ZONE24
WALL  =INTFLOOR   : SURF=251 : AREA=     86.78 : ADJACENT=ZONE11 : BACK
WALL  =INTFLOOR   : SURF=259 : AREA=   106.875 : ADJACENT=ZONE11 : BACK
WALL  =INTWALL    : SURF=401 : AREA=      35.7 : ADJACENT=ZONE25 : FRONT
WALL  =INTWALL    : SURF=403 : AREA=      12.5 : ADJACENT=ZONE21 : FRONT
WALL  =OUTWALL    : SURF=405 : AREA=     33.65 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=POS005_009 : SURF=406 : AREA=     14.55 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL  =OUTWALL    : SURF=407 : AREA=      40.6 : EXTERNAL : ORI=WEST : FSKY=0.5
WALL  =INTWALL    : SURF=408 : AREA=      64.8 : INTERNAL
WALL  =INTWALL    : SURF=409 : AREA=      64.8 : INTERNAL
WALL  =GROUNDFLOOR : SURF=410 : AREA=     86.78 : EXTERNAL : ORI=HORIZONTAL : FSKY=0.5 : GEOSURF=0.4
WALL  =INTWALL    : SURF=411 : AREA=      29.7 : ADJACENT=ZONE21 : FRONT
WALL  =OUTWALL    : SURF=413 : AREA=     20.54 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=POS013_027 : SURF=414 : AREA=      9.16 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL  =GROUNDFLOOR : SURF=415 : AREA=     53.35 : EXTERNAL : ORI=HORIZONTAL : FSKY=0.5 : GEOSURF=0.2
WALL  =INTWALL    : SURF=416 : AREA=     29.64 : ADJACENT=ZONE21 : FRONT
WALL  =OUTWALL    : SURF=418 : AREA=     23.29 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=POS027     : SURF=419 : AREA=      6.35 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL  =INTWALL    : SURF=420 : AREA=      32.4 : ADJACENT=ZONE29 : FRONT
WALL  =GROUNDFLOOR : SURF=422 : AREA=     53.35 : EXTERNAL : ORI=HORIZONTAL : FSKY=0.5 : GEOSURF=0.2
 REGIME
 GAIN        = PERS_ISO01 : SCALE= SCHEDULE 58*SUMMER_OCCUPANCY
 INFILTRATION= INFIL001
 VENTILATION = VENTMECH
 COOLING     = COOL001
 CAPACITANCE = 4591.68 : VOLUME= 478.3   : TINITIAL= 20      : PHINITIAL= 50      : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  Z o n e  ZONE29  /  A i r n o d e  ZONE29
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE29
AIRNODE ZONE29
WALL  =INTFLOOR   : SURF=267 : AREA=        51 : ADJACENT=ZONE11 : BACK
WALL  =INTWALL    : SURF=319 : AREA=      17.8 : BOUNDARY=IDENTICAL
WALL  =INTWALL    : SURF=421 : AREA=      32.4 : ADJACENT=ZONE24 : BACK
 REGIME
 CAPACITANCE = 0.12    : VOLUME= 0.1     : TINITIAL= 20      : PHINITIAL= 50      : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  Z o n e  ZONE15  /  A i r n o d e  ZONE15
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE15
AIRNODE ZONE15
WALL  =INTWALL    : SURF=274 : AREA=    25.075 : ADJACENT=ZONE14 : BACK
WALL  =INTWALL    : SURF=281 : AREA=      24.8 : ADJACENT=ZONE14 : BACK
WALL  =INTWALL    : SURF=332 : AREA=       8.5 : ADJACENT=ZONE13 : BACK
WALL  =INTWALL    : SURF=340 : AREA=        17 : ADJACENT=ZONE20 : BACK
 REGIME
 CAPACITANCE = 0.12    : VOLUME= 0.1     : TINITIAL= 20      : PHINITIAL= 50      : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  Z o n e  ZONE27  /  A i r n o d e  ZONE27
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE27
AIRNODE ZONE27
WALL  =INTFLOOR   : SURF=279 : AREA=      85.5 : ADJACENT=ZONE14 : BACK
WALL  =INTFLOOR   : SURF=293 : AREA=      85.5 : ADJACENT=ZONE14 : BACK
WALL  =INTFLOOR   : SURF=299 : AREA=      22.3 : ADJACENT=ZONE14 : BACK
WALL  =INTFLOOR   : SURF=305 : AREA=      22.3 : ADJACENT=ZONE14 : BACK
WALL  =INTFLOOR   : SURF=311 : AREA=      22.3 : ADJACENT=ZONE14 : BACK
WALL  =INTFLOOR   : SURF=318 : AREA=      23.2 : ADJACENT=ZONE14 : BACK
WALL  =INTFLOOR   : SURF=328 : AREA=      85.5 : ADJACENT=ZONE13 : BACK
WALL  =INTFLOOR   : SURF=336 : AREA=     42.75 : ADJACENT=ZONE13 : BACK
WALL  =INTWALL    : SURF=348 : AREA=      36.2 : ADJACENT=ZONE26 : BACK
 REGIME
 CAPACITANCE = 0.12    : VOLUME= 0.1     : TINITIAL= 20      : PHINITIAL= 50      : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  Z o n e  ZONE20  /  A i r n o d e  ZONE20
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE20
AIRNODE ZONE20
WALL  =INTWALL    : SURF=321 : AREA=      25.9 : ADJACENT=ZONE13 : BACK
WALL  =INTWALL    : SURF=337 : AREA=      25.9 : ADJACENT=ZONE1 : FRONT
WALL  =INTWALL    : SURF=339 : AREA=        17 : ADJACENT=ZONE15 : FRONT
WALL  =INTWALL    : SURF=341 : AREA=        17 : ADJACENT=ZONE1 : FRONT
WALL  =INTFLOOR   : SURF=343 : AREA=    38.125 : ADJACENT=ZONE3 : FRONT
WALL  =INTFLOOR   : SURF=345 : AREA=    38.125 : ADJACENT=ZONE26 : FRONT
 REGIME
 INFILTRATION= INFIL001
 CAPACITANCE = 924.48  : VOLUME= 96.3    : TINITIAL= 20      : PHINITIAL= 50      : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  Z o n e  ZONE26  /  A i r n o d e  ZONE26
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE26
AIRNODE ZONE26
WALL  =INTFLOOR   : SURF=346 : AREA=    38.125 : ADJACENT=ZONE20 : BACK
WALL  =INTWALL    : SURF=347 : AREA=      36.2 : ADJACENT=ZONE27 : FRONT
 REGIME
 CAPACITANCE = 0.12    : VOLUME= 0.1     : TINITIAL= 20      : PHINITIAL= 50      : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  Z o n e  ZONE30  /  A i r n o d e  ZONE30
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE30
AIRNODE ZONE30
WALL  =INTFLOOR   : SURF=356 : AREA=      27.1 : ADJACENT=ZONE17 : BACK
WALL  =OUTWALL    : SURF=365 : AREA=     30.64 : EXTERNAL : ORI=SOUTH : FSKY=0.5
WINDOW=TRIPLE     : SURF=366 : AREA=     17.56 : EXTERNAL : ORI=SOUTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_SOUTH
WALL  =INTFLOOR   : SURF=376 : AREA=     47.58 : ADJACENT=ZONE18 : BACK
WALL  =INTFLOOR   : SURF=400 : AREA=      49.5 : ADJACENT=ZONE19 : BACK
 REGIME
 CAPACITANCE = 0.12    : VOLUME= 0.1     : TINITIAL= 20      : PHINITIAL= 50      : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  Z o n e  ZONE22  /  A i r n o d e  ZONE22
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE22
AIRNODE ZONE22
WALL  =INTFLOOR   : SURF=364 : AREA=      64.5 : ADJACENT=ZONE17 : BACK
WALL  =OUTWALL    : SURF=367 : AREA=     29.94 : EXTERNAL : ORI=SOUTH : FSKY=0.5
WINDOW=TRIPLE     : SURF=368 : AREA=     17.56 : EXTERNAL : ORI=SOUTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_SOUTH
WALL  =INTFLOOR   : SURF=388 : AREA=         4 : ADJACENT=ZONE18 : BACK
WALL  =INTFLOOR   : SURF=395 : AREA=      18.7 : ADJACENT=ZONE18 : BACK
 REGIME
 CAPACITANCE = 0.12    : VOLUME= 0.1     : TINITIAL= 20      : PHINITIAL= 50      : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  Z o n e  ZONE18  /  A i r n o d e  ZONE18
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE18
AIRNODE ZONE18
WALL  =OUTWALL    : SURF=369 : AREA=     11.59 : EXTERNAL : ORI=SOUTH : FSKY=0.5
WINDOW=POS023     : SURF=370 : AREA=      9.28 : EXTERNAL : ORI=SOUTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_SOUTH
WALL  =INTWALL    : SURF=371 : AREA=     20.87 : ADJACENT=ZONE1 : FRONT
WALL  =INTWALL    : SURF=373 : AREA=      32.1 : BOUNDARY=IDENTICAL
WALL  =INTWALL    : SURF=374 : AREA=      64.2 : INTERNAL
WALL  =INTFLOOR   : SURF=375 : AREA=     47.58 : ADJACENT=ZONE30 : FRONT : GEOSURF=0.6
WALL  =INTFLOOR   : SURF=377 : AREA=     47.58 : ADJACENT=ZONE31 : FRONT
WALL  =INTWALL    : SURF=380 : AREA=     7.125 : BOUNDARY=IDENTICAL
WALL  =INTWALL    : SURF=381 : AREA=     7.125 : ADJACENT=ZONE1 : FRONT
WALL  =INTWALL    : SURF=383 : AREA=      7.91 : ADJACENT=ZONE1 : FRONT
WALL  =INTFLOOR   : SURF=385 : AREA=         4 : ADJACENT=ROOM228 : FRONT
WALL  =INTFLOOR   : SURF=387 : AREA=         4 : ADJACENT=ZONE22 : FRONT
WALL  =OUTWALL    : SURF=389 : AREA=    10.875 : EXTERNAL : ORI=SOUTH : FSKY=0.5
WALL  =INTWALL    : SURF=390 : AREA=     24.15 : ADJACENT=ZONE1 : FRONT
WALL  =INTFLOOR   : SURF=392 : AREA=      18.7 : ADJACENT=ROOM228 : FRONT
WALL  =INTFLOOR   : SURF=394 : AREA=      18.7 : ADJACENT=ZONE22 : FRONT
 REGIME
 INFILTRATION= INFIL001
 CAPACITANCE = 1614.3  : VOLUME= 168.16  : TINITIAL= 20      : PHINITIAL= 50      : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  Z o n e  ZONE25  /  A i r n o d e  ZONE25
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE25
AIRNODE ZONE25
WALL  =INTWALL    : SURF=402 : AREA=      35.7 : ADJACENT=ZONE24 : BACK
WALL  =INTWALL    : SURF=423 : AREA=      35.7 : BOUNDARY=IDENTICAL
 REGIME
 CAPACITANCE = 971.52  : VOLUME= 101.2   : TINITIAL= 20      : PHINITIAL= 50      : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  Z o n e  ZONE21  /  A i r n o d e  ZONE21
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE21
AIRNODE ZONE21
WALL  =INTWALL    : SURF=404 : AREA=      12.5 : ADJACENT=ZONE24 : BACK
WALL  =INTWALL    : SURF=412 : AREA=      29.7 : ADJACENT=ZONE24 : BACK
WALL  =INTWALL    : SURF=417 : AREA=     29.64 : ADJACENT=ZONE24 : BACK
 REGIME
 CAPACITANCE = 0.12    : VOLUME= 0.1     : TINITIAL= 20      : PHINITIAL= 50      : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  O u t p u t s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
OUTPUTS
 TRANSFER : TIMEBASE=1.000
 AIRNODES = ROOM228 
 NTYPES =   1 : TAIR - air temperature of zone
 AIRNODES = ROOM228 
 NTYPES =   2 : QSENS - sensible energy demand of zone, heating(-), cooling(+)
        =   4 : QINF - sensible infiltration energy gain of zone
        =   5 : QVENT - tsensible ventilation energy gain of zone
        =  25 : TOP - operative zone temperature
        =  30 : QHEAT - sensible heating demand of zone (positive values)
        =  31 : QCOOL - sensible cooling demand of zone (positive values)
 AIRNODES = ROOM228 
 NTYPES = 904 : BAL_4 - energy balance for all zones
        = 906 : SURF = 1, 2, 6, 7, 3,  : BAL_6 - energy balance for a surface
 AIRNODES = ROOM228 
 NTYPES =   9 : RELHUM - relativ humidity of zone air
        =  17 : SURF = 1, 2, 6, 7, 3,  : TSI - inside surface temperature
        =  18 : SURF = 1, 2, 6, 7, 3,  : TSO - outside surface temperature
 AIRNODES = ROOM228 
 NTYPES = 904 : BAL_4 - energy balance for all zones
        = 901 : BAL_1 - solar balance for all zones
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*  E n d
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
END
_EXTENSION_WINPOOL_START_
WINDOW 4.1  DOE-2 Data File : Multi Band Calculation
Unit System : SI
Name        : TRNSYS 15 WINDOW LIB
Desc        : Waermeschutzglas,Ar, 1.4 71/59
Window ID   : 2001
Tilt        : 90.0
Glazings    : 2
Frame       : 11                       2.270
Spacer      :  1 Class1                2.330  -0.010   0.138
Total Height: 1219.2 mm
Total Width :  914.4 mm
Glass Height: 1079.5 mm
Glass Width :  774.7 mm
Mullion     : None
Gap        Thick   Cond  dCond    Vis   dVis   Dens   dDens     Pr     dPr
1 Argon     16.0 0.01620  5.000  2.110  6.300  1.780 -0.0060  0.680 0.00066
2              0       0      0      0      0      0       0      0       0
3              0       0      0      0      0      0       0      0       0
4              0       0      0      0      0      0       0      0       0
5              0       0      0      0      0      0       0      0       0
Angle     0    10    20    30    40    50    60    70    80    90 Hemis
Tsol  0.426 0.428 0.422 0.413 0.402 0.380 0.333 0.244 0.113 0.000 0.354
Abs1  0.118 0.118 0.120 0.123 0.129 0.135 0.142 0.149 0.149 0.000 0.132
Abs2  0.190 0.192 0.198 0.201 0.200 0.199 0.199 0.185 0.117 0.000 0.191
Abs3      0     0     0     0     0     0     0     0     0     0     0
Abs4      0     0     0     0     0     0     0     0     0     0     0
Abs5      0     0     0     0     0     0     0     0     0     0     0
Abs6      0     0     0     0     0     0     0     0     0     0     0
Rfsol 0.266 0.262 0.260 0.262 0.269 0.286 0.326 0.422 0.621 1.000 0.314
Rbsol 0.215 0.209 0.207 0.210 0.219 0.237 0.272 0.356 0.560 0.999 0.260
Tvis  0.706 0.710 0.701 0.688 0.670 0.635 0.556 0.403 0.188 0.000 0.590
Rfvis 0.121 0.115 0.114 0.118 0.132 0.163 0.228 0.376 0.649 1.000 0.203
Rbvis 0.103 0.096 0.093 0.096 0.108 0.132 0.179 0.286 0.520 0.999 0.162
SHGC  0.589 0.593 0.591 0.586 0.574 0.551 0.505 0.405 0.218 0.000 0.518
SC: 0.55
Layer ID#         9052     9065        0        0        0        0
Tir              0.000    0.000        0        0        0        0
Emis F           0.840    0.140        0        0        0        0
Emis B           0.840    0.840        0        0        0        0
Thickness(mm)      4.0      4.0        0        0        0        0
Cond(W/m2-C     ) 225.0    225.0        0        0        0        0
Spectral File     None     None     None     None     None     None
Overall and Center of Glass Ig U-values (W/m2-C)
Outdoor Temperature                 -17.8 C      15.6 C      26.7 C      37.8 C
Solar      WdSpd  hcout hrout  hin
(W/m2)     (m/s)     (W/m2-C)
0        0.00  12.25  3.25  7.62  1.54 1.54  1.31 1.31  1.35 1.35  1.47 1.47
0        6.71  25.47  3.21  7.64  1.62 1.62  1.36 1.36  1.40 1.40  1.53 1.53
783        0.00  12.25  3.39  7.99  1.69 1.69  1.54 1.54  1.51 1.51  1.54 1.54
783        6.71  25.47  3.30  7.81  1.79 1.79  1.63 1.63  1.58 1.58  1.59 1.59
WINDOW 4.1  DOE-2 Data File : Multi Band Calculation
Unit System : SI
Name        : TRNSYS 15 WINDOW LIB
Desc        : Insulating, 0.7, Krypton
Window ID   : 4001
Tilt        : 90.0
Glazings    : 3
Frame       : 11                       2.270
Spacer      :  1 Class1                2.330  -0.010   0.138
Total Height: 1219.2 mm
Total Width :  914.4 mm
Glass Height: 1079.5 mm
Glass Width :  774.7 mm
Mullion     : None
Gap        Thick   Cond  dCond    Vis   dVis   Dens   dDens     Pr     dPr
1 Krypton    8.0 0.00860  2.800  2.280  7.500  3.740 -0.0137  0.660 0.00002
2 Krypton    8.0 0.00860  2.800  2.280  7.500  3.740 -0.0137  0.660 0.00002
3              0       0      0      0      0      0       0      0       0
4              0       0      0      0      0      0       0      0       0
5              0       0      0      0      0      0       0      0       0
Angle     0    10    20    30    40    50    60    70    80    90 Hemis
Tsol  0.268 0.270 0.263 0.253 0.243 0.223 0.183 0.116 0.042 0.000 0.207
Abs1  0.327 0.330 0.339 0.345 0.347 0.351 0.367 0.380 0.313 0.001 0.347
Abs2  0.066 0.066 0.067 0.068 0.070 0.071 0.070 0.064 0.051 0.000 0.067
Abs3  0.108 0.110 0.112 0.113 0.110 0.107 0.101 0.082 0.041 0.000 0.100
Abs4      0     0     0     0     0     0     0     0     0     0     0
Abs5      0     0     0     0     0     0     0     0     0     0     0
Abs6      0     0     0     0     0     0     0     0     0     0     0
Rfsol 0.231 0.223 0.220 0.221 0.230 0.247 0.279 0.357 0.554 0.999 0.269
Rbsol 0.231 0.223 0.220 0.221 0.230 0.247 0.279 0.357 0.554 0.999 0.269
Tvis  0.625 0.632 0.615 0.595 0.570 0.523 0.425 0.265 0.097 0.000 0.484
Rfvis 0.137 0.125 0.121 0.125 0.142 0.172 0.226 0.336 0.554 0.999 0.199
Rbvis 0.137 0.125 0.121 0.125 0.142 0.172 0.226 0.336 0.554 0.999 0.199
SHGC  0.407 0.412 0.406 0.398 0.387 0.365 0.319 0.233 0.112 0.000 0.341
SC: 0.39
Layer ID#         9059F    9052     9060        0        0        0
Tir              0.000    0.000    0.000        0        0        0
Emis F           0.840    0.840    0.070        0        0        0
Emis B           0.070    0.840    0.840        0        0        0
Thickness(mm)      4.0      4.0      4.0        0        0        0
Cond(W/m2-C     ) 225.0    225.0    225.0        0        0        0
Spectral File     None     None     None     None     None     None
Overall and Center of Glass Ig U-values (W/m2-C)
Outdoor Temperature                 -17.8 C      15.6 C      26.7 C      37.8 C
Solar      WdSpd  hcout hrout  hin
(W/m2)     (m/s)     (W/m2-C)
0        0.00  12.25  3.20  7.17  0.63 0.63  0.65 0.65  0.67 0.67  0.69 0.69
0        6.71  25.47  3.19  7.18  0.64 0.64  0.66 0.66  0.68 0.68  0.71 0.71
783        0.00  12.25  3.55  8.29  0.72 0.72  0.74 0.74  0.77 0.77  0.79 0.79
783        6.71  25.47  3.38  8.21  0.74 0.74  0.75 0.75  0.77 0.77  0.79 0.79
WINDOW 4.1  DOE-2 Data File : Multi Band Calculation
Unit System : SI
Name        : TRNSYS 14.2 WINDOW LIB
Desc        : No glazing = open
Window ID   : 10001
Tilt        : 90.0
Glazings    : 1
Frame       : 11                       2.270
Spacer      :  1 Class1                2.330  -0.010   0.138
Total Height: 1219.2 mm
Total Width :  914.4 mm
Glass Height: 1079.5 mm
Glass Width :  774.7 mm
Mullion     : None
Gap        Thick   Cond  dCond    Vis   dVis   Dens   dDens     Pr     dPr
1              0       0      0      0      0      0       0      0       0
2              0       0      0      0      0      0       0      0       0
3              0       0      0      0      0      0       0      0       0
4              0       0      0      0      0      0       0      0       0
5              0       0      0      0      0      0       0      0       0
Angle     0    10    20    30    40    50    60    70    80    90 Hemis
Tsol  1.000 1.000 1.000 1.000 1.000 1.000 1.000 1.000 1.000 1.000 0.999
Abs1  0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.001 0.000 0.001
Abs2      0     0     0     0     0     0     0     0     0     0     0
Abs3      0     0     0     0     0     0     0     0     0     0     0
Abs4      0     0     0     0     0     0     0     0     0     0     0
Abs5      0     0     0     0     0     0     0     0     0     0     0
Abs6      0     0     0     0     0     0     0     0     0     0     0
Rfsol 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000
Rbsol 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000
Tvis  1.000 1.000 1.000 1.000 1.000 1.000 1.000 1.000 1.000 1.000 0.999
Rfvis 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000
Rbvis 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000
SHGC  1.000 1.000 1.000 1.000 1.000 1.000 1.000 1.000 1.000 0.000 1.000
SC: 1.0
Layer ID#         9052        0        0        0        0        0
Tir              0.000        0        0        0        0        0
Emis F           1.000        0        0        0        0        0
Emis B           1.000        0        0        0        0        0
Thickness(mm)    0.001        0        0        0        0        0
Cond(W/m2-C     ) 999.0        0        0        0        0        0
Spectral File     None     None     None     None     None     None
Overall and Center of Glass Ig U-values (W/m2-C)
Outdoor Temperature                 -17.8 C      15.6 C      26.7 C      37.8 C
Solar      WdSpd  hcout hrout  hin
(W/m2)     (m/s)     (W/m2-C)
0        0.00  12.25  3.42  8.23  5.27 5.27  4.95 4.95  4.94 4.94  5.53 5.53
0        6.71  25.47  3.33  8.29  6.26 6.26  5.73 5.73  5.68 5.68  6.46 6.46
783        0.00  12.25  3.49  8.17  5.25 5.25  4.58 4.58  5.24 5.24  5.66 5.66
783        6.71  25.47  3.37  8.27  6.25 6.25  5.53 5.53  5.95 5.95  6.57 6.57
*** END OF LIBRARY ***
***************************************************************************************************
*WinID   Description                              Design         U-Value g-value T-sol Rf-sol T-vis
***************************************************************************************************
  2001   Waermeschutzglas,Ar, 1.4 71/59           4/16/4           1.4  0.589  0.426  0.266  0.706
  4001   Insulating, 0.7, Krypton                 4/8/4/8/4        0.68  0.407  0.268  0.231  0.625
 10001   No glazing = open                        0.001            5.68  1  1  0  1
_EXTENSION_WINPOOL_END_
          ***** WALL TRANSFERFUNCTION CALCULATIONS *****
              ---------- WALL TYPE OUTWALL             ----------
       THERMAL CONDUCTANCE, U=     0.47220 kJ/h m2K; U-Wert=     0.12831 W/m2K
              (incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
                        TRANSFERFUNCTION COEFFICIENTS
   K            A              B              C              D
   0       2.1664880E+00    1.4941859E-08    1.3594604E+02    1.0000000E+00
   1      -5.1626650E+00    1.5678719E-04   -3.2396483E+02   -1.7972276E+00
   2       4.3549828E+00    3.6969384E-03    2.7304031E+02    1.0527114E+00
   3      -1.5684135E+00    9.4702863E-03   -9.9002477E+01   -2.3297156E-01
   4       2.4111882E-01    4.8248043E-03    1.4836511E+01    1.7498815E-02
   5      -1.3025818E-02    5.5308256E-04   -8.5049327E-01   -3.7867559E-04
   6       2.3080730E-04    1.3367874E-05    1.3695979E-02    1.5039292E-06
   7      -7.1874572E-07    5.7183774E-08   -4.8402076E-05
   8       4.8217520E-10    3.4122444E-11    2.8330727E-08
  SUM      1.8715339E-02    1.8715339E-02    1.8715339E-02    3.9633938E-02
              ---------- WALL TYPE INTWALL             ----------
       THERMAL CONDUCTANCE, U=    60.48000 kJ/h m2K; U-Wert=     4.35685 W/m2K
              (incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
                        TRANSFERFUNCTION COEFFICIENTS
   K            A              B              C              D
   0       1.3643561E+02    2.4523224E+01    1.3643561E+02    1.0000000E+00
   1      -8.3598248E+01    3.0209570E+01   -8.3598248E+01   -8.3195199E-02
   2       2.6113051E+00    7.1578697E-01    2.6113051E+00    3.9741583E-06
   3      -7.6332918E-05    1.4006143E-05   -7.6332918E-05
  SUM      5.5448595E+01    5.5448595E+01    5.5448595E+01    9.1680877E-01
              ---------- WALL TYPE INTFLOOR            ----------
       THERMAL CONDUCTANCE, U=    20.02649 kJ/h m2K; U-Wert=     2.85909 W/m2K
              (incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
                        TRANSFERFUNCTION COEFFICIENTS
   K            A              B              C              D
   0       1.3591505E+02    5.5464044E-01    4.8674940E+01    1.0000000E+00
   1      -1.6203728E+02    5.3300691E+00   -5.1743306E+01   -5.9724260E-01
   2       3.5240814E+01    2.5042177E+00    1.1798720E+01    1.9596098E-02
   3      -6.6159971E-01    6.8734728E-02   -2.7285626E-01   -2.7184320E-05
   4       7.2575131E-04    5.1739309E-05    2.1572959E-04
  SUM      8.4577137E+00    8.4577137E+00    8.4577137E+00    4.2232631E-01
              ---------- WALL TYPE ROOF                ----------
       THERMAL CONDUCTANCE, U=     0.34521 kJ/h m2K; U-Wert=     0.09435 W/m2K
              (incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
                        TRANSFERFUNCTION COEFFICIENTS
   K            A              B              C              D
   0       2.2657674E+00    1.9806379E-13    1.3594604E+02    1.0000000E+00
   1      -6.9170769E+00    4.0822983E-07   -4.1502477E+02   -2.4670763E+00
   2       8.1409673E+00    7.0392405E-05    4.8844598E+02    2.2442229E+00
   3      -4.6725429E+00    7.5243126E-04   -2.8042731E+02   -9.3552198E-01
   4       1.3737763E+00    1.5575064E-03    8.2337052E+01    1.8323953E-01
   5      -2.0052002E-01    8.6758907E-04   -1.2054922E+01   -1.5547561E-02
   6       1.3397353E-02    1.4372842E-04    8.0336957E-01    5.3578226E-04
   7      -3.7248398E-04    7.0304141E-06   -2.2231129E-02   -5.5084064E-06
   8       3.2326315E-06    9.4400483E-08    1.9711055E-04    1.8089477E-08
   9      -9.3292759E-09    3.0973529E-10   -5.4537335E-07
  SUM      3.3991809E-03    3.3991809E-03    3.3991806E-03    9.8468336E-03
              ---------- WALL TYPE GROUNDFLOOR         ----------
       THERMAL CONDUCTANCE, U=     0.08007 kJ/h m2K; U-Wert=     0.02216 W/m2K
              (incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
                        TRANSFERFUNCTION COEFFICIENTS
   K            A              B              C              D
   0       2.1664905E+00   -8.2422957E-13    3.7770219E-01    1.0000000E+00
   1      -8.3062921E+00    3.8858170E-12   -1.4482826E+00   -3.2489666E+00
   2       1.3020361E+01    1.0209690E-09    2.2693688E+00    4.1987902E+00
   3      -1.0788399E+01    5.5713242E-08   -1.8795046E+00   -2.7787585E+00
   4       5.1128462E+00    4.4823352E-07    8.9114391E-01    1.0096736E+00
   5      -1.4069812E+00    9.5739196E-07   -2.4581467E-01   -2.0019349E-01
   6       2.1974507E-01    6.8082536E-07    3.8483756E-02    2.0495957E-02
   7      -1.8543765E-02    1.7671247E-07   -3.2275584E-03   -1.0367126E-03
   8       7.9166489E-04    1.7131858E-08    1.3581963E-04    2.5048501E-05
   9      -1.6095843E-05    6.0862308E-10   -2.7993726E-06   -2.5645336E-07
  10       1.4027476E-07    6.9098112E-12    2.5214797E-08
  SUM      2.3380257E-06    2.3376480E-06    2.3377143E-06    2.9195849E-05
  ** ERROR - STABILITY CRITERIA FOR WALL TYPE GROUNDFLOOR          NOT FULLFILLED
CHECK LAYER VALUES 
             NO FILE GENERATED **
    
    