[TRNSYS-users] craeting new type 107, absorption chiller data
    jeannieboef 
    jeannieboef at gmail.com
       
    Wed Nov 14 10:36:20 PST 2012
    
    
  
That's right. at other water inlet temps the other 2 columns of  
performance must also change. try get this performance data fro
  your supplier. Also, don't forget the oft neglected Part Load  
Performance data set.
Sent from my iPhone
On 14.11.2012, at 17:43, David BRADLEY <d.bradley at tess-inc.com> wrote:
> Dear Talib,
>   The method of adding data to extend the range of the performance  
> file is correct. However, you need to also extend the actual  
> performance data as well. For example, the provided data file shows  
> a normalized capacity of 1.0469 and a fraction of design energy  
> input of 0.98 for the following inlet conditions:
>
> Fraction of Design Load: 1.0
> Chilled Water Setpoint: 10.0 C
> Entering Cooling Water Temperature: 32.2 C
> Inlet Hot Water Temperature: 116.11 C
>
> simply changing the inlet hot water temperature range so that the  
> top value is 95C would result in the same performance (normalized  
> capacity of 1.0469 and a fraction of design energy input of 0.98)  
> for a different set of inlet conditions. More likely, the  
> performance of the chiller would be quite different at such a low  
> inlet hot water temperature. Some chillers may simply not be able to  
> operate at lower inlet hot water temperatures.
> Best,
>  David
>
>
>
> On 11/14/2012 07:16, Talib Ahmadu wrote:
>> Dear all,
>> I am using trnsys 16 to model a cooling system. The absorption  
>> chiller i intend to model has its generator temperature outside the  
>> range of the default temperature of type 107 data. What i have done  
>> was to edit the inlet hot water temperature column of performance  
>> data of type 107 from (108.89C to 116.11C) to another range (75C to  
>> 95C), to conform with the chiller i intend to  
>> model.                 Please i want to know if this is correct.
>> Thanks.
>> T. Ahmadu
>>
>>
>> _______________________________________________
>> TRNSYS-users mailing list
>> TRNSYS-users at cae.wisc.edu
>> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>
> -- 
> ***************************
> David BRADLEY
> Principal
> Thermal Energy Systems Specialists, LLC
> 22 North Carroll Street - suite 370
> Madison, WI  53703 USA
>
> P:+1.608.274.2577
> F:+1.608.278.1475
> d.bradley at tess-inc.com
>
> http://www.tess-inc.com
> http://www.trnsys.com
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20121114/5f92f5a6/attachment-0005.htm>
    
    
More information about the TRNSYS-users
mailing list