[TRNSYS-users] adjacent wall not found.
    David BRADLEY 
    d.bradley at tess-inc.com
       
    Fri Nov  9 09:26:03 PST 2012
    
    
  
Sofie,
   Its hard to know without looking at the idf file itself. Often times, 
this is caused by a wall whose normal vector is pointing the wrong way. 
The fix is simple: you simply have to select "reverse faces." The hard 
part is to figure out which wall is giving you trouble. Often times, you 
can look in the *.b17 for an adjacent wall whose adjacency is set to 
"undefined" and then start looking back in the idf file in 
Sketchup/Trnsys3D.
Best,
  David
On 11/7/2012 06:32, Sofie Van den Bergh wrote:
>
> Dear,
>
> When opening my multizone building model from sketchup(.idf) in 
> Trnsys. Open studio, I receive the error for several zones that "an 
> adjacent wall is not found".
>
> Opening the idf in sketchup again and checking each surface, they all 
> are modeled correctly, the wireframe model is pure (no overlappings or 
> mismachings) and the boundary conditions are inserted correctly.
>
> What is possibly causing this error?
>
> What happens if I press "set to undefined" when opening the idf in 
> Trnsys?
>
> Thanks in advance for your help,
>
> ir.-arch. Sofie Van Den Bergh
>
> Project Engineer MEP
>
> VK *HEALTHCARE*| *BUILDINGS*|*INDUSTRY*| *INFRA*
>
> *Value by design*
>
> VK ENGINEERING  Avenue Clemenceaulaan 87, 1070 Bruxelles Brussel, Belgium
> *t*   +32 2 414 07 77 *f*  +32 2 414 04 98 *e*   sofie.v at vkgroup.be *w 
> *www.vkgroup.be
>
> * VK NOMINATED FOR KMO LAUREATE 2012 ***
>
> ****DISCLAIMER****
> This communication is confidential and for the sole useof the 
> addressee. If you are not the intended recipient,
> please immediately notify the sender by e-mail at the address shown 
> and then delete it from your system
> without copying, disclosing or forwarding its contents. Thank you.
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20121109/31a368a7/attachment-0005.htm>
    
    
More information about the TRNSYS-users
mailing list