[TRNSYS-users] Beam radiation distribution calculation with	GEOSURF all set to 0
    Marion Hiller 
    hiller at transsolar.com
       
    Wed Nov  7 04:14:44 PST 2012
    
    
  
Dear Eloise, 
 
thanks for bringing this up. 
The text in the brackets of the manual should be removed.. 
 
If all GESURF values are set to 0, the beam radiation is treated as
diffuse radiation and it is distributed acc. to the 
selected diffuse radiation mode. 
 
Best regards, 
 
Marion Hiller 
 
 
 
Dipl.-Ing. Marion Hiller 
TRANSSOLAR: KlimaEngineering - Technologien für energieeffizientes Bauen
und Nutzerkomfort in Gebäude 
Munich - New York - Stuttgart + 49.711.67976.0 
Transsolar Energietechnik GmbH, Curiestrasse 2, 70563 Stuttgart 
Amtsgericht Stuttgart - HRB 23347, Steuernummer 99073/00911, USt-IdNr.:
DE152272639
Geschäftsführer: Dipl.Ing. Matthias Schuler, Dipl.Ing. Thomas Auer,
Dipl.Phys. Stefan Holst, Prof. Dipl.-Ing. Bleicher 
 
 
  _____  
Von: Sok, Eloise [mailto:Eloise.Sok at saint-gobain.com] 
Gesendet: Mittwoch, 7. November 2012 11:33
An: trnsys-users at cae.wisc.edu
Betreff: [TRNSYS-users] Beam radiation distribution calculation with
GEOSURF all set to 0
Vertraulichkeit: Vertraulich
 
Dear TRNSYS users, 
 
I have a question regarding the calculation of the beam radiation
distribution under the standard mode. 
 
In TRNSYS 17’s manual, it is specified that under the standard mode for
beam radiation distribution calculation, if the GEOSURF values of all
surfaces of a zone are all set to 0, then “the direct radiation is
distributed the same way as the diffuse radiation (by “absorptance”
weighted area ratios)”.
 
But let’s suppose that I run a simulation under the detailed mode for
diffuse radiation distribution and under the standard mode for beam
radiation distribution with geosurf all set to 0. Does it imply that
that on one hand the Gebhart method will be applied for the diffuse part
of the entering solar radiation, and that on the other hand the weighted
area ratios method will be applied for the direct part? Or will the
total entering solar radiation be considered as 100% diffuse and in that
case only the Gebhart method will be applied for calculating the
distribution?
 
Thank you in advance for you responses!
 
Best regards, 
 
 
Eloïse SOK 
--------------------------------------------------
Saint-Gobain Glass France, CRDC 
A.T.O.M. Dpt – Building energy performances’ group 
 
Tel: +33(0)3 44 92 47 88
Mob: +33(0)7 61 68 06 74
E-mail: Eloise.Sok at saint-gobain.com
 
Confidential-property of Saint-Gobain, the information contained herein
are considered confidential. Their representation or reproduction is
prohibited without the prior written consent of the sender or author.
 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20121107/e3a75634/attachment-0005.htm>
    
    
More information about the TRNSYS-users
mailing list