[TRNSYS-users] Fwd: Error creating the wall transfer function coeffients
王洋
wanghongyang1767 at gmail.com
Thu Nov 15 13:28:42 PST 2012
Dear all,
I have a question about *.BUI file. I create a project with about 30 zones
using TRNSYS 16.
Before I created the seventeenth zone using the same exterior wall and
floor as well as interior wall etc for the project, it worked well. But
when the seventeenth zone created, it appeared an ERROR in TRNBuild: Error
creating the wall transfer function coeffients. Please see the attached
figure. The second file is its INF file.
If you had some relative experience, PLEASE tell me how to solve with this
problem.
Thanks in advance!
Br.
wang
---------- Forwarded message ----------
From: ÍõÑó <wanghongyang1767 at gmail.com>
Date: 2012/11/15
Subject: Error creating the wall transfer function coeffients
To: trnsys-users at cae.wisc.edu
Dear all,
I have a question about *.BUI file. I create a project with about 30 zones
using TRNSYS 16.
Before I created the seventeenth zone using the same exterior wall and
floor as well as interior wall etc for the project, it worked well. But
when the seventeenth zone created, it appeared an ERROR in TRNBuild: Error
creating the wall transfer function coeffients. Please see the attached
figure. The second file is its INF file.
If you had some relative experience, PLEASE tell me how to solve with this
problem.
Thanks in advance!
Br.
wang
2012/11/12 <trnsys-users-request at cae.wisc.edu>
> Send TRNSYS-users mailing list submissions to
> trnsys-users at cae.wisc.edu
>
> To subscribe or unsubscribe via the World Wide Web, visit
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
> or, via email, send a message with subject or body 'help' to
> trnsys-users-request at cae.wisc.edu
>
> You can reach the person managing the list at
> trnsys-users-owner at cae.wisc.edu
>
> When replying, please edit your Subject line so it is more specific
> than "Re: Contents of TRNSYS-users digest..."
>
> Today's Topics:
>
> 1. Re: Type 15-2: Relationship between data arrangements,
> simulation times and convergence (David BRADLEY)
> 2. simulation trend opposite to reality (validation)
> (Karol Bandurski)
>
>
> ---------- ÒÑת·¢Óʼþ ----------
> From: David BRADLEY <d.bradley at tess-inc.com>
> To: Flynn Ciaran <ciaran.flynn at aalto.fi>
> Cc: "trnsys-users at cae.wisc.edu" <trnsys-users at cae.wisc.edu>
> Date: Mon, 12 Nov 2012 11:09:38 -0600
> Subject: Re: [TRNSYS-users] Type 15-2: Relationship between data
> arrangements, simulation times and convergence
> Ciar¨¢n,
> Option 1) is incorrect. Type15 is intended to be used with year-long
> weather files that have a 1-hour data interval. The component knows from
> the simulation start and stop time what day of the year it is, so if you
> trick it by setting the simulation start time to hour zero and rearrange
> the weather file to start in the middle of the year, what the Type
> calculates about the sunup and sundown times and what the data file says is
> happening are not going to match at all. Option 2 is the only correct one.
> Best,
> David
>
>
> On 11/12/2012 06:32, Flynn Ciaran wrote:
>
> Hello,****
>
> ** **
>
> I have a couple of questions concerning the relationship between the
> arrangement of data in TMY2 weather files, TRNSYS simulation times and
> convergence errors. I tried looking at the source code but I could not
> figure out the answer..
> I am running a simulation for one year, using Type 15-2 for weather,
> starting at 1h on July 1st and ending at 24h on June 30th. This leaves me
> with two options:
> 1) Either I rearrange the tm2 file to start at 1h on the 1st of July and
> end at 24h on June 30th, and set the simulation start and stop times to 0
> and 8760h respectively, or
> 2) Either I leave the weather file as it is and set the simulation start
> and stop times at 4344h and 13104h respectively.****
>
> ** **
>
> When I use a provided weather file (e.g. CA-BC-Vancouver-718920.tm2) and
> set the simulation time step at 0.1h, I get the following:****
>
> ** **
>
> ** **
>
> Failed convergence time steps****
>
> Time steps where:
> calculated total horizontal radiation > horizontal extraterrestrial
> radiation****
>
> Time steps where:
> direct normal radiation > solar constant****
>
> Time steps where:
> calculated horizontal beam radiation > total horizontal radiation****
>
> 1)****
>
> 7719****
>
> 10664****
>
> 124****
>
> 3498****
>
> 2)****
>
> 6424****
>
> -****
>
> -****
>
> 13****
>
> ** **
>
> So my question are:****
>
> - Why is TRNSYS giving different error messages if the same
> weather data are used ? (I believe that there are no other types in my file
> that could explain the reason for this)****
>
> - What parameters do the radiation values calculated by TRNSYS
> depend on and how are they calculated? ****
>
> - What is the best approach in this situation (minimal radiation
> errors)?****
>
> ** **
>
> Thanks a lot,****
>
> Ciar¨¢n****
>
> ** **
>
> ** **
>
> ** **
>
> ** **
>
>
> _______________________________________________
> TRNSYS-users mailing listTRNSYS-users at cae.wisc.eduhttps://mailman.cae.wisc.edu/listinfo/trnsys-users
>
>
> --
> ***************************
> David BRADLEY
> Principal
> Thermal Energy Systems Specialists, LLC
> 22 North Carroll Street - suite 370
> Madison, WI 53703 USA
>
> P:+1.608.274.2577
> F:+1.608.278.1475d.bradley at tess-inc.com
> http://www.tess-inc.comhttp://www.trnsys.com
>
>
>
> ---------- ÒÑת·¢Óʼþ ----------
> From: "Karol Bandurski" <karol.bandurski at put.poznan.pl>
> To: <trnsys-users at cae.wisc.edu>, <bldg-sim at lists.onebuilding.org>
> Cc:
> Date: Mon, 12 Nov 2012 18:22:45 +0100
> Subject: [TRNSYS-users] simulation trend opposite to reality (validation)
>
> Dear All,****
>
> ** **
>
> I simulate the dwelling in TRNSYS. Last time a try to validate my model
> and I compare simulation results with measurements.****
>
> *Heat consumption* has been measured in dwelling every week (the same day
> of week and the same hour).****
>
> Trnsys simulation generate results for dwelling¡¯s model with ideal heating
> assumptions (set temperature 20/21) ¨CNTYPE2 (sensible *energy demand*).***
> *
>
> ** **
>
> Total *heat consumption (measurements)* of dwelling and *energy demand
> (simulation)* of simulated model are quite similar (36 weeks from
> September to June), but if we look on weekly results there are bigger
> difference with interesting regularity:****
>
> ** **
>
> if *heat consumption* decreases from one week to the next, then *energy
> demand* increase, and vice versa (I enclose graph).****
>
> ** **
>
> Could you tell me what can cause this lack of coincidence?****
>
> I will be grateful for any hints!****
>
> ****
>
> Regards,****
>
> Karol****
>
> ** **
>
> ------------------------------------------------****
>
> Karol Bandurski MSc.****
>
> Institute of Environmental Engineering <http://www.ee.put.poznan.pl/>****
>
> Poznan University of Technology****
>
> www.ee.put.poznan.pl****
>
> www.put.poznan.pl****
>
> ** **
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20121115/03425776/attachment-0001.htm>
-------------- next part --------------
*********************************************************************************************************************************************************************************************************
* TRNBuild 1.0.94
*********************************************************************************************************************************************************************************************************
* BUILDING DESCRIPTIONS FILE TRNSYS
* FOR BUILDING: V:\Gr_Biomasse\Pr_Laufend\102239_FOSBOS_2009\8 Wang\program\TRNSYS\Nov5_Building\BuildingProject12.inf
* GET BY WORKING WITH TRNBuild 1.0 for Windows
*********************************************************************************************************************************************************************************************************
*
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* C o m m e n t s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*#C ---------------------------------------------------- TYPES --------------------------------- *
*#C
*#C -----------------------------------------------------LAYERS --------------------------------- *
*#C
*#C -------------------------------------------------------- INPUTS ----------------------------- *
*#C
*#C ------------------------------------------------------SCHEDULES ----------------------------- *
*#C
*#C -------------------------------------------------------- WALLS ------------------------------ *
*#C
*#C ------------------------------------------------------ WINDOWS ------------------------------ *
*#C
*#C -------------------------------------------------------- GAINS ------------------------------ *
*#C
*#C -------------------------------------------------------- COMFORT----------------------------- *
*#C
*#C ---------------------------------------------------- INFILTRATION --------------------------- *
*#C
*#C ---------------------------------------------------- VENTILATION ---------------------------- *
*#C
*#C ------------------------------------------------------- HEATING ----------------------------- *
*#C
*#C -------------------------------------------------- ORIENTATIONS ----------------------------- *
*#C
*#C -------------------------------------------------------- ZONES ------------------------------ *
*#C
*#C ------------------------------------------------------- BUILDING ---------------------------- *
*#C
*#C ------------------------------- GEOSURF ----------------------------------------------------- *
*#C
*#C --------------------------------------------------- OUTPUTS --------------------------------- *
*#C
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* P r o j e c t
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*+++ PROJECT
*+++ TITLE=FOS
*+++ DESCRIPTION=SCHOOL
*+++ CREATED=WANG
*+++ ADDRESS=ERDING
*+++ CITY=MUNICH
*+++ SWITCH=UNDEFINED
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* P r o p e r t i e s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
PROPERTIES
DENSITY=1.204 : CAPACITY=1.012 : HVAPOR=2454.0 : SIGMA=2.041e-007 : RTEMP=293.15
*--- alpha calculation -------------------
KFLOORUP=7.2 : EFLOORUP=0.31 : KFLOORDOWN=3.888 : EFLOORDOWN=0.31
KCEILUP=7.2 : ECEILUP=0.31 : KCEILDOWN=3.888 : ECEILDOWN=0.31
KVERTICAL=5.76 : EVERTICAL=0.3
*
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
TYPES
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
*
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* L a y e r s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
LAYER CONCRETE
CONDUCTIVITY= 7.56 : CAPACITY= 0.8 : DENSITY= 2400
LAYER INSUL
CONDUCTIVITY= 0.1152 : CAPACITY= 0.8 : DENSITY= 40
LAYER INSULROOF
CONDUCTIVITY= 0.126 : CAPACITY= 0.8 : DENSITY= 40
LAYER ESTRICH
CONDUCTIVITY= 2.16 : CAPACITY= 1 : DENSITY= 800
LAYER AIRLAYER
CONDUCTIVITY=0.09252 : CAPACITY= 1.005 : DENSITY= 1.205
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* I n p u t s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
INPUTS CNAT_1 T_COOL_ON S_NORTH S_SOUTH S_EAST S_WEST BRIGHT WINTER SUMMER TCOOL
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* S c h e d u l e s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
SCHEDULE WEEKEND
HOURS =0.000 1.000 24.0
VALUES=0 0 0
SCHEDULE OCCUPANCY
HOURS =0.000 7.000 9.750 10.000 11.500 11.750 13.250 14.000 16.250 24.0
VALUES=0 1. 0 1. 0 1. 0 1. 0 0
SCHEDULE SUMMER_OCCUPANCY
DAYS=1 2 3 4 5 6 7
HOURLY=OCCUPANCY OCCUPANCY OCCUPANCY OCCUPANCY OCCUPANCY WEEKEND WEEKEND
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* W a l l s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
WALL OUTWALL
LAYERS = CONCRETE INSUL
THICKNESS= 0.26 0.24
ABS-FRONT= 0.75 : ABS-BACK= 0.3
HFRONT = 11 : HBACK= 64
WALL INTWALL
LAYERS = CONCRETE
THICKNESS= 0.125
ABS-FRONT= 0.6 : ABS-BACK= 0.6
HFRONT = 11 : HBACK= 11
WALL INTFLOOR
LAYERS = ESTRICH CONCRETE
THICKNESS= 0.065 0.15
ABS-FRONT= 0.8 : ABS-BACK= 0.4
HFRONT = 11 : HBACK= 11
WALL ROOF
LAYERS = CONCRETE INSULROOF
THICKNESS= 0.3 0.36
ABS-FRONT= 0.35 : ABS-BACK= 0.75
HFRONT = 11 : HBACK= 64
WALL GROUNDFLOOR
LAYERS = AIRLAYER CONCRETE INSUL
THICKNESS= 0.99 0.4 0.2
ABS-FRONT= 0.6 : ABS-BACK= 0.6
HFRONT = 11 : HBACK= 999
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* W i n d o w s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
WINDOW TRIPLE
WINID=4001 : HINSIDE=11 : HOUTSIDE=64 : SLOPE=90 : SPACID=1 : WWID=2.5 : WHEIG=2.8 : FFRAME=0.1896 : UFRAME=3.852 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
CCISHADE=0.5
WINDOW POS016
WINID=4001 : HINSIDE=11 : HOUTSIDE=64 : SLOPE=90 : SPACID=1 : WWID=1.03 : WHEIG=0.8 : FFRAME=0.496 : UFRAME=4.644 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
CCISHADE=0.5
WINDOW POS015_016
WINID=4001 : HINSIDE=11 : HOUTSIDE=64 : SLOPE=90 : SPACID=1 : WWID=1.03 : WHEIG=1.6 : FFRAME=0.3246 : UFRAME=4.644 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
CCISHADE=0.5
WINDOW POS005_008
WINID=4001 : HINSIDE=11 : HOUTSIDE=64 : SLOPE=90 : SPACID=1 : WWID=2.92 : WHEIG=2.8 : FFRAME=0.2882 : UFRAME=4.572 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
CCISHADE=0.5
WINDOW POS005_010
WINID=4001 : HINSIDE=11 : HOUTSIDE=64 : SLOPE=90 : SPACID=1 : WWID=1.67 : WHEIG=2.8 : FFRAME=0.26 : UFRAME=4.572 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
CCISHADE=0.5
WINDOW POS2_010_005
WINID=4001 : HINSIDE=11 : HOUTSIDE=64 : SLOPE=90 : SPACID=1 : WWID=2.92 : WHEIG=2.8 : FFRAME=0.2286 : UFRAME=4.572 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
CCISHADE=0.5
WINDOW POS005_009
WINID=4001 : HINSIDE=11 : HOUTSIDE=64 : SLOPE=90 : SPACID=1 : WWID=2.08 : WHEIG=2.85 : FFRAME=0.1809 : UFRAME=4.572 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
CCISHADE=0.5
WINDOW POS005
WINID=4001 : HINSIDE=11 : HOUTSIDE=64 : SLOPE=90 : SPACID=1 : WWID=0.417 : WHEIG=2.85 : FFRAME=0.44 : UFRAME=4.104 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
CCISHADE=0.5
WINDOW POS027
WINID=4001 : HINSIDE=11 : HOUTSIDE=64 : SLOPE=90 : SPACID=1 : WWID=1.28 : WHEIG=2.85 : FFRAME=0.397 : UFRAME=4.14 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
CCISHADE=0.5
WINDOW POS010
WINID=4001 : HINSIDE=11 : HOUTSIDE=64 : SLOPE=90 : SPACID=1 : WWID=1.25 : WHEIG=2.25 : FFRAME=0.185 : UFRAME=4.572 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
CCISHADE=0.5
WINDOW POS023
WINID=4001 : HINSIDE=11 : HOUTSIDE=64 : SLOPE=90 : SPACID=1 : WWID=1.25 : WHEIG=2.25 : FFRAME=0.296 : UFRAME=4.068 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
CCISHADE=0.5
WINDOW POS025
WINID=4001 : HINSIDE=11 : HOUTSIDE=64 : SLOPE=90 : SPACID=1 : WWID=2.08 : WHEIG=2.825 : FFRAME=0.212 : UFRAME=3.924 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
CCISHADE=0.5
WINDOW POS013_027
WINID=4001 : HINSIDE=11 : HOUTSIDE=64 : SLOPE=90 : SPACID=1 : WWID=1.25 : WHEIG=2.8 : FFRAME=0.312 : UFRAME=4.464 : ABSFRAME=0.6 : RISHADE=0 : RESHADE=0 : REFLISHADE=0.5 : REFLOSHADE=0.5 : ;
CCISHADE=0.5
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* D e f a u l t G a i n s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
GAIN PERS_ISO01
CONVECTIVE=144 : RADIATIVE=72 : HUMIDITY=0.059
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* O t h e r G a i n s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* C o m f o r t
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* I n f i l t r a t i o n
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
INFILTRATION INFIL001
AIRCHANGE=0.01
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* V e n t i l a t i o n
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
VENTILATION VENTMECH
TEMPERATURE=INPUT 2*WINTER+17
AIRCHANGE=SCHEDULE 2.38*SUMMER_OCCUPANCY+0.37
HUMIDITY=50
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* C o o l i n g
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
COOLING COOL001
ON=INPUT 1*TCOOL
POWER=999999999
HUMIDITY=100
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* H e a t i n g
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
HEATING HEAT001
ON=INPUT 20*WINTER
POWER=999999999
HUMIDITY=0
RRAD=0.4
*
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONES ROOM228 ZONE31 ZONE10 ZONE1 ZONE17 ZONE19 ZONE8 ZONE9 ZONE6 ZONE11 ZONE4 ZONE5 ZONE2 ZONE7 ZONE12 ZONE3 ZONE14 ZONE13 ZONE24 ZONE29 ZONE15 ZONE27 ZONE20 ZONE26 ZONE30 ZONE22 ZONE18 ZONE25 ;
ZONE21
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* O r i e n t a t i o n s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ORIENTATIONS NORTH SOUTH EAST WEST HORIZONTAL
*
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
BUILDING
*++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
*
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e ROOM228 / A i r n o d e ROOM228
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ROOM228
AIRNODE ROOM228
WALL =INTWALL : SURF= 1 : AREA= 29.33 : BOUNDARY=IDENTICAL : GEOSURF=0.1
WALL =OUTWALL : SURF= 2 : AREA= 11.77 : EXTERNAL : ORI=SOUTH : FSKY=0.5
WINDOW=TRIPLE : SURF= 3 : AREA= 17.56 : EXTERNAL : ORI=SOUTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_SOUTH
WALL =INTFLOOR : SURF= 6 : AREA= 57.21 : BOUNDARY=IDENTICAL : GEOSURF=0.6
WALL =ROOF : SURF= 7 : AREA= 79.91 : EXTERNAL : ORI=HORIZONTAL : FSKY=0.5
WALL =INTWALL : SURF= 18 : AREA= 30.35 : ADJACENT=ZONE31 : BACK : GEOSURF=0.1
WALL =INTWALL : SURF= 27 : AREA= 30.35 : ADJACENT=ZONE10 : BACK : GEOSURF=0.1
WALL =INTFLOOR : SURF=386 : AREA= 4 : ADJACENT=ZONE18 : BACK
WALL =INTFLOOR : SURF=393 : AREA= 18.7 : ADJACENT=ZONE18 : BACK
REGIME
GAIN = PERS_ISO01 : SCALE= SCHEDULE 31*SUMMER_OCCUPANCY
INFILTRATION= INFIL001
VENTILATION = VENTMECH
COOLING = COOL001
HEATING = HEAT001
CAPACITANCE = 2301.4 : VOLUME= 239.73 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e ZONE31 / A i r n o d e ZONE31
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE31
AIRNODE ZONE31
WALL =OUTWALL : SURF= 8 : AREA= 18.44 : EXTERNAL : ORI=SOUTH : FSKY=0.5
WINDOW=TRIPLE : SURF= 9 : AREA= 17.56 : EXTERNAL : ORI=SOUTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_SOUTH
WALL =OUTWALL : SURF= 10 : AREA= 17.94 : EXTERNAL : ORI=SOUTH : FSKY=0.5
WINDOW=TRIPLE : SURF= 11 : AREA= 17.56 : EXTERNAL : ORI=SOUTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_SOUTH
WALL =INTWALL : SURF= 12 : AREA= 36 : ADJACENT=ZONE1 : FRONT : GEOSURF=0.1
WALL =INTWALL : SURF= 13 : AREA= 35.5 : ADJACENT=ZONE1 : FRONT : GEOSURF=0.1
WALL =OUTWALL : SURF= 14 : AREA= 30.35 : EXTERNAL : ORI=WEST : FSKY=0.5 : GEOSURF=0.1
WALL =INTWALL : SURF= 16 : AREA= 60.7 : INTERNAL : GEOSURF=0.1
WALL =INTWALL : SURF= 17 : AREA= 30.35 : ADJACENT=ROOM228 : FRONT : GEOSURF=0.1
WALL =ROOF : SURF= 5 : AREA= 86.8 : EXTERNAL : ORI=HORIZONTAL : FSKY=0.5
WALL =INTFLOOR : SURF= 19 : AREA= 10.2 : BOUNDARY=IDENTICAL : GEOSURF=0.1
WALL =ROOF : SURF= 20 : AREA= 85.5 : EXTERNAL : ORI=HORIZONTAL : FSKY=0.5
WALL =INTFLOOR : SURF= 21 : AREA= 37.92 : BOUNDARY=IDENTICAL : GEOSURF=0.3
WALL =INTFLOOR : SURF= 62 : AREA= 27.1 : ADJACENT=ZONE17 : FRONT
WALL =INTFLOOR : SURF= 64 : AREA= 49.5 : ADJACENT=ZONE19 : FRONT : GEOSURF=0.1
WALL =INTFLOOR : SURF=378 : AREA= 47.58 : ADJACENT=ZONE18 : BACK
WALL =INTFLOOR : SURF=379 : AREA= 10.2 : BOUNDARY=IDENTICAL
REGIME
GAIN = PERS_ISO01 : SCALE= SCHEDULE 52*SUMMER_OCCUPANCY
INFILTRATION= INFIL001
VENTILATION = VENTMECH
COOLING = COOL001
HEATING = HEAT001
CAPACITANCE = 4596.48 : VOLUME= 478.8 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e ZONE10 / A i r n o d e ZONE10
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE10
AIRNODE ZONE10
WALL =OUTWALL : SURF= 22 : AREA= 17.94 : EXTERNAL : ORI=SOUTH : FSKY=0.5
WINDOW=TRIPLE : SURF= 23 : AREA= 17.56 : EXTERNAL : ORI=SOUTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_SOUTH
WALL =INTWALL : SURF= 24 : AREA= 35.5 : ADJACENT=ZONE1 : FRONT : GEOSURF=0.1
WALL =INTWALL : SURF= 26 : AREA= 30.35 : ADJACENT=ROOM228 : FRONT
WALL =INTWALL : SURF= 4 : AREA= 60.7 : INTERNAL
WALL =ROOF : SURF= 28 : AREA= 85.5 : EXTERNAL : ORI=HORIZONTAL : FSKY=0.5
WALL =INTFLOOR : SURF= 29 : AREA= 85.5 : ADJACENT=ZONE1 : FRONT : GEOSURF=0.2
WALL =OUTWALL : SURF= 31 : AREA= 17.94 : EXTERNAL : ORI=SOUTH : FSKY=0.5
WINDOW=TRIPLE : SURF= 32 : AREA= 17.56 : EXTERNAL : ORI=SOUTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_SOUTH
WALL =INTWALL : SURF= 33 : AREA= 35.5 : ADJACENT=ZONE1 : FRONT
WALL =INTWALL : SURF= 35 : AREA= 60.7 : INTERNAL
WALL =INTWALL : SURF= 36 : AREA= 60.7 : INTERNAL
WALL =ROOF : SURF= 37 : AREA= 85.5 : EXTERNAL : ORI=HORIZONTAL : FSKY=0.5
WALL =INTFLOOR : SURF= 38 : AREA= 85.5 : ADJACENT=ZONE1 : FRONT : GEOSURF=0.2
WALL =OUTWALL : SURF= 42 : AREA= 17.94 : EXTERNAL : ORI=SOUTH : FSKY=0.5
WINDOW=TRIPLE : SURF= 43 : AREA= 17.56 : EXTERNAL : ORI=SOUTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_SOUTH
WALL =INTWALL : SURF= 44 : AREA= 35.5 : ADJACENT=ZONE1 : FRONT
WALL =ROOF : SURF= 48 : AREA= 85.5 : EXTERNAL : ORI=HORIZONTAL : FSKY=0.5
WALL =INTFLOOR : SURF= 49 : AREA= 85.5 : ADJACENT=ZONE1 : FRONT : GEOSURF=0.1
WALL =OUTWALL : SURF= 51 : AREA= 18.44 : EXTERNAL : ORI=SOUTH : FSKY=0.5
WINDOW=TRIPLE : SURF= 52 : AREA= 17.56 : EXTERNAL : ORI=SOUTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_SOUTH
WALL =INTWALL : SURF= 53 : AREA= 36 : ADJACENT=ZONE1 : FRONT : GEOSURF=0.1
WALL =OUTWALL : SURF= 56 : AREA= 30.35 : EXTERNAL : ORI=EAST : FSKY=0.5
WALL =ROOF : SURF= 57 : AREA= 86.78 : EXTERNAL : ORI=HORIZONTAL : FSKY=0.5
WALL =INTFLOOR : SURF= 58 : AREA= 22.28 : ADJACENT=ZONE1 : FRONT : GEOSURF=0.1
WALL =INTFLOOR : SURF= 60 : AREA= 64.5 : ADJACENT=ZONE17 : FRONT : GEOSURF=0.2
REGIME
GAIN = PERS_ISO01 : SCALE= SCHEDULE 104*SUMMER_OCCUPANCY
INFILTRATION= INFIL001
VENTILATION = VENTMECH
COOLING = COOL001
HEATING = HEAT001
CAPACITANCE = 9216 : VOLUME= 960 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e ZONE1 / A i r n o d e ZONE1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE1
AIRNODE ZONE1
WALL =INTWALL : SURF= 25 : AREA= 35.5 : ADJACENT=ZONE10 : BACK
WALL =INTFLOOR : SURF= 30 : AREA= 85.5 : ADJACENT=ZONE10 : BACK
WALL =INTWALL : SURF= 34 : AREA= 35.5 : ADJACENT=ZONE10 : BACK
WALL =INTFLOOR : SURF= 39 : AREA= 85.5 : ADJACENT=ZONE10 : BACK
WALL =INTWALL : SURF= 40 : AREA= 36 : ADJACENT=ZONE31 : BACK
WALL =INTWALL : SURF= 41 : AREA= 35.5 : ADJACENT=ZONE31 : BACK
WALL =INTWALL : SURF= 45 : AREA= 35.5 : ADJACENT=ZONE10 : BACK
WALL =INTFLOOR : SURF= 50 : AREA= 85.5 : ADJACENT=ZONE10 : BACK
WALL =INTWALL : SURF= 54 : AREA= 36 : ADJACENT=ZONE10 : BACK
WALL =INTFLOOR : SURF= 59 : AREA= 22.28 : ADJACENT=ZONE10 : BACK
WALL =INTWALL : SURF= 67 : AREA= 21.7 : ADJACENT=ZONE19 : BACK
WALL =INTWALL : SURF= 69 : AREA= 8.925 : ADJACENT=ZONE8 : BACK
WALL =INTWALL : SURF= 46 : AREA= 8.93 : ADJACENT=ZONE8 : BACK
WALL =INTWALL : SURF= 89 : AREA= 9.3 : ADJACENT=ZONE8 : BACK
WALL =INTWALL : SURF=101 : AREA= 25.6 : ADJACENT=ZONE9 : BACK
WALL =INTWALL : SURF=105 : AREA= 17 : ADJACENT=ZONE9 : BACK
WALL =INTWALL : SURF=113 : AREA= 9.3 : ADJACENT=ZONE6 : BACK
WALL =INTWALL : SURF=118 : AREA= 25.6 : ADJACENT=ZONE12 : BACK
WALL =INTWALL : SURF=125 : AREA= 9.3 : ADJACENT=ZONE5 : BACK
WALL =INTWALL : SURF=133 : AREA= 9.3 : ADJACENT=ZONE5 : BACK
WALL =INTWALL : SURF=142 : AREA= 26.7 : ADJACENT=ZONE7 : BACK
WALL =INTWALL : SURF=146 : AREA= 17.75 : ADJACENT=ZONE7 : BACK
WALL =INTWALL : SURF=149 : AREA= 9.32 : ADJACENT=ZONE2 : BACK
WALL =INTWALL : SURF=161 : AREA= 8.5 : ADJACENT=ZONE2 : BACK
WALL =INTWALL : SURF=167 : AREA= 8.5 : ADJACENT=ZONE2 : BACK
WALL =INTWALL : SURF=175 : AREA= 9.33 : ADJACENT=ZONE2 : BACK
WALL =INTWALL : SURF=183 : AREA= 9.33 : ADJACENT=ZONE2 : BACK
WALL =INTWALL : SURF=192 : AREA= 8.9 : ADJACENT=ZONE2 : BACK
WALL =INTWALL : SURF=208 : AREA= 8.1 : ADJACENT=ZONE2 : BACK
WALL =INTWALL : SURF=216 : AREA= 8.1 : ADJACENT=ZONE2 : BACK
WALL =INTWALL : SURF=226 : AREA= 8.91 : ADJACENT=ZONE2 : BACK
WALL =INTFLOOR : SURF=232 : AREA= 20.45 : ADJACENT=ZONE2 : BACK
WALL =INTWALL : SURF=234 : AREA= 8.91 : ADJACENT=ZONE2 : BACK
WALL =INTWALL : SURF=243 : AREA= 8.925 : ADJACENT=ZONE11 : BACK
WALL =INTWALL : SURF=253 : AREA= 8.925 : ADJACENT=ZONE11 : BACK
WALL =INTWALL : SURF=261 : AREA= 8.925 : ADJACENT=ZONE11 : BACK
WALL =INTWALL : SURF=273 : AREA= 8.925 : ADJACENT=ZONE14 : BACK
WALL =INTWALL : SURF=295 : AREA= 12.75 : ADJACENT=ZONE14 : BACK
WALL =INTWALL : SURF=301 : AREA= 12.75 : ADJACENT=ZONE14 : BACK
WALL =INTWALL : SURF=307 : AREA= 12.75 : ADJACENT=ZONE14 : BACK
WALL =INTWALL : SURF=313 : AREA= 13.26 : ADJACENT=ZONE14 : BACK
WALL =INTWALL : SURF=323 : AREA= 8.5 : ADJACENT=ZONE13 : BACK
WALL =INTWALL : SURF=330 : AREA= 8.5 : ADJACENT=ZONE13 : BACK
WALL =INTWALL : SURF=338 : AREA= 25.9 : ADJACENT=ZONE20 : BACK
WALL =INTWALL : SURF=342 : AREA= 17 : ADJACENT=ZONE20 : BACK
WALL =INTWALL : SURF=351 : AREA= 11.9 : ADJACENT=ZONE17 : BACK
WALL =INTWALL : SURF=360 : AREA= 28.3 : ADJACENT=ZONE17 : BACK
WALL =INTWALL : SURF=362 : AREA= 32.1 : ADJACENT=ZONE17 : BACK
WALL =INTWALL : SURF=372 : AREA= 20.87 : ADJACENT=ZONE18 : BACK
WALL =INTWALL : SURF=382 : AREA= 7.125 : ADJACENT=ZONE18 : BACK
WALL =INTWALL : SURF=384 : AREA= 7.91 : ADJACENT=ZONE18 : BACK
WALL =INTWALL : SURF=391 : AREA= 24.15 : ADJACENT=ZONE18 : BACK
REGIME
CAPACITANCE = 0.12 : VOLUME= 0.1 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e ZONE17 / A i r n o d e ZONE17
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE17
AIRNODE ZONE17
WALL =INTFLOOR : SURF= 61 : AREA= 64.5 : ADJACENT=ZONE10 : BACK
WALL =INTFLOOR : SURF= 63 : AREA= 27.1 : ADJACENT=ZONE31 : BACK
WALL =OUTWALL : SURF=349 : AREA= 11.9 : EXTERNAL : ORI=SOUTH : FSKY=0.5
WALL =INTWALL : SURF=350 : AREA= 11.9 : ADJACENT=ZONE1 : FRONT
WALL =OUTWALL : SURF=352 : AREA= 32.1 : EXTERNAL : ORI=WEST : FSKY=0.5
WALL =INTWALL : SURF=353 : AREA= 32.1 : ADJACENT=ZONE19 : FRONT
WALL =INTFLOOR : SURF=355 : AREA= 27.1 : ADJACENT=ZONE30 : FRONT
WALL =OUTWALL : SURF=357 : AREA= 19.86 : EXTERNAL : ORI=SOUTH : FSKY=0.5
WINDOW=POS010 : SURF=358 : AREA= 8.44 : EXTERNAL : ORI=SOUTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_SOUTH
WALL =INTWALL : SURF=359 : AREA= 28.3 : ADJACENT=ZONE1 : FRONT
WALL =INTWALL : SURF=361 : AREA= 32.1 : ADJACENT=ZONE1 : FRONT
WALL =INTFLOOR : SURF=363 : AREA= 64.5 : ADJACENT=ZONE22 : FRONT : GEOSURF=0.6
REGIME
INFILTRATION= INFIL001
CAPACITANCE = 2332.8 : VOLUME= 243 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e ZONE19 / A i r n o d e ZONE19
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE19
AIRNODE ZONE19
WALL =INTFLOOR : SURF= 65 : AREA= 49.5 : ADJACENT=ZONE31 : BACK
WALL =INTWALL : SURF= 66 : AREA= 21.7 : ADJACENT=ZONE1 : FRONT
WALL =INTWALL : SURF=354 : AREA= 32.1 : ADJACENT=ZONE17 : BACK
WALL =OUTWALL : SURF=396 : AREA= 6.94 : EXTERNAL : ORI=SOUTH : FSKY=0.5
WINDOW=POS025 : SURF=397 : AREA= 14.76 : EXTERNAL : ORI=SOUTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_SOUTH
WALL =INTWALL : SURF=398 : AREA= 32.1 : BOUNDARY=IDENTICAL
WALL =INTFLOOR : SURF=399 : AREA= 49.5 : ADJACENT=ZONE30 : FRONT : GEOSURF=0.6
REGIME
INFILTRATION= INFIL001
CAPACITANCE = 1445.2 : VOLUME= 150.54 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e ZONE8 / A i r n o d e ZONE8
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE8
AIRNODE ZONE8
WALL =INTWALL : SURF= 68 : AREA= 8.925 : ADJACENT=ZONE1 : FRONT
WALL =INTWALL : SURF= 70 : AREA= 25.58 : ADJACENT=ZONE9 : FRONT
WALL =OUTWALL : SURF= 72 : AREA= 16.95 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=TRIPLE : SURF= 73 : AREA= 17.56 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL =OUTWALL : SURF= 74 : AREA= 29.07 : EXTERNAL : ORI=WEST : FSKY=0.5
WALL =INTWALL : SURF= 75 : AREA= 58.14 : INTERNAL
WALL =INTFLOOR : SURF= 76 : AREA= 86.78 : ADJACENT=ZONE6 : FRONT
WALL =INTFLOOR : SURF= 78 : AREA= 86.78 : ADJACENT=ZONE11 : FRONT : GEOSURF=0.3
WALL =INTWALL : SURF= 15 : AREA= 8.93 : ADJACENT=ZONE1 : FRONT
WALL =INTWALL : SURF= 47 : AREA= 25.07 : ADJACENT=ZONE4 : FRONT
WALL =OUTWALL : SURF= 80 : AREA= 16.44 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=TRIPLE : SURF= 81 : AREA= 17.56 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL =INTWALL : SURF= 82 : AREA= 58.14 : INTERNAL
WALL =INTWALL : SURF= 83 : AREA= 58.14 : INTERNAL
WALL =INTFLOOR : SURF= 84 : AREA= 85.5 : ADJACENT=ZONE5 : FRONT
WALL =INTFLOOR : SURF= 86 : AREA= 85.5 : ADJACENT=ZONE11 : FRONT : GEOSURF=0.3
WALL =INTWALL : SURF= 88 : AREA= 9.3 : ADJACENT=ZONE1 : FRONT
WALL =INTWALL : SURF= 90 : AREA= 24.7 : ADJACENT=ZONE4 : FRONT
WALL =OUTWALL : SURF= 94 : AREA= 16.44 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=TRIPLE : SURF= 95 : AREA= 17.56 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL =INTFLOOR : SURF= 98 : AREA= 85.5 : ADJACENT=ZONE11 : FRONT : GEOSURF=0.3
WALL =INTFLOOR : SURF= 96 : AREA= 85.5 : ADJACENT=ZONE5 : FRONT
WALL =INTWALL : SURF=198 : AREA= 29.07 : ADJACENT=ZONE2 : BACK
REGIME
GAIN = PERS_ISO01 : SCALE= SCHEDULE 78*SUMMER_OCCUPANCY
INFILTRATION= INFIL001
VENTILATION = VENTMECH
COOLING = COOL001
HEATING = HEAT001
CAPACITANCE = 6909.12 : VOLUME= 719.7 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e ZONE9 / A i r n o d e ZONE9
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE9
AIRNODE ZONE9
WALL =INTWALL : SURF= 71 : AREA= 25.58 : ADJACENT=ZONE8 : BACK
WALL =INTWALL : SURF=100 : AREA= 25.6 : ADJACENT=ZONE1 : FRONT
WALL =OUTWALL : SURF=102 : AREA= 14.52 : EXTERNAL : ORI=WEST : FSKY=0.5
WINDOW=POS016 : SURF=103 : AREA= 2.48 : EXTERNAL : ORI=WEST : FSKY=0.5 : ESHADE=INPUT 0.7*S_WEST
WALL =INTWALL : SURF=104 : AREA= 17 : ADJACENT=ZONE1 : FRONT : GEOSURF=0.1
WALL =INTFLOOR : SURF=106 : AREA= 37.6 : ADJACENT=ZONE7 : FRONT
WALL =INTFLOOR : SURF=108 : AREA= 37.6 : ADJACENT=ZONE12 : FRONT : GEOSURF=0.6
REGIME
GAIN = PERS_ISO01 : SCALE= SCHEDULE 2*SUMMER_OCCUPANCY
INFILTRATION= INFIL001
COOLING = COOL001
HEATING = HEAT001
CAPACITANCE = 889.92 : VOLUME= 92.7 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e ZONE6 / A i r n o d e ZONE6
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE6
AIRNODE ZONE6
WALL =INTFLOOR : SURF= 77 : AREA= 86.78 : ADJACENT=ZONE8 : BACK : GEOSURF=0.6
WALL =INTWALL : SURF=110 : AREA= 26.7 : ADJACENT=ZONE7 : FRONT
WALL =INTWALL : SURF=112 : AREA= 9.3 : ADJACENT=ZONE1 : FRONT
WALL =OUTWALL : SURF=114 : AREA= 18.44 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=TRIPLE : SURF=119 : AREA= 17.56 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL =OUTWALL : SURF=120 : AREA= 30.35 : EXTERNAL : ORI=WEST : FSKY=0.5
WALL =INTWALL : SURF=121 : AREA= 30.35 : ADJACENT=ZONE5 : FRONT
WALL =ROOF : SURF=123 : AREA= 86.78 : EXTERNAL : ORI=HORIZONTAL : FSKY=0.5
REGIME
GAIN = PERS_ISO01 : SCALE= SCHEDULE 26*SUMMER_OCCUPANCY
INFILTRATION= INFIL001
VENTILATION = VENTMECH
COOLING = COOL001
HEATING = HEAT001
CAPACITANCE = 2295.35 : VOLUME= 239.1 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e ZONE11 / A i r n o d e ZONE11
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE11
AIRNODE ZONE11
WALL =INTFLOOR : SURF= 79 : AREA= 86.78 : ADJACENT=ZONE8 : BACK
WALL =INTFLOOR : SURF= 87 : AREA= 85.5 : ADJACENT=ZONE8 : BACK
WALL =INTFLOOR : SURF= 99 : AREA= 85.5 : ADJACENT=ZONE8 : BACK
WALL =INTWALL : SURF= 92 : AREA= 25.6 : ADJACENT=ZONE12 : FRONT
WALL =INTWALL : SURF=242 : AREA= 8.925 : ADJACENT=ZONE1 : FRONT
WALL =OUTWALL : SURF=244 : AREA= 19.76 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=POS005_009 : SURF=245 : AREA= 14.75 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL =OUTWALL : SURF=246 : AREA= 29.07 : EXTERNAL : ORI=WEST : FSKY=0.5
WALL =INTWALL : SURF=247 : AREA= 58.14 : INTERNAL
WALL =INTWALL : SURF=248 : AREA= 58.14 : INTERNAL
WALL =INTFLOOR : SURF=250 : AREA= 86.78 : ADJACENT=ZONE24 : FRONT : GEOSURF=0.3
WALL =INTWALL : SURF=252 : AREA= 8.925 : ADJACENT=ZONE1 : FRONT
WALL =INTWALL : SURF=254 : AREA= 33.575 : ADJACENT=ZONE4 : FRONT
WALL =OUTWALL : SURF=256 : AREA= 24.94 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=TRIPLE : SURF=257 : AREA= 17.56 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL =INTFLOOR : SURF=258 : AREA= 106.875 : ADJACENT=ZONE24 : FRONT : GEOSURF=0.4
WALL =INTWALL : SURF=260 : AREA= 8.925 : ADJACENT=ZONE1 : FRONT
WALL =INTWALL : SURF=262 : AREA= 16.575 : ADJACENT=ZONE4 : FRONT
WALL =OUTWALL : SURF=264 : AREA= 13.56 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=POS005_010 : SURF=265 : AREA= 11.94 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL =INTFLOOR : SURF=266 : AREA= 51 : ADJACENT=ZONE29 : FRONT : GEOSURF=0.3
WALL =INTFLOOR : SURF=268 : AREA= 13.125 : BOUNDARY=IDENTICAL
WALL =INTWALL : SURF=269 : AREA= 29.07 : ADJACENT=ZONE14 : FRONT
REGIME
GAIN = PERS_ISO01 : SCALE= SCHEDULE 68*SUMMER_OCCUPANCY
INFILTRATION= INFIL001
VENTILATION = VENTMECH
COOLING = COOL001
HEATING = HEAT001
CAPACITANCE = 6909.98 : VOLUME= 719.79 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e ZONE4 / A i r n o d e ZONE4
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE4
AIRNODE ZONE4
WALL =INTWALL : SURF= 55 : AREA= 25.07 : ADJACENT=ZONE8 : BACK
WALL =INTWALL : SURF= 91 : AREA= 24.7 : ADJACENT=ZONE8 : BACK
WALL =INTWALL : SURF=127 : AREA= 26.2 : ADJACENT=ZONE5 : BACK
WALL =INTWALL : SURF=135 : AREA= 26.2 : ADJACENT=ZONE5 : BACK
WALL =INTWALL : SURF=255 : AREA= 33.575 : ADJACENT=ZONE11 : BACK
WALL =INTWALL : SURF=263 : AREA= 16.575 : ADJACENT=ZONE11 : BACK
WALL =INTWALL : SURF=283 : AREA= 9.2 : ADJACENT=ZONE14 : BACK
REGIME
CAPACITANCE = 0.12 : VOLUME= 0.1 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e ZONE5 / A i r n o d e ZONE5
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE5
AIRNODE ZONE5
WALL =INTFLOOR : SURF= 85 : AREA= 85.5 : ADJACENT=ZONE8 : BACK : GEOSURF=0.3
WALL =INTFLOOR : SURF= 97 : AREA= 85.5 : ADJACENT=ZONE8 : BACK : GEOSURF=0.3
WALL =INTWALL : SURF=122 : AREA= 30.35 : ADJACENT=ZONE6 : BACK
WALL =INTWALL : SURF=124 : AREA= 9.3 : ADJACENT=ZONE1 : FRONT
WALL =INTWALL : SURF=126 : AREA= 26.2 : ADJACENT=ZONE4 : FRONT
WALL =OUTWALL : SURF=128 : AREA= 17.94 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=TRIPLE : SURF=129 : AREA= 17.56 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL =INTWALL : SURF=130 : AREA= 60.7 : INTERNAL
WALL =ROOF : SURF=131 : AREA= 85.5 : EXTERNAL : ORI=HORIZONTAL : FSKY=0.5
WALL =INTWALL : SURF=132 : AREA= 9.3 : ADJACENT=ZONE1 : FRONT
WALL =INTWALL : SURF=134 : AREA= 26.2 : ADJACENT=ZONE4 : FRONT
WALL =OUTWALL : SURF=136 : AREA= 17.94 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=TRIPLE : SURF=137 : AREA= 17.56 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL =INTWALL : SURF=138 : AREA= 30.35 : ADJACENT=ZONE2 : FRONT
WALL =ROOF : SURF=140 : AREA= 85.5 : EXTERNAL : ORI=HORIZONTAL : FSKY=0.5
REGIME
GAIN = PERS_ISO01 : SCALE= SCHEDULE 52*SUMMER_OCCUPANCY
INFILTRATION= INFIL001
VENTILATION = VENTMECH
COOLING = COOL001
HEATING = HEAT001
CAPACITANCE = 4613.75 : VOLUME= 480.6 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e ZONE2 / A i r n o d e ZONE2
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE2
AIRNODE ZONE2
WALL =OUTWALL : SURF=115 : AREA= 17.94 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=TRIPLE : SURF=116 : AREA= 17.56 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL =INTWALL : SURF=139 : AREA= 30.35 : ADJACENT=ZONE5 : BACK
WALL =INTWALL : SURF=148 : AREA= 9.32 : ADJACENT=ZONE1 : FRONT
WALL =INTWALL : SURF=150 : AREA= 26.18 : ADJACENT=ZONE3 : FRONT
WALL =INTWALL : SURF=152 : AREA= 60.7 : INTERNAL
WALL =INTWALL : SURF=153 : AREA= 60.7 : INTERNAL
WALL =INTWALL : SURF=154 : AREA= 60.7 : INTERNAL
WALL =INTWALL : SURF=155 : AREA= 60.7 : INTERNAL
WALL =ROOF : SURF=156 : AREA= 85.5 : EXTERNAL : ORI=HORIZONTAL : FSKY=0.5
WALL =INTFLOOR : SURF=157 : AREA= 171 : INTERNAL : GEOSURF=0.2
WALL =INTWALL : SURF=158 : AREA= 27 : ADJACENT=ZONE3 : FRONT
WALL =INTWALL : SURF=160 : AREA= 8.5 : ADJACENT=ZONE1 : FRONT
WALL =OUTWALL : SURF=162 : AREA= 17.94 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=TRIPLE : SURF=163 : AREA= 17.56 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL =ROOF : SURF=164 : AREA= 85.5 : EXTERNAL : ORI=HORIZONTAL : FSKY=0.5
WALL =INTFLOOR : SURF=165 : AREA= 171 : INTERNAL : GEOSURF=0.2
WALL =INTWALL : SURF=166 : AREA= 8.5 : ADJACENT=ZONE1 : FRONT
WALL =INTWALL : SURF=168 : AREA= 35.875 : ADJACENT=ZONE3 : FRONT
WALL =OUTWALL : SURF=170 : AREA= 23.995 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=POS005_008 : SURF=171 : AREA= 20.38 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL =ROOF : SURF=172 : AREA= 106.875 : EXTERNAL : ORI=HORIZONTAL : FSKY=0.5
WALL =INTFLOOR : SURF=173 : AREA= 213.75 : INTERNAL : GEOSURF=0.2
WALL =INTWALL : SURF=174 : AREA= 9.33 : ADJACENT=ZONE1 : FRONT
WALL =INTWALL : SURF=176 : AREA= 17.295 : ADJACENT=ZONE3 : FRONT
WALL =OUTWALL : SURF=178 : AREA= 14.69 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=POS005_010 : SURF=179 : AREA= 11.94 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL =ROOF : SURF=180 : AREA= 64.125 : EXTERNAL : ORI=HORIZONTAL : FSKY=0.5
WALL =INTFLOOR : SURF=181 : AREA= 128.25 : INTERNAL : GEOSURF=0.2
WALL =INTWALL : SURF=182 : AREA= 9.33 : ADJACENT=ZONE1 : FRONT
WALL =INTWALL : SURF=184 : AREA= 26.7 : ADJACENT=ZONE3 : FRONT
WALL =OUTWALL : SURF=186 : AREA= 18.47 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=TRIPLE : SURF=188 : AREA= 17.56 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL =OUTWALL : SURF=187 : AREA= 30.35 : EXTERNAL : ORI=EAST : FSKY=0.5
WALL =ROOF : SURF=189 : AREA= 86.78 : EXTERNAL : ORI=HORIZONTAL : FSKY=0.5
WALL =INTFLOOR : SURF=190 : AREA= 173.56 : INTERNAL : GEOSURF=0.2
WALL =INTWALL : SURF=191 : AREA= 8.9 : ADJACENT=ZONE1 : FRONT
WALL =INTWALL : SURF=193 : AREA= 25.1 : ADJACENT=ZONE3 : FRONT
WALL =OUTWALL : SURF=195 : AREA= 16.44 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=TRIPLE : SURF=196 : AREA= 17.56 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL =INTWALL : SURF=197 : AREA= 29.07 : ADJACENT=ZONE8 : FRONT
WALL =INTWALL : SURF=199 : AREA= 58.14 : INTERNAL
WALL =INTWALL : SURF=200 : AREA= 58.14 : INTERNAL
WALL =INTWALL : SURF=201 : AREA= 58.14 : INTERNAL
WALL =INTWALL : SURF=202 : AREA= 58.14 : INTERNAL
WALL =INTFLOOR : SURF=203 : AREA= 85.5 : ADJACENT=ZONE14 : FRONT
WALL =INTWALL : SURF=205 : AREA= 25.9 : ADJACENT=ZONE3 : FRONT
WALL =INTWALL : SURF=207 : AREA= 8.1 : ADJACENT=ZONE1 : FRONT
WALL =OUTWALL : SURF=209 : AREA= 16.44 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=TRIPLE : SURF=210 : AREA= 17.56 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL =INTFLOOR : SURF=211 : AREA= 85.5 : ADJACENT=ZONE13 : FRONT
WALL =INTWALL : SURF=213 : AREA= 34.4 : ADJACENT=ZONE3 : FRONT
WALL =INTWALL : SURF=215 : AREA= 8.1 : ADJACENT=ZONE1 : FRONT
WALL =OUTWALL : SURF=217 : AREA= 22.12 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=POS2_010_005 : SURF=218 : AREA= 20.38 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL =INTFLOOR : SURF=219 : AREA= 42.75 : ADJACENT=ZONE13 : FRONT
WALL =INTFLOOR : SURF=221 : AREA= 85.5 : ADJACENT=ZONE14 : FRONT
WALL =INTWALL : SURF=223 : AREA= 16.59 : ADJACENT=ZONE3 : FRONT
WALL =INTWALL : SURF=225 : AREA= 8.91 : ADJACENT=ZONE1 : FRONT
WALL =OUTWALL : SURF=227 : AREA= 13.56 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=POS005_010 : SURF=228 : AREA= 11.94 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL =INTFLOOR : SURF=229 : AREA= 44.6 : ADJACENT=ZONE14 : FRONT
WALL =INTFLOOR : SURF=231 : AREA= 20.45 : ADJACENT=ZONE1 : FRONT
WALL =INTWALL : SURF=233 : AREA= 8.91 : ADJACENT=ZONE1 : FRONT
WALL =INTWALL : SURF=235 : AREA= 25.6 : ADJACENT=ZONE3 : FRONT
WALL =OUTWALL : SURF=239 : AREA= 16.95 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=TRIPLE : SURF=240 : AREA= 17.56 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL =OUTWALL : SURF=237 : AREA= 29.07 : EXTERNAL : ORI=EAST : FSKY=0.5
WALL =INTFLOOR : SURF=238 : AREA= 45.5 : ADJACENT=ZONE14 : FRONT
REGIME
GAIN = PERS_ISO01 : SCALE= SCHEDULE 233*SUMMER_OCCUPANCY
INFILTRATION= INFIL001
VENTILATION = VENTMECH
COOLING = COOL001
HEATING = HEAT001
CAPACITANCE = 23025.4 : VOLUME= 2398.48 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e ZONE7 / A i r n o d e ZONE7
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE7
AIRNODE ZONE7
WALL =INTFLOOR : SURF=107 : AREA= 37.6 : ADJACENT=ZONE9 : BACK : GEOSURF=0.6
WALL =INTWALL : SURF=111 : AREA= 26.7 : ADJACENT=ZONE6 : BACK
WALL =INTWALL : SURF=141 : AREA= 26.7 : ADJACENT=ZONE1 : FRONT
WALL =OUTWALL : SURF=143 : AREA= 12.79 : EXTERNAL : ORI=WEST : FSKY=0.5
WINDOW=POS015_016 : SURF=144 : AREA= 4.96 : EXTERNAL : ORI=WEST : FSKY=0.5 : ESHADE=INPUT 0.7*S_WEST
WALL =INTWALL : SURF=145 : AREA= 17.75 : ADJACENT=ZONE1 : FRONT
WALL =ROOF : SURF=147 : AREA= 37.6 : EXTERNAL : ORI=HORIZONTAL : FSKY=0.5
REGIME
GAIN = PERS_ISO01 : SCALE= SCHEDULE 2*SUMMER_OCCUPANCY
INFILTRATION= INFIL001
COOLING = COOL001
HEATING = HEAT001
CAPACITANCE = 889.92 : VOLUME= 92.7 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e ZONE12 / A i r n o d e ZONE12
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE12
AIRNODE ZONE12
WALL =INTFLOOR : SURF=109 : AREA= 37.6 : ADJACENT=ZONE9 : BACK
WALL =INTWALL : SURF=117 : AREA= 25.6 : ADJACENT=ZONE1 : FRONT
WALL =INTWALL : SURF= 93 : AREA= 25.6 : ADJACENT=ZONE11 : BACK
REGIME
CAPACITANCE = 0.12 : VOLUME= 0.1 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e ZONE3 / A i r n o d e ZONE3
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE3
AIRNODE ZONE3
WALL =INTWALL : SURF=151 : AREA= 26.18 : ADJACENT=ZONE2 : BACK
WALL =INTWALL : SURF=159 : AREA= 27 : ADJACENT=ZONE2 : BACK
WALL =INTWALL : SURF=169 : AREA= 35.875 : ADJACENT=ZONE2 : BACK
WALL =INTWALL : SURF=177 : AREA= 17.295 : ADJACENT=ZONE2 : BACK
WALL =INTWALL : SURF=185 : AREA= 26.7 : ADJACENT=ZONE2 : BACK
WALL =INTWALL : SURF=194 : AREA= 25.1 : ADJACENT=ZONE2 : BACK
WALL =INTWALL : SURF=206 : AREA= 25.9 : ADJACENT=ZONE2 : BACK
WALL =INTWALL : SURF=214 : AREA= 34.4 : ADJACENT=ZONE2 : BACK
WALL =INTWALL : SURF=224 : AREA= 16.59 : ADJACENT=ZONE2 : BACK
WALL =INTWALL : SURF=236 : AREA= 25.6 : ADJACENT=ZONE2 : BACK
WALL =INTFLOOR : SURF=344 : AREA= 38.125 : ADJACENT=ZONE20 : BACK
REGIME
CAPACITANCE = 0.12 : VOLUME= 0.1 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e ZONE14 / A i r n o d e ZONE14
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE14
AIRNODE ZONE14
WALL =INTFLOOR : SURF=204 : AREA= 85.5 : ADJACENT=ZONE2 : BACK
WALL =INTFLOOR : SURF=222 : AREA= 85.5 : ADJACENT=ZONE2 : BACK
WALL =INTFLOOR : SURF=230 : AREA= 44.6 : ADJACENT=ZONE2 : BACK
WALL =INTFLOOR : SURF=241 : AREA= 45.5 : ADJACENT=ZONE2 : BACK
WALL =INTWALL : SURF=270 : AREA= 29.07 : ADJACENT=ZONE11 : BACK
WALL =INTWALL : SURF=271 : AREA= 8.925 : ADJACENT=ZONE1 : FRONT
WALL =INTWALL : SURF=272 : AREA= 25.075 : ADJACENT=ZONE15 : FRONT
WALL =OUTWALL : SURF=275 : AREA= 19.25 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=POS005_009 : SURF=276 : AREA= 14.75 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL =INTWALL : SURF=249 : AREA= 29.1 : ADJACENT=ZONE13 : FRONT
WALL =INTFLOOR : SURF=278 : AREA= 85.5 : ADJACENT=ZONE27 : FRONT : GEOSURF=0.3
WALL =INTWALL : SURF=280 : AREA= 24.8 : ADJACENT=ZONE15 : FRONT
WALL =INTWALL : SURF=282 : AREA= 9.2 : ADJACENT=ZONE4 : FRONT
WALL =OUTWALL : SURF=284 : AREA= 22.06 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=POS005_010 : SURF=285 : AREA= 11.94 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL =INTWALL : SURF=286 : AREA= 29.1 : ADJACENT=ZONE13 : FRONT
WALL =INTWALL : SURF=288 : AREA= 40.4 : INTERNAL
WALL =INTWALL : SURF=289 : AREA= 40.4 : INTERNAL
WALL =INTWALL : SURF=290 : AREA= 40.4 : INTERNAL
WALL =INTWALL : SURF=291 : AREA= 40.4 : INTERNAL
WALL =INTFLOOR : SURF=292 : AREA= 85.5 : ADJACENT=ZONE27 : FRONT : GEOSURF=0.3
WALL =INTWALL : SURF=294 : AREA= 12.75 : ADJACENT=ZONE1 : FRONT
WALL =OUTWALL : SURF=296 : AREA= 9.25 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=POS005 : SURF=297 : AREA= 3.5 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL =INTFLOOR : SURF=298 : AREA= 22.3 : ADJACENT=ZONE27 : FRONT : GEOSURF=0.1
WALL =INTWALL : SURF=300 : AREA= 12.75 : ADJACENT=ZONE1 : FRONT
WALL =OUTWALL : SURF=302 : AREA= 9.25 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=POS005 : SURF=303 : AREA= 3.5 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL =INTFLOOR : SURF=304 : AREA= 22.3 : ADJACENT=ZONE27 : FRONT
WALL =INTWALL : SURF=306 : AREA= 12.75 : ADJACENT=ZONE1 : FRONT
WALL =OUTWALL : SURF=308 : AREA= 6.4 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=POS027 : SURF=309 : AREA= 6.35 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL =INTFLOOR : SURF=310 : AREA= 22.3 : ADJACENT=ZONE27 : FRONT : GEOSURF=0.1
WALL =INTWALL : SURF=312 : AREA= 13.26 : ADJACENT=ZONE1 : FRONT
WALL =OUTWALL : SURF=314 : AREA= 9.76 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=POS005 : SURF=315 : AREA= 3.5 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL =OUTWALL : SURF=316 : AREA= 20.2 : EXTERNAL : ORI=EAST : FSKY=0.5
WALL =INTFLOOR : SURF=317 : AREA= 23.2 : ADJACENT=ZONE27 : FRONT
REGIME
GAIN = PERS_ISO01 : SCALE= SCHEDULE 22*SUMMER_OCCUPANCY
INFILTRATION= INFIL001
VENTILATION = VENTMECH
COOLING = COOL001
HEATING = HEAT001
CAPACITANCE = 6932.16 : VOLUME= 722.1 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e ZONE13 / A i r n o d e ZONE13
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE13
AIRNODE ZONE13
WALL =INTFLOOR : SURF=212 : AREA= 85.5 : ADJACENT=ZONE2 : BACK
WALL =INTFLOOR : SURF=220 : AREA= 42.75 : ADJACENT=ZONE2 : BACK
WALL =INTWALL : SURF=277 : AREA= 29.1 : ADJACENT=ZONE14 : BACK
WALL =INTWALL : SURF=287 : AREA= 29.1 : ADJACENT=ZONE14 : BACK
WALL =INTWALL : SURF=320 : AREA= 25.9 : ADJACENT=ZONE20 : FRONT
WALL =INTWALL : SURF=322 : AREA= 8.5 : ADJACENT=ZONE1 : FRONT
WALL =OUTWALL : SURF=324 : AREA= 19.25 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=POS005_009 : SURF=325 : AREA= 14.75 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL =INTWALL : SURF=326 : AREA= 58.14 : INTERNAL
WALL =INTFLOOR : SURF=327 : AREA= 85.5 : ADJACENT=ZONE27 : FRONT : GEOSURF=0.6
WALL =INTWALL : SURF=329 : AREA= 8.5 : ADJACENT=ZONE1 : FRONT
WALL =INTWALL : SURF=331 : AREA= 8.5 : ADJACENT=ZONE15 : FRONT
WALL =OUTWALL : SURF=333 : AREA= 10.65 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=POS027 : SURF=334 : AREA= 6.35 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL =INTFLOOR : SURF=335 : AREA= 42.75 : ADJACENT=ZONE27 : FRONT
REGIME
GAIN = PERS_ISO01 : SCALE= SCHEDULE 29*SUMMER_OCCUPANCY
INFILTRATION= INFIL001
VENTILATION = VENTMECH
COOLING = COOL001
HEATING = HEAT001
CAPACITANCE = 3430 : VOLUME= 357.3 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e ZONE24 / A i r n o d e ZONE24
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE24
AIRNODE ZONE24
WALL =INTFLOOR : SURF=251 : AREA= 86.78 : ADJACENT=ZONE11 : BACK
WALL =INTFLOOR : SURF=259 : AREA= 106.875 : ADJACENT=ZONE11 : BACK
WALL =INTWALL : SURF=401 : AREA= 35.7 : ADJACENT=ZONE25 : FRONT
WALL =INTWALL : SURF=403 : AREA= 12.5 : ADJACENT=ZONE21 : FRONT
WALL =OUTWALL : SURF=405 : AREA= 33.65 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=POS005_009 : SURF=406 : AREA= 14.55 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL =OUTWALL : SURF=407 : AREA= 40.6 : EXTERNAL : ORI=WEST : FSKY=0.5
WALL =INTWALL : SURF=408 : AREA= 64.8 : INTERNAL
WALL =INTWALL : SURF=409 : AREA= 64.8 : INTERNAL
WALL =GROUNDFLOOR : SURF=410 : AREA= 86.78 : EXTERNAL : ORI=HORIZONTAL : FSKY=0.5 : GEOSURF=0.4
WALL =INTWALL : SURF=411 : AREA= 29.7 : ADJACENT=ZONE21 : FRONT
WALL =OUTWALL : SURF=413 : AREA= 20.54 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=POS013_027 : SURF=414 : AREA= 9.16 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL =GROUNDFLOOR : SURF=415 : AREA= 53.35 : EXTERNAL : ORI=HORIZONTAL : FSKY=0.5 : GEOSURF=0.2
WALL =INTWALL : SURF=416 : AREA= 29.64 : ADJACENT=ZONE21 : FRONT
WALL =OUTWALL : SURF=418 : AREA= 23.29 : EXTERNAL : ORI=NORTH : FSKY=0.5
WINDOW=POS027 : SURF=419 : AREA= 6.35 : EXTERNAL : ORI=NORTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_NORTH
WALL =INTWALL : SURF=420 : AREA= 32.4 : ADJACENT=ZONE29 : FRONT
WALL =GROUNDFLOOR : SURF=422 : AREA= 53.35 : EXTERNAL : ORI=HORIZONTAL : FSKY=0.5 : GEOSURF=0.2
REGIME
GAIN = PERS_ISO01 : SCALE= SCHEDULE 58*SUMMER_OCCUPANCY
INFILTRATION= INFIL001
VENTILATION = VENTMECH
COOLING = COOL001
CAPACITANCE = 4591.68 : VOLUME= 478.3 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e ZONE29 / A i r n o d e ZONE29
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE29
AIRNODE ZONE29
WALL =INTFLOOR : SURF=267 : AREA= 51 : ADJACENT=ZONE11 : BACK
WALL =INTWALL : SURF=319 : AREA= 17.8 : BOUNDARY=IDENTICAL
WALL =INTWALL : SURF=421 : AREA= 32.4 : ADJACENT=ZONE24 : BACK
REGIME
CAPACITANCE = 0.12 : VOLUME= 0.1 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e ZONE15 / A i r n o d e ZONE15
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE15
AIRNODE ZONE15
WALL =INTWALL : SURF=274 : AREA= 25.075 : ADJACENT=ZONE14 : BACK
WALL =INTWALL : SURF=281 : AREA= 24.8 : ADJACENT=ZONE14 : BACK
WALL =INTWALL : SURF=332 : AREA= 8.5 : ADJACENT=ZONE13 : BACK
WALL =INTWALL : SURF=340 : AREA= 17 : ADJACENT=ZONE20 : BACK
REGIME
CAPACITANCE = 0.12 : VOLUME= 0.1 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e ZONE27 / A i r n o d e ZONE27
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE27
AIRNODE ZONE27
WALL =INTFLOOR : SURF=279 : AREA= 85.5 : ADJACENT=ZONE14 : BACK
WALL =INTFLOOR : SURF=293 : AREA= 85.5 : ADJACENT=ZONE14 : BACK
WALL =INTFLOOR : SURF=299 : AREA= 22.3 : ADJACENT=ZONE14 : BACK
WALL =INTFLOOR : SURF=305 : AREA= 22.3 : ADJACENT=ZONE14 : BACK
WALL =INTFLOOR : SURF=311 : AREA= 22.3 : ADJACENT=ZONE14 : BACK
WALL =INTFLOOR : SURF=318 : AREA= 23.2 : ADJACENT=ZONE14 : BACK
WALL =INTFLOOR : SURF=328 : AREA= 85.5 : ADJACENT=ZONE13 : BACK
WALL =INTFLOOR : SURF=336 : AREA= 42.75 : ADJACENT=ZONE13 : BACK
WALL =INTWALL : SURF=348 : AREA= 36.2 : ADJACENT=ZONE26 : BACK
REGIME
CAPACITANCE = 0.12 : VOLUME= 0.1 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e ZONE20 / A i r n o d e ZONE20
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE20
AIRNODE ZONE20
WALL =INTWALL : SURF=321 : AREA= 25.9 : ADJACENT=ZONE13 : BACK
WALL =INTWALL : SURF=337 : AREA= 25.9 : ADJACENT=ZONE1 : FRONT
WALL =INTWALL : SURF=339 : AREA= 17 : ADJACENT=ZONE15 : FRONT
WALL =INTWALL : SURF=341 : AREA= 17 : ADJACENT=ZONE1 : FRONT
WALL =INTFLOOR : SURF=343 : AREA= 38.125 : ADJACENT=ZONE3 : FRONT
WALL =INTFLOOR : SURF=345 : AREA= 38.125 : ADJACENT=ZONE26 : FRONT
REGIME
INFILTRATION= INFIL001
CAPACITANCE = 924.48 : VOLUME= 96.3 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e ZONE26 / A i r n o d e ZONE26
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE26
AIRNODE ZONE26
WALL =INTFLOOR : SURF=346 : AREA= 38.125 : ADJACENT=ZONE20 : BACK
WALL =INTWALL : SURF=347 : AREA= 36.2 : ADJACENT=ZONE27 : FRONT
REGIME
CAPACITANCE = 0.12 : VOLUME= 0.1 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e ZONE30 / A i r n o d e ZONE30
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE30
AIRNODE ZONE30
WALL =INTFLOOR : SURF=356 : AREA= 27.1 : ADJACENT=ZONE17 : BACK
WALL =OUTWALL : SURF=365 : AREA= 30.64 : EXTERNAL : ORI=SOUTH : FSKY=0.5
WINDOW=TRIPLE : SURF=366 : AREA= 17.56 : EXTERNAL : ORI=SOUTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_SOUTH
WALL =INTFLOOR : SURF=376 : AREA= 47.58 : ADJACENT=ZONE18 : BACK
WALL =INTFLOOR : SURF=400 : AREA= 49.5 : ADJACENT=ZONE19 : BACK
REGIME
CAPACITANCE = 0.12 : VOLUME= 0.1 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e ZONE22 / A i r n o d e ZONE22
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE22
AIRNODE ZONE22
WALL =INTFLOOR : SURF=364 : AREA= 64.5 : ADJACENT=ZONE17 : BACK
WALL =OUTWALL : SURF=367 : AREA= 29.94 : EXTERNAL : ORI=SOUTH : FSKY=0.5
WINDOW=TRIPLE : SURF=368 : AREA= 17.56 : EXTERNAL : ORI=SOUTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_SOUTH
WALL =INTFLOOR : SURF=388 : AREA= 4 : ADJACENT=ZONE18 : BACK
WALL =INTFLOOR : SURF=395 : AREA= 18.7 : ADJACENT=ZONE18 : BACK
REGIME
CAPACITANCE = 0.12 : VOLUME= 0.1 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e ZONE18 / A i r n o d e ZONE18
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE18
AIRNODE ZONE18
WALL =OUTWALL : SURF=369 : AREA= 11.59 : EXTERNAL : ORI=SOUTH : FSKY=0.5
WINDOW=POS023 : SURF=370 : AREA= 9.28 : EXTERNAL : ORI=SOUTH : FSKY=0.5 : ESHADE=INPUT 0.7*S_SOUTH
WALL =INTWALL : SURF=371 : AREA= 20.87 : ADJACENT=ZONE1 : FRONT
WALL =INTWALL : SURF=373 : AREA= 32.1 : BOUNDARY=IDENTICAL
WALL =INTWALL : SURF=374 : AREA= 64.2 : INTERNAL
WALL =INTFLOOR : SURF=375 : AREA= 47.58 : ADJACENT=ZONE30 : FRONT : GEOSURF=0.6
WALL =INTFLOOR : SURF=377 : AREA= 47.58 : ADJACENT=ZONE31 : FRONT
WALL =INTWALL : SURF=380 : AREA= 7.125 : BOUNDARY=IDENTICAL
WALL =INTWALL : SURF=381 : AREA= 7.125 : ADJACENT=ZONE1 : FRONT
WALL =INTWALL : SURF=383 : AREA= 7.91 : ADJACENT=ZONE1 : FRONT
WALL =INTFLOOR : SURF=385 : AREA= 4 : ADJACENT=ROOM228 : FRONT
WALL =INTFLOOR : SURF=387 : AREA= 4 : ADJACENT=ZONE22 : FRONT
WALL =OUTWALL : SURF=389 : AREA= 10.875 : EXTERNAL : ORI=SOUTH : FSKY=0.5
WALL =INTWALL : SURF=390 : AREA= 24.15 : ADJACENT=ZONE1 : FRONT
WALL =INTFLOOR : SURF=392 : AREA= 18.7 : ADJACENT=ROOM228 : FRONT
WALL =INTFLOOR : SURF=394 : AREA= 18.7 : ADJACENT=ZONE22 : FRONT
REGIME
INFILTRATION= INFIL001
CAPACITANCE = 1614.3 : VOLUME= 168.16 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e ZONE25 / A i r n o d e ZONE25
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE25
AIRNODE ZONE25
WALL =INTWALL : SURF=402 : AREA= 35.7 : ADJACENT=ZONE24 : BACK
WALL =INTWALL : SURF=423 : AREA= 35.7 : BOUNDARY=IDENTICAL
REGIME
CAPACITANCE = 971.52 : VOLUME= 101.2 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* Z o n e ZONE21 / A i r n o d e ZONE21
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
ZONE ZONE21
AIRNODE ZONE21
WALL =INTWALL : SURF=404 : AREA= 12.5 : ADJACENT=ZONE24 : BACK
WALL =INTWALL : SURF=412 : AREA= 29.7 : ADJACENT=ZONE24 : BACK
WALL =INTWALL : SURF=417 : AREA= 29.64 : ADJACENT=ZONE24 : BACK
REGIME
CAPACITANCE = 0.12 : VOLUME= 0.1 : TINITIAL= 20 : PHINITIAL= 50 : WCAPR= 1
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* O u t p u t s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
OUTPUTS
TRANSFER : TIMEBASE=1.000
AIRNODES = ROOM228
NTYPES = 1 : TAIR - air temperature of zone
AIRNODES = ROOM228
NTYPES = 2 : QSENS - sensible energy demand of zone, heating(-), cooling(+)
= 4 : QINF - sensible infiltration energy gain of zone
= 5 : QVENT - tsensible ventilation energy gain of zone
= 25 : TOP - operative zone temperature
= 30 : QHEAT - sensible heating demand of zone (positive values)
= 31 : QCOOL - sensible cooling demand of zone (positive values)
AIRNODES = ROOM228
NTYPES = 904 : BAL_4 - energy balance for all zones
= 906 : SURF = 1, 2, 6, 7, 3, : BAL_6 - energy balance for a surface
AIRNODES = ROOM228
NTYPES = 9 : RELHUM - relativ humidity of zone air
= 17 : SURF = 1, 2, 6, 7, 3, : TSI - inside surface temperature
= 18 : SURF = 1, 2, 6, 7, 3, : TSO - outside surface temperature
AIRNODES = ROOM228
NTYPES = 904 : BAL_4 - energy balance for all zones
= 901 : BAL_1 - solar balance for all zones
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
* E n d
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
END
_EXTENSION_WINPOOL_START_
WINDOW 4.1 DOE-2 Data File : Multi Band Calculation
Unit System : SI
Name : TRNSYS 15 WINDOW LIB
Desc : Waermeschutzglas,Ar, 1.4 71/59
Window ID : 2001
Tilt : 90.0
Glazings : 2
Frame : 11 2.270
Spacer : 1 Class1 2.330 -0.010 0.138
Total Height: 1219.2 mm
Total Width : 914.4 mm
Glass Height: 1079.5 mm
Glass Width : 774.7 mm
Mullion : None
Gap Thick Cond dCond Vis dVis Dens dDens Pr dPr
1 Argon 16.0 0.01620 5.000 2.110 6.300 1.780 -0.0060 0.680 0.00066
2 0 0 0 0 0 0 0 0 0
3 0 0 0 0 0 0 0 0 0
4 0 0 0 0 0 0 0 0 0
5 0 0 0 0 0 0 0 0 0
Angle 0 10 20 30 40 50 60 70 80 90 Hemis
Tsol 0.426 0.428 0.422 0.413 0.402 0.380 0.333 0.244 0.113 0.000 0.354
Abs1 0.118 0.118 0.120 0.123 0.129 0.135 0.142 0.149 0.149 0.000 0.132
Abs2 0.190 0.192 0.198 0.201 0.200 0.199 0.199 0.185 0.117 0.000 0.191
Abs3 0 0 0 0 0 0 0 0 0 0 0
Abs4 0 0 0 0 0 0 0 0 0 0 0
Abs5 0 0 0 0 0 0 0 0 0 0 0
Abs6 0 0 0 0 0 0 0 0 0 0 0
Rfsol 0.266 0.262 0.260 0.262 0.269 0.286 0.326 0.422 0.621 1.000 0.314
Rbsol 0.215 0.209 0.207 0.210 0.219 0.237 0.272 0.356 0.560 0.999 0.260
Tvis 0.706 0.710 0.701 0.688 0.670 0.635 0.556 0.403 0.188 0.000 0.590
Rfvis 0.121 0.115 0.114 0.118 0.132 0.163 0.228 0.376 0.649 1.000 0.203
Rbvis 0.103 0.096 0.093 0.096 0.108 0.132 0.179 0.286 0.520 0.999 0.162
SHGC 0.589 0.593 0.591 0.586 0.574 0.551 0.505 0.405 0.218 0.000 0.518
SC: 0.55
Layer ID# 9052 9065 0 0 0 0
Tir 0.000 0.000 0 0 0 0
Emis F 0.840 0.140 0 0 0 0
Emis B 0.840 0.840 0 0 0 0
Thickness(mm) 4.0 4.0 0 0 0 0
Cond(W/m2-C ) 225.0 225.0 0 0 0 0
Spectral File None None None None None None
Overall and Center of Glass Ig U-values (W/m2-C)
Outdoor Temperature -17.8 C 15.6 C 26.7 C 37.8 C
Solar WdSpd hcout hrout hin
(W/m2) (m/s) (W/m2-C)
0 0.00 12.25 3.25 7.62 1.54 1.54 1.31 1.31 1.35 1.35 1.47 1.47
0 6.71 25.47 3.21 7.64 1.62 1.62 1.36 1.36 1.40 1.40 1.53 1.53
783 0.00 12.25 3.39 7.99 1.69 1.69 1.54 1.54 1.51 1.51 1.54 1.54
783 6.71 25.47 3.30 7.81 1.79 1.79 1.63 1.63 1.58 1.58 1.59 1.59
WINDOW 4.1 DOE-2 Data File : Multi Band Calculation
Unit System : SI
Name : TRNSYS 15 WINDOW LIB
Desc : Insulating, 0.7, Krypton
Window ID : 4001
Tilt : 90.0
Glazings : 3
Frame : 11 2.270
Spacer : 1 Class1 2.330 -0.010 0.138
Total Height: 1219.2 mm
Total Width : 914.4 mm
Glass Height: 1079.5 mm
Glass Width : 774.7 mm
Mullion : None
Gap Thick Cond dCond Vis dVis Dens dDens Pr dPr
1 Krypton 8.0 0.00860 2.800 2.280 7.500 3.740 -0.0137 0.660 0.00002
2 Krypton 8.0 0.00860 2.800 2.280 7.500 3.740 -0.0137 0.660 0.00002
3 0 0 0 0 0 0 0 0 0
4 0 0 0 0 0 0 0 0 0
5 0 0 0 0 0 0 0 0 0
Angle 0 10 20 30 40 50 60 70 80 90 Hemis
Tsol 0.268 0.270 0.263 0.253 0.243 0.223 0.183 0.116 0.042 0.000 0.207
Abs1 0.327 0.330 0.339 0.345 0.347 0.351 0.367 0.380 0.313 0.001 0.347
Abs2 0.066 0.066 0.067 0.068 0.070 0.071 0.070 0.064 0.051 0.000 0.067
Abs3 0.108 0.110 0.112 0.113 0.110 0.107 0.101 0.082 0.041 0.000 0.100
Abs4 0 0 0 0 0 0 0 0 0 0 0
Abs5 0 0 0 0 0 0 0 0 0 0 0
Abs6 0 0 0 0 0 0 0 0 0 0 0
Rfsol 0.231 0.223 0.220 0.221 0.230 0.247 0.279 0.357 0.554 0.999 0.269
Rbsol 0.231 0.223 0.220 0.221 0.230 0.247 0.279 0.357 0.554 0.999 0.269
Tvis 0.625 0.632 0.615 0.595 0.570 0.523 0.425 0.265 0.097 0.000 0.484
Rfvis 0.137 0.125 0.121 0.125 0.142 0.172 0.226 0.336 0.554 0.999 0.199
Rbvis 0.137 0.125 0.121 0.125 0.142 0.172 0.226 0.336 0.554 0.999 0.199
SHGC 0.407 0.412 0.406 0.398 0.387 0.365 0.319 0.233 0.112 0.000 0.341
SC: 0.39
Layer ID# 9059F 9052 9060 0 0 0
Tir 0.000 0.000 0.000 0 0 0
Emis F 0.840 0.840 0.070 0 0 0
Emis B 0.070 0.840 0.840 0 0 0
Thickness(mm) 4.0 4.0 4.0 0 0 0
Cond(W/m2-C ) 225.0 225.0 225.0 0 0 0
Spectral File None None None None None None
Overall and Center of Glass Ig U-values (W/m2-C)
Outdoor Temperature -17.8 C 15.6 C 26.7 C 37.8 C
Solar WdSpd hcout hrout hin
(W/m2) (m/s) (W/m2-C)
0 0.00 12.25 3.20 7.17 0.63 0.63 0.65 0.65 0.67 0.67 0.69 0.69
0 6.71 25.47 3.19 7.18 0.64 0.64 0.66 0.66 0.68 0.68 0.71 0.71
783 0.00 12.25 3.55 8.29 0.72 0.72 0.74 0.74 0.77 0.77 0.79 0.79
783 6.71 25.47 3.38 8.21 0.74 0.74 0.75 0.75 0.77 0.77 0.79 0.79
WINDOW 4.1 DOE-2 Data File : Multi Band Calculation
Unit System : SI
Name : TRNSYS 14.2 WINDOW LIB
Desc : No glazing = open
Window ID : 10001
Tilt : 90.0
Glazings : 1
Frame : 11 2.270
Spacer : 1 Class1 2.330 -0.010 0.138
Total Height: 1219.2 mm
Total Width : 914.4 mm
Glass Height: 1079.5 mm
Glass Width : 774.7 mm
Mullion : None
Gap Thick Cond dCond Vis dVis Dens dDens Pr dPr
1 0 0 0 0 0 0 0 0 0
2 0 0 0 0 0 0 0 0 0
3 0 0 0 0 0 0 0 0 0
4 0 0 0 0 0 0 0 0 0
5 0 0 0 0 0 0 0 0 0
Angle 0 10 20 30 40 50 60 70 80 90 Hemis
Tsol 1.000 1.000 1.000 1.000 1.000 1.000 1.000 1.000 1.000 1.000 0.999
Abs1 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.001 0.000 0.001
Abs2 0 0 0 0 0 0 0 0 0 0 0
Abs3 0 0 0 0 0 0 0 0 0 0 0
Abs4 0 0 0 0 0 0 0 0 0 0 0
Abs5 0 0 0 0 0 0 0 0 0 0 0
Abs6 0 0 0 0 0 0 0 0 0 0 0
Rfsol 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000
Rbsol 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000
Tvis 1.000 1.000 1.000 1.000 1.000 1.000 1.000 1.000 1.000 1.000 0.999
Rfvis 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000
Rbvis 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000 0.000
SHGC 1.000 1.000 1.000 1.000 1.000 1.000 1.000 1.000 1.000 0.000 1.000
SC: 1.0
Layer ID# 9052 0 0 0 0 0
Tir 0.000 0 0 0 0 0
Emis F 1.000 0 0 0 0 0
Emis B 1.000 0 0 0 0 0
Thickness(mm) 0.001 0 0 0 0 0
Cond(W/m2-C ) 999.0 0 0 0 0 0
Spectral File None None None None None None
Overall and Center of Glass Ig U-values (W/m2-C)
Outdoor Temperature -17.8 C 15.6 C 26.7 C 37.8 C
Solar WdSpd hcout hrout hin
(W/m2) (m/s) (W/m2-C)
0 0.00 12.25 3.42 8.23 5.27 5.27 4.95 4.95 4.94 4.94 5.53 5.53
0 6.71 25.47 3.33 8.29 6.26 6.26 5.73 5.73 5.68 5.68 6.46 6.46
783 0.00 12.25 3.49 8.17 5.25 5.25 4.58 4.58 5.24 5.24 5.66 5.66
783 6.71 25.47 3.37 8.27 6.25 6.25 5.53 5.53 5.95 5.95 6.57 6.57
*** END OF LIBRARY ***
***************************************************************************************************
*WinID Description Design U-Value g-value T-sol Rf-sol T-vis
***************************************************************************************************
2001 Waermeschutzglas,Ar, 1.4 71/59 4/16/4 1.4 0.589 0.426 0.266 0.706
4001 Insulating, 0.7, Krypton 4/8/4/8/4 0.68 0.407 0.268 0.231 0.625
10001 No glazing = open 0.001 5.68 1 1 0 1
_EXTENSION_WINPOOL_END_
***** WALL TRANSFERFUNCTION CALCULATIONS *****
---------- WALL TYPE OUTWALL ----------
THERMAL CONDUCTANCE, U= 0.47220 kJ/h m2K; U-Wert= 0.12831 W/m2K
(incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
TRANSFERFUNCTION COEFFICIENTS
K A B C D
0 2.1664880E+00 1.4941859E-08 1.3594604E+02 1.0000000E+00
1 -5.1626650E+00 1.5678719E-04 -3.2396483E+02 -1.7972276E+00
2 4.3549828E+00 3.6969384E-03 2.7304031E+02 1.0527114E+00
3 -1.5684135E+00 9.4702863E-03 -9.9002477E+01 -2.3297156E-01
4 2.4111882E-01 4.8248043E-03 1.4836511E+01 1.7498815E-02
5 -1.3025818E-02 5.5308256E-04 -8.5049327E-01 -3.7867559E-04
6 2.3080730E-04 1.3367874E-05 1.3695979E-02 1.5039292E-06
7 -7.1874572E-07 5.7183774E-08 -4.8402076E-05
8 4.8217520E-10 3.4122444E-11 2.8330727E-08
SUM 1.8715339E-02 1.8715339E-02 1.8715339E-02 3.9633938E-02
---------- WALL TYPE INTWALL ----------
THERMAL CONDUCTANCE, U= 60.48000 kJ/h m2K; U-Wert= 4.35685 W/m2K
(incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
TRANSFERFUNCTION COEFFICIENTS
K A B C D
0 1.3643561E+02 2.4523224E+01 1.3643561E+02 1.0000000E+00
1 -8.3598248E+01 3.0209570E+01 -8.3598248E+01 -8.3195199E-02
2 2.6113051E+00 7.1578697E-01 2.6113051E+00 3.9741583E-06
3 -7.6332918E-05 1.4006143E-05 -7.6332918E-05
SUM 5.5448595E+01 5.5448595E+01 5.5448595E+01 9.1680877E-01
---------- WALL TYPE INTFLOOR ----------
THERMAL CONDUCTANCE, U= 20.02649 kJ/h m2K; U-Wert= 2.85909 W/m2K
(incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
TRANSFERFUNCTION COEFFICIENTS
K A B C D
0 1.3591505E+02 5.5464044E-01 4.8674940E+01 1.0000000E+00
1 -1.6203728E+02 5.3300691E+00 -5.1743306E+01 -5.9724260E-01
2 3.5240814E+01 2.5042177E+00 1.1798720E+01 1.9596098E-02
3 -6.6159971E-01 6.8734728E-02 -2.7285626E-01 -2.7184320E-05
4 7.2575131E-04 5.1739309E-05 2.1572959E-04
SUM 8.4577137E+00 8.4577137E+00 8.4577137E+00 4.2232631E-01
---------- WALL TYPE ROOF ----------
THERMAL CONDUCTANCE, U= 0.34521 kJ/h m2K; U-Wert= 0.09435 W/m2K
(incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
TRANSFERFUNCTION COEFFICIENTS
K A B C D
0 2.2657674E+00 1.9806379E-13 1.3594604E+02 1.0000000E+00
1 -6.9170769E+00 4.0822983E-07 -4.1502477E+02 -2.4670763E+00
2 8.1409673E+00 7.0392405E-05 4.8844598E+02 2.2442229E+00
3 -4.6725429E+00 7.5243126E-04 -2.8042731E+02 -9.3552198E-01
4 1.3737763E+00 1.5575064E-03 8.2337052E+01 1.8323953E-01
5 -2.0052002E-01 8.6758907E-04 -1.2054922E+01 -1.5547561E-02
6 1.3397353E-02 1.4372842E-04 8.0336957E-01 5.3578226E-04
7 -3.7248398E-04 7.0304141E-06 -2.2231129E-02 -5.5084064E-06
8 3.2326315E-06 9.4400483E-08 1.9711055E-04 1.8089477E-08
9 -9.3292759E-09 3.0973529E-10 -5.4537335E-07
SUM 3.3991809E-03 3.3991809E-03 3.3991806E-03 9.8468336E-03
---------- WALL TYPE GROUNDFLOOR ----------
THERMAL CONDUCTANCE, U= 0.08007 kJ/h m2K; U-Wert= 0.02216 W/m2K
(incl. alpha_i=7.7 W/m^2 K and alpha_o=25 W/m^2 K)
TRANSFERFUNCTION COEFFICIENTS
K A B C D
0 2.1664905E+00 -8.2422957E-13 3.7770219E-01 1.0000000E+00
1 -8.3062921E+00 3.8858170E-12 -1.4482826E+00 -3.2489666E+00
2 1.3020361E+01 1.0209690E-09 2.2693688E+00 4.1987902E+00
3 -1.0788399E+01 5.5713242E-08 -1.8795046E+00 -2.7787585E+00
4 5.1128462E+00 4.4823352E-07 8.9114391E-01 1.0096736E+00
5 -1.4069812E+00 9.5739196E-07 -2.4581467E-01 -2.0019349E-01
6 2.1974507E-01 6.8082536E-07 3.8483756E-02 2.0495957E-02
7 -1.8543765E-02 1.7671247E-07 -3.2275584E-03 -1.0367126E-03
8 7.9166489E-04 1.7131858E-08 1.3581963E-04 2.5048501E-05
9 -1.6095843E-05 6.0862308E-10 -2.7993726E-06 -2.5645336E-07
10 1.4027476E-07 6.9098112E-12 2.5214797E-08
SUM 2.3380257E-06 2.3376480E-06 2.3377143E-06 2.9195849E-05
** ERROR - STABILITY CRITERIA FOR WALL TYPE GROUNDFLOOR NOT FULLFILLED
CHECK LAYER VALUES
NO FILE GENERATED **
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Error creating the wall transfer function coeffients.bmp
Type: image/bmp
Size: 983094 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20121115/03425776/attachment-0001.bin>
More information about the TRNSYS-users
mailing list