Juan Francisco,
   I may be misinterpreting what you mean by non-symmetric adjacent 
walls. However, if it is the case I am imagining, you have a zone 
containing one wall that is adjacent to two other zones (draw a large 
box with a T-shape in it so that you have one box on top and two smaller 
boxes underneath). In this case, you have to break up the wall in the 
zone on top into two walls, each one adjacent to a single zone. The zone 
on top will end up having 5 walls instead of 4.
Kind regards,
  David