[TRNSYS-users] Type 107: Absorption chiller data file: How do I calculate the fraction of capacity?
David BRADLEY
d.bradley at tess-inc.com
Fri May 11 12:00:42 PDT 2012
Leon,
I believe that fraction of capacity is the currently available
capacity (due to non-design inlet temperatures, flow rates, ambient
conditions, etc.) divided by the machine's rated capacity (at design
conditions) and that the fraction of design load is the current load on
the machine divided by its rated load.
The idea in all this is that the performance is based on two things:
1. the capacity and required energy input are a function of the inlet
conditions as compared to design input conditions. 2. the required
energy input (but NOT the capacity) depends on how much of the design
load the machine currently has to meet.
Best,
David
On 5/10/2012 17:54, Leon Becker wrote:
> Dear TRNSYS User,
>
> for a research project I'm trying to simulate a hot water fired absorption chiller with TRNSYS 16. I thought I could create a datafile representing the performance of the Yazaki WFC-SC5 using the type 107 in the TRNSYS library.
> After reading the Mathematical references and the existing threads I still don't understand the difference between fraction of design load and fraction of capacity. As far as I understand, the values I need to calculate for the data file are:
>
> fraction of design load=capacity/rated capacity
> fraction of design energy input= (required heat/ratedheat input) *fraction of design load
> fraction of capacity=???
>
> Please correct me, if I'm wrong. Moreover, I still don't get how to really calculate the fraction of capacity.
>
> It would be a great help if someone could explain me the missing equation.
>
> Does anyone have another idea how to simulate an absorption chiller with TRNSYS?
>
> Thanks a lot.
> Best regards,
>
> Leon Becker
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
More information about the TRNSYS-users
mailing list