[TRNSYS-users] External data files for heat pump & absorbtion chiller
    David BRADLEY 
    d.bradley at tess-inc.com
       
    Fri May 11 11:50:35 PDT 2012
    
    
  
Santeri,
   In my experience, it is not overly difficult to find heat pump 
performance data. Try Florida Heat Pumps (http://www.fhp-mfg.com/) as 
they have a fairly extensive line of water to water heat pumps. It is 
also nice that heat pumps normalize fairly well. That is to say that if 
you take two heat pumps and divide their performance at off-design 
conditions by the corresponding rated condition, both heat pumps will 
end up looking quite similar.
   It is, however, comparatively difficult to get data for absorption 
chillers. If you are not finding printed catalog data, you might try 
calling a manufacturer's representative; they may have access to data 
that you can use. Also more and more often manufacturers are developing 
in-house software to assist in assessing off-design performance. I have 
had some luck in getting manufacturers to let me use the software and 
then making a performance map of my own. One word of caution: absorption 
chiller performance does NOT normalize well.
Best,
David
On 5/10/2012 08:33, Santeri Siren wrote:
> Dear all,
>
> I need to use a water to water ground heat pump (type 668) and 
> absorbtion chiller in my simulations. It seems to be very difficult to 
> find product catalogues that include the information required in the 
> external data files. Could someone with experience please tell me 
> which manufacturers do provide this kind of information and perhaps 
> send me a link. The only catalogue data file that I was able to for 
> water to water heat pump was this one from Carrier:
>
> http://www.docs.hvacpartners.com/idc/groups/public/documents/techlit/50psw-3pd.pdf
>
> Best regards. Santeri Siren
>
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com