[TRNSYS-users] Radiator type 1231 with type 56
    David BLANDIN 
    David.BLANDIN at cardonnel.fr
       
    Thu May  3 05:47:56 PDT 2012
    
    
  
Hi,
It might be due to the fact that you cannot have an Inlet Water Temperature (inlet3) below the Room temperature (inlet 1) with this component.
Inlet water temperature > Room temperature +0.5
An idea is thus to control the inlet3 to max(inlet temperature, room temperature +0.5)
Best regards,
David BLANDIN
CARDONNEL Ingénierie
Le confort durable du bâtiment
5 rue de la Mare à Tissier
91280 SAINT PIERRE DU PERRAY
Tél : 01 64 98 19 22 - Fax 01 64 98 25 09
david.blandin at cardonnel.fr<mailto:david.blandin at cardonnel.fr>
De : trnsys-users-bounces at cae.wisc.edu [mailto:trnsys-users-bounces at cae.wisc.edu] De la part de Richard Thygesen
Envoyé : mercredi 25 avril 2012 16:15
À : TRNSYS-users at engr.wisc.edu
Objet : [TRNSYS-users] Radiator type 1231 with type 56
Hi.
I'm trying to use the radiator model type 1231 together with type 56.
Is it possible to connect air temperatures from a zone in type 56 to the type 1231 room temperature input? When I do that I get a run time error.
Best regards
richard.thygesen at mdh.se<mailto:richard.thygesen at mdh.se>