[TRNSYS-users] Question active layer in type 56
David BRADLEY
d.bradley at tess-inc.com
Tue May 15 10:36:26 PDT 2012
Richard,
The active layer model does handle no-flow. The air temperature may
not be the best variable to watch to determine whether the system is
operating properly; radiant floor systems often try to keep people
comfortable by keeping the zone surfaces either cool or warm and letting
the air temperature float through a wider range than is generally
acceptable in purely air-based systems. You might look instead at the
inside surface temperature of your radiant slab. I would think that you
would see a slower response to turning the GSHP on and off there.
Best,
David
On 5/15/2012 01:48, Richard Thygesen wrote:
>
> Hi.
>
> Have any of you out there had problem with controlling an active layer
> in type 56?
>
> I have connected the active layer to a GSHP system but the indoor
> temperature rise sharply when the controller turns the GSHP off and
> return to a "normal" 20°C when the GSHP starts again. Is the active
> layer incapable of handle a no flow situation?
>
> Does anyone know what the problem might be?
>
> Best regards
>
> *Richard Thygesen*
>
> Doctoral student
>
> *Mälardalen University*
>
> School of Sustainable Development of Society and Technology
>
> Phone: +46(0)21-10 31 82
>
> _richard.thygesen at mdh.se <mailto:richard.thygesen at mdh.se>_
>
> www.mdh.se <http://www.mdh.se/>
>
> *Beskrivning: Beskrivning: mälardalens högskola*
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120515/9b5fb9c9/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2447 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120515/9b5fb9c9/attachment-0001.jpeg>
More information about the TRNSYS-users
mailing list