Eva,
It isn't entirely clear what you have to change. However, Type56
thinks that it should be expecting 23 inputs but it is receiving 27.
There is a discrepancy between your *.b17 file and your Studio project
that needs to be resolved. I would start by opening TRNBuild and making
sure that the list of inputs (in the project window) is correct. Then
save the *.b17 project and exit to the Studio. Right click on the Type56
icon and tell it to "update building variable list." Last, make any
required connection corrections.
Best,
David
On 5/10/2012 12:03, Eva gklezakou wrote:
> Dear Sirs,
>
> when I run my simulation the below message is appeared, what do I have
> to change in order to get results?
> *** Fatal Error at time : 5000.000000
> Generated by Unit : 12
> Generated by Type : 56
> TRNSYS Message 103 : The TRNSYS TYPE checking routine has found
> an inconsistency in the specified component between the input file and
> the information expected by the Type
> Reported information : An illegal number of INPUTS has been
> specified for this component. Please check the component
> configuration. 23 INPUTS are required and 27 were specified.
>
> Thank you.
>
> Regards,
> Eva
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120511/ac811863/attachment-0001.htm>
More information about the TRNSYS-users
mailing list