Alessandro,
If you can email the *.b17 file, it is a bit easier to tell what the
problem may be. If I had to guess, I would say that one of your walls is
either too massive or not massive enough for TRNBuild to generate
transfer function coefficients. To determine which wall is causing the
problem, look in the *.inf file (it is text based). If it is a very low
thermal mass wall, you can treat it as a purely resistive wall (i.e.
treat it as though it had no thermal mass by using "massless" layers
only.) If it is a very thick or highly thermally massive wall, you can
increase the timebase to 2 hours (click on the outputs button in the
main project window).
Kind regards,
David
On 4/30/2012 04:55, Alessandro Rinaldi wrote:
> Hi, i am creating a package wall in TRNBUILd but after entering all
> the layers and thicknesses tells me "ERROR- STABILITY CRITERIA FOR
> WALL TYPE NOT FULLFILLED"..what is the problem?how can i solve it?thanks
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120501/03e2c3ba/attachment-0001.htm>
More information about the TRNSYS-users
mailing list