Laurent,
There is no flat plate HX module in TRNSYS yet, just HX simple models that
either allow you to input "constant effectiveness" (Type91) or
"overall heat transfer coefficient" (Type5).
This makes things kind of difficult because those two inputs are determined
by the fluid properties, flowrate, temperature, number of plates, material,
area of plates, etc. SInce the flowrates and temperatures can be changing,
so can the overall HTC. Also, you need to find a way to determine the
overall HTC based on the geometry of the HX. This requires a lot of
iterative calculations and is not that easy to accomplish.
Currently as a workaround, I am using GEA's software which is pretty good
to size a flat plate heat exchanger for me, and then I give it the
parameters that I would use it TRNSYS. It let's me select different size
heat exchangers and then eventually, the software will spit out it's
"Overall HTC" (in W/m^2-K) and a "nominal surface area" (in m^2). I simply
multiply the values and use this as my input for "Overall heat
transfer coefficient" in Type5b (I have found the *counter flow* version is
the closest match for flat plates when using an overall HTC). You can login
to the software as a web app here or download it too once you register a
username.
http://flatplateselect.com/site/pub/login.aspx?ReturnUrl=%2fsite%2fDefault.aspx
This isn't a perfect method obviously, because the overall HTC will change
with varying temperatures and flowrates, but as long as you are in the ball
park, it will be pretty close. If your flows and incoming temperatures
don't change, then you will be even more accurate. If you only have one
variable that changes frequently, you could develop a fit curve equation
that determines the overall HTC and use that equation as an input for the
"overall heat transfer coefficient". But this would require going through
the GEA software and spitting out multiple outputs by changing your single
input at several different points. Then you would have to put the data in
excel or something similar to find an equation.
This is the best method I have come up with so far, but I am currently
developing a set of equations using EES from Nellis & Klein's "Heat
Transfer" book, that will mimic a flat plate by actually supplying
dimensions, # of plates, thermal conductivty of plates, etc. It will also
allow me to supply inputs that vary and should always give me
an accurate heat transfer coefficient. I plan to tie the inputs to TRNSYS
inputs (possibly using the Type66, or just perhaps writing new Fortran
code) and execute the EES code in TRNSYS eventually. I'm working on it, but
I"ll let you know how it turns out. The EES side is basically done, but I
need to verify the equations.
Hope this helps.
Nick LaHam
2012/3/9 <trnsys-users-request at cae.wisc.edu>
> Send TRNSYS-users mailing list submissions to
> trnsys-users at cae.wisc.edu
>
> To subscribe or unsubscribe via the World Wide Web, visit
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
> or, via email, send a message with subject or body 'help' to
> trnsys-users-request at cae.wisc.edu
>
> You can reach the person managing the list at
> trnsys-users-owner at cae.wisc.edu
>
> When replying, please edit your Subject line so it is more specific
> than "Re: Contents of TRNSYS-users digest..."
>
> Today's Topics:
>
> 1. type 56 (gabriela vlad)
> 2. Natural ventilation (Chou Shen)
> 3. Water to Water Plate Heat Exchanger (REYNIER Laurent)
> 4. on cooled ceiling (Enyuan Hu)
>
>
> ---------- Forwarded message ----------
> From: gabriela vlad <gabi_ev at yahoo.com>
> To: "trnsys-users at cae.wisc.edu" <trnsys-users at cae.wisc.edu>
> Cc:
> Date: Fri, 9 Mar 2012 03:34:57 -0800 (PST)
> Subject: [TRNSYS-users] type 56
> Dear users,
>
> I want to model a building with type 56. I divided the building into
> several thermal zones but two of them which are adjacent zones aren't
> separated by a wall (there is only air between them). Please, give me your
> opinion, How can the two zones be separated?
>
>
> ---------- Forwarded message ----------
> From: Chou Shen <csz59 at mst.edu>
> To: trnsys-users at cae.wisc.edu
> Cc:
> Date: Fri, 9 Mar 2012 08:24:34 -0600
> Subject: [TRNSYS-users] Natural ventilation
> Hello,
>
> I am trying to use TRNSYS to simulate the situation when a building takes
> natural ventilation rather than air conditioning system in swing seasons.
> In that way, the air conditioning turns off when outdoor temperature is in
> the range of [tlow, thigh]. I want to see how much energy saving is
> achieved by implementing natural ventilation. Can I achieve my goal? How
> can I implement natural ventilation in TRNSYS? Thanks!
>
> --
> Chou Shen
> Graduate Research Assistant
> Department of Civil, Architectural & Environmental Engineering
> Missouri University of Science and Technology
>
>
>
>
>
> ---------- Forwarded message ----------
> From: REYNIER Laurent <Laurent.REYNIER at cstb.fr>
> To: "trnsys-users at cae.wisc.edu" <trnsys-users at cae.wisc.edu>
> Cc:
> Date: Fri, 9 Mar 2012 15:52:28 +0000
> Subject: [TRNSYS-users] Water to Water Plate Heat Exchanger
>
> Dear TRNSYS users,****
>
> I’m searching for a reliable model of a water-to-water plate heat
> exchanger.****
>
> Can you give me your opinion on the one you are using and which TRNSYS
> type you use for simulation.****
>
> ** **
>
> Thank you in advance for your help.****
>
> Sincerely yours.****
>
> Laurent.****
>
> ** **
>
> ** **
>
> *Laurent REYNIER***
>
> *Département ESE/ Division Energie/ Ingénieur Etudes et Recherche***
>
> *Centre Scientifique et Technique du Bâtiment*
>
> *84 avenue Jean Jaurès - Champs-sur-Marne - 77447 Marne-la-Vallée Cedex 2*
> ****
>
> *Tél : 01 61 44 80 55*
>
> *Fax : 01 64 68 83 50*
>
> *Évitez d’imprimer vos emails inutilement. Respectez l’environnement*****
>
> *Ce message et toutes les pièces jointes sont confidentiels et exclusifs
> pour le destinataire du message. N'importe quelle autre distribution,
> utilisation ou reproduction est non autorisée et interdite. Si vous
> receviez ce message par erreur, informez svp l'expéditeur immédiatement et
> supprimez le message de votre système. *****
>
> *This message and any attachments are confidential, for the exclusive use
> of the addressee and may be legally privileged. Any other distribution, use
> or reproduction is unauthorised and prohibited. If you received this
> message in error, please notify the sender immediately and delete the
> message from your system*****
>
> ** **
>
>
> ---------- Forwarded message ----------
> From: Enyuan Hu <bearcharge at gmail.com>
> To: trnsys-users <trnsys-users at cae.wisc.edu>
> Cc:
> Date: Fri, 9 Mar 2012 11:36:37 -0500
> Subject: [TRNSYS-users] on cooled ceiling
> Dear TRNSYSers,
>
> I was wondering if anyone can help me on the cooled ceiling mode.
> Specifically, I have several questions:
>
> 1. how should the cooled ceiling layer be defined? can we define it as
> part of the roof layer (category EXTERNAL and orientation Horizontal) or
> should we define it separately? separate definition is my feeling after
> reviewing some literature.
>
> 2. how should we set up the layer parameters? in the manual, it indicates
> that parameters like norm area can be obtained from the producer, does that
> mean that's the only way to reasonably set up parameters and otherwise
> there will be problem?
>
> 3. if would be best if some user can generously provide an example on
> this. This may be asking too much, but I really think it would help indeed.
>
> Thanks.
>
> Enyuan
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120312/7e811f4a/attachment-0005.htm>
More information about the TRNSYS-users
mailing list