[TRNSYS-users] type 660 simple building model
Thibaut VITTE
thibaut.vitte at h3c-energies.fr
Thu Mar 29 07:29:14 PDT 2012
Dear Trnsys users,
I'm using type 660 to modelize "quickly" a simple building. Having
troubles to analyse the results, I've tested it and compared it with
regular type 56.
the building is an office building with high internal loads, large
glazed surfaces.
the heated area is 9200m², with an overall loss coefficient of 0.7
W/m²°C, 69 kJ/K.m3.
The annual results seem quite good, since I'm finding diffrences in
annual heating/cooling loads less than 10%.
As far as temperatures and free floating building functionning (see
picture attached), it's not that good, but I understand that a simple
capacitance model is limited for that purpose.
But the problem is for maximum heating/cooling power. I have inputed
night set back for cooling and heating. And I think that the whole
building capacitance is taken into account when a moving setpoint is
applied! Which implies great instantaneous power. ( 6 times greater than
the one calculated by type 56.) (see picture). The wole building (air +
walls) is heated or cooled when a setpoint changes (as I understand the
model), which is not quite the reality..
Am I right? Is there a simple model that can calculate approximately the
instantaneous power with moving setpoint (in Trnsys type 12, setpoints
are only parameters)?
Thanks in advance.
Thibaut
-------------- next part --------------
A non-text attachment was scrubbed...
Name: heating loads 400 1st hrs.png
Type: image/png
Size: 22693 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120329/ecac6972/attachment-0003.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: temperature 1st 400 hrs.png
Type: image/png
Size: 22034 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120329/ecac6972/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: annual temperature.png
Type: image/png
Size: 22506 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120329/ecac6972/attachment-0005.png>
More information about the TRNSYS-users
mailing list