Dear LEE
Law 1. With impeller diameter (D) held constant:
Law 1a. Flow is proportional to shaft speed:
Law 1b. Pressure or Head is proportional to the square of shaft speed:
Law 1c. Power is proportional to the cube of shaft speed:
Law 2. With shaft speed (N) held constant:
Law 2a. Flow is proportional to impeller diameter:
Law 2b. Pressure or Head is proportional to the square of impeller diameter:
Law 2c. Power is proportional to the cube of impeller diameter:
where
* is the volumetric flow rate (e.g. CFM, GPM or L/s),
* is the impeller diameter (e.g. in or mm),
* is the shaft rotational speed (e.g. rpm),
* is the pressure or head developed by the fan/pump (e.g. ft or m), and
* is the shaft power (e.g. W).
Regards
Nidal Abdalla