[TRNSYS-users] Shading & solar radiation
David BRADLEY
d.bradley at tess-inc.com
Mon Jun 18 08:29:03 PDT 2012
Sascha,
The equation is simply comparing two values; it doesn't know about
the units. So if Radiation_Input (the output from your weather data
reader probably - Type99?) is in W/m2 then X also needs to be in W/m2.
It is more likely that Radiation_Input is in kJ/h.m2 though, in which
case X also needs to be in kJ/h.m2.
Best,
David
On 6/15/2012 05:04, Heinze wrote:
>
> Hello again,
>
> i have another question about external shading and the radiation.
>
> I know that it can be controlled with an equation using the radiation
> as input like: Radiation_Input ? Equation:
> =gt(Radiation_Input, *X*) ? Output linked to type 56 Shading
>
> But with the X in the equation i am not sure. I have a german TRY
> (.dat) weather file and the radiation in this file is already given in
> W/m². Do i still need to convert this to kJ/hr m² ?
>
> Best regards
>
> Sascha Heinze
>
>
>