[TRNSYS-users] weird Qcool

王洋 wanghongyang1767 at gmail.com
Mon Jun 18 06:16:12 PDT 2012


Dear Mr. Adrien,

Many thanks for your quick reply!
Did you put a lower ACH for the simulation already? After that, the cooling
system works fine? I did. I set the ACH from 2.0 to 0.5 1/h, however, Qcool
is still 0, in addition, Tair_room in summer is up to 33/34 °C. It means
the cooling system is still not working after reducing the ACH of
ventilation system.
So I think it is not reason of ventilation system. I guess there is
something wrong with the cooling system in TRNSYS. But I still can't find
the solution.
Please give us some suggestions for that! I don't know why there are so
many bugs or problems in TRNSYS although it has been a mature BES tool.

Many thanks in advance!

Br.
wang
2012/6/18 Adrien JEZEQUEL - ITF <a.jezequel at itf.biz>

>  Hi wang,
>
> i check your ventilation system.
>
>    - Airchange of ventilation : 2.75 Vol/h when your building is used
>    - Temperature : 17 °C in summer
>
> With 2.75 Vol/h at 17°C in your thermal zone, this is normal that Qcool is
> equal to 0 since your air is only refreshed by your ventilation system!
> Your cooling system is not used!
> Try to put a lower airflowrate, you will see that cooling system is then
> used and works fine.
>
> Best regards
>  ------------------------------
>   [image: www.itf.biz] <http://www.itf.biz>
> www.itf.biz Adrien JEZEQUEL
> Simulations Thermiques Dynamiques  *ITF*
>  62, Rue du Bolliet
> 73230 St Alban Leysse
> FRANCE
>   Phone :
> Fax :
> Mail:
>   +33(0) 479 750 029
> +33(0) 479 852 122
> a.jezequel at itf.biz ou aj at itf.biz  *Afin de contribuer au respect de
> l'environnement, merci de n'imprimer cet e-mail que si nécessaire
> Please, consider our environmental responsability before printing this
> email
> *
>
> Le 18/06/2012 12:40, 王洋 a écrit :
>
>
> Dear Mr. Adrien,
>
> Many thanks for your patient and careful answers!
>
> You are right!
> Set point for cooling is 26°C in your model. The problem comes from your
> ventilation system : Temperature of air flow = 17°C in summer. So your
> ventilation system cools your thermal zone.. Your cooling system is then
> shunted since Tair < 26°C, that's why you obtain QCool = 0. i advice you to
> adjust your air flow temperature.
> Due to the lower set temperature of ventilation in summer, the Qcool = 0.
> Since 17 °C is our design standard, so generally it can't be adjusted. In
> addition, I found there is another Weird phenomenon about Qcool and Tcool.
> I adjust Tcool based on your suggestion and Equation (Tcool = 35 - 9 *
> Summer ). I change it into e.g. Tcool = 35 - 8/10/11.../25 * Summer etc.,
> but Tcool doesn't work i.e. Tair_room is keeping the same temperature
> (please see the 1st attached on line plotter) in all the set point Tcool
> situatuins (27/25/24.../10 °C), therefore, Qcool is 0 all the time. I
> checked and adjusted many times for this simulation. It also exists this
> problem. It made me drive the nuts.
>
> If you are free, please help me have a look the program and give me some
> solutions or advices. Pleasae see the 2nd and 3rd attached.
>
> Many thanks in advance! I'm very appreciated for all your help!
>
> Br.
> wang
>
>
> 2012/6/13 ITF - Adrien JEZEQUEL <a.jezequel at itf.biz>
>
>>  My answer just here below in your previous message.
>>
>> best regards
>>   ------------------------------
>>   [image: www.itf.biz] <http://www.itf.biz>
>> www.itf.biz Adrien JEZEQUEL
>> Simulations Thermiques Dynamiques  *ITF*
>>  62, Rue du Bolliet
>> 73230 St Alban Leysse
>> FRANCE
>>   Phone :
>> Fax :
>> Mail:
>>   +33(0) 479 750 029
>> +33(0) 479 852 122 <%2B33%280%29%20479%20852%20122>
>> a.jezequel at itf.biz ou aj at itf.biz  *Afin de contribuer au respect de
>> l'environnement, merci de n'imprimer cet e-mail que si nécessaire
>> Please, consider our environmental responsability before printing this
>> email
>> *
>>
>>  Le 13/06/2012 12:58, 王洋 a écrit :
>>
>> Dear Adrien JEZEQUEL,
>>
>> Many thanks for your patient reply and checking for my programs.
>>
>> You are right. The problem is indeed Internal Gains. I define a Schedule
>> based on your advice. After running, it seems better than the previous.
>> However, there are some unreasonable situations. Please see the Attached
>> image.
>> 1. Tair and Top are higher than the set point 21 °C in winter all the
>> time. Tair is closed to 23 °C basically, and it is only 21 °C when no
>> occupancy. I guess the reason is the compensation of internal gains and
>> mechanical ventilation.
>>
>>  In winter your Tair is equal at least at Tset heat (21°C in your
>> model). Temperatures grow up due to solar and internal heat gains, that's
>> why you obtain Tair > 21°C in winter.
>>
>>  Do you have some solutions to make sure that the set point is 21 °C in
>> winter?
>>
>>  check Tair without internal heat gain and solar gain to be sure that
>> your thermal zone is heated at 21°C.
>>
>>
>> 2.Tair and Top are lower than the set point 26 °C in summer all the time.
>> The maximal is only 25.4 °C. I guess the reason is due to the influence of
>> mechanical ventilation, and only a few hot days (Toutdoor>26 °C) in summer.
>> I would like to ensure that the set point is 26 °C in summer. Do you have
>> some solutions to that problem? Only reduce air change rate of mechanical
>> ventilation? Anything else?
>>
>>  Set point for cooling is 26°C in your model. The problem comes from
>> your ventilation system : Temperature of air flow = 17°C in summer. So your
>> ventilation system cools your thermal zone.. Your cooling system is then
>> shunted since Tair < 26°C, that's why you obtain QCool = 0. i advice you to
>> adjust your air flow temperature.
>>
>>
>> 3.Qinf and Qvent are different all over the year although the
>> infiltration rate and ventilation rate settings are the same all over the
>> year. I think Since the weather conditions especially outdoor temperature,
>> wind direction and wind velocity are different all over the year. Am I
>> right?
>>
>>  Yes, you are right. But it's very difficult to take into account
>> accuracy airflows due to infiltration rate, since this is generaly due in
>> one hand to imperfections and in other hand, as you say, to local situation
>> : you have to estimate wind velocity and direction near your building,
>> then, calculate pressure coefficient on each elements of your facade, and
>> then approach your infiltration rate with a law like m' = C.dp.n. You
>> may find some litteratures from Martin Liddament but in first
>> approximation, I advice you to take a constant value equal to 1/20eme
>> airflowrate obtain under 50Pa which seems to be perfect for energy studies.
>>
>>
>> 4. Based on Energy_zone.BAL file, Qcool is 0 all the time. Do you have
>> some ideas? I think it is due to mechanical ventilation and only a few hot
>> days (Toutdoor>26 °C) in summer. Anything else reasons?
>>
>>  See point 2.
>>
>>
>> Many thanks in advance!
>>
>> Br.
>>
>> wang
>>
>>
>>
>>
>>
>>
>>
>> 2012/6/13 ITF - Adrien JEZEQUEL <a.jezequel at itf.biz>
>>
>>>  Dear Wang,
>>>
>>>
>>> You are right : the Tcool I gave you was equal to 26, not to 24°C. Tset
>>> value is not important as well, the most important is that you understand
>>> how to do to define Tset.
>>> In your model, your heating and cooling advices seem to work fine. Your
>>> problem comes frome your internal gain : 31 people are defined all the time
>>> in a room of approximatively 80 m², without schedule.
>>> Because of your important internal gains, air temperature increases
>>> until 35°C in winter. Then air temperature is refreshed because Tcool =
>>> 35°C in winter.
>>>  In summer, air is cooled at 24°C, because this is the temperature you
>>> define in your cooling advice.
>>>
>>>
>>> Best regards
>>>  ------------------------------
>>>   [image: www.itf.biz] <http://www.itf.biz>
>>> www.itf.biz Adrien JEZEQUEL
>>> Simulations Thermiques Dynamiques  *ITF*
>>>  62, Rue du Bolliet
>>> 73230 St Alban Leysse
>>> FRANCE
>>>   Phone :
>>> Fax :
>>> Mail:
>>>   +33(0) 479 750 029
>>> +33(0) 479 852 122 <%2B33%280%29%20479%20852%20122>
>>> a.jezequel at itf.biz ou aj at itf.biz  *Afin de contribuer au respect de
>>> l'environnement, merci de n'imprimer cet e-mail que si nécessaire
>>> Please, consider our environmental responsability before printing this
>>> email
>>> *
>>>
>>>  Le 12/06/2012 18:19, 王洋 a écrit :
>>>
>>> Dear Adrien Jezequel,
>>>
>>> Thanks for your quick reply!
>>> Tcool = 35 - 9 * Summer means if in summer, Tcool = 26 °C?
>>>
>>> I tried to run the simulation based on your solution Tcool = 35 - 9 *
>>> Summer, the result is also like the last Attached.
>>> Oppositely, it is not my heating system seems to work all the time, it
>>> is my cooling system seems to work all the time.
>>> I set internal gains all the year.
>>>
>>> Please see the Attached *.tpf and *.bui files, if you have free time ,
>>> please help me have a look and give me some solutions.
>>>
>>> Many thanks in advance!
>>>
>>> Br.
>>>
>>> wang
>>>
>>>
>>> 2012/6/12 ITF - Adrien JEZEQUEL <a.jezequel at itf.biz>
>>>
>>>>  Or sorry, I made a mistake in my previous mail :
>>>>
>>>>    - Tcool = 35 - 9 * Summer (instead of 35*winter  - 9*summer)
>>>>
>>>> Regarding your heating system it may be something like :
>>>>
>>>>    - Theat = 21*Winter
>>>>
>>>> Regarding your attached picture, your heating system seems to work all
>>>> the time.
>>>> In summer, either you cool at 21°C, either there is no internal gains
>>>> defined, and you heat at 21°C.
>>>> Check your differents inputs.
>>>> You can procede step by step (internal gain = 0, ventilation = 0,
>>>> infiltration rate = 0...) to see the influence of each parameters in your
>>>> model to catch your issue.
>>>>
>>>> Best regards
>>>>   ------------------------------
>>>>   [image: www.itf.biz] <http://www.itf.biz>
>>>> www.itf.biz Adrien JEZEQUEL
>>>> Simulations Thermiques Dynamiques  *ITF*
>>>>  62, Rue du Bolliet
>>>> 73230 St Alban Leysse
>>>> FRANCE
>>>>   Phone :
>>>> Fax :
>>>> Mail:
>>>>   +33(0) 479 750 029 <%2B33%280%29%20479%20750%20029>
>>>> +33(0) 479 852 122 <%2B33%280%29%20479%20852%20122>
>>>> a.jezequel at itf.biz ou aj at itf.biz  *Afin de contribuer au respect de
>>>> l'environnement, merci de n'imprimer cet e-mail que si nécessaire
>>>> Please, consider our environmental responsability before printing this
>>>> email
>>>> *
>>>>
>>>>  Le 12/06/2012 17:47, 王洋 a écrit :
>>>>
>>>> Dear Adrien Jezequel,
>>>>
>>>> Many thanks!
>>>>
>>>> I think you'd better put for cooling temperatures
>>>>
>>>>    - 35°C in winter (no cool) - heating temperature at 21°C
>>>>     - 24°C in summer
>>>>
>>>>  which may be translated in an equation tool by something like :
>>>>
>>>>    - summer = GE(TIME,2162)*LT(TIME,6552)
>>>>    - winter = 1 - summer
>>>>     - Tcool = 35*Winter - 9*Summer
>>>>
>>>> For Tcool = 35*Winter - 9*Summer, do you mean if in winter, Tcool = 35
>>>> °C, so Cooling doesn't work ; if in summer, Tcool = -9°C or 24 °C?
>>>>
>>>> Meanwhile, another weird phenomena appear: After running based on your
>>>> solution in winter, indoor temperature becomes 35 °C also not 21 °C,
>>>> although I set heating temperature as 21 °C; in summer, however, indoor
>>>> temperature becomes 21 °C. Please see the Attached On-Line Plotter image.
>>>> Furthermore, when I create another Tcool equation as
>>>> 35*winter+24*summer, the result is also like the Attached On-Line
>>>> Plotter image.
>>>>
>>>> Please give me some solutions or advices!
>>>> I think the point how to set that Cooling doesn't work in winter? The
>>>> possible reason of that problem is that I also set a Mechanical Ventilation
>>>> in winter (Tset=19 °C) and summer (Tset=17 °C). I guess Maybe the
>>>> Mechanical Ventilation will influence on Cooling and heating?
>>>>
>>>> Many thanks in advance!
>>>>
>>>> Br.
>>>>
>>>> wang
>>>>
>>>>
>>>> 2012/6/12 <trnsys-users-request at cae.wisc.edu>
>>>>
>>>>> Send TRNSYS-users mailing list submissions to
>>>>>        trnsys-users at cae.wisc.edu
>>>>>
>>>>> To subscribe or unsubscribe via the World Wide Web, visit
>>>>>        https://mailman.cae.wisc.edu/listinfo/trnsys-users
>>>>> or, via email, send a message with subject or body 'help' to
>>>>>        trnsys-users-request at cae.wisc.edu
>>>>>
>>>>> You can reach the person managing the list at
>>>>>        trnsys-users-owner at cae.wisc.edu
>>>>>
>>>>> When replying, please edit your Subject line so it is more specific
>>>>> than "Re: Contents of TRNSYS-users digest..."
>>>>>
>>>>> Today's Topics:
>>>>>
>>>>>   1. Re: TRNSYS-users Digest, Vol 90, Issue 23
>>>>>      (jose.gonzalez at imdea.org)
>>>>>   2. Re: weird Qcool (ITF - Adrien JEZEQUEL)
>>>>>   3. Flue gas stack in TRNSYS (Mazen Darwish)
>>>>>   4. AutoReply: TRNSYS-users Digest, Vol 90, Issue 23
>>>>>      (kelelo1 at kelelo.com)
>>>>>
>>>>>
>>>>> ---------- 已转发邮件 ----------
>>>>> From: <jose.gonzalez at imdea.org>
>>>>> To: trnsys-users at cae.wisc.edu
>>>>> Cc:
>>>>> Date: Tue, 12 Jun 2012 14:56:21 +0200 (CEST)
>>>>> Subject: Re: [TRNSYS-users] TRNSYS-users Digest, Vol 90, Issue 23
>>>>> I am out of the office from Monday, June 11 to Friday, June 15 and
>>>>> unable to respond at this time.
>>>>>
>>>>> For any urgent matters, please contact Dr. Manuel Romero (
>>>>> manuel.romero_at_imdea.org).
>>>>>
>>>>> Thank you for your understanding.
>>>>>
>>>>> Best regards,
>>>>>
>>>>> José Gonzalez-Aguilar
>>>>>
>>>>>
>>>>>
>>>>> ---------- 已转发邮件 ----------
>>>>> From: ITF - Adrien JEZEQUEL <a.jezequel at itf.biz>
>>>>> To: trnsys-users at cae.wisc.edu
>>>>> Cc:
>>>>> Date: Tue, 12 Jun 2012 15:26:28 +0200
>>>>> Subject: Re: [TRNSYS-users] weird Qcool
>>>>>  Dear Wang,
>>>>>
>>>>> As far as I understand, the cooling set temperature you define in your
>>>>> model is :
>>>>>
>>>>>    - 24°C in summer, which seems to be correct
>>>>>    - and 0°C in winter... which seems to be wrong, since you don't
>>>>>    refresh your thermal zone at 0°C in winter!
>>>>>
>>>>> That's why you obtain huge cooling loads.
>>>>> BAL_ENERGY is not 0 because you heat and cool in the same time in
>>>>> winter.
>>>>>
>>>>> I think you'd better put for cooling temperatures
>>>>>
>>>>>    - 35°C in winter (no cool) - heating temperature at 21°C
>>>>>     - 24°C in summer
>>>>>
>>>>> which may be translated in an equation tool by something like :
>>>>>
>>>>>    - summer = GE(TIME,2162)*LT(TIME,6552)
>>>>>    - winter = 1 - summer
>>>>>     - Tcool = 35*Winter - 9*Summer
>>>>>
>>>>> Best regards
>>>>>  ------------------------------
>>>>>   [image: www.itf.biz] <http://www.itf.biz>
>>>>> www.itf.biz Adrien JEZEQUEL
>>>>> Simulations Thermiques Dynamiques  *ITF*
>>>>>  62, Rue du Bolliet
>>>>> 73230 St Alban Leysse
>>>>> FRANCE
>>>>>   Phone :
>>>>> Fax :
>>>>> Mail:
>>>>>   +33(0) 479 750 029 <%2B33%280%29%20479%20750%20029>
>>>>> +33(0) 479 852 122 <%2B33%280%29%20479%20852%20122>
>>>>> a.jezequel at itf.biz ou aj at itf.biz  *Afin de contribuer au respect de
>>>>> l'environnement, merci de n'imprimer cet e-mail que si nécessaire
>>>>> Please, consider our environmental responsability before printing this
>>>>> email
>>>>> *
>>>>>
>>>>> Le 12/06/2012 14:55, 王洋 a écrit :
>>>>>
>>>>> Dear all,
>>>>>
>>>>> I make a simulation. The cooling set temperature is 24*Summer schedule
>>>>> (2162 h to 6552 h), The heating set temperature is 21*Winter schedule (the
>>>>> rest hours). After running, however, it appears WEIRD phenomenon. Please
>>>>> see the ATTACHED Energy_zone.BAL file. During the winter period, there are
>>>>> Qcools and Qcool is very large up to 47000 kJ. And then it results in wrong
>>>>> BAL_ENERG, it is not 0.
>>>>>
>>>>> Please give me some advices and solutions to that!
>>>>>
>>>>> Many thanks in advance!
>>>>>
>>>>> Br.
>>>>>
>>>>> wang
>>>>>
>>>>> 2012/6/11 <trnsys-users-request at cae.wisc.edu>
>>>>>
>>>>>> Send TRNSYS-users mailing list submissions to
>>>>>>        trnsys-users at cae.wisc.edu
>>>>>>
>>>>>> To subscribe or unsubscribe via the World Wide Web, visit
>>>>>>        https://mailman.cae.wisc.edu/listinfo/trnsys-users
>>>>>> or, via email, send a message with subject or body 'help' to
>>>>>>        trnsys-users-request at cae.wisc.edu
>>>>>>
>>>>>> You can reach the person managing the list at
>>>>>>        trnsys-users-owner at cae.wisc.edu
>>>>>>
>>>>>> When replying, please edit your Subject line so it is more specific
>>>>>> than "Re: Contents of TRNSYS-users digest..."
>>>>>>
>>>>>> Today's Topics:
>>>>>>
>>>>>>   1. Re: TRNSYS-users Digest, Vol 90, Issue 21
>>>>>>      (jose.gonzalez at imdea.org)
>>>>>>   2. AutoReply: TRNSYS-users Digest, Vol 90, Issue 21
>>>>>>      (kelelo1 at kelelo.com)
>>>>>>   3. type666 (Andr?s Montero)
>>>>>>   4. Type 673 heating problem (Santeri Siren)
>>>>>>
>>>>>>
>>>>>> ---------- 已转发邮件 ----------
>>>>>> From: <jose.gonzalez at imdea.org>
>>>>>> To: trnsys-users at cae.wisc.edu
>>>>>> Cc:
>>>>>> Date: Mon, 11 Jun 2012 16:07:28 +0200 (CEST)
>>>>>> Subject: Re: [TRNSYS-users] TRNSYS-users Digest, Vol 90, Issue 21
>>>>>> I am out of the office from Monday, June 11 to Friday, June 15 and
>>>>>> unable to respond at this time.
>>>>>>
>>>>>> For any urgent matters, please contact Dr. Manuel Romero (
>>>>>> manuel.romero_at_imdea.org).
>>>>>>
>>>>>> Thank you for your understanding.
>>>>>>
>>>>>> Best regards,
>>>>>>
>>>>>> José Gonzalez-Aguilar
>>>>>>
>>>>>>
>>>>>>
>>>>>> ---------- 已转发邮件 ----------
>>>>>> From: kelelo1 at kelelo.com
>>>>>> To: trnsys-users at cae.wisc.edu
>>>>>> Cc:
>>>>>> Date: Mon, 11 Jun 2012 14:10:47 GMT
>>>>>> Subject: [TRNSYS-users] AutoReply: TRNSYS-users Digest, Vol 90, Issue
>>>>>> 21
>>>>>>
>>>>>> I will be out of the office from June 8 - 23 on a backpacking trip
>>>>>> with my son and his Venture Crew at Philmont Scout Ranch in New Mexico. I
>>>>>> will not have access to email or phone service while I am gone, but I will
>>>>>> reply to your message as soon as possible after I return to the office on
>>>>>> Monday, June 25th.
>>>>>>
>>>>>> Thank you for your patience,
>>>>>> Mark Thornbloom
>>>>>>
>>>>>>
>>>>>>
>>>>>>
>>>>>> ---------- 已转发邮件 ----------
>>>>>> From: "Andrés Montero" <andresmonteroi at gmail.com>
>>>>>> To: trnsys-users at cae.wisc.edu
>>>>>> Cc:
>>>>>> Date: Mon, 11 Jun 2012 16:57:30 +0200
>>>>>> Subject: [TRNSYS-users] type666
>>>>>> Dear Trnsys users,
>>>>>>
>>>>>>  In order to simulate a water-cooled chiller, first I need to create
>>>>>> the 2 external files for this component.
>>>>>> I'm trying to find some catalogues with information of a 40 to 45 kW
>>>>>> water-cooled chiller but the web pages I run into it, ask me to register,
>>>>>> but I'm still waiting the username and pasword. Does anyone has a catalgoue
>>>>>> with this type of info regarding this cooling capacity machine?
>>>>>>
>>>>>>  Best regards,
>>>>>>
>>>>>>  Andrés
>>>>>>
>>>>>>  --
>>>>>> Andrés Montero I.
>>>>>>
>>>>>>
>>>>>>
>>>>>> ---------- 已转发邮件 ----------
>>>>>> From: Santeri Siren <santeri.siren1 at gmail.com>
>>>>>> To: "trnsys käyttäjät" <trnsys-users at cae.wisc.edu>
>>>>>> Cc:
>>>>>> Date: Mon, 11 Jun 2012 19:56:40 +0300
>>>>>> Subject: [TRNSYS-users] Type 673 heating problem
>>>>>> Dear all,
>>>>>>
>>>>>> I cant make type673 heating mode to work. Cooling mode works just
>>>>>> fine but when I change the cooling control signal to 0 and heating control
>>>>>> signal to 1 it doesnt work anymore. When the heating mode is used nothing
>>>>>> happens. Does anyone know why?
>>>>>>
>>>>>> Best regards,
>>>>>> Santeri Siren
>>>>>>
>>>>>> _______________________________________________
>>>>>> TRNSYS-users mailing list
>>>>>> TRNSYS-users at cae.wisc.edu
>>>>>> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>>>>>>
>>>>>>
>>>>>
>>>>>
>>>>> _______________________________________________
>>>>> TRNSYS-users mailing listTRNSYS-users at cae.wisc.eduhttps://mailman.cae.wisc.edu/listinfo/trnsys-users
>>>>>
>>>>>
>>>>>
>>>>> ---------- 已转发邮件 ----------
>>>>> From: Mazen Darwish <mazentd at gmail.com>
>>>>> To: trnsys-users at cae.wisc.edu
>>>>> Cc:
>>>>> Date: Tue, 12 Jun 2012 16:05:51 +0200
>>>>> Subject: [TRNSYS-users] Flue gas stack in TRNSYS
>>>>> Hello everyone ,
>>>>>
>>>>> Is there a way to model a flue gas stack in TRNSYS , i need to
>>>>> recirculate hot air and flue gases from the economizer in an HRSG back to a
>>>>> solar tower .
>>>>>
>>>>> i appreciate your ideas.
>>>>>
>>>>> Mazen Darwish
>>>>> KTH Royal Institute of Technology
>>>>> Department of Energy Technology
>>>>> Brinellvägen 68, SE-100 44 Stockholm, Sweden
>>>>> Mobile: +46-(0)-723 08 18 93 <%2B46-%280%29-723%2008%2018%2093>
>>>>>
>>>>>
>>>>> ---------- 已转发邮件 ----------
>>>>> From: kelelo1 at kelelo.com
>>>>> To: trnsys-users at cae.wisc.edu
>>>>> Cc:
>>>>> Date: Tue, 12 Jun 2012 14:23:03 GMT
>>>>> Subject: [TRNSYS-users] AutoReply: TRNSYS-users Digest, Vol 90, Issue
>>>>> 23
>>>>>
>>>>> I will be out of the office from June 8 - 23 on a backpacking trip
>>>>> with my son and his Venture Crew at Philmont Scout Ranch in New Mexico. I
>>>>> will not have access to email or phone service while I am gone, but I will
>>>>> reply to your message as soon as possible after I return to the office on
>>>>> Monday, June 25th.
>>>>>
>>>>> Thank you for your patience,
>>>>> Mark Thornbloom
>>>>>
>>>>>
>>>>>
>>>>> _______________________________________________
>>>>> TRNSYS-users mailing list
>>>>> TRNSYS-users at cae.wisc.edu
>>>>> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>>>>>
>>>>>
>>>>
>>>
>>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120618/0cbcb94e/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: logo_itf_2010.jpg
Type: image/jpeg
Size: 2583 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120618/0cbcb94e/attachment-0008.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Tcool for lower ach.jpg
Type: image/jpeg
Size: 280702 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120618/0cbcb94e/attachment-0009.jpg>


More information about the TRNSYS-users mailing list