[TRNSYS-users] TRNSYS-users Digest, Vol 90, Issue 24
ITF - Adrien JEZEQUEL
a.jezequel at itf.biz
Tue Jun 12 09:00:07 PDT 2012
Or sorry, I made a mistake in my previous mail :
* Tcool = 35 - 9 * Summer (instead of 35*winter - 9*summer)
Regarding your heating system it may be something like :
* Theat = 21*Winter
Regarding your attached picture, your heating system seems to work all
the time.
In summer, either you cool at 21°C, either there is no internal gains
defined, and you heat at 21°C.
Check your differents inputs.
You can procede step by step (internal gain = 0, ventilation = 0,
infiltration rate = 0...) to see the influence of each parameters in
your model to catch your issue.
Best regards
------------------------------------------------------------------------
www.itf.biz <http://www.itf.biz>
www.itf.biz <http://www.itf.biz>
Adrien JEZEQUEL
Simulations Thermiques Dynamiques
*ITF*
62, Rue du Bolliet
73230 St Alban Leysse
FRANCE
Phone :
Fax :
Mail:
+33(0) 479 750 029
+33(0) 479 852 122
a.jezequel at itf.biz ou aj at itf.biz
/Afin de contribuer au respect de l'environnement, merci de n'imprimer
cet e-mail que si nécessaire
Please, consider our environmental responsability before printing this email
/
Le 12/06/2012 17:47, 王洋 a écrit :
> Dear Adrien Jezequel,
>
> Many thanks!
>
> I think you'd better put for cooling temperatures
>
> * 35°C in winter (no cool) - heating temperature at 21°C
> * 24°C in summer
>
> which may be translated in an equation tool by something like :
>
> * summer = GE(TIME,2162)*LT(TIME,6552)
> * winter = 1 - summer
> * Tcool = 35*Winter - 9*Summer
>
> For Tcool = 35*Winter - 9*Summer, do you mean if in winter, Tcool = 35
> °C, so Cooling doesn't work ; if in summer, Tcool = -9°C or 24 °C?
>
> Meanwhile, another weird phenomena appear: After running based on your
> solution in winter, indoor temperature becomes 35 °C also not 21 °C,
> although I set heating temperature as 21 °C; in summer, however,
> indoor temperature becomes 21 °C. Please see the Attached On-Line
> Plotter image.
> Furthermore, when I create another Tcool equation as
> 35*winter+24*summer, the result is also like the Attached On-Line
> Plotter image.
>
> Please give me some solutions or advices!
> I think the point how to set that Cooling doesn't work in winter? The
> possible reason of that problem is that I also set a Mechanical
> Ventilation in winter (Tset=19 °C) and summer (Tset=17 °C). I guess
> Maybe the Mechanical Ventilation will influence on Cooling and heating?
>
> Many thanks in advance!
>
> Br.
>
> wang
>
>
> 2012/6/12 <trnsys-users-request at cae.wisc.edu
> <mailto:trnsys-users-request at cae.wisc.edu>>
>
> Send TRNSYS-users mailing list submissions to
> trnsys-users at cae.wisc.edu <mailto:trnsys-users at cae.wisc.edu>
>
> To subscribe or unsubscribe via the World Wide Web, visit
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
> or, via email, send a message with subject or body 'help' to
> trnsys-users-request at cae.wisc.edu
> <mailto:trnsys-users-request at cae.wisc.edu>
>
> You can reach the person managing the list at
> trnsys-users-owner at cae.wisc.edu
> <mailto:trnsys-users-owner at cae.wisc.edu>
>
> When replying, please edit your Subject line so it is more specific
> than "Re: Contents of TRNSYS-users digest..."
>
> Today's Topics:
>
> 1. Re: TRNSYS-users Digest, Vol 90, Issue 23
> (jose.gonzalez at imdea.org <mailto:jose.gonzalez at imdea.org>)
> 2. Re: weird Qcool (ITF - Adrien JEZEQUEL)
> 3. Flue gas stack in TRNSYS (Mazen Darwish)
> 4. AutoReply: TRNSYS-users Digest, Vol 90, Issue 23
> (kelelo1 at kelelo.com <mailto:kelelo1 at kelelo.com>)
>
>
> ---------- 已转发邮件 ----------
> From: <jose.gonzalez at imdea.org <mailto:jose.gonzalez at imdea.org>>
> To: trnsys-users at cae.wisc.edu <mailto:trnsys-users at cae.wisc.edu>
> Cc:
> Date: Tue, 12 Jun 2012 14:56:21 +0200 (CEST)
> Subject: Re: [TRNSYS-users] TRNSYS-users Digest, Vol 90, Issue 23
> I am out of the office from Monday, June 11 to Friday, June 15 and
> unable to respond at this time.
>
> For any urgent matters, please contact Dr. Manuel Romero
> (manuel.romero_at_imdea.org <http://manuel.romero_at_imdea.org>).
>
> Thank you for your understanding.
>
> Best regards,
>
> José Gonzalez-Aguilar
>
>
>
> ---------- 已转发邮件 ----------
> From: ITF - Adrien JEZEQUEL <a.jezequel at itf.biz
> <mailto:a.jezequel at itf.biz>>
> To: trnsys-users at cae.wisc.edu <mailto:trnsys-users at cae.wisc.edu>
> Cc:
> Date: Tue, 12 Jun 2012 15:26:28 +0200
> Subject: Re: [TRNSYS-users] weird Qcool
> Dear Wang,
>
> As far as I understand, the cooling set temperature you define in
> your model is :
>
> * 24°C in summer, which seems to be correct
> * and 0°C in winter... which seems to be wrong, since you don't
> refresh your thermal zone at 0°C in winter!
>
> That's why you obtain huge cooling loads.
> BAL_ENERGY is not 0 because you heat and cool in the same time in
> winter.
>
> I think you'd better put for cooling temperatures
>
> * 35°C in winter (no cool) - heating temperature at 21°C
> * 24°C in summer
>
> which may be translated in an equation tool by something like :
>
> * summer = GE(TIME,2162)*LT(TIME,6552)
> * winter = 1 - summer
> * Tcool = 35*Winter - 9*Summer
>
> Best regards
>
> ------------------------------------------------------------------------
> www.itf.biz <http://www.itf.biz>
> www.itf.biz <http://www.itf.biz>
>
> Adrien JEZEQUEL
> Simulations Thermiques Dynamiques
> *ITF*
> 62, Rue du Bolliet
> 73230 St Alban Leysse
> FRANCE
> Phone :
> Fax :
> Mail:
> +33(0) 479 750 029
> +33(0) 479 852 122 <tel:%2B33%280%29%20479%20852%20122>
> a.jezequel at itf.biz <mailto:a.jezequel at itf.biz> ou aj at itf.biz
> <mailto:aj at itf.biz>
>
> /Afin de contribuer au respect de l'environnement, merci de
> n'imprimer cet e-mail que si nécessaire
> Please, consider our environmental responsability before printing
> this email
> /
>
> Le 12/06/2012 14:55, 王洋 a écrit :
>> Dear all,
>>
>> I make a simulation. The cooling set temperature is 24*Summer
>> schedule (2162 h to 6552 h), The heating set temperature is
>> 21*Winter schedule (the rest hours). After running, however, it
>> appears WEIRD phenomenon. Please see the ATTACHED Energy_zone.BAL
>> file. During the winter period, there are Qcools and Qcool is
>> very large up to 47000 kJ. And then it results in wrong
>> BAL_ENERG, it is not 0.
>>
>> Please give me some advices and solutions to that!
>>
>> Many thanks in advance!
>>
>> Br.
>>
>> wang
>>
>> 2012/6/11 <trnsys-users-request at cae.wisc.edu
>> <mailto:trnsys-users-request at cae.wisc.edu>>
>>
>> Send TRNSYS-users mailing list submissions to
>> trnsys-users at cae.wisc.edu <mailto:trnsys-users at cae.wisc.edu>
>>
>> To subscribe or unsubscribe via the World Wide Web, visit
>> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>> or, via email, send a message with subject or body 'help' to
>> trnsys-users-request at cae.wisc.edu
>> <mailto:trnsys-users-request at cae.wisc.edu>
>>
>> You can reach the person managing the list at
>> trnsys-users-owner at cae.wisc.edu
>> <mailto:trnsys-users-owner at cae.wisc.edu>
>>
>> When replying, please edit your Subject line so it is more
>> specific
>> than "Re: Contents of TRNSYS-users digest..."
>>
>> Today's Topics:
>>
>> 1. Re: TRNSYS-users Digest, Vol 90, Issue 21
>> (jose.gonzalez at imdea.org <mailto:jose.gonzalez at imdea.org>)
>> 2. AutoReply: TRNSYS-users Digest, Vol 90, Issue 21
>> (kelelo1 at kelelo.com <mailto:kelelo1 at kelelo.com>)
>> 3. type666 (Andr?s Montero)
>> 4. Type 673 heating problem (Santeri Siren)
>>
>>
>> ---------- 已转发邮件 ----------
>> From: <jose.gonzalez at imdea.org <mailto:jose.gonzalez at imdea.org>>
>> To: trnsys-users at cae.wisc.edu <mailto:trnsys-users at cae.wisc.edu>
>> Cc:
>> Date: Mon, 11 Jun 2012 16:07:28 +0200 (CEST)
>> Subject: Re: [TRNSYS-users] TRNSYS-users Digest, Vol 90, Issue 21
>> I am out of the office from Monday, June 11 to Friday, June
>> 15 and unable to respond at this time.
>>
>> For any urgent matters, please contact Dr. Manuel Romero
>> (manuel.romero_at_imdea.org <http://manuel.romero_at_imdea.org>).
>>
>> Thank you for your understanding.
>>
>> Best regards,
>>
>> José Gonzalez-Aguilar
>>
>>
>>
>> ---------- 已转发邮件 ----------
>> From: kelelo1 at kelelo.com <mailto:kelelo1 at kelelo.com>
>> To: trnsys-users at cae.wisc.edu <mailto:trnsys-users at cae.wisc.edu>
>> Cc:
>> Date: Mon, 11 Jun 2012 14:10:47 GMT
>> Subject: [TRNSYS-users] AutoReply: TRNSYS-users Digest, Vol
>> 90, Issue 21
>>
>> I will be out of the office from June 8 - 23 on a backpacking
>> trip with my son and his Venture Crew at Philmont Scout Ranch
>> in New Mexico. I will not have access to email or phone
>> service while I am gone, but I will reply to your message as
>> soon as possible after I return to the office on Monday, June
>> 25th.
>>
>> Thank you for your patience,
>> Mark Thornbloom
>>
>>
>>
>>
>> ---------- 已转发邮件 ----------
>> From: "Andrés Montero" <andresmonteroi at gmail.com
>> <mailto:andresmonteroi at gmail.com>>
>> To: trnsys-users at cae.wisc.edu <mailto:trnsys-users at cae.wisc.edu>
>> Cc:
>> Date: Mon, 11 Jun 2012 16:57:30 +0200
>> Subject: [TRNSYS-users] type666
>> Dear Trnsys users,
>>
>> In order to simulate a water-cooled chiller, first I need to
>> create the 2 external files for this component.
>> I'm trying to find some catalogues with information of a 40
>> to 45 kW water-cooled chiller but the web pages I run into
>> it, ask me to register, but I'm still waiting the username
>> and pasword. Does anyone has a catalgoue with this type of
>> info regarding this cooling capacity machine?
>>
>> Best regards,
>>
>> Andrés
>>
>> --
>> Andrés Montero I.
>>
>>
>>
>> ---------- 已转发邮件 ----------
>> From: Santeri Siren <santeri.siren1 at gmail.com
>> <mailto:santeri.siren1 at gmail.com>>
>> To: "trnsys käyttäjät" <trnsys-users at cae.wisc.edu
>> <mailto:trnsys-users at cae.wisc.edu>>
>> Cc:
>> Date: Mon, 11 Jun 2012 19:56:40 +0300
>> Subject: [TRNSYS-users] Type 673 heating problem
>> Dear all,
>>
>> I cant make type673 heating mode to work. Cooling mode works
>> just fine but when I change the cooling control signal to 0
>> and heating control signal to 1 it doesnt work anymore. When
>> the heating mode is used nothing happens. Does anyone know why?
>>
>> Best regards,
>> Santeri Siren
>>
>> _______________________________________________
>> TRNSYS-users mailing list
>> TRNSYS-users at cae.wisc.edu <mailto:TRNSYS-users at cae.wisc.edu>
>> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>>
>>
>>
>>
>> _______________________________________________
>> TRNSYS-users mailing list
>> TRNSYS-users at cae.wisc.edu <mailto:TRNSYS-users at cae.wisc.edu>
>> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>
>
> ---------- 已转发邮件 ----------
> From: Mazen Darwish <mazentd at gmail.com <mailto:mazentd at gmail.com>>
> To: trnsys-users at cae.wisc.edu <mailto:trnsys-users at cae.wisc.edu>
> Cc:
> Date: Tue, 12 Jun 2012 16:05:51 +0200
> Subject: [TRNSYS-users] Flue gas stack in TRNSYS
> Hello everyone ,
> Is there a way to model a flue gas stack in TRNSYS , i need to
> recirculate hot air and flue gases from the economizer in an HRSG
> back to a solar tower .
> i appreciate your ideas.
> Mazen Darwish
> KTH Royal Institute of Technology
> Department of Energy Technology
> Brinellvägen 68, SE-100 44 Stockholm, Sweden
> Mobile: +46-(0)-723 08 18 93 <tel:%2B46-%280%29-723%2008%2018%2093>
>
>
> ---------- 已转发邮件 ----------
> From: kelelo1 at kelelo.com <mailto:kelelo1 at kelelo.com>
> To: trnsys-users at cae.wisc.edu <mailto:trnsys-users at cae.wisc.edu>
> Cc:
> Date: Tue, 12 Jun 2012 14:23:03 GMT
> Subject: [TRNSYS-users] AutoReply: TRNSYS-users Digest, Vol 90,
> Issue 23
>
> I will be out of the office from June 8 - 23 on a backpacking trip
> with my son and his Venture Crew at Philmont Scout Ranch in New
> Mexico. I will not have access to email or phone service while I
> am gone, but I will reply to your message as soon as possible
> after I return to the office on Monday, June 25th.
>
> Thank you for your patience,
> Mark Thornbloom
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu <mailto:TRNSYS-users at cae.wisc.edu>
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120612/e7ee978b/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: logo_itf_2010.jpg
Type: image/jpeg
Size: 2583 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120612/e7ee978b/attachment-0005.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2583 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120612/e7ee978b/attachment-0003.jpe>
More information about the TRNSYS-users
mailing list