[TRNSYS-users] Number of instance of Type 56 in a project and macros in dck files
David BRADLEY
d.bradley at tess-inc.com
Fri Jun 8 13:52:40 PDT 2012
Marcello,
1. It is not possible to have more than one instance of Type56 in your
project. However, if you define two zones in Type56 that have no
ADJACENT walls between then then in effect you have modeled two
buildings. This can be extended so that if you have two groups of zones
that have internal ADJACENT walls but no walls shared between the two
groups, you have in effect modeled two multizone buildings.
2. Macro information is not saved at the *.dck level, only in the Studio
rendition of the project (the *.tpf). Connection line path information
and line properties (color, style, etc.) are also not saved in the
*.dck. These are both features that the developers have considered
adding but at the moment, I am not aware of any concrete plans to do so.
Kind regards,
david
On 6/8/2012 04:37, marcello.caciolo at aximaseitha-gdfsuez.com wrote:
>
> Dear TRNSYS users,
>
> I have two questions about Type 56 and Studio :
>
> 1) When trying to add a type 56 to a project which already contains
> one, the message "The maximum number of instances(1) allowed for type
> 56 is already reached!". I would like to know if there is a way to
> change the maximum number of instances of type 56 or not, and in the
> latter case which is the reason. (Element of context: Having more than
> one type 56 in a project would be very useful for us when dealing
> with complex buildings with many different zones without adjacencies.
> In this case, the input and output list of type 56 can become very
> long and not easy to manage when connecting type 56 to other types.)
>
> 2) We are planning to make a wizard to create automatically dck files.
> We observed that dck files can contain some graphical information for
> Simulation Studio, as:
>
> *$UNIT_NAME xxx
>
> *$LAYER xxx
>
> *$POSITION xpos ypos
>
> However, in order to create dck files readly usable in Simulation
> Studio, we would like to specify macros. Does some special statement
> like these ones exist in order to specify macros? If not, has someone
> any experience or tips in creating wizards to create input files
> (maybe directly tpf files?) for Simulation Studio?
>
> Thank you for your answers.
>
> Best regards,
>
> *Marcello CACIOLO*
> Responsable Outils et Méthodes d'Analyse Energétique
> ___________________________________________________
>
> logo AximaSeitha
> *
> **Cellule Efficacité Energétique***
>
> Direction Commerciale*
> *46 Boulevard de la Prairie au Duc BP 40119
> 44000 Nantes Cédex 2
> Tel. 02 40 41 06 57
>
>
> mail: marcello.caciolo at aximaseitha-gdfsuez.com
>
> _
> _www.aximaseitha-gdfsuez.com
>
> P*Pensez à l'environnement avant d'imprimer ce message*
>
>
> GDF SUEZ Mail Disclaimer:
> http://www.gdfsuez.com/disclaimer/disclaimer-fr.html
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120608/9b92b938/attachment-0005.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 3512 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120608/9b92b938/attachment-0003.jpe>
More information about the TRNSYS-users
mailing list