Dear Wang,
As far as I understand, the cooling set temperature you define in your 
model is :
  * 24°C in summer, which seems to be correct
  * and 0°C in winter... which seems to be wrong, since you don't
    refresh your thermal zone at 0°C in winter!
That's why you obtain huge cooling loads.
BAL_ENERGY is not 0 because you heat and cool in the same time in winter.
I think you'd better put for cooling temperatures
  * 35°C in winter (no cool) - heating temperature at 21°C
  * 24°C in summer
which may be translated in an equation tool by something like :
  * summer = GE(TIME,2162)*LT(TIME,6552)
  * winter = 1 - summer
  * Tcool = 35*Winter - 9*Summer
Best regards
------------------------------------------------------------------------
www.itf.biz <http://www.itf.biz>
www.itf.biz <http://www.itf.biz>
	Adrien JEZEQUEL
Simulations Thermiques Dynamiques
*ITF*
	62, Rue du Bolliet
73230 St Alban Leysse
FRANCE
Phone :
Fax :
Mail:
	+33(0) 479 750 029
+33(0) 479 852 122
a.jezequel at itf.biz ou aj at itf.biz
/Afin de contribuer au respect de l'environnement, merci de n'imprimer 
cet e-mail que si nécessaire
Please, consider our environmental responsability before printing this email
/
Le 12/06/2012 14:55, ?? a écrit :
> Dear all,
>
> I make a simulation. The cooling set temperature is 24*Summer schedule 
> (2162 h to 6552 h), The heating set temperature is 21*Winter schedule 
> (the rest hours). After running, however, it appears WEIRD phenomenon. 
> Please see the ATTACHED Energy_zone.BAL file. During the winter 
> period, there are Qcools and Qcool is very large up to 47000 kJ. And 
> then it results in wrong BAL_ENERG, it is not 0.
>
> Please give me some advices and solutions to that!
>
> Many thanks in advance!
>
> Br.
>
> wang
>
> 2012/6/11 <trnsys-users-request at cae.wisc.edu 
> <mailto:trnsys-users-request at cae.wisc.edu>>
>
>     Send TRNSYS-users mailing list submissions to
>     trnsys-users at cae.wisc.edu <mailto:trnsys-users at cae.wisc.edu>
>
>     To subscribe or unsubscribe via the World Wide Web, visit
>     https://mailman.cae.wisc.edu/listinfo/trnsys-users
>     or, via email, send a message with subject or body 'help' to
>     trnsys-users-request at cae.wisc.edu
>     <mailto:trnsys-users-request at cae.wisc.edu>
>
>     You can reach the person managing the list at
>     trnsys-users-owner at cae.wisc.edu
>     <mailto:trnsys-users-owner at cae.wisc.edu>
>
>     When replying, please edit your Subject line so it is more specific
>     than "Re: Contents of TRNSYS-users digest..."
>
>     Today's Topics:
>
>       1. Re: TRNSYS-users Digest, Vol 90, Issue 21
>          (jose.gonzalez at imdea.org <mailto:jose.gonzalez at imdea.org>)
>       2. AutoReply: TRNSYS-users Digest, Vol 90, Issue 21
>          (kelelo1 at kelelo.com <mailto:kelelo1 at kelelo.com>)
>       3. type666 (Andr?s Montero)
>       4. Type 673 heating problem (Santeri Siren)
>
>
>     ---------- ????? ----------
>     From: <jose.gonzalez at imdea.org <mailto:jose.gonzalez at imdea.org>>
>     To: trnsys-users at cae.wisc.edu <mailto:trnsys-users at cae.wisc.edu>
>     Cc:
>     Date: Mon, 11 Jun 2012 16:07:28 +0200 (CEST)
>     Subject: Re: [TRNSYS-users] TRNSYS-users Digest, Vol 90, Issue 21
>     I am out of the office from Monday, June 11 to Friday, June 15 and
>     unable to respond at this time.
>
>     For any urgent matters, please contact Dr. Manuel Romero
>     (manuel.romero_at_imdea.org <http://manuel.romero_at_imdea.org>).
>
>     Thank you for your understanding.
>
>     Best regards,
>
>     José Gonzalez-Aguilar
>
>
>
>     ---------- ????? ----------
>     From: kelelo1 at kelelo.com <mailto:kelelo1 at kelelo.com>
>     To: trnsys-users at cae.wisc.edu <mailto:trnsys-users at cae.wisc.edu>
>     Cc:
>     Date: Mon, 11 Jun 2012 14:10:47 GMT
>     Subject: [TRNSYS-users] AutoReply: TRNSYS-users Digest, Vol 90,
>     Issue 21
>
>     I will be out of the office from June 8 - 23 on a backpacking trip
>     with my son and his Venture Crew at Philmont Scout Ranch in New
>     Mexico. I will not have access to email or phone service while I
>     am gone, but I will reply to your message as soon as possible
>     after I return to the office on Monday, June 25th.
>
>     Thank you for your patience,
>     Mark Thornbloom
>
>
>
>
>     ---------- ????? ----------
>     From: "Andrés Montero" <andresmonteroi at gmail.com
>     <mailto:andresmonteroi at gmail.com>>
>     To: trnsys-users at cae.wisc.edu <mailto:trnsys-users at cae.wisc.edu>
>     Cc:
>     Date: Mon, 11 Jun 2012 16:57:30 +0200
>     Subject: [TRNSYS-users] type666
>     Dear Trnsys users,
>
>     In order to simulate a water-cooled chiller, first I need to
>     create the 2 external files for this component.
>     I'm trying to find some catalogues with information of a 40 to 45
>     kW water-cooled chiller but the web pages I run into it, ask me to
>     register, but I'm still waiting the username and pasword. Does
>     anyone has a catalgoue with this type of info regarding this
>     cooling capacity machine?
>
>     Best regards,
>
>     Andrés
>
>     -- 
>     Andrés Montero I.
>
>
>
>     ---------- ????? ----------
>     From: Santeri Siren <santeri.siren1 at gmail.com
>     <mailto:santeri.siren1 at gmail.com>>
>     To: "trnsys käyttäjät" <trnsys-users at cae.wisc.edu
>     <mailto:trnsys-users at cae.wisc.edu>>
>     Cc:
>     Date: Mon, 11 Jun 2012 19:56:40 +0300
>     Subject: [TRNSYS-users] Type 673 heating problem
>     Dear all,
>
>     I cant make type673 heating mode to work. Cooling mode works just
>     fine but when I change the cooling control signal to 0 and heating
>     control signal to 1 it doesnt work anymore. When the heating mode
>     is used nothing happens. Does anyone know why?
>
>     Best regards,
>     Santeri Siren
>
>     _______________________________________________
>     TRNSYS-users mailing list
>     TRNSYS-users at cae.wisc.edu <mailto:TRNSYS-users at cae.wisc.edu>
>     https://mailman.cae.wisc.edu/listinfo/trnsys-users
>
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120612/40339ee3/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: logo_itf_2010.jpg
Type: image/jpeg
Size: 2583 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120612/40339ee3/attachment-0001.jpg>
    
    
More information about the TRNSYS-users
mailing list