[TRNSYS-users] Infiltration clarification
jeannieboef
jeannieboef at gmail.com
Sat Jul 28 13:48:24 PDT 2012
The 50 Pa rating is based on the blower door pressure test. Actual
pressure differences under normal conditions tend to avarage at about
1-2 Pa. Maybe you can find a CEN norm that defines a good pressure dP
to assume for annual energy simulations. Or check the mathematical
referance for the other infiltration types, because they often also
reference standards and norms. If I find anything, I'll post it.
Sent from my iPhone
On 28.07.2012, at 18:34, Marcus <jones.0bj3 at gmail.com> wrote:
> Say I want to simulate a passive house in TRNSYS using type 56. For
> an airtight building shell, passive house infiltration should be say
> ≤ 0.6 ACH @ 50 pascal pressure.
> (http://www.passivehouse.us/passiveHouse/PassiveHouseInfo.html)
>
> The type 56 TRNBLD units for infiltration; are they at static or at
> 50 pa? If they are at static, I need to divide 0.6 by ~ 20 (estimate
> from Sherman 1987), so I input Airchange = 0.03 1/hr. Correct?
>
> Cheers,
>
> Marcus
> --
> Marcus Jones, M.Sc., LEED®AP BD+C
> Freelance energy consultant
> Vienna, Austria
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120728/02e0beb9/attachment-0005.htm>
More information about the TRNSYS-users
mailing list