[TRNSYS-users] Water inlet according to temperature
    David BRADLEY 
    d.bradley at tess-inc.com
       
    Thu Jul 12 08:37:11 PDT 2012
    
    
  
Marko,
   Your tank needs to have two inlet/outlet port pairs on the solar loop 
side (and probably at least one on the load side as well). It is easiest 
to do this with Type534 from the TESS Storage Library. One of your solar 
loop port pairs will come in to node 1 and out of node 5 (assuming that 
you have a 5 node tank). The other will come into node 3 and out of node 
5. You can use a Type11 controlled flow diverter and either an equation 
or a controller Type to watch your collector outlet temperature, then 
send the water to the correct inlet port. You'll need to have a flow 
mixer from your two outlet ports in node 5 even though they both come 
out of the same node because only one of the two will have flow 
(depending on which inlet is being used).
Kind regards,
  David
On 7/12/2012 08:01, Heikkilä Marko wrote:
> Dear TRNSYS users and developers,
>
> I would like to control the water inlet of the storage tank according to supply water temperature from the solar collector. Let`s think that there are two inlets for the water located at the top of of tank and in the middle of tank. When the supply water temperature rises above 60 C, the water flows to the top of the tank. While the water temperature is below 60 C, water flows to the middle of the tank. Can someone give me an advice how to build the control system and which types would be suitable for the purpose?
>
> Thanks in advance!
>
> Marko Heikkilä
> Aalto university
> School of Engineering
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
>
-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
    
    
More information about the TRNSYS-users
mailing list